Without being there...........
..........I'd say the coil is dirty........
..............causing a restriction in air-flow.

Which is allowing the excessive air-flow pressure to blow the water off the
coil.
(being you say the drain is clean)

Get a competent tech to clean the coil and check the refrigerate charge.
(not just pressures.............they need to check the SH & SC)
As someone may have put some refrigerate in it to keep it from freezing.
(at some point..........as the coil got dirty)


--
kjpro
_-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-_

( kjpro @ starband . net ) remove spaces to e-mail

Want it done yesterday? Or done right today, to save money tomorrow!!

_________________________ __


"Gary M" wrote in message
...
I really hope someone will be able to help me here; I own a 99 Oakwood
home with a Intertherm/Nordyne HVAC unit. The coils of the unit are in
an 'A' configuration and sit in a plastic tray which rests over the
blower cabinet. Ostensibly, this is to catch the condensate and drain
it away via a hose which leads outside. This part of it works fine and
I have cleared the hose more than once.
The problem I have is this; A lot of the water doesn't reach the
drain hose. Instead, it leaks down into and onto the blower equipment
below. This has led to the sequencer and the cicuit breaker shorting
out and they have been replaced. The repairman told me that the drain
had gotten clogged, but that is not the case now. The water seems to
be coming from some other part of the tray. Before I get another
serviceman out here to tell me, "Your drain hose was clogged. That'll
be $xx.xx." I would like to know if there is another cause and better
still, if there is something 'I' can do about it without having to
dismantle the entire cooling system.
Thanks in advance,
-Gary M-



  #2   Report Post  
CBHvac
 
Posts: n/a
Default Condensate everywhere


"Gary M" wrote in message
...
I really hope someone will be able to help me here; I own a 99 Oakwood
home with a Intertherm/Nordyne HVAC unit. The coils of the unit are in
an 'A' configuration and sit in a plastic tray which rests over the
blower cabinet. Ostensibly, this is to catch the condensate and drain
it away via a hose which leads outside.


That part we all know..its a standard slap in...the way that Oakwood and
every other mobile home maker wanted that used that crappy Nordyne set up.


This part of it works fine and
I have cleared the hose more than once.
The problem I have is this; A lot of the water doesn't reach the
drain hose. Instead, it leaks down into and onto the blower equipment
below. This has led to the sequencer and the cicuit breaker shorting
out and they have been replaced. The repairman told me that the drain
had gotten clogged, but that is not the case now. The water seems to
be coming from some other part of the tray. Before I get another
serviceman out here to tell me, "Your drain hose was clogged. That'll
be $xx.xx." I would like to know if there is another cause and better
still, if there is something 'I' can do about it without having to
dismantle the entire cooling system.
Thanks in advance,
-Gary M-



Well...since we deal with this about once a week in a setup like yours,
offer a few suggestions...

did the last service tech seal the pan to the blower compartment with either
a foam tape that is applied to the top of the blower that the A coil
assembly sets on, or with a good quality metal tape around the sides, or a
combination of both?

did the last service tech insure that after he cleaned the drain, that the
coil blower and coil had a slight tilt towards the drain? Did he put a level
on it? Was it dead level? IF it was, its should NOT be on those..

Does your system have a proper condensate trap on the drain line? If not, it
needs one, or the unit, IF sealed properly, might not be draining until the
unit shuts down and you are getting water not so much leaking, but being
pulled into the works..

Did they speed the fan up trying to get better air flow, instead of properly
balancing your single duct line? In other words....has someone put that
sucker on high, and opened all your vents in the triler? If so, its all
wrong, and you are not getting the cooling you need, and should have...and
the air flow could be such that the condensate is being literally stripped
off the coil before it can flow into the pan.


Those are normally plastic pans in the coil assembly, and under normal
circumstances, you will need to replace the coil long before the pan gives
you any trouble. IF the rear or front of the A coils covers have rusted out,
its possible that the coil is getting water pulled over the lip of the pan
that way...




  #3   Report Post  
Peter Swinson
 
Posts: n/a
Default Condensate everywhere

I have seen these pans crack in the center where the injection molding
circles are. Don't try to repair it because it will recrack. Replace the
coil.
"CBHvac" wrote in message
news

"Gary M" wrote in message
...
I really hope someone will be able to help me here; I own a 99 Oakwood
home with a Intertherm/Nordyne HVAC unit. The coils of the unit are in
an 'A' configuration and sit in a plastic tray which rests over the
blower cabinet. Ostensibly, this is to catch the condensate and drain
it away via a hose which leads outside.


That part we all know..its a standard slap in...the way that Oakwood and
every other mobile home maker wanted that used that crappy Nordyne set up.


This part of it works fine and
I have cleared the hose more than once.
The problem I have is this; A lot of the water doesn't reach the
drain hose. Instead, it leaks down into and onto the blower equipment
below. This has led to the sequencer and the cicuit breaker shorting
out and they have been replaced. The repairman told me that the drain
had gotten clogged, but that is not the case now. The water seems to
be coming from some other part of the tray. Before I get another
serviceman out here to tell me, "Your drain hose was clogged. That'll
be $xx.xx." I would like to know if there is another cause and better
still, if there is something 'I' can do about it without having to
dismantle the entire cooling system.
Thanks in advance,
-Gary M-



Well...since we deal with this about once a week in a setup like yours,
offer a few suggestions...

did the last service tech seal the pan to the blower compartment with

either
a foam tape that is applied to the top of the blower that the A coil
assembly sets on, or with a good quality metal tape around the sides, or a
combination of both?

did the last service tech insure that after he cleaned the drain, that the
coil blower and coil had a slight tilt towards the drain? Did he put a

level
on it? Was it dead level? IF it was, its should NOT be on those..

