UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Jerry.
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...

Anyone know of any issues with Honeywell 3 port mid position valves, i.e.
installation, location or in service problems etc., I've had three or four
go faulty in the last 4 years since the system (and I hasten to add) was
professionally installed and it sounds like I might be approaching another !

It's either been problems with the valve it's self or the motor drive not
operating (opening the required port(s)) and thus causing the boiler to
overheat and cut out due to there being no flow - and causing hot water and
steam to be forced up into the boiler feed / expansion tank :~(


  #2   Report Post  
Lurch
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...

On Sun, 15 Feb 2004 22:17:23 -0000, "Jerry."
wrote:

Anyone know of any issues with Honeywell 3 port mid position valves, i.e.
installation, location or in service problems etc., I've had three or four
go faulty in the last 4 years since the system (and I hasten to add) was
professionally installed and it sounds like I might be approaching another !

It's either been problems with the valve it's self or the motor drive not
operating (opening the required port(s)) and thus causing the boiler to
overheat and cut out due to there being no flow - and causing hot water and
steam to be forced up into the boiler feed / expansion tank :~(

I've never come across a problem with them, at least not the way you
say, they'll normally go on for years. It sounds as if it's not been
installed correctly. Check the honywell site for your valve and have a
look at the technical specs and data sheet.
http://tinyurl.com/2ohlc
...

SJW
A.C.S. Ltd.
  #3   Report Post  
Peter
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...

Should be very reliable though motor life varies dramatically with
temperature. Do you have unusually high ambient/flow temperatures or high
spec supply voltage?
Otherwise I have seen the rubber 'ball' which directs the flow to have
swollen for some reason, something in the system water assumedly. As you
describe a complete blocking of the flow which normally could not happen
with a three port valve, this could be the case. Perhaps you could do a
complete drain and flush next time, or maybe Honeywell would be interested
in examining your valve.
"Jerry." wrote in message
...
Anyone know of any issues with Honeywell 3 port mid position valves, i.e.
installation, location or in service problems etc., I've had three or four
go faulty in the last 4 years since the system (and I hasten to add) was
professionally installed and it sounds like I might be approaching another

!

It's either been problems with the valve it's self or the motor drive not
operating (opening the required port(s)) and thus causing the boiler to
overheat and cut out due to there being no flow - and causing hot water

and
steam to be forced up into the boiler feed / expansion tank :~(




  #4   Report Post  
Jerry.
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...


"Peter" wrote in message
...
snip

[ re subject line ]
Should be very reliable though motor life varies dramatically with
temperature. Do you have unusually high ambient/flow temperatures or high
spec supply voltage?


Well it was installed in a loft, on the east aspect and the problems this
time started after a couple of (relatively) deep overnight frosts.... Hummm
!

Otherwise I have seen the rubber 'ball' which directs the flow to have
swollen for some reason, something in the system water assumedly. As you
describe a complete blocking of the flow which normally could not happen
with a three port valve, this could be the case. Perhaps you could do a
complete drain and flush next time, or maybe Honeywell would be interested
in examining your valve.


One more question, would one expect a symphonic flow if there was a complete
pump failure but the ports on the above valve had opened IYSWIM ?


  #5   Report Post  
Lurch
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...

One more question, would one expect a symphonic flow if there was a complete
pump failure but the ports on the above valve had opened IYSWIM ?

Is that making music with water?
...

SJW
A.C.S. Ltd.


  #6   Report Post  
Lurch
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...

On Mon, 16 Feb 2004 08:49:44 -0000, "Jerry."
wrote:
Should be very reliable though motor life varies dramatically with
temperature. Do you have unusually high ambient/flow temperatures or high
spec supply voltage?


Well it was installed in a loft, on the east aspect and the problems this
time started after a couple of (relatively) deep overnight frosts.... Hummm
!

With the proper frost protection?
...

SJW
A.C.S. Ltd.
  #7   Report Post  
Jerry.
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...


"Lurch" wrote in message
...
One more question, would one expect a symphonic flow if there was a

complete
pump failure but the ports on the above valve had opened IYSWIM ?

Is that making music with water?


Not sure what you mean by that, but if you mean making steam, hammer blow
type sounds, and forcing water up into the feed / expansion tank, YES :~(

One pipe form the boiler is VERY hot (can't touch it for more than a second
or two) and the other is not more than warm. This morning there was not heat
in any radiator and the HW hasn't been re heated....


  #8   Report Post  
Jerry.
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...


"Lurch" wrote in message
...
On Mon, 16 Feb 2004 08:49:44 -0000, "Jerry."
wrote:
Should be very reliable though motor life varies dramatically with
temperature. Do you have unusually high ambient/flow temperatures or

high
spec supply voltage?


Well it was installed in a loft, on the east aspect and the problems this
time started after a couple of (relatively) deep overnight frosts....

Hummm
!

With the proper frost protection?


Well it doesn't seem to have any type of frost stat if that is what you
mean.

Even more Ho Hummms...


  #9   Report Post  
Lurch
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...

On Mon, 16 Feb 2004 09:35:02 -0000, "Jerry."
wrote:


"Lurch" wrote in message
...
One more question, would one expect a symphonic flow if there was a

complete
pump failure but the ports on the above valve had opened IYSWIM ?

Is that making music with water?


Not sure what you mean by that, but if you mean making steam, hammer blow
type sounds, and forcing water up into the feed / expansion tank, YES :~(

One pipe form the boiler is VERY hot (can't touch it for more than a second
or two) and the other is not more than warm. This morning there was not heat
in any radiator and the HW hasn't been re heated....

