On 2/27/20 12:44 AM, Jeff Urban wrote:
You do not need another breaker for the pump if the one
in the house is properly rated. However for lights and
outlets you do.


As usual, you are wrong.

You put a breaker at the source (service panel) to protect
the line running to the pump.
You are required to have a disconnect AT the pump. Another
breaker in a sub panel for the pump/well house is the
easiest way to accomplish that.

As I said previously, and using a 30 amp service to the
pump as an example.

1. 30 amp dual breaker for a 10-3 run to the pump.
2. A four slot sub panel (rated at 30 amps minimum) at the
pump.
3. A 30 amp dual breaker for the pump.
4. An additional 20 amp single for any outlets.
5. And a 15-20 Amp breaker for any lighting circuit.

If the pump motor is electrically connected to the well
casing, do NOT ground it through the ground from the service
panel. Use the service panel for the grounds on the outlet
and lighting circuits only.

It's NOT that complicated people.
Try not to make it complicated or unsafe.


--