  #1   Report Post  
William Deans
 
Posts: n/a
Default NEC Clarification Needed

Greetings,

The NEC states that you cannot put metalic boxes onto masonry which may be
damp without a 1/4" airspace. Does this mean that you cannot use metal
boxes / emt on masonry basement walls? What about metal boxes / emt on
masonry basement walls of a row home between the homes?

Thank you for your time and energy,
William


  #2   Report Post  
 
Posts: n/a
Default

i am not an electrician but one code reference i found said that the
airspace (6 mm) applies to surfaces that might be wet a lot, or washed
down, such as would be found in dairies, commercial laundries, etc.

i've commonly seen metal boxes screwed directly into concrete block
basement walls, using pipe/conduit to carry the romex from above down
to the box.

don't know what a 'row home between the homes' is.

William Deans wrote:
Greetings,

The NEC states that you cannot put metalic boxes onto masonry which

may be
damp without a 1/4" airspace. Does this mean that you cannot use

metal
boxes / emt on masonry basement walls? What about metal boxes / emt

on
masonry basement walls of a row home between the homes?

Thank you for your time and energy,
William


  #3   Report Post  
William Deans
 
Posts: n/a
Default

Thank you for your response Roger.

Normally a basement wall is in direct contact with the earth. I have heard
that masonry in direct contact with earth should be considered damp even if
it isn't actually damp? Is this a requirement of the NEC?

In a row-home two of the four basement walls are in contact with the earth.
The other two basement walls have another basement on the other side.
(unless of course it is an end of row, in which case three of the walls are
in direct contact with earth.) If you are not allowed to have emt run along
masonry in contact with the earth one might reason that the walls between
the row homes are not in contact with earth and therefore it is acceptable.
One might also reason that it is unacceptable because it relies upon aspects
of an adjoining structure. Running Romex within EMT for supplemental
protection as you mention probably has different rules than using a conduit
system.

You have commonly seen metal boxes screwed directly into concrete block
basement walls [ without an airspace? ] Did the boxes have "supplemental
corrosion protection?" Unless masonry in contact with earth is NOT always
considered moist as I have been told I do not see how this could be code
compliant? Please help me to understand. Is it a violation of the NEC proper
but inspectors simply choose to allow it?

Thanks again,
William

wrote in message
oups.com...
i am not an electrician but one code reference i found said that the
airspace (6 mm) applies to surfaces that might be wet a lot, or washed
down, such as would be found in dairies, commercial laundries, etc.

i've commonly seen metal boxes screwed directly into concrete block
basement walls, using pipe/conduit to carry the romex from above down
to the box.

don't know what a 'row home between the homes' is.

William Deans wrote:
Greetings,

The NEC states that you cannot put metalic boxes onto masonry which

may be
damp without a 1/4" airspace. Does this mean that you cannot use

metal
boxes / emt on masonry basement walls? What about metal boxes / emt

on
masonry basement walls of a row home between the homes?

Thank you for your time and energy,
William




  #4   Report Post  
Ron
 
Posts: n/a
Default

The 1/4" air gap for damp installations comes from Article 312.2(A). This
article applies to cabinets, cutout boxes (disconnects), meter socket
enclosures. The article is also refer to by other sections such as
overcurrent protective devices, panelboards, etc.
There is no similar requirement for boxes (junction or device) or raceway
(conduit) to follow 312.2(A). The equipment must be placed or equipped to
prevent moisture from entering or accumulating within the box or fitting.
See 314.15(A) in the 2002 NEC at the library.



"William Deans" wrote in message
news:1114904211.2f18791c8024dea92296a217f938eb09@t eranews...
Greetings,

The NEC states that you cannot put metalic boxes onto masonry which may be
damp without a 1/4" airspace. Does this mean that you cannot use metal
boxes / emt on masonry basement walls? What about metal boxes / emt on
masonry basement walls of a row home between the homes?

Thank you for your time and energy,
William




  #5   Report Post  
The Real Tom
 
Posts: n/a
Default

On Sat, 30 Apr 2005 19:36:39 -0400, "William Deans"
wrote:

Greetings,

The NEC states that you cannot put metalic boxes onto masonry which may be
damp without a 1/4" airspace. Does this mean that you cannot use metal


For my education, where in masonry (damp) are you rquired to have the
1/4" air space. Please reply with article and section and NEC
version.

Thank you very much for this.

boxes / emt on masonry basement walls? What about metal boxes / emt on


I've 'electrified' my unfinished basement with emt and it was all done
with a real inspection also. All surface mounted though, if that
makes a difference in your point.

masonry basement walls of a row home between the homes?

Thank you for your time and energy,
William


Thank you,


tom


  #6   Report Post  
The Real Tom
 
Posts: n/a
Default

On Sun, 1 May 2005 11:32:45 -0400, "Ron" wrote:

The 1/4" air gap for damp installations comes from Article 312.2(A). This
article applies to cabinets, cutout boxes (disconnects), meter socket
enclosures. The article is also refer to by other sections such as
overcurrent protective devices, panelboards, etc.
There is no similar requirement for boxes (junction or device) or raceway
(conduit) to follow 312.2(A). The equipment must be placed or equipped to
prevent moisture from entering or accumulating within the box or fitting.
See 314.15(A) in the 2002 NEC at the library.


Ah good stuff. I was confused where 'device boxes' were in this
requriment, and you cleared it up, it isn't.


Just my 2 cents:
As for basements, only 'some basements' need to be treated as damp
locations (ART 100), not all have to be treated as damp locations.

thx,

tom @ www.WorkAtHomePlans.com








"William Deans" wrote in message
news:1114904211.2f18791c8024dea92296a217f938eb09@ teranews...
Greetings,

The NEC states that you cannot put metalic boxes onto masonry which may be
damp without a 1/4" airspace. Does this mean that you cannot use metal
boxes / emt on masonry basement walls? What about metal boxes / emt on
masonry basement walls of a row home between the homes?

Thank you for your time and energy,
William




  #7   Report Post  
Goedjn
 
Posts: n/a
Default




Just my 2 cents:
As for basements, only 'some basements' need to be treated as damp
locations (ART 100), not all have to be treated as damp locations.


On the other hand, it's not all that freaking hard to mount
your panel on standoffs, so why not just do it?

  #8   Report Post  
The Real Tom
 
Posts: n/a
Default

On Mon, 02 May 2005 12:10:57 -0400, Goedjn wrote:




Just my 2 cents:
As for basements, only 'some basements' need to be treated as damp
locations (ART 100), not all have to be treated as damp locations.


On the other hand, it's not all that freaking hard to mount
your panel on standoffs, so why not just do it?



I think the original question was about 'boxes'

tom
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Alternating Current Clarification needed Patrick Home Ownership 12 March 29th 05 02:38 PM
VIEWSONIC G810 schematic needed David Electronics Repair 1 June 25th 04 11:11 PM
AC Advice Needed! unix-freak Home Ownership 27 June 14th 04 03:53 PM
help needed with broken crt neck pcb Asimov Electronics Repair 0 March 25th 04 05:43 PM
No fee needed for extra principal payments Ablang Home Ownership 0 November 18th 03 02:08 AM


All times are GMT +1. The time now is 03:37 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"