Home |
Search |
Today's Posts |
#1
|
|||
|
|||
House Foundation Type Differences
What are the differences between:
1. Post Tension type, and 2. Pier and Grade Beam type. I saw this in the builder's documents. Same builder but two different cities in the same locale (Bay Area, California). What're the implications on the soil type (e.g. would one be used in more solid soil type, etc)? Thanks, Raymond |
#2
|
|||
|
|||
On 19 Jan 2005 08:02:44 -0800, someone wrote:
What are the differences between: 1. Post Tension type, and 2. Pier and Grade Beam type. Well, many kinds of concrete structures can be post tensioned as well as pre tensioned, but apparently you are talking about a slab on grade. Piers and grade beams sounds like a perimeter foundation. Piers are hard points like footing with a short post on it. A grade beam is a beam that runs along the soil (the grade) rather than spans in the air (a "regular" beam if you will). A grade beam or a pier could, BTW, be post tensioned.... The "documents" in construction include the drawings, but apparently you are using the term in the more common meaning to refer to only written word material? Really need the "plans" (actually, only SOME "drawings" are actually "plans", the rest are sections, elevations, details, etc.) to know what exactly is being referred to. The design of the house as well as the soil conditions would influence what was more appropriate. Reply to NG only - this e.mail address goes to a kill file. |
#3
|
|||
|
|||
It's more a question of economics and the engineer's discretion as to which
is used - both can be equally good or bad. In residential applications, post-tensioned is usually cheaper right now b/c less steel is used, but it is critical that the tendons are adequately and properly tensioned. I've looked at a lot of homes where the tendons were understressed or not stressed at all. If going P-T I would hire a testing lab to observe the stressing of the tendons. In either case have an engineer perfrom a pre-pour inspection FOR YOU, not for the builder. It's amazing what the builder's guy will pass. Jeff wrote in message ups.com... What are the differences between: 1. Post Tension type, and 2. Pier and Grade Beam type. I saw this in the builder's documents. Same builder but two different cities in the same locale (Bay Area, California). What're the implications on the soil type (e.g. would one be used in more solid soil type, etc)? Thanks, Raymond |
#4
|
|||
|
|||
Pier and Grade beam are pretty well explained by someone.
Down here common practice is to use grade beams. Piers are only used in situations where you require a heck of a lot more strength than is present at excavation depths or in situations where you definently need to put your foundation on a layer of rock (for example in docks, large buildings or houses on sandy soils vulnerable to liquefaction). Piers tend to be more expensive than the grade beam, since they require more work to design, more supervision in the field, and more specialized equipment to build. Post tensioned is probably that: some kind of grade beam with post tensioned foundation. Might be that the technology is specific to one company, but the builder doesn't wanna say "ABC Inc.'s post tensioned foundation technology" in his document. |
#5
|
|||
|
|||
"Mario" wrote in message
ups.com... Pier and Grade beam are pretty well explained by someone. Down here common practice is to use grade beams. Piers are only used in situations where you require a heck of a lot more strength than is present at excavation depths or in situations where you definently need to put your foundation on a layer of rock (for example in docks, large buildings or houses on sandy soils vulnerable to liquefaction). One exception I ran into is my home that is currently almost finished in TX hill country. The builder would only allow a home I picked out to be built on piers or pilings, no exceptions, no matter the grade or the soil type makeup. The grade is slightly downslope at 3 degrees with a two foot dropoff at the front of the house. The soil is approximately 2 inches to nothing at the dropoff. Beneath is a one to two foot layer of caliche and its corresponding rock type. Beneath that is fractured rock and in some cases solid rock near the dropoff. None of which was going any place. I decreased the dropoff later by moving the soil from the septic tank excavation to the front of the house. Then backgraded to a more desirable slope to the front of the house. Piers tend to be more expensive than the grade beam, since they require more work to design, more supervision in the field, and more specialized equipment to build. The builder hired out a drilling machine normally seen for the installation of utility poles. They used a 24 inch auger bit. The average footing for the piers was around 4 feet in depth. The workers used 1X12s for the forms for the actual piers. The footings were tied to the piers with rebar during the pours. They also used rebar in the piers and footing themselves. They used a transit twice to verify the location and height of each pier before pouring. A strip of flashing type metal was inserted to the top of the pier during the pour and was exposed around 10 inches. This was used to tie the pier to the sill. A wider piece of flashing was placed flat on top of each pier where the sill actully rode on the pier. Post tensioned is probably that: some kind of grade beam with post tensioned foundation. Might be that the technology is specific to one company, but the builder doesn't wanna say "ABC Inc.'s post tensioned foundation technology" in his document. |
#6
|
|||
|
|||
Strange way to build a foundation - I've never seen one like that in the
