Hi there,

I have a Vaillant Combi boiler (according to hte manual, it is eithera VCW
GB 221H , 240H or 280H - Im afraid I cant find any indication on the boiler
itself).

Over the past couple of weeks, I have noticed that although the boiler is on
for central heating, the thermostat in hall seems to indicate the acutal
temperature is lower than the set temperature by several degrees. I do this
by listening for the click on the thermostat so I know it isnt incredibly
accurate. In addition, the radiators are reasonably warm.

However, today on furhter investigation, I did notice that the pressure
gauge on the boiler is indicating just below the first mark on the gauge
which I think is 0.5bar. The instrucitons indicate that the pressure should
be around 1bar.

According to the manual (and fairly obvious to even my limited knowledge)
the water pressure needs topping up. The instruictions I have recommedn
getting a plumber to do this but I dont fancy paying someone good money to
do something that is probably straight forward (I have done this on a boiler
at a previous house). The isntructions dont mention which is the correct
valve for water inlet.

Can anyone tell me which is the correct valve to open and whether this could
cause the symptoms I am seeing ?

Thanks

Tim


  #2   Report Post  
andrewpreece
 
Posts: n/a
Default


"Tim Smith" wrote in message
...
Hi there,

I have a Vaillant Combi boiler (according to hte manual, it is eithera VCW
GB 221H , 240H or 280H - Im afraid I cant find any indication on the

boiler
itself).

Over the past couple of weeks, I have noticed that although the boiler is

on
for central heating, the thermostat in hall seems to indicate the acutal
temperature is lower than the set temperature by several degrees. I do

this
by listening for the click on the thermostat so I know it isnt incredibly
accurate. In addition, the radiators are reasonably warm.

However, today on furhter investigation, I did notice that the pressure
gauge on the boiler is indicating just below the first mark on the gauge
which I think is 0.5bar. The instrucitons indicate that the pressure

should
be around 1bar.

According to the manual (and fairly obvious to even my limited knowledge)
the water pressure needs topping up. The instruictions I have recommedn
getting a plumber to do this but I dont fancy paying someone good money to
do something that is probably straight forward (I have done this on a

boiler
at a previous house). The isntructions dont mention which is the correct
valve for water inlet.

Can anyone tell me which is the correct valve to open and whether this

could
cause the symptoms I am seeing ?

Thanks

Tim



I had a Vaillant 242: in that case the filling loop was a length of braided
flexible pipe, with one end going to the cold water inlet pipe. There were
two knurled plastic knobs on valves at each end of the pipe, and you had to
open both in order to get water flowing in ( I think it is two valves to
prevent back-contamination of the domestic water supply by pressurised water
flowing back from the boiler ). I believe you have to open them in a
particular order, though offhand I can't remember what order it is!

Your cold water inlet pipe, should be fairly easily identifiable as it will
be 15mm and will be cold to the touch, if the HW and CH are or have been in
recent use ( the gas pipe is 15mm but not so cold ). Anyway, that's my best
to offer on the subject, perhaps someone with knowledge of the exact model
can be more helpful. Oh, by the way, if your system pressure keeps falling,
get it looked at, as continually topping the system up leads to corrosion
and early failure.

Andy.


  #3   Report Post  
Tim Smith
 
Posts: n/a
Default


"andrewpreece" wrote in message
...

"Tim Smith" wrote in message
...
Hi there,

I have a Vaillant Combi boiler (according to hte manual, it is eithera

VCW
GB 221H , 240H or 280H - Im afraid I cant find any indication on the

boiler
itself).

Over the past couple of weeks, I have noticed that although the boiler

is
on
for central heating, the thermostat in hall seems to indicate the acutal
temperature is lower than the set temperature by several degrees. I do

this
by listening for the click on the thermostat so I know it isnt

incredibly
accurate. In addition, the radiators are reasonably warm.

However, today on furhter investigation, I did notice that the pressure
gauge on the boiler is indicating just below the first mark on the gauge
which I think is 0.5bar. The instrucitons indicate that the pressure

should
be around 1bar.

According to the manual (and fairly obvious to even my limited

knowledge)
the water pressure needs topping up. The instruictions I have recommedn
getting a plumber to do this but I dont fancy paying someone good money

to
do something that is probably straight forward (I have done this on a

boiler
at a previous house). The isntructions dont mention which is the correct
valve for water inlet.