Sorry, obviously not everyone has my sense of humour, look at
'symphonic flow'.
...

SJW
A.C.S. Ltd.
  #10   Report Post  
Lurch
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...

On Mon, 16 Feb 2004 09:36:36 -0000, "Jerry."
wrote:


"Lurch" wrote in message
...
On Mon, 16 Feb 2004 08:49:44 -0000, "Jerry."
wrote:
Should be very reliable though motor life varies dramatically with
temperature. Do you have unusually high ambient/flow temperatures or

high
spec supply voltage?

Well it was installed in a loft, on the east aspect and the problems this
time started after a couple of (relatively) deep overnight frosts....

Hummm
!

With the proper frost protection?


Well it doesn't seem to have any type of frost stat if that is what you
mean.

Even more Ho Hummms...

I think it would be recommended to fit a frost protection kit to the
components in the loft. Assuming the boiler is in the loft also you
want a wall mounted frost stat by the boiler and a pipe stat on the
return, connected in series across the permanent live feed and the
trigger wire on the valve, usually the brown.
...

SJW
A.C.S. Ltd.


  #11   Report Post  
Jerry.
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...


"Lurch" wrote in message
...
On Mon, 16 Feb 2004 09:35:02 -0000, "Jerry."
wrote:

snip
Sorry, obviously not everyone has my sense of humour, look at
'symphonic flow'.
..


Oh right, I was a bit short on humour this morning....


  #12   Report Post  
Phil Nettleton
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...


"Jerry." wrote in message
...
Anyone know of any issues with Honeywell 3 port mid position valves, i.e.
installation, location or in service problems etc., I've had three or four
go faulty in the last 4 years since the system (and I hasten to add) was
professionally installed and it sounds like I might be approaching another

!

It's either been problems with the valve it's self or the motor drive not
operating (opening the required port(s)) and thus causing the boiler to
overheat and cut out due to there being no flow - and causing hot water

and
steam to be forced up into the boiler feed / expansion tank :~(


this last part dosnt make sense as the valve will never shut both ports no
flow will be caused by a pump failure
if the valve is not powered the hw port is open if it is the ch port will
open or a blockage in the system
phil n


  #13   Report Post  
Set Square
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...

In an earlier contribution to this discussion,
Phil Nettleton wrote:

"Jerry." wrote in message
...
Anyone know of any issues with Honeywell 3 port mid position
valves, i.e. installation, location or in service problems etc.,
I've had three or four go faulty in the last 4 years since the
system (and I hasten to add) was professionally installed and it
sounds like I might be approaching another !

It's either been problems with the valve it's self or the motor
drive not operating (opening the required port(s)) and thus causing
the boiler to overheat and cut out due to there being no flow - and
causing hot water and steam to be forced up into the boiler feed /
expansion tank :~(


this last part dosnt make sense as the valve will never shut both
ports no flow will be caused by a pump failure
if the valve is not powered the hw port is open if it is the ch port
will open or a blockage in the system
phil n



I agree entirely. Unlike using two 2-port valves - which can both be closed
at the same time - the 3-port valve doesn't have a position which shuts off
all the flow, and is unlikely to be the cause of your current problems. The
water always has somewhere to go unless all your radiators have TRVs on them
and they are all shut. If this *is* the case, you need to make some design
changes to the system!

It is far more likely that your lack of flow is due to problems with the
pump. How is this wired - is it simply wired in parallel with the boiler or
is it connected to the boiler's pump-over-run connection?
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is Black Hole!


  #14   Report Post  
Jerry.
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...


"Set Square" wrote in message
...
snip

It is far more likely that your lack of flow is due to problems with the
pump. How is this wired - is it simply wired in parallel with the boiler

or
is it connected to the boiler's pump-over-run connection?
--


Yes the pump is connected via a pump-over-run connection. It's looking like
a defective sensor on the boiler, there is no electrical feed to pump.

I starting to suspect this / might / have been the (intermittent) fault
since the boiler was first installed and not the three position valve.......

Thanks to all for the replies.


  #15   Report Post  
Set Square
 
Posts: n/a
Default Honeywell 3 port mid position valve - problems with...

In an earlier contribution to this discussion,
Jerry. wrote:

"Set Square" wrote in message
...
snip

It is far more likely that your lack of flow is due to problems with
the pump. How is this wired - is it simply wired in parallel with
the boiler or is it connected to the boiler's pump-over-run
connection? --


Yes the pump is connected via a pump-over-run connection. It's
looking like a defective sensor on the boiler, there is no electrical
feed to pump.

I starting to suspect this / might / have been the (intermittent)
fault since the boiler was first installed and not the three position
valve.......

Thanks to all for the replies.



You *have* got a permanent live feed to the boiler in addition to the
switched live, haven't you? Without this, the pump won't over-run - but it
will still run when the switched live (coming from the programmer and/or
room stat) is on.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is Black Hole!


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
NO HW NO CH, Honeywell diverter valve Clive Long,UK UK diy 6 October 7th 03 05:03 PM
Danfoss Control Box wiring - with one single 2 port valve Gavin Adam UK diy 4 October 6th 03 09:06 PM
Mid-Position 3 Port Valve - Hot Water (A) position & OFF - but HW flow to boiler? Clivedodd UK diy 3 September 9th 03 01:53 AM
Leaving a Honeywell CH valve energised, wiring choices Toby UK diy 1 July 14th 03 07:20 PM