Hill Country, although nothing surprises me any more. You should be OK, unless you're on the Buda Cap formation (thin veneer of calich/limestone underlain by highly expansive clay, almost always misdiagnosed as nonplastic until all the cracks show up in the home a year later), of which there is a lot around. Where exactly are you building? Jeff "Lil' Dave" wrote in message ink.net... "Mario" wrote in message ups.com... Pier and Grade beam are pretty well explained by someone. Down here common practice is to use grade beams. Piers are only used in situations where you require a heck of a lot more strength than is present at excavation depths or in situations where you definently need to put your foundation on a layer of rock (for example in docks, large buildings or houses on sandy soils vulnerable to liquefaction). One exception I ran into is my home that is currently almost finished in TX hill country. The builder would only allow a home I picked out to be built on piers or pilings, no exceptions, no matter the grade or the soil type makeup. The grade is slightly downslope at 3 degrees with a two foot dropoff at the front of the house. The soil is approximately 2 inches to nothing at the dropoff. Beneath is a one to two foot layer of caliche and its corresponding rock type. Beneath that is fractured rock and in some cases solid rock near the dropoff. None of which was going any place. I decreased the dropoff later by moving the soil from the septic tank excavation to the front of the house. Then backgraded to a more desirable slope to the front of the house. Piers tend to be more expensive than the grade beam, since they require more work to design, more supervision in the field, and more specialized equipment to build. The builder hired out a drilling machine normally seen for the installation of utility poles. They used a 24 inch auger bit. The average footing for the piers was around 4 feet in depth. The workers used 1X12s for the forms for the actual piers. The footings were tied to the piers with rebar during the pours. They also used rebar in the piers and footing themselves. They used a transit twice to verify the location and height of each pier before pouring. A strip of flashing type metal was inserted to the top of the pier during the pour and was exposed around 10 inches. This was used to tie the pier to the sill. A wider piece of flashing was placed flat on top of each pier where the sill actully rode on the pier. Post tensioned is probably that: some kind of grade beam with post tensioned foundation. Might be that the technology is specific to one company, but the builder doesn't wanna say "ABC Inc.'s post tensioned foundation technology" in his document. |
#7
|
|||
|
|||
A few miles northwest of Wimberley. No, I'm not the typical, uppity Houston
businessman retiree, the type that have flooded the area with their money, increased land value beyond any reasonable expectation and their corresponding tax values as well. I know about the soil problems over in the Buda/Kyle area. There is no clay out where I'm at. Forty years ago, this was considered semi-arid, almost desert country. The juniper type cedars came along. They can and do grow in solid rock. They also are choking out the oaks as they soak up vast amounts of ground water, and overcrowd the oaks as well by blocking sunlight. They create better soil conditions by actually creating soil from rock, but at a heavy price to ground water and trees native to the area. They love septic tanks as well. " wrote in message ... Strange way to build a foundation - I've never seen one like that in the Hill Country, although nothing surprises me any more. You should be OK, unless you're on the Buda Cap formation (thin veneer of calich/limestone underlain by highly expansive clay, almost always misdiagnosed as nonplastic until all the cracks show up in the home a year later), of which there is a lot around. Where exactly are you building? Jeff "Lil' Dave" wrote in message ink.net... "Mario" wrote in message ups.com... Pier and Grade beam are pretty well explained by someone. Down here common practice is to use grade beams. Piers are only used in situations where you require a heck of a lot more strength than is present at excavation depths or in situations where you definently need to put your foundation on a layer of rock (for example in docks, large buildings or houses on sandy soils vulnerable to liquefaction). One exception I ran into is my home that is currently almost finished in TX hill country. The builder would only allow a home I picked out to be built on piers or pilings, no exceptions, no matter the grade or the soil type makeup. The grade is slightly downslope at 3 degrees with a two foot dropoff at the front of the house. The soil is approximately 2 inches to nothing at the dropoff. Beneath is a one to two foot layer of caliche and its corresponding rock type. Beneath that is fractured rock and in some cases solid rock near the dropoff. None of which was going any place. I decreased the dropoff later by moving the soil from the septic tank excavation to the front of the house. Then backgraded to a more desirable slope to the front of the house. Piers tend to be more expensive than the grade beam, since they require more work to design, more supervision in the field, and more specialized equipment to build. The builder hired out a drilling machine normally seen for the installation of utility poles. They used a 24 inch auger bit. The average footing for the piers was around 4 feet in depth. The workers used 1X12s for the forms for the actual piers. The footings were tied to the piers with rebar during the pours. They also used rebar in the piers and footing themselves. They used a transit twice to verify the location and height of each pier before pouring. A strip of flashing type metal was inserted to the top of the pier during the pour and was exposed around 10 inches. This was used to tie the pier to the sill. A wider piece of flashing was placed flat on top of each pier where the sill actully rode on the pier. Post tensioned is probably that: some kind of grade beam with post tensioned foundation. Might be that the technology is specific to one company, but the builder doesn't wanna say "ABC Inc.'s post tensioned foundation technology" in his document. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
buying a house with Weyerhaeuser siding | Home Repair | |||
Contacting contractor to buy our house? (Long) | Home Repair | |||
house rebuilt year | Home Ownership | |||
Crack in foundation and home buying decision | Home Ownership | |||
Mayhem! Horror stories of house building and buying | Home Ownership |