house wiring voltage drop
Suspected a wiring problem at a friends house where her computer and
monitor fed via a UPS is connected. The UPS sounds it's alarm sometimes when there is no apparent reason. The outlet in question has 120v no load and 110v with a 1500 watt load. At my house voltage only drops from 120v to 115 volt under the same 1500 watt load. Just wondering if this much voltage drop (10v @ 1500 watts) is excessive and does it warrant further investigation of the friends wiring? I only tested the one outlet at the computer so plan to go back and check some others. |
#2
Posted to sci.electronics.repair
|
|||
|
|||
house wiring voltage drop
On Thu, 16 May 2013 09:25:32 -0400, bilfre wrote:
Suspected a wiring problem at a friends house where her computer and monitor fed via a UPS is connected. The UPS sounds it's alarm sometimes when there is no apparent reason. The outlet in question has 120v no load and 110v with a 1500 watt load. At my house voltage only drops from 120v to 115 volt under the same 1500 watt load. Just wondering if this much voltage drop (10v @ 1500 watts) is excessive and does it warrant further investigation of the friends wiring? I only tested the one outlet at the computer so plan to go back and check some others. That voltage drop is excessive. The National Electric Code specifies a drop of no more than 5% from the breaker box to the furthest outlet at full load (Note that a 1500 watt load is about 85% of full load). Checking the drop at various points from the breaker box to the outlet supplying the computer is a good idea. The faq at http://www.psihq.com/iread/faqvolt.htm also has suggestions. PlainBill |
#4
Posted to sci.electronics.repair
|
|||
|
|||
house wiring voltage drop
On May 16, 8:16*pm, bilfre wrote:
On 2013-05-16 16:17:16 +0000, said: That voltage drop is excessive. *The National Electric Code specifies a drop of no more than 5% from the breaker box to the furthest outlet at full load (Note that a 1500 watt load is about 85% of full load). Checking the drop at various points from the breaker box to the outlet supplying the computer is a good idea. *The faq at http://www.psihq.com/iread/faqvolt.htmalso has suggestions. PlainBill Hi PlainBill, Thanks for the response and the link. * I will go back to my friends and look for the problem. *I suspect there is a loose connection at one end or the other since it seems to be intermittent. *Checked my own wiring with same load and only had a 4 volt drop. billfre Your own experience is more typical. 10 V is excessive. Aluminum wiring??? I would be careful not to keep the load on continuously just in case there is some heating somewhere in the walls. P = IV = 20 x 10 = 200Watts, probably not enuf to start a fire but just in case!!! |
#5
Posted to sci.electronics.repair
|
|||
|
|||
house wiring voltage drop
On 5/16/2013 9:23 PM, wrote:
On May 16, 8:16 pm, bilfre wrote: On 2013-05-16 16:17:16 +0000, said: That voltage drop is excessive. The National Electric Code specifies a drop of no more than 5% from the breaker box to the furthest outlet at full load (Note that a 1500 watt load is about 85% of full load). Checking the drop at various points from the breaker box to the outlet supplying the computer is a good idea. The faq at http://www.psihq.com/iread/faqvolt.htmalso has suggestions. PlainBill Hi PlainBill, Thanks for the response and the link. I will go back to my friends and look for the problem. I suspect there is a loose connection at one end or the other since it seems to be intermittent. Checked my own wiring with same load and only had a 4 volt drop. billfre Your own experience is more typical. 10 V is excessive. Aluminum wiring??? I would be careful not to keep the load on continuously just in case there is some heating somewhere in the walls. P = IV = 20 x 10 = 200Watts, probably not enuf to start a fire but just in case!!! I could have started a fire in my home a few years ago. I plugged a couple of chest freezers into an outlet with out trouble for a couple of years. One evening I smelled a burned plastic smell in our living room. I could not isolate it before I didn't smell it. A week or three passed and the smell recurred, this time I moved a TV away from the wall and found the plug was hot and slightly deformed. The outlet was also hot. I removed the paneling and found the wiring looped through this outlet on it way to the one I plugged the freezers into. The connection to the outlet was poor and caused the heating with the extra current going to the freezers. The heat over time had caused the 35 year old outlet to pretty much crumble during removal. So, I guess I would say, make sure that most of that voltage drop is NOT at one outlet. Mikek |