Can anyone tell me which is the correct valve to open and whether this

could
cause the symptoms I am seeing ?

Thanks

Tim



I had a Vaillant 242: in that case the filling loop was a length of

braided
flexible pipe, with one end going to the cold water inlet pipe. There were
two knurled plastic knobs on valves at each end of the pipe, and you had

to
open both in order to get water flowing in ( I think it is two valves to
prevent back-contamination of the domestic water supply by pressurised wat

er
flowing back from the boiler ). I believe you have to open them in a
particular order, though offhand I can't remember what order it is!

Your cold water inlet pipe, should be fairly easily identifiable as it

will
be 15mm and will be cold to the touch, if the HW and CH are or have been

in
recent use ( the gas pipe is 15mm but not so cold ). Anyway, that's my

best
to offer on the subject, perhaps someone with knowledge of the exact model
can be more helpful. Oh, by the way, if your system pressure keeps

falling,
get it looked at, as continually topping the system up leads to corrosion
and early failure.

Andy.

Thanks Andy,

I think I have identified the cold water inlet - as you say it is cold ! It
also has a T-joint. One side goes into the boiler (presumably for the
ho****er) and the other (via a braided pipe and two valves) connects to a
hot pipe. I guess this is teh connection into the sealed heating "circuit".

Anyone any idea which order the valves should be opened in ? I guess they
could be defined as the valve at the ho****er "circuit" end and the valve at
the end cold supply end.

Thanks again.

Tim


  #4   Report Post  
Junior Member
 
Posts: 1
Unhappy

Quote:
Originally Posted by Tim Smith
Hi there,

....................
According to the manual (and fairly obvious to even my limited knowledge)
the water pressure needs topping up. The instruictions I have recommedn
getting a plumber to do this but I dont fancy paying someone good money to
do something that is probably straight forward (I have done this on a boiler
at a previous house). The isntructions dont mention which is the correct
valve for water inlet.

Can anyone tell me which is the correct valve to open and whether this could
cause the symptoms I am seeing ?

Thanks

Tim
Funny old thing, I have exactly the same problem. My instructions reckon there should be a filling line somewhere on the central heating return line. But I have looked high and low and cannot find on. I was wondering if there is an auto fill mechanism, but cannot find it. To be honest the boiler was running ok, but I got a bit nervous running it when the pressure reads dead zero. Maybe this setup is geared around getting plumbers more work??
  #5   Report Post  
andrewpreece
 
Posts: n/a
Default


"Tim Smith" wrote in message
...

"andrewpreece" wrote in message
...

"Tim Smith" wrote in message
...
Hi there,

I have a Vaillant Combi boiler (according to hte manual, it is eithera

VCW
GB 221H , 240H or 280H - Im afraid I cant find any indication on the

boiler
itself).

Over the past couple of weeks, I have noticed that although the boiler

is
on
for central heating, the thermostat in hall seems to indicate the

acutal
temperature is lower than the set temperature by several degrees. I do

this
by listening for the click on the thermostat so I know it isnt

incredibly
accurate. In addition, the radiators are reasonably warm.

However, today on furhter investigation, I did notice that the

pressure
gauge on the boiler is indicating just below the first mark on the

gauge
which I think is 0.5bar. The instrucitons indicate that the pressure

should
be around 1bar.

According to the manual (and fairly obvious to even my limited

knowledge)
the water pressure needs topping up. The instruictions I have

recommedn
getting a plumber to do this but I dont fancy paying someone good

money
to
do something that is probably straight forward (I have done this on a

boiler
at a previous house). The isntructions dont mention which is the

correct
valve for water inlet.

Can anyone tell me which is the correct valve to open and whether this

could
cause the symptoms I am seeing ?

Thanks

Tim



I had a Vaillant 242: in that case the filling loop was a length of

braided
flexible pipe, with one end going to the cold water inlet pipe. There

were
two knurled plastic knobs on valves at each end of the pipe, and you had

to
open both in order to get water flowing in ( I think it is two valves to
prevent back-contamination of the domestic water supply by pressurised

wat
er
flowing back from the boiler ). I believe you have to open them in a
particular order, though offhand I can't remember what order it is!

