I am in the process of renovating a house and intend to re-wire the whole
building & install a new consumer unit. Fixed appliances likely to be
installed include an electric cooker, boiler, water softener, waste
disposal, central heating pump, shower pump, fire alarms, security sensors.
There will also be an outside socket in the garden shed.

The house has three floors and an extension. I want to choose a CU that
gives me enough MCB/RCBO slots for all the circuits, plus some spare for the
future.

I suspect that my two areas of ignorance (below) have been discussed at
length on this newsgroup, although I can't find any information at
http://www.diyfaq.org.uk/electrical.html. So I wonder if someone could
kindly point me to threads or website links that cover the following:

A. The typical electrical circuits to be found in a house (e.g. 2 x ring
mains, 2 x lighting, 1 x cooker etc...). I want to find a list of appliances
that would have their own circuit protection.

B. The relative merits of RCDs and RCBOs.

Thanks in advance for your assistance.




  #2   Report Post  
Christian McArdle
 
Posts: n/a
Default Typical domestic electrical circuits

A. The typical electrical circuits to be found in a house (e.g. 2 x ring
mains, 2 x lighting, 1 x cooker etc...). I want to find a list of

appliances
that would have their own circuit protection.


Technically, you have a maximum of 100m2 for a ring circuit. However, it is
better to anticipate the likely load and use this as maximum. In particular,
a well stocked kitchen often has more equipment than should be installed on
a single ring main, especially if, like me, you cycle the machines all
simultaneously whilst cooking.

As an example, my house has the following circuits installed into a 16
outgoing way Contactum CU. TN-S earthing, 100A DP switch incomer. (60A
cutout). RCBOs are double width, as they were the cheapest Type B RCBOs I
could find.

1. B32A/0.03 RCBO. Ring main for entire house except kitchen. (May split
into two RCBO circuits in future when loft conversion built).

2. B32A/0.03 RCBO. Ring main for kitchen. (including 2.2kW dual fuel cooker)

3. B32A/0.03 RCBO. External electrics (outside socket, outside lighting,
future shed supply)

4. B32A MCB. Radial circuit for kitchen fixed integrated appliances.
(dishwasher, washing machine, dryer) remotely switched sockets concealed
under worktop.

5. B16A MCB. Radial circuit for fridge/freezer only. Reduces risk of
defrosting, as only a fault on that circuit, or the main service fuse will
cut the power.

6. B16A MCB. Heating system. (Immersion, central heating, heat bank).

7. B6A MCB. Most of house lighting circuit.

8. B6A MCB. New lighting circuit (kitchen only currently)

9. B6A MCB. Alarms (Interlinked smoke/heat detectors + intruder alarm)

If I had an electric hob, there would be a separate B32A MCB circuit for it.
When I moved in, the house had 3 operational circuits, a single ring main, a
single lighting circuit and a cooker circuit used solely to power the skanky
fridge freezer they left behind, as only 2 double sockets were installed in
the entire kitchen.

If designing from scratch, rather than upgrading the previously stingy, but
safe and well executed system, I would use at least two lighting circuits.
It is traditional to do upstairs/downstairs split. However, I would prefer
to randomise the circuits, so in the event of the MCB popping, a nearby
light will work. It does have the disadvantage that someone might assume the
upstairs/downstairs thing and work on a live circuit, though. Quite frankly,
if you make assumptions like those, a quick jolt could help you change your
attitude!

I would also split the rest of the house ring main into two. However, there
is no real reason to change my preexisting circuit. It comes well within the
100m2 requirement. Loading is likely to be very light, with no fixed
appliances or heating loads expected. The major requirement is during a gas
failure, where I might use up to around 5kW of electric heating. My entire
house heating requirement at -3C outside is only 8kW, so it would be
difficult to blow the ring using thermostatically controlled heaters anyway.

B. The relative merits of RCDs and RCBOs.


30mA RCD (whole house) = BAD!!!

30mA RCD (split load) = Much cheaper than RCBOs

30mA RCBO = Much less prone to nuisance tripping. Tripping has fewer
consequences. Warm feeling of having done it right.

Obviously, if a TT earthing system, the 100A DP incomer switch should be
exchanged for a 100A/100mA time delay RCD. The use of split load RCD/RCBO
would remain exactly the same, though. If I had such a system, I would also
consider using an RCBO on the kitchen radial, to prevent any earth leakage
in the kitchen fixed appliance heating elements taking out my lighting and
heating.