Does your system have a proper condensate trap on the drain line? If not,

it
needs one, or the unit, IF sealed properly, might not be draining until

the
unit shuts down and you are getting water not so much leaking, but being
pulled into the works..

Did they speed the fan up trying to get better air flow, instead of

properly
balancing your single duct line? In other words....has someone put that
sucker on high, and opened all your vents in the triler? If so, its all
wrong, and you are not getting the cooling you need, and should have...and
the air flow could be such that the condensate is being literally stripped
off the coil before it can flow into the pan.


Those are normally plastic pans in the coil assembly, and under normal
circumstances, you will need to replace the coil long before the pan gives
you any trouble. IF the rear or front of the A coils covers have rusted

out,
its possible that the coil is getting water pulled over the lip of the pan
that way...






  #4   Report Post  
kjpro
 
Posts: n/a
Default Condensate everywhere

"Peter Swinson" wrote in message
news:3aAYa.91304$o%2.40854@sccrnsc02...
I have seen these pans crack in the center where the injection molding
circles are. Don't try to repair it because it will recrack. Replace the
coil.


Aaaaaaaaaaaaaaaw....

You mean JB Weld won't work!!!! :-0

They won't like to hear that!! :-)

--
kjpro
_-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-_

( kjpro @ starband . net ) remove spaces to e-mail

Want it done yesterday? Or done right today, to save money tomorrow!!

_________________________ __





  #5   Report Post  
D.S.
 
Posts: n/a
Default Condensate everywhere

Here is a different water leak that comes from line before it gets to the
unit go to this page and click on water leak picture show
http://homemyhome.com/photoshow.html



"Peter Swinson" wrote in message
news:3aAYa.91304$o%2.40854@sccrnsc02...
I have seen these pans crack in the center where the injection molding
circles are. Don't try to repair it because it will recrack. Replace the
coil.
"CBHvac" wrote in message
news

"Gary M" wrote in message
...
I really hope someone will be able to help me here; I own a 99 Oakwood
home with a Intertherm/Nordyne HVAC unit. The coils of the unit are in
an 'A' configuration and sit in a plastic tray which rests over the
blower cabinet. Ostensibly, this is to catch the condensate and drain
it away via a hose which leads outside.


That part we all know..its a standard slap in...the way that Oakwood and
every other mobile home maker wanted that used that crappy Nordyne set

up.


This part of it works fine and
I have cleared the hose more than once.
The problem I have is this; A lot of the water doesn't reach the
drain hose. Instead, it leaks down into and onto the blower equipment
below. This has led to the sequencer and the cicuit breaker shorting
out and they have been replaced. The repairman told me that the drain
had gotten clogged, but that is not the case now. The water seems to
be coming from some other part of the tray. Before I get another
serviceman out here to tell me, "Your drain hose was clogged. That'll
be $xx.xx." I would like to know if there is another cause and better
still, if there is something 'I' can do about it without having to
dismantle the entire cooling system.
Thanks in advance,
-Gary M-



Well...since we deal with this about once a week in a setup like yours,
offer a few suggestions...

did the last service tech seal the pan to the blower compartment with

either
a foam tape that is applied to the top of the blower that the A coil
assembly sets on, or with a good quality metal tape around the sides, or

a
combination of both?

did the last service tech insure that after he cleaned the drain, that

the
coil blower and coil had a slight tilt towards the drain? Did he put a

level
on it? Was it dead level? IF it was, its should NOT be on those..

Does your system have a proper condensate trap on the drain line? If

not,
it
needs one, or the unit, IF sealed properly, might not be draining until

the
unit shuts down and you are getting water not so much leaking, but being
pulled into the works..

Did they speed the fan up trying to get better air flow, instead of

properly
balancing your single duct line? In other words....has someone put that
sucker on high, and opened all your vents in the triler? If so, its all
wrong, and you are not getting the cooling you need, and should

have...and
the air flow could be such that the condensate is being literally

stripped
off the coil before it can flow into the pan.


Those are normally plastic pans in the coil assembly, and under normal
circumstances, you will need to replace the coil long before the pan

gives
you any trouble. IF the rear or front of the A coils covers have rusted

out,
its possible that the coil is getting water pulled over the lip of the

pan
that way...










  #6   Report Post  
pjm@see_my_sig_for_address.com
 
Posts: n/a
Default Condensate everywhere

On Fri, 08 Aug 2003 02:22:56 GMT, "D.S." wrote:


"CBHvac" wrote in message
news

"D.S." wrote in message
igy.com...
Here is a different water leak that comes from line before it gets to

the
unit go to this page and click on water leak picture show
http://homemyhome.com/photoshow.html



I have to admit..other than the way you present what you call photos, I

cant
see ****...just lots of glare..
A very cheap POS case, and some OmegaFlex..

That line, is called a suction line, btw...thought you might want to at
least know what its called, even if you dont know why its got condensation
on it..

I know it's condensation but if I want to call it a leak since that is

what it's actually doing in the end, when it drips into the opening and then
LEAKS into the plenum, which is actually just wood from frame of the house
where the old return used to be , before this unit was put in and changed to
a down draft or whatever.

