On 10/02/2019 21:26, John Rumm wrote:
On 07/02/2019 19:17, wrote:
On 07/02/2019 18:50, Cynic wrote:
I've not got tables to hand but check your earth loop impedance
against disconnection times for the 40A mcb

The sub-main earth loop impedance (20m of 10mm2 and 20m of 16mm2)
should be about 60mOhm (37mOhm + 23mOhm) so about 0.4 ohms total
(TN-C-S) - about 600A fault current. A type C MCB needs 10x rated
current, so 500A for a 50A MCB. Unless I've boobed it should be OK.



I think I must be missing something here... where does the 20m of 10mm^2
come into this?

Sadly, it was me that was missing something - I'd forgotten about the
extg CPC being in parallel with the new single. I must be getting old.

Looking at just the submain as it currently stands:

16mm^2 T&E has a round trip resistance live + CPC of 4.23 mOhms/meter
[1], so that is a contribution of 85 mOhms.

If we are going with the standard estimate of 0.35 Ohms for the supply
impedance (in the absence of a measurement), that gives a total Zs of
0.435 Ohms. So just inside the limit for a 50A Type C using the new cMin
adjusted max ELI factors[2].

So a prospective fault current of 230 / 0.435 = 525A, adequate to trip
in the instant part of the curve.

Now if you increase the CPC size to 16mm^2 with the addition of a 10mm^2
single, then the situation improves further?