Your cold water inlet pipe, should be fairly easily identifiable as it

will
be 15mm and will be cold to the touch, if the HW and CH are or have been

in
recent use ( the gas pipe is 15mm but not so cold ). Anyway, that's my

best
to offer on the subject, perhaps someone with knowledge of the exact

model
can be more helpful. Oh, by the way, if your system pressure keeps

falling,
get it looked at, as continually topping the system up leads to

corrosion
and early failure.

Andy.

Thanks Andy,

I think I have identified the cold water inlet - as you say it is cold !

It
also has a T-joint. One side goes into the boiler (presumably for the
ho****er) and the other (via a braided pipe and two valves) connects to a
hot pipe. I guess this is teh connection into the sealed heating

"circuit".

Anyone any idea which order the valves should be opened in ? I guess they
could be defined as the valve at the ho****er "circuit" end and the valve

at
the end cold supply end.

Thanks again.

Tim


I'm not too sure that it is necessary to open them in a particular order,
thinking about it: the fact is, if you crack them both open your system will
pressurise. I may be getting confused. These filling loops have a valve at
each end so that you can disconnect them when you're finished - not that a
lot of people bother! The theory is that either yucky combi water will
feedback into the mains water if there is a leak in the filling valves/you
don't turn them off properly, or that if the mains pressure exceeds that in
your combi ( which it should do anyway ) that the system will sowly
pressurise from the mains. Once it reaches 3 atmospheres the pressure relief
valve will blow off and dump a lot of your CH system water out of the
blow-off pipe ( the blow off pipe probably exits via your wall somewhere -
it would pay to keep an eye on this pipe especially when the CH turns on of
an evening to see if it is blowing off ).

Anyway, given that you are supposed to remove the filling pipe once finished
with it, you can see that it needs a valve either end or you would have a
gusher, either from the mains cold water end, or the CH loop end. So, ignore
the fact that I talked about an order to things, and just crack both the
valves open slowly. You'll want about 1 to 1.5 bar pressure in the system.
You may have a leak in the pipework, or a punctured diaphragm in your
pressure relief vessel ( big red doughnut shaped thingy, at the back of the
combi somewhere ), if you coninue to lose pressure,

Andy.




  #6   Report Post  
Tim Smith
 
Posts: n/a
Default


"rogersmp" wrote in message
...

Tim Smith Wrote:
Hi there,

....................
According to the manual (and fairly obvious to even my limited
knowledge)
the water pressure needs topping up. The instruictions I have
recommedn
getting a plumber to do this but I dont fancy paying someone good money
to
do something that is probably straight forward (I have done this on a
boiler
at a previous house). The isntructions dont mention which is the
correct
valve for water inlet.

Can anyone tell me which is the correct valve to open and whether this
could
cause the symptoms I am seeing ?

Thanks

Tim


Funny old thing, I have exactly the same problem. My instructions
reckon there should be a filling line somewhere on the central heating
return line. But I have looked high and low and cannot find on. I was
wondering if there is an auto fill mechanism, but cannot find it. To be
honest the boiler was running ok, but I got a bit nervous running it
when the pressure reads dead zero. Maybe this setup is geared around
getting plumbers more work??


--
rogersmp



Roger,

When you say you have the same problem, do you mean pressure at zero or lack
of temperature (tested in my rahter unscientific manner) or even both ?

Tim


  #7   Report Post  
andrewpreece
 
Posts: n/a
Default


"rogersmp" wrote in message
...

Tim Smith Wrote:
Hi there,

....................
According to the manual (and fairly obvious to even my limited
knowledge)
the water pressure needs topping up. The instruictions I have
recommedn
getting a plumber to do this but I dont fancy paying someone good money
to
do something that is probably straight forward (I have done this on a
boiler
at a previous house). The isntructions dont mention which is the
correct
valve for water inlet.

Can anyone tell me which is the correct valve to open and whether this
could
cause the symptoms I am seeing ?

Thanks

Tim


Funny old thing, I have exactly the same problem. My instructions
reckon there should be a filling line somewhere on the central heating
return line. But I have looked high and low and cannot find on. I was
wondering if there is an auto fill mechanism, but cannot find it. To be
honest the boiler was running ok, but I got a bit nervous running it
when the pressure reads dead zero. Maybe this setup is geared around
getting plumbers more work??


--
rogersmp


Has your filling loop been removed? They are really supposed to be removed
once you've topped up the system. There will still be a connection point on
the coldwater pipe and the CH return ( or flow? ). Some combis have built in
filling loops: my Vaillant has two valves built into the underside of the
casing, it takes two special little keys to open or shut the valves. It's
all very inconspicuous.