To help with glare turn down your brightness on moniter , it's the setting
that resembles a sun with a minus sign on one side and a plus sign on the
other..........


And do it now, or he'll sue.

Regardless of the fact that his suggestion is meaningless
bull****.



Paul ( pjm @ pobox . com ) - remove spaces to email me
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~


Coming eventually - PMTherm version 2.0 !! http://pmilligan.net/pmtherm.htm
Free superheat charts for 38 Ref's online at http://pmilligan.net/pmtherm/
My personal site is at http://www.pmilligan.net ,
featuring free HVAC, psychrometric, stock market, and other software
http://helpthecritters.com/ is my domain for helping critters
  #7   Report Post  
D.S.
 
Posts: n/a
Default Condensate everywhere


wrote in message
...
On Fri, 08 Aug 2003 01:43:20 GMT, "D.S." wrote:

Here is a different water leak that comes from line before it gets to the
unit go to this page and click on water leak picture show
http://homemyhome.com/photoshow.html



Geez, I love the part about how you're going to sue the
builder and his brother and everyone else you ever met for "UNSAFE
CONDITIONS(CONSTRUCTION DUST)" and "SLANDEROUS STATEMENTS"

http://homemyhome.com/sue.html

And you're going to sue, including the AC contractor (s):

ARE THERE ANY LAWYERS IN TOWN THAT DO NOT HAVE A CONFLICT OF INTEREST
WITH
THE CITY,
AIRPORT,
CINNABAR ,
WOOD SYSTEMS ,
TERRELL HEATING AND AIR,
HORIZON PAINTING ,
WOOD & IRON FABRICATORS AND
WHITE CONSTRUCTION , MILL CREEK?

Among your complaints :

"A copper tube that connects to blower unit from outside a/c unit
gurgles when a/c is turned on."

"2nd is I can hear my neighbors a/c unit when it's running."

" 3rd is the sound of dripping rain vibrating through the sheetrock ,
(this was with ear against the wall, might not count)"

"4th was still hearing the fireworks going off at driller's stadium
tonight."

"They did the cleaning but didn't let the Maids finish on Monday "

"Maybe soon I can get the floor moulding or is it called trim,
whatever it is I want it pulled off and walls/doors/window areas
behind it finished "

"To the Terrell worker who likes the F word, if you shut the opening
for underneath the house the dogs won't do that under there also if
someone calls the dog catcher again tomorrow because of my dogs being
out you will pay to get them out since you can't shut the gate."

"The rules where broken by only having one sub-contracter here by
themself"

"Work was finally done to fix leaks, they tried anyway. Terrell was 42
minutes late"

"Whortman Air has an ad out talking about refrigarent 22 being banned
in 2008 I believe. Combine this with the minimum Seer rating going to
12 in a couple years too gives a double whamy on the units being
installed for the project.We sign rights away for a livetime and they
give us an A/C systems which will be obsolete in a few years."


Ok maybe I've gone overboard here and there , hey another item to sue about
, making me go looney after more than 8 months of this...... lol

Wait I'm not the only looney , you actually took the time to look at it
that much................






"Peter Swinson" wrote in message
news:3aAYa.91304$o%2.40854@sccrnsc02...
I have seen these pans crack in the center where the injection molding
circles are. Don't try to repair it because it will recrack. Replace

the
coil.
"CBHvac" wrote in message
news
"Gary M" wrote in message
...
I really hope someone will be able to help me here; I own a 99

Oakwood
home with a Intertherm/Nordyne HVAC unit. The coils of the unit are

in
an 'A' configuration and sit in a plastic tray which rests over the
blower cabinet. Ostensibly, this is to catch the condensate and

drain
it away via a hose which leads outside.

That part we all know..its a standard slap in...the way that Oakwood

and
every other mobile home maker wanted that used that crappy Nordyne

set
up.


This part of it works fine and
I have cleared the hose more than once.
The problem I have is this; A lot of the water doesn't reach the
drain hose. Instead, it leaks down into and onto the blower

equipment
below. This has led to the sequencer and the cicuit breaker

shorting
out and they have been replaced. The repairman told me that the

drain
had gotten clogged, but that is not the case now. The water seems

to
be coming from some other part of the tray. Before I get another
serviceman out here to tell me, "Your drain hose was clogged.

That'll
be $xx.xx." I would like to know if there is another cause and

better
still, if there is something 'I' can do about it without having to
dismantle the entire cooling system.
Thanks in advance,
-Gary M-


Well...since we deal with this about once a week in a setup like

yours,
offer a few suggestions...

did the last service tech seal the pan to the blower compartment with
either
a foam tape that is applied to the top of the blower that the A coil
assembly sets on, or with a good quality metal tape around the sides,

or
a
combination of both?

did the last service tech insure that after he cleaned the drain,

that
the
coil blower and coil had a slight tilt towards the drain? Did he put

a
level
on it? Was it dead level? IF it was, its should NOT be on those..

Does your system have a proper condensate trap on the drain line? If

not,
it
needs one, or the unit, IF sealed properly, might not be draining

until
the
unit shuts down and you are getting water not so much leaking, but

being
pulled into the works..

Did they speed the fan up trying to get better air flow, instead of
properly
balancing your single duct line? In other words....has someone put

that
sucker on high, and opened all your vents in the triler? If so, its

all
wrong, and you are not getting the cooling you need, and should

have...and
the air flow could be such that the condensate is being literally

stripped
off the coil before it can flow into the pan.