#6
Posted to sci.electronics.repair
|
|||
|
|||
house wiring voltage drop
On Thu, 16 May 2013 21:16:51 -0400, bilfre wrote:
On 2013-05-16 16:17:16 +0000, said: That voltage drop is excessive. The National Electric Code specifies a drop of no more than 5% from the breaker box to the furthest outlet at full load (Note that a 1500 watt load is about 85% of full load). Checking the drop at various points from the breaker box to the outlet supplying the computer is a good idea. The faq at http://www.psihq.com/iread/faqvolt.htm also has suggestions. PlainBill Hi PlainBill, Thanks for the response and the link. I will go back to my friends and look for the problem. I suspect there is a loose connection at one end or the other since it seems to be intermittent. Checked my own wiring with same load and only had a 4 volt drop. billfre With standard wiring practices there are several outlets in this run of wire. The most likely point for a problem is at the point an outlet or switch is connected to the wire. IF you can determine intermediate points along the wire run, the best approach is to determine if the majority of the drop occurs between a pair of outlets. Someone else gave a wattage - they miscalulated. The TOTAL power dissipation for the drop is about 125 watts - still a sizeable amount. The EXTRA dissipation is about 75 watts. One approach would be to hook up the 1500 watt load, then carefully check outlets to see if any feel warm. If no suspects are identified, wait 15 minutes or so (with the load still present), then repeat. PlainBill |
#7
Posted to sci.electronics.repair
|
|||
|
|||
house wiring voltage drop
In article 201305162116512010-nobody@nowhereca,
bilfre wrote: On 2013-05-16 16:17:16 +0000, said: That voltage drop is excessive. The National Electric Code specifies a drop of no more than 5% from the breaker box to the furthest outlet at full load (Note that a 1500 watt load is about 85% of full load). Checking the drop at various points from the breaker box to the outlet supplying the computer is a good idea. The faq at http://www.psihq.com/iread/faqvolt.htm also has suggestions. PlainBill Hi PlainBill, Thanks for the response and the link. I will go back to my friends and look for the problem. I suspect there is a loose connection at one end or the other since it seems to be intermittent. Checked my own wiring with same load and only had a 4 volt drop. Billfre- Also look for evidence of a poor neutral connection. When that happens, voltage will divide according to the load on each line. If that were the case, ten volts drop at a high current load could cause a ten volt rise across the other line-to-neutral circuit. Five or ten volts doesn't sound like a serious problem, but a poor neutral connection could get worse with age. Fred |
#8
Posted to sci.electronics.repair
|
|||
|
|||
house wiring voltage drop
On 2013-05-18 03:59:39 +0000, Fred McKenzie said:
Billfre- Also look for evidence of a poor neutral connection. When that happens, voltage will divide according to the load on each line. If that were the case, ten volts drop at a high current load could cause a ten volt rise across the other line-to-neutral circuit. Five or ten volts doesn't sound like a serious problem, but a poor neutral connection could get worse with age. Fred Fred, Thanks for that tip, I think it may be the problem here. I went back and tightened the screws on both leads at the outlet and at the hot side on the breaker. One screw at the outlet tightened maybe a quarter turn. This brought the voltage drop down from 10v to 7v. Still over the 5% specified by code. I also put a voltmeter on another outlet in the same room that was on a different breaker. When I loaded the outlet that had the 7v drop, the voltage at the other outlet went up a couple of volts from 120v to 122v and I wondered, what could cause that? Then you posted about the poor neutral and I thought about the 2v rise I had measured at an adjacent circuit. Then remembered that I did not check tightness of the neutral wire connection in the panel. Think I will go back again and make sure the neutral wire is good and tight at the panelboard. Maybe that is why it is still over the 5% drop spec. Does this make sense? |
#9
Posted to sci.electronics.repair
|
|||
|
|||
house wiring voltage drop