As for your list of appliances:

electric cooker = Own dedicated circuit on B32A MCB. Do not install cooker
unit with built in socket. They look bad and trail leads over the cooker.

boiler = put on a dedicated central heating circuit MCB (not RCBO). Can
share with immersion, especially if sharing controls, such as programmers.
All central heating valves, programmers and other controls should be from
the same central heating circuit. The CH side (as opposed to the immersion)
should be fused down to 3A, either internally in the boiler or in a separate
FCU. If there is no immersion on this circuit, use a B3A MCB instead, and a
DP switch to isolate the entire circuit next to the boiler.

water softener = 3A FCU off nearby ring main/kitchen fixed appliance radial.
Some softeners don't require electrical supply.

waste disposal = 3A FCU (or as advised in installation instructions) off
nearby ring main/kitchen fixed appliance radial

central heating pump = off same circuit as boiler. Will be internal to
boiler, or connected directly to it in a modern system.

fire alarms = either wire from a regularly used lighting circuit, or give
own small radial circuit (i.e. B6A or B3A MCB).

outside socket in the garden shed = separate RCBO circuit only shared with
other outside electrics. DO NOT spur from internal socket circuits. DO NOT
share the RCD/RCBO with any other circuit or appliances. The outside socket
should be off a 13A DP switched FCU rather than directly on the radial. This
enables you to turn it off inside, preventing nuisance RCD trips and
electricity theft.

Christian.


  #3   Report Post  
Andrew Gabriel
 
Posts: n/a
Default Typical domestic electrical circuits

In article ,
"Christian McArdle" writes:

As an example, my house has the following circuits installed into a 16
outgoing way Contactum CU. TN-S earthing, 100A DP switch incomer. (60A
cutout). RCBOs are double width, as they were the cheapest Type B RCBOs I
could find.


Mine's pretty identical to yours. House was originally rewired
around 1970, although the original Wylex CU was probably older.
Cabling still perfect, but sockets were crap quality and worn out.
Completely rewired kitchen and bathroom during refit and brought
service and bathroom bonding up to spec and fitted new CU. Most
of the ground floor lighting has been rewired as a side effect
of bringing it under home automation control.

4. B32A MCB. Radial circuit for kitchen fixed integrated appliances.
(dishwasher, washing machine, dryer) remotely switched sockets concealed
under worktop.

5. B16A MCB. Radial circuit for fridge/freezer only. Reduces risk of
defrosting, as only a fault on that circuit, or the main service fuse will
cut the power.


These two I have on one circuit, but not RCD protected.

7. B6A MCB. Most of house lighting circuit.

8. B6A MCB. New lighting circuit (kitchen only currently)


I would suggest using C6A for lighting circuits. It may reduce
the chance of a filament lamp tripping the MCB. BS1361 cartridge
fuse is another option (probably a better option).

9. B6A MCB. Alarms (Interlinked smoke/heat detectors + intruder alarm)

If I had an electric hob, there would be a separate B32A MCB circuit for it.


I put the circuit in although I don't ever intend having an
electric hob myself. For now, it has an unswitched 13A socket
on the end with the gas hob spark generator plugged into it,
and a 45A cooker switch ;-)

I would also split the rest of the house ring main into two.


Strangely, the 1970 rewire did install two ring circuits, but they
were joined into one big ring in the CU, which also makes me think
the CU was older and not changed at that time.

B. The relative merits of RCDs and RCBOs.


30mA RCD (whole house) = BAD!!!


and doesn't conform to the regs

30mA RCD (split load) = Much cheaper than RCBOs

30mA RCBO = Much less prone to nuisance tripping. Tripping has fewer
consequences. Warm feeling of having done it right.


One disadvantage of most RCBO's is they give no clue what tripped
them, earth leakage or current draw. There were some types where
the dolly only moved halfway to the off position when the RCD part
caused the trip, but I haven't seen them for a long time now.

As for your list of appliances:

electric cooker = Own dedicated circuit on B32A MCB. Do not install cooker
unit with built in socket. They look bad and trail leads over the cooker.


....and the cooker doesn't want RCD protection, but all the worktop
sockets do, which is incompatible with a combined socket.

boiler = put on a dedicated central heating circuit MCB (not RCBO). Can
share with immersion, especially if sharing controls, such as programmers.
All central heating valves, programmers and other controls should be from
the same central heating circuit.


Moreover, all the central heating controls should all be switched off
by the one boiler isolation switch.

fire alarms = either wire from a regularly used lighting circuit, or give
own small radial circuit (i.e. B6A or B3A MCB).


There are some rules (which I don't remember, and didn't seem very
sensible to me) about sharing smoke detectors with lighting circuits,
and relate to the type of battery backup the smoke detectors have.
In my case, the smoke detectors run off the alarm anyway, and use
the alarm battery in the event of a mains failure.

--
Andrew Gabriel
  #4   Report Post  
Christian McArdle
 
Posts: n/a
Default Typical domestic electrical circuits

I would suggest using C6A for lighting circuits. It may reduce
the chance of a filament lamp tripping the MCB. BS1361 cartridge
fuse is another option (probably a better option).