Those are normally plastic pans in the coil assembly, and under

normal
circumstances, you will need to replace the coil long before the pan

gives
you any trouble. IF the rear or front of the A coils covers have

rusted
out,
its possible that the coil is getting water pulled over the lip of

the
pan
that way...









Paul ( pjm @ pobox . com ) - remove spaces to email me
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~


Coming eventually - PMTherm version 2.0 !!

http://pmilligan.net/pmtherm.htm
Free superheat charts for 38 Ref's online at http://pmilligan.net/pmtherm/
My personal site is at http://www.pmilligan.net ,
featuring free HVAC, psychrometric, stock market, and other software
http://helpthecritters.com/ is my domain for helping critters



  #8   Report Post  
pjm@see_my_sig_for_address.com
 
Posts: n/a
Default Condensate everywhere

On Fri, 08 Aug 2003 02:51:21 GMT, "D.S." wrote:


wrote in message
.. .
On Fri, 08 Aug 2003 01:43:20 GMT, "D.S." wrote:



" 3rd is the sound of dripping rain vibrating through the sheetrock ,
(this was with ear against the wall, might not count)"


"To the Terrell worker who likes the F word, if you shut the opening
for underneath the house the dogs won't do that under there also if
someone calls the dog catcher again tomorrow because of my dogs being
out you will pay to get them out since you can't shut the gate."

"The rules where broken by only having one sub-contracter here by
themself"

"Work was finally done to fix leaks, they tried anyway. Terrell was 42
minutes late"


Ok maybe I've gone overboard here and there , hey another item to sue about
, making me go looney after more than 8 months of this...... lol

Wait I'm not the only looney , you actually took the time to look at it
that much................


Never said I was sane :-). Besides, it was compelling stuff !

I got this mental picture of you, at 2:AM when the world is
silent ( except your world, of course :-) ), ear pressed against the
wall, holding your breath, listening for rain drops, and the echos of
that guy who was 42 minutes late and then stepped in dog****, cursing
in your crawlspace all alone :-)



Paul ( pjm @ pobox . com ) - remove spaces to email me
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~


Coming eventually - PMTherm version 2.0 !! http://pmilligan.net/pmtherm.htm
Free superheat charts for 38 Ref's online at http://pmilligan.net/pmtherm/
My personal site is at http://www.pmilligan.net ,
featuring free HVAC, psychrometric, stock market, and other software
http://helpthecritters.com/ is my domain for helping critters
  #9   Report Post  
pjm@see_my_sig_for_address.com
 
Posts: n/a
Default Condensate everywhere

On Thu, 7 Aug 2003 23:03:43 -0700, "CBHvac"
wrote:

First, your a bitchaholic..seen your page before, and it hasnt changed much.


Well put :-)

Second, its not a leak, its condensation and its dripping, not leaking. A
leak, you jackass, would mean that the pipe that is SWEATING, would carry
water, and its not. Glad this isnt rocket science, and your not workin for
NASA...


Ummm.... considering recent events.......

I also suggest that you learn how in hell to use a digital camera, since you
plain suck ass at it, and THAT, sir, is a fact, and I dont have to assume
****.


Oh, stop beating around the bush :-)

As a ****tard that wants to whine and cry, even about an inspector using his
TV as a table...lol...oh my god..thats hilarious...not the fact it happened,
the fact that he found a way to bitch about it..


****, I missed that one !!!



Paul ( pjm @ pobox . com ) - remove spaces to email me
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~


Coming eventually - PMTherm version 2.0 !! http://pmilligan.net/pmtherm.htm
Free superheat charts for 38 Ref's online at http://pmilligan.net/pmtherm/
My personal site is at http://www.pmilligan.net ,
featuring free HVAC, psychrometric, stock market, and other software
http://helpthecritters.com/ is my domain for helping critters
  #10   Report Post  
D.S.
 
Posts: n/a
Default Condensate everywhere

I love reading this , it's been fun and I take it you had a rough day.PJM is
at least funnier than you. Did you miss this page
http://homemyhome.com/id45.html it shows what was found by another company
on the work done.It took 6 months to get this far and another 2 months for
them to come back out to caulk instead of making an actual chamber .This
area is about 4' long 2' wide and 2' tall . Wouldn't it make more sense for
the air to go thru a chamber of some sort instead of filling up this area
before making it into the 2 main ducts? At least it wouldn't leak (excuse
the use of that word) air through the wall and cracks and out the baseboard.
Yes I bitch , yes some is petty .No I didn't wait till work was
stopped to complain. Yes the companies know of the web site, they will not
sue me because then it will become more public and you can't win a suit on
slander if it's true. Sorry for the offense you took for pokeing fun at you
.. If you get that upset about it don't dish it out. Why is it when a regular
on a newsgroup doesn't like a post grammer always becomes an issue? After
the condensation leaves it's location of origin and drips to a flat area
then goes down an open hole would it not then become a leak. It could be
called draining I suppose but wouldn't it need to be a drain hole to say
it's draining and not leaking?
Yes it's the same site and it's been up since December just new rework was
done recently and you would have to live in this neighborhood to really
understand it all and my neighbors feel the same about thier houses.
Excuse not posting this below, I didn't feel like it . Just sue
me......lol


"CBHvac" wrote in message
...

"D.S." wrote in message
igy.com...

