Electronics Repair (sci.electronics.repair) Discussion of repairing electronic equipment. Topics include requests for assistance, where to obtain servicing information and parts, techniques for diagnosis and repair, and annecdotes about success, failures and problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Glen Walpert
 
Posts: n/a
Default Commercial mains wiring: 12ga wire for 30 amp load?

On Thu, 10 Nov 2005 22:40:32 -0800, Esther & Fester Bestertester
wrote:

Thus spake :

You have 2 issues. Foiust, is the motor supposed to be running on 230
or 208? That couild be the extra current.
If the motor is really exceeding the nameplate amps I would
investigate futher.


Nameplate: 230V, 16.5A.

I presume that if an autotransformer boosts the voltage
10%, it must draw 10%(?) more current in order to do so. Is
this correct? (Nothing is free.)
FBt


Correct, except that there will also be an additional bit of current
draw due to losses in the autotransformer, which will probably be over
95% efficient:

For 208V in, 230V out at 16.5A out to motor and 95% autotransformer
efficiency:

Iin = (16.5*(230/208))/.95 = 19.2A

Which is slightly under your measured 20A, which indicates that you
are running slightly over 100% load on your motor if my voltage
guesses are right. Hopefully the nameplate service factor is at least
1.15 continuous (if the motor runs continuously).

BTW congratulations on responding to one of only 2 posters who
understand your situation (the other being Tom Horne of the Tacoma
Park VFD). But consider that anyone responding to your question here
cannot be aware of all pertinent circumstances such as possible
derating requirements for high ambient temperature or more than 3
current carrying conductors in a conduit, which a competent local
electrical designer would take into consideration, as well as
considering the length of the wiring run and resulting voltage drop.

Since you did not seem to understand the very basic fact that the 90 C
wire ampacity rating is provided only to allow for various derating
requirements, and the usable ampacity cannot exceed the rating for the
conductor at the max temp ratings of the connections at either end
(probably 75 C max for your circuit breaker, which will be labeled
with temp rating), I suggest you find a competent local electrical
designer or inspector to examine your installation. The $100 or so
could save a lot more in the long run.

  #2   Report Post  
Fred Bloggs
 
Posts: n/a
Default Commercial mains wiring: 12ga wire for 30 amp load?



Glen Walpert wrote:
On Thu, 10 Nov 2005 22:40:32 -0800, Esther & Fester Bestertester
wrote:


Thus spake :


You have 2 issues. Foiust, is the motor supposed to be running on 230
or 208? That couild be the extra current.
If the motor is really exceeding the nameplate amps I would
investigate futher.


Nameplate: 230V, 16.5A.

I presume that if an autotransformer boosts the voltage
10%, it must draw 10%(?) more current in order to do so. Is
this correct? (Nothing is free.)
FBt



Correct, except that there will also be an additional bit of current
draw due to losses in the autotransformer, which will probably be over
95% efficient:

For 208V in, 230V out at 16.5A out to motor and 95% autotransformer
efficiency:

Iin = (16.5*(230/208))/.95 = 19.2A

Which is slightly under your measured 20A, which indicates that you
are running slightly over 100% load on your motor if my voltage
guesses are right. Hopefully the nameplate service factor is at least
1.15 continuous (if the motor runs continuously).

BTW congratulations on responding to one of only 2 posters who
understand your situation (the other being Tom Horne of the Tacoma
Park VFD). But consider that anyone responding to your question here
cannot be aware of all pertinent circumstances such as possible
derating requirements for high ambient temperature or more than 3
current carrying conductors in a conduit, which a competent local
electrical designer would take into consideration, as well as
considering the length of the wiring run and resulting voltage drop.

Since you did not seem to understand the very basic fact that the 90 C
wire ampacity rating is provided only to allow for various derating
requirements, and the usable ampacity cannot exceed the rating for the
conductor at the max temp ratings of the connections at either end
(probably 75 C max for your circuit breaker, which will be labeled
with temp rating), I suggest you find a competent local electrical
designer or inspector to examine your installation. The $100 or so
could save a lot more in the long run.


Since he went with an autotransformer, he should derate the wiring for
NEC "general use" and that puts 12ga THHN at 20A. He needs to reinstall
at 10ga- maybe- depending on circuit run length. 10ga would be good for
up to 100', 8ga would be recommended for over 150', 6ga for up to 300'
etc at 2.5% voltage drop..This may explain why he went with an
autotransformer- burned the old motor out with overload at low voltage
and upped the breaker from 20A motor time delay to 30A to eliminate LRA
trips. He should therefore reinstall the 20A breaker with the 10ga or
larger and get rid of the autotransformer unless the motor specifically
calls out 230V which is rare these days.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using Splicers and Tap Connectors with Aluminum Wiring instead of Twist On Wire Nuts? Harry Muscle Home Repair 7 October 28th 05 09:01 PM
Grounding Rodney Kelp Electronics Repair 43 December 6th 04 01:39 AM
Wiring Ring mains to MCBs in consumer units jamie T UK diy 12 May 29th 04 09:08 AM
Wiring mains smoke alarms David Robinson UK diy 17 December 10th 03 03:11 PM