On 25.05.2013 14:16, bilfre wrote:
On 2013-05-18 03:59:39 +0000, Fred McKenzie said: Billfre- Also look for evidence of a poor neutral connection. When that happens, voltage will divide according to the load on each line. If that were the case, ten volts drop at a high current load could cause a ten volt rise across the other line-to-neutral circuit. Five or ten volts doesn't sound like a serious problem, but a poor neutral connection could get worse with age. Fred Fred, Thanks for that tip, I think it may be the problem here. I went back and tightened the screws on both leads at the outlet and at the hot side on the breaker. One screw at the outlet tightened maybe a quarter turn. This brought the voltage drop down from 10v to 7v. Still over the 5% specified by code. I also put a voltmeter on another outlet in the same room that was on a different breaker. When I loaded the outlet that had the 7v drop, the voltage at the other outlet went up a couple of volts from 120v to 122v and I wondered, what could cause that? Then you posted about the poor neutral and I thought about the 2v rise I had measured at an adjacent circuit. Then remembered that I did not check tightness of the neutral wire connection in the panel. Think I will go back again and make sure the neutral wire is good and tight at the panelboard. Maybe that is why it is still over the 5% drop spec. Does this make sense? Measure the drop at the breaker too. |
#10
Posted to sci.electronics.repair
|
|||
|
|||
house wiring voltage drop
On Sat, 25 May 2013 19:02:17 +0200, tuinkabouter
wrote: On 25.05.2013 14:16, bilfre wrote: On 2013-05-18 03:59:39 +0000, Fred McKenzie said: Billfre- Also look for evidence of a poor neutral connection. When that happens, voltage will divide according to the load on each line. If that were the case, ten volts drop at a high current load could cause a ten volt rise across the other line-to-neutral circuit. Five or ten volts doesn't sound like a serious problem, but a poor neutral connection could get worse with age. Fred Fred, Thanks for that tip, I think it may be the problem here. I went back and tightened the screws on both leads at the outlet and at the hot side on the breaker. One screw at the outlet tightened maybe a quarter turn. This brought the voltage drop down from 10v to 7v. Still over the 5% specified by code. I also put a voltmeter on another outlet in the same room that was on a different breaker. When I loaded the outlet that had the 7v drop, the voltage at the other outlet went up a couple of volts from 120v to 122v and I wondered, what could cause that? Then you posted about the poor neutral and I thought about the 2v rise I had measured at an adjacent circuit. Then remembered that I did not check tightness of the neutral wire connection in the panel. Think I will go back again and make sure the neutral wire is good and tight at the panelboard. Maybe that is why it is still over the 5% drop spec. Does this make sense? Measure the drop at the breaker too. My experience with an open or loose neutral wire, is that the problem is usually outside of house. The problem is usually with the electric company's wiring. Call the electric company. They usually don't charge to check their equipment. |
#11
Posted to sci.electronics.repair
|
|||
|
|||
house wiring voltage drop
|
#12
Posted to sci.electronics.repair
|
|||
|
|||
house wiring voltage drop
In article 2013052711075876283-nobody@nowhereca,
bilfre wrote: On 2013-05-25 21:49:15 +0000, y said: My experience with an open or loose neutral wire, is that the problem is usually outside of house. The problem is usually with the electric company's wiring. Call the electric company. They usually don't charge to check their equipment. The problem is only at one wall outlet inside the house. Please explain how it could be caused by a problem outside the house. . Bilfre- This problem exists somewhere between a power company transformer and where the neutral connects in your breaker box. When I had the problem, I called the power company. Their man checked the transformer, but said I would have to hire an electrician to fix my end of the circuit. While he had the meter removed, he went ahead and tightened the connection there, which solved my problem. Fred |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
12v Voltage Drop? | UK diy | |||
Voltage drop | Home Repair | |||
Will my voltage drop? | Home Repair | |||
Low voltage lights - voltage drop/cable size | UK diy | |||
Low-voltage house wiring from hell | Home Repair |