"CBHvac" wrote in message
news

"D.S." wrote in message
igy.com...
Here is a different water leak that comes from line before it gets

to
the
unit go to this page and click on water leak picture show
http://homemyhome.com/photoshow.html


I have to admit..other than the way you present what you call photos,

I
cant
see ****...just lots of glare..
A very cheap POS case, and some OmegaFlex..

That line, is called a suction line, btw...thought you might want to

at
least know what its called, even if you dont know why its got

condensation
on it..

I know it's condensation but if I want to call it a leak since that

is
what it's actually doing in the end, when it drips into the opening and

then
LEAKS into the plenum, which is actually just wood from frame of the

house
where the old return used to be , before this unit was put in and

changed
to
a down draft or whatever.


And you want to put up a page of bitchin...LOL...

First, your a bitchaholic..seen your page before, and it hasnt changed

much.
Second, its not a leak, its condensation and its dripping, not leaking. A
leak, you jackass, would mean that the pipe that is SWEATING, would carry
water, and its not. Glad this isnt rocket science, and your not workin for
NASA...


Glad I am not your neighbor..and you are glad of that too....
Trust me..

Have the inspectors stopped coming to your home now? Do they run to the
other side of the street when you come out? Have you bitched, cryed and
whined enough that the property values have hit new lows in your area?
They must have...if sound insulation would exceed 50% of the value of your
home...sheeeesh....


Just a few thought genuis..

1- On your rumors page, its HIRE....not higher..

2- What are your qualifications to determine what is an unsafe condition?
Are you licenced and bonded with the State of OK as an inspector?

3- Oh screw it...I could go on, but I am afraid that it might be beyond

your
comphrension skills since YOU let the work be done to your home, and didnt
stop it...and choose now to whine..




To help with glare turn down your brightness on moniter , it's the

setting
that resembles a sun with a minus sign on one side and a plus sign on

the
other..........



Actually Jackass, its not. I suggest that if you are that ****ing

brilliant,
you look at what the brightness setting on a T40 is, and how you set it.
I also suggest that you learn how in hell to use a digital camera, since

you
plain suck ass at it, and THAT, sir, is a fact, and I dont have to assume
****.


Oh...dont like it?
So sue me....LOL
You are out to sue everyone else....of course, its prob the ONLY way you
will ever have more than you do...LOL

I hope that all those people listed on your site know about it....and if
they dont...they will...LOL





All thoughts presented are based upon the assinine way that the original
poster presented himself, and in the manner that his page represents him.
As a ****tard that wants to whine and cry, even about an inspector using

his
TV as a table...lol...oh my god..thats hilarious...not the fact it

happened,
the fact that he found a way to bitch about it..














"Peter Swinson" wrote in message
news:3aAYa.91304$o%2.40854@sccrnsc02...
I have seen these pans crack in the center where the injection

molding
circles are. Don't try to repair it because it will recrack.

Replace
the
coil.
"CBHvac" wrote in message
news
"Gary M" wrote in message
...
I really hope someone will be able to help me here; I own a 99
Oakwood
home with a Intertherm/Nordyne HVAC unit. The coils of the

unit
are
in
an 'A' configuration and sit in a plastic tray which rests

over
the
blower cabinet. Ostensibly, this is to catch the condensate

and
drain
it away via a hose which leads outside.

That part we all know..its a standard slap in...the way that

Oakwood
and
every other mobile home maker wanted that used that crappy

Nordyne
set
up.


This part of it works fine and
I have cleared the hose more than once.
The problem I have is this; A lot of the water doesn't reach

the
drain hose. Instead, it leaks down into and onto the blower
equipment
below. This has led to the sequencer and the cicuit breaker

shorting
out and they have been replaced. The repairman told me that

the
drain
had gotten clogged, but that is not the case now. The water

seems
to
be coming from some other part of the tray. Before I get

another
serviceman out here to tell me, "Your drain hose was clogged.
That'll
be $xx.xx." I would like to know if there is another cause and
better
still, if there is something 'I' can do about it without

having
to
dismantle the entire cooling system.
Thanks in advance,
-Gary M-


Well...since we deal with this about once a week in a setup

like
yours,
offer a few suggestions...

did the last service tech seal the pan to the blower compartment

with
either
a foam tape that is applied to the top of the blower that the A

coil
assembly sets on, or with a good quality metal tape around the

sides,
or
a
combination of both?

did the last service tech insure that after he cleaned the

drain,
that
the
coil blower and coil had a slight tilt towards the drain? Did he

put
a
level
on it? Was it dead level? IF it was, its should NOT be on

those..

Does your system have a proper condensate trap on the drain

line?
If

not,
it
needs one, or the unit, IF sealed properly, might not be

draining
until
the
unit shuts down and you are getting water not so much leaking,

but
being
pulled into the works..

Did they speed the fan up trying to get better air flow, instead

of
properly
balancing your single duct line? In other words....has someone

put
that
sucker on high, and opened all your vents in the triler? If so,

its
all
wrong, and you are not getting the cooling you need, and should
have...and
the air flow could be such that the condensate is being

literally
stripped
off the coil before it can flow into the pan.


Those are normally plastic pans in the coil assembly, and under

normal
circumstances, you will need to replace the coil long before the

pan
gives
you any trouble. IF the rear or front of the A coils covers have
rusted
out,
its possible that the coil is getting water pulled over the lip

of
the
pan
that way...


















  #11   Report Post  
D.S.
 