Andy.


  #8   Report Post  
Tim Smith
 
Posts: n/a
Default


"andrewpreece" wrote in message
...

"rogersmp" wrote in message
...

Tim Smith Wrote:
Hi there,

....................
According to the manual (and fairly obvious to even my limited
knowledge)
the water pressure needs topping up. The instruictions I have
recommedn
getting a plumber to do this but I dont fancy paying someone good

money
to
do something that is probably straight forward (I have done this on a
boiler
at a previous house). The isntructions dont mention which is the
correct
valve for water inlet.

Can anyone tell me which is the correct valve to open and whether this
could
cause the symptoms I am seeing ?

Thanks

Tim


Funny old thing, I have exactly the same problem. My instructions
reckon there should be a filling line somewhere on the central heating
return line. But I have looked high and low and cannot find on. I was
wondering if there is an auto fill mechanism, but cannot find it. To be
honest the boiler was running ok, but I got a bit nervous running it
when the pressure reads dead zero. Maybe this setup is geared around
getting plumbers more work??


--
rogersmp


Has your filling loop been removed? They are really supposed to be removed
once you've topped up the system. There will still be a connection point

on
the coldwater pipe and the CH return ( or flow? ). Some combis have built

in
filling loops: my Vaillant has two valves built into the underside of the
casing, it takes two special little keys to open or shut the valves. It's
all very inconspicuous.

Andy.



Thanks all,

I took the plunge at opened the valves and the pressure increased on the
gauge. Ill keep an eye on it and see if the heating is any better and if the
pressure drops again.

Thanks

Tim


  #9   Report Post  
Ed Sirett
 
Posts: n/a
Default

On Thu, 06 Jan 2005 22:06:33 +0000, andrewpreece wrote:


p

Has your filling loop been removed? They are really supposed to be removed
once you've topped up the system. There will still be a connection point on
the coldwater pipe and the CH return ( or flow? ). Some combis have built in
filling loops: my Vaillant has two valves built into the underside of the
casing, it takes two special little keys to open or shut the valves. It's
all very inconspicuous.

You must have a Eco/Turbomax/Thermocompact Plus model. About 5 years old
or less.
The OP has something from about 10-20 years ago.

--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


  #10   Report Post  
andrewpreece
 
Posts: n/a
Default


"Ed Sirett" wrote in message
news
On Thu, 06 Jan 2005 22:06:33 +0000, andrewpreece wrote:


p

Has your filling loop been removed? They are really supposed to be

removed
once you've topped up the system. There will still be a connection point

on
the coldwater pipe and the CH return ( or flow? ). Some combis have

built in
filling loops: my Vaillant has two valves built into the underside of

the
casing, it takes two special little keys to open or shut the valves.

It's
all very inconspicuous.

You must have a Eco/Turbomax/Thermocompact Plus model. About 5 years old
or less.
The OP has something from about 10-20 years ago.


Yes, that's right, it's a Turbomax. Ed, we talked a while back when I was
concerned that the HW from my Turbomax was hotter than I had it set when I
installed it, yet I hadn't touched the HW temperature control: I was miffed
because the Turbomax gives the impression from the display that the HW can
be set to an exact temperature. I spent an entire day faultfinding and
decided something must be broken, but I've come to the conclusion it's OK
after all. I reckon the Turbomax only controls the CH loop temperature, and
the HW temperature is determined by both the CH loop temperature and the
temperature of the water as it enters from the ground.
When I was concerned about the HW being hotter than I'd set it, a few
months back, the ground-water temperature was 16C, about as warm as it gets!
I shall have to twiddle the dial a few times a year to keep the HW
temperature constant at the taps, but that's no big deal, now that I know,

Andy.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
new combi experience report Fred UK diy 12 December 5th 04 09:11 PM
Vaillant Combi Boiler Issue Dave Clark UK diy 7 March 6th 04 02:02 AM
Vaillant Aquaplus storage combi boiler Ben Mack UK diy 2 January 20th 04 01:24 PM
New Combi boiler GB UK diy 7 September 7th 03 11:34 PM
Vaillant Combi Boiler Ed Sirett UK diy 5 July 31st 03 08:52 PM


All times are GMT +1. The time now is 01:13 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"