Ouch! The PressureTrol on Most steam boilers should be set per another
reply with 0.5 psi cut-in and 1 psi rising differential cut-out (or if it
does not go down to 0.5 it may be a control that you set to 2 psi cut-out
and 1 psi decreasing differential cut-in). In other words it should
operate between 0.5 and 1.5 psi (not more than about 2 psi). Systems with
a Vaporstat run even lower (in ounces of pressure).


Depends on the system. I have a low pressure setup that runs between 5#
and 9# with a cutout at 11#. I also operate two boilers at 110# with
cutout at 120#. They modulate depending on load. We use about 8 to 10,000
gallons of water a day to make steam.