Posts: n/a
Default Condensate everywhere


"CBHvac" wrote in message
...

wrote in message
...
On Fri, 08 Aug 2003 01:43:20 GMT, "D.S." wrote:

Here is a different water leak that comes from line before it gets to

the
unit go to this page and click on water leak picture show
http://homemyhome.com/photoshow.html



Geez, I love the part about how you're going to sue the
builder and his brother and everyone else you ever met for "UNSAFE
CONDITIONS(CONSTRUCTION DUST)" and "SLANDEROUS STATEMENTS"

http://homemyhome.com/sue.html

And you're going to sue, including the AC contractor (s):

ARE THERE ANY LAWYERS IN TOWN THAT DO NOT HAVE A CONFLICT OF INTEREST
WITH
THE CITY,
AIRPORT,
CINNABAR ,
WOOD SYSTEMS ,
TERRELL HEATING AND AIR,
HORIZON PAINTING ,
WOOD & IRON FABRICATORS AND
WHITE CONSTRUCTION , MILL CREEK?

Among your complaints :

"A copper tube that connects to blower unit from outside a/c unit
gurgles when a/c is turned on."



Well...DUH...


Loudly in the hallway is normal?



"2nd is I can hear my neighbors a/c unit when it's running."


I cant hear mine....but then, they cant hear mine either...its nice and
quiet...LOL


" 3rd is the sound of dripping rain vibrating through the sheetrock ,
(this was with ear against the wall, might not count)"


I missed THAT one...hilarious...


"4th was still hearing the fireworks going off at driller's stadium
tonight."


Fireworks....NOT a 737..LOL


5 miiles away


"They did the cleaning but didn't let the Maids finish on Monday "



LOL..


another that you had to be here



"Maybe soon I can get the floor moulding or is it called trim,
whatever it is I want it pulled off and walls/doors/window areas
behind it finished "


Demanding little redneck aint he?



"To the Terrell worker who likes the F word, if you shut the opening
for underneath the house the dogs won't do that under there also if
someone calls the dog catcher again tomorrow because of my dogs being
out you will pay to get them out since you can't shut the gate."




Different time period , they would not shut crawl space entrance when they
left for the day. Dogs pulled on insullation on ducts that was hanging down
since they used staples to hold insulation so it left pieces dangling and
tempting to a young dog. I have accepted the actions of my dogs even though
they would not have gotten under there had they closed the opening.I can't
close it when they leave if I'm at work

I think he said someplace, that he took responsibility for his dogs under
the home...I mean..I own a couple, and they are MY responsibility..if I

know
the basements open, and I dont want them in the basement, I make sure they
cant get there...sheeeesh...
Common sense lacking in OK...


"The rules where broken by only having one sub-contracter here by
themself"


HUH??

Another one you have to be here to understand. They have a written
guidelines for the project . One day my neighbor came home and found a
worker in his son's bed sleeping.



"Work was finally done to fix leaks, they tried anyway. Terrell was 42
minutes late"


Holy Crap Batman...do each and every job with a stopwatch...
Forget lunch man...you got to PEE??? DAMMIT man..hes got a STOPWATCH!!!!!


I had to wait 2 months for this day and was missing work and the
contractor for this house was not happy either about them being late . It's
not hard to make an 8 am appointment


"Whortman Air has an ad out talking about refrigarent 22 being banned
in 2008 I believe. Combine this with the minimum Seer rating going to
12 in a couple years too gives a double whamy on the units being
installed for the project.We sign rights away for a livetime and they
give us an A/C systems which will be obsolete in a few years."



Idiot...
To think some believe this..


Not True?






"Peter Swinson" wrote in message
news:3aAYa.91304$o%2.40854@sccrnsc02...
I have seen these pans crack in the center where the injection

molding
circles are. Don't try to repair it because it will recrack. Replace

the
coil.
"CBHvac" wrote in message
news
"Gary M" wrote in message
...
I really hope someone will be able to help me here; I own a 99

Oakwood
home with a Intertherm/Nordyne HVAC unit. The coils of the unit

are
in
an 'A' configuration and sit in a plastic tray which rests over

the
blower cabinet. Ostensibly, this is to catch the condensate and

drain
it away via a hose which leads outside.

That part we all know..its a standard slap in...the way that

Oakwood
and
every other mobile home maker wanted that used that crappy Nordyne

set
up.


This part of it works fine and
I have cleared the hose more than once.
The problem I have is this; A lot of the water doesn't reach the
drain hose. Instead, it leaks down into and onto the blower

equipment
below. This has led to the sequencer and the cicuit breaker

shorting
out and they have been replaced. The repairman told me that the

drain
had gotten clogged, but that is not the case now. The water seems

to
be coming from some other part of the tray. Before I get another
serviceman out here to tell me, "Your drain hose was clogged.

That'll
be $xx.xx." I would like to know if there is another cause and

better
still, if there is something 'I' can do about it without having

to
dismantle the entire cooling system.
Thanks in advance,
-Gary M-


Well...since we deal with this about once a week in a setup like

yours,
offer a few suggestions...

did the last service tech seal the pan to the blower compartment

with
either
a foam tape that is applied to the top of the blower that the A

coil
assembly sets on, or with a good quality metal tape around the

sides,
or
a
combination of both?

did the last service tech insure that after he cleaned the drain,

that
the
coil blower and coil had a slight tilt towards the drain? Did he

put
a
level
on it? Was it dead level? IF it was, its should NOT be on those..

Does your system have a proper condensate trap on the drain line?

If
not,
it
needs one, or the unit, IF sealed properly, might not be draining

until
the
unit shuts down and you are getting water not so much leaking, but

being
pulled into the works..

Did they speed the fan up trying to get better air flow, instead of
properly
balancing your single duct line? In other words....has someone put

that
sucker on high, and opened all your vents in the triler? If so, its

all
wrong, and you are not getting the cooling you need, and should
have...and
the air flow could be such that the condensate is being literally
stripped
off the coil before it can flow into the pan.


Those are normally plastic pans in the coil assembly, and under

normal
circumstances, you will need to replace the coil long before the

pan
gives
you any trouble. IF the rear or front of the A coils covers have

rusted
out,
its possible that the coil is getting water pulled over the lip of

the
pan
that way...









Paul ( pjm @ pobox . com ) - remove spaces to email me
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~


Coming eventually - PMTherm version 2.0 !!

http://pmilligan.net/pmtherm.htm
Free superheat charts for 38 Ref's online at

http://pmilligan.net/pmtherm/
My personal site is at http://www.pmilligan.net ,
featuring free HVAC, psychrometric, stock market, and other software
http://helpthecritters.com/ is my domain for helping critters






  #12   Report Post  
CBHvac
 
Posts: n/a
Default Condensate everywhere


wrote in message
...
On Fri, 08 Aug 2003 01:43:20 GMT, "D.S." wrote:

Here is a different water leak that comes from line before it gets to the
unit go to this page and click on water leak picture show
http://homemyhome.com/photoshow.html



Geez, I love the part about how you're going to sue the
builder and his brother and everyone else you ever met for "UNSAFE
CONDITIONS(CONSTRUCTION DUST)" and "SLANDEROUS STATEMENTS"

http://homemyhome.com/sue.html

And you're going to sue, including the AC contractor (s):

ARE THERE ANY LAWYERS IN TOWN THAT DO NOT HAVE A CONFLICT OF INTEREST
WITH
THE CITY,
AIRPORT,
CINNABAR ,
WOOD SYSTEMS ,
TERRELL HEATING AND AIR,
HORIZON PAINTING ,
WOOD & IRON FABRICATORS AND
WHITE CONSTRUCTION , MILL CREEK?

Among your complaints :

"A copper tube that connects to blower unit from outside a/c unit
gurgles when a/c is turned on."



Well...DUH...


"2nd is I can hear my neighbors a/c unit when it's running."


I cant hear mine....but then, they cant hear mine either...its nice and
quiet...LOL


" 3rd is the sound of dripping rain vibrating through the sheetrock ,
(this was with ear against the wall, might not count)"


I missed THAT one...hilarious...


"4th was still hearing the fireworks going off at driller's stadium
tonight."


Fireworks....NOT a 737..LOL


"They did the cleaning but didn't let the Maids finish on Monday "



LOL..


"Maybe soon I can get the floor moulding or is it called trim,
whatever it is I want it pulled off and walls/doors/window areas
behind it finished "


Demanding little redneck aint he?



"To the Terrell worker who likes the F word, if you shut the opening
for underneath the house the dogs won't do that under there also if
someone calls the dog catcher again tomorrow because of my dogs being
out you will pay to get them out since you can't shut the gate."



I think he said someplace, that he took responsibility for his dogs under
the home...I mean..I own a couple, and they are MY responsibility..if I know
the basements open, and I dont want them in the basement, I make sure they
cant get there...sheeeesh...
Common sense lacking in OK...


"The rules where broken by only having one sub-contracter here by
themself"


HUH??


"Work was finally done to fix leaks, they tried anyway. Terrell was 42
minutes late"


Holy Crap Batman...do each and every job with a stopwatch...
Forget lunch man...you got to PEE??? DAMMIT man..hes got a STOPWATCH!!!!!


"Whortman Air has an ad out talking about refrigarent 22 being banned
in 2008 I believe. Combine this with the minimum Seer rating going to
12 in a couple years too gives a double whamy on the units being
installed for the project.We sign rights away for a livetime and they
give us an A/C systems which will be obsolete in a few years."



Idiot...
To think some believe this..




"Peter Swinson" wrote in message
news:3aAYa.91304$o%2.40854@sccrnsc02...
I have seen these pans crack in the center where the injection molding
circles are. Don't try to repair it because it will recrack. Replace

the
coil.
"CBHvac" wrote in message
news
"Gary M" wrote in message
...
I really hope someone will be able to help me here; I own a 99

Oakwood
home with a Intertherm/Nordyne HVAC unit. The coils of the unit are

in
an 'A' configuration and sit in a plastic tray which rests over the
blower cabinet. Ostensibly, this is to catch the condensate and

drain
it away via a hose which leads outside.

That part we all know..its a standard slap in...the way that Oakwood

and
every other mobile home maker wanted that used that crappy Nordyne

set
up.


This part of it works fine and
I have cleared the hose more than once.
The problem I have is this; A lot of the water doesn't reach the
drain hose. Instead, it leaks down into and onto the blower

equipment
below. This has led to the sequencer and the cicuit breaker

shorting
out and they have been replaced. The repairman told me that the

drain
had gotten clogged, but that is not the case now. The water seems

to
be coming from some other part of the tray. Before I get another
serviceman out here to tell me, "Your drain hose was clogged.

That'll
be $xx.xx." I would like to know if there is another cause and

better
still, if there is something 'I' can do about it without having to
dismantle the entire cooling system.
Thanks in advance,
-Gary M-


Well...since we deal with this about once a week in a setup like

yours,
offer a few suggestions...

did the last service tech seal the pan to the blower compartment with
either
a foam tape that is applied to the top of the blower that the A coil
assembly sets on, or with a good quality metal tape around the sides,

or
a
combination of both?

did the last service tech insure that after he cleaned the drain,

that
the
coil blower and coil had a slight tilt towards the drain? Did he put

a
level
on it? Was it dead level? IF it was, its should NOT be on those..

Does your system have a proper condensate trap on the drain line? If

not,
it
needs one, or the unit, IF sealed properly, might not be draining

until
the
unit shuts down and you are getting water not so much leaking, but

being
pulled into the works..

Did they speed the fan up trying to get better air flow, instead of
properly
balancing your single duct line? In other words....has someone put

that
sucker on high, and opened all your vents in the triler? If so, its

all
wrong, and you are not getting the cooling you need, and should

have...and
the air flow could be such that the condensate is being literally

stripped
off the coil before it can flow into the pan.


Those are normally plastic pans in the coil assembly, and under

normal
circumstances, you will need to replace the coil long before the pan

gives
you any trouble. IF the rear or front of the A coils covers have

rusted
out,
its possible that the coil is getting water pulled over the lip of

the
pan
that way...









Paul ( pjm @ pobox . com ) - remove spaces to email me
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~


Coming eventually - PMTherm version 2.0 !!

http://pmilligan.net/pmtherm.htm
Free superheat charts for 38 Ref's online at http://pmilligan.net/pmtherm/
My personal site is at http://www.pmilligan.net ,
featuring free HVAC, psychrometric, stock market, and other software
http://helpthecritters.com/ is my domain for helping critters



  #13   Report Post  
CBHvac
 
Posts: n/a
Default Condensate everywhere


wrote in message
...
On Fri, 08 Aug 2003 03:46:19 GMT, "D.S." wrote:

I love reading this , it's been fun and I take it you had a rough day.PJM

is
at least funnier than you.


Told ya so, CB :-)



Yea..but I do real HVAC work, and not like that hack that he allowed work on
his home..

I aint paid to be a standup comedian.



Paul ( pjm @ pobox . com ) - remove spaces to email me
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~


Coming eventually - PMTherm version 2.0 !!

http://pmilligan.net/pmtherm.htm
Free superheat charts for 38 Ref's online at http://pmilligan.net/pmtherm/
My personal site is at http://www.pmilligan.net ,
featuring free HVAC, psychrometric, stock market, and other software
http://helpthecritters.com/ is my domain for helping critters



  #14   Report Post  
AugustaGa
 
Posts: n/a
Default Condensate everywhere

So...people have problems with their stick built homes too....what a
wonder...I thought all stick builts were perfect..

"D.S." wrote in message
igy.com...
Here is a different water leak that comes from line before it gets to the
unit go to this page and click on water leak picture show
http://homemyhome.com/photoshow.html



  #15   Report Post  
kjpro
 
Posts: n/a
Default Condensate everywhere

"D.S." wrote in message
igy.com...

LEAKS into the plenum, which is actually just wood from frame of the house
where the old return used to be , before this unit was put in and changed

to
a down draft or whatever.


Wow, A warm air "supply" plenum...............made of wood????

Now that's gotta be a nice job! :-)

--
kjpro
_-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-_

( kjpro @ starband . net ) remove spaces to e-mail

Want it done yesterday? Or done right today, to save money tomorrow!!

_________________________ __







  #16   Report Post  
kjpro
 
Posts: n/a
Default Condensate everywhere

"AugustaGa" wrote in message
...
So...people have problems with their stick built homes too....what a
wonder...I thought all stick builts were perfect..


No, there are Hacks as building contractors too.

And an occasional HO that thinks they can build a home if they can work with
wood!!

But, as the last note..............
........an occasional home F***ed up........vers "EVERY" trailer is no
competition!!


--
kjpro
_-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-__-~-_

( kjpro @ starband . net ) remove spaces to e-mail

Want it done yesterday? Or done right today, to save money tomorrow!!

_________________________ __





  #17   Report Post  
Noon-Air
 
Posts: n/a
Default Condensate everywhere


wrote in message
news
On Sat, 09 Aug 2003 23:04:43 GMT, "kjpro" ( kjpro @ starband . com )
see-my-sig-for-e-mail wrote:

"AugustaGa" wrote in message
...
So...people have problems with their stick built homes too....what a
wonder...I thought all stick builts were perfect..


No, there are Hacks as building contractors too.

And an occasional HO that thinks they can build a home if they can work

with
wood!!


Or can reliably identify the hammer section at Home Depot 9
out of 10 times....


and they can find the section with those sharp pointed poundie thingies too
:-)


Paul ( pjm @ pobox . com ) - remove spaces to email me
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~


Coming eventually - PMTherm version 2.0 !!

http://pmilligan.net/pmtherm.htm
Free superheat charts for 38 Ref's online at http://pmilligan.net/pmtherm/
My personal site is at http://www.pmilligan.net ,
featuring free HVAC, psychrometric, stock market, and other software
http://helpthecritters.com/ is my domain for helping critters



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Condensate pump wiring Rick Home Repair 29 October 21st 03 02:39 AM
condensate --> ice on air conditioning evaporator coil? Bill Christens-Barry Home Repair 6 July 5th 03 09:15 AM


All times are GMT +1. The time now is 01:43 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"