I'm not worried. I do not possess a filament light bulb in the house, except
in my Maglite. I prefer MCBs to fuses whenever possible, as it is easier to
reset at 2am, especially when you've got no spares.

I would also split the rest of the house ring main into two.


Strangely, the 1970 rewire did install two ring circuits, but they
were joined into one big ring in the CU, which also makes me think
the CU was older and not changed at that time.


Mine is similar, but not quite. The ring went down from the old CU, round
the ground floor and then up, past the CU to the upstairs and back down
again. I can split it simply by cutting the cable and crimping an extension.
I'm just too tight to buy another RCBO until I have to!

Christian.



  #5   Report Post  
John Aston
 
Posts: n/a
Default Typical domestic electrical circuits


Christian McArdle wrote in message
. net...

snip

Technically, you have a maximum of 100m2 for a ring circuit. However, it

is
better to anticipate the likely load and use this as maximum. In

particular,
a well stocked kitchen often has more equipment than should be installed

on
a single ring main, especially if, like me, you cycle the machines all
simultaneously whilst cooking.

extended snip


Thanks for such a comprehensive reply.

Based on your excellent response and a bit of background reading, I have
pencilled in the following circuits (and protection) for my house:

Ring Main A ...32A RCBO
G/F Kitchen (incl. fridge/freezer)

Ring Main B ...32A RCBO
G/F Dining Room, Lounge, Hall

Ring Main C ...32A RCBO
1/F Bedrooms, Bathroom, Landing

Ring Main D ...32A RCBO
Extension: Playroom, Utilities (washer/dryer), Study

Radial A ...6A MCB
Lights on east side of house

Radial B ...6A MCB
Lights on west side of house

Radial C ...6A MCB
Lights in extension

Radial D ...32A MCB
Cooker

Radial E ...16A RCBO
Immersion Heater/boiler controls/pumps

Radial F ...6A MCB
Fire/Security alarms

Radial G ...20A RCBO
Garden sockets & lights

Assuming that the RCBOs are double width, I guess that I need at least a
17-way consumer unit. Did you put your RCBOs side-by-side? I read somewhere
on this NG that a RCBO can "trip" an adjacent RCBO.

The garden lights must be switched on/off from the house. The shed
sockets/lights must be switched on/off in the shed. Is it still OK to run
the whole lot off one circuit ("Radial G", above)?

Obviously, if a TT earthing system, the 100A DP incomer switch should be
exchanged for a 100A/100mA time delay RCD.


My earthing system is TN-S. I guess you'd advise that I would be better
served by a switch than a 100A/100mA time delay RCD at the incomer.

My thanks again for your help.




  #6   Report Post  
Christian McArdle
 
Posts: n/a
Default Typical domestic electrical circuits

Ring Main A ...32A RCBO
G/F Kitchen (incl. fridge/freezer)


Absolutely do not put your fridge/freezer on an RCBO circuit, unless you
like coming home from holiday to a rotting stinking mess. It is better to
put it on its own circuit, or at least shared on another MCB only circuit.
You can always cut out one of your lighting circuits to make room.

Ring Main B ...32A RCBO
G/F Dining Room, Lounge, Hall


OK.

Ring Main C ...32A RCBO
1/F Bedrooms, Bathroom, Landing


OK.

Ring Main D ...32A RCBO
Extension: Playroom, Utilities (washer/dryer), Study


OK. Although containing high current devices, having just a washing and a
dryer on the circuit shouldn't cause any overload.

Radial C ...6A MCB
Lights in extension


Might be overkill, could probably combined with another lighting circuit.

Radial D ...32A MCB
Cooker


OK.

Radial E ...16A RCBO
Immersion Heater/boiler controls/pumps


Use an MCB, rather than an RCBO. Although an RCBO is less prone to nuisance
trips than a shared RCD, there's still a chance of a spurious pop when you
are on your winter skiing break, leading to your house freezing, possibly
causing damage.

Radial G ...20A RCBO
Garden sockets & lights


OK.

Assuming that the RCBOs are double width, I guess that I need at least a
17-way consumer unit. Did you put your RCBOs side-by-side? I read

somewhere
on this NG that a RCBO can "trip" an adjacent RCBO.


You can put them side by side, no problem. When populating the consumer
unit, it is best to order as reducing ratings, starting with the heaviest
circuits next to the incomer. Remember that with an RCBO installation, you
want a "standard" isolator incomer (except for TT), rather than a fancy
split load unit.

The garden lights must be switched on/off from the house. The shed
sockets/lights must be switched on/off in the shed. Is it still OK to run
the whole lot off one circuit ("Radial G", above)?


Absolutely. Consider having a DP switch (or even FCU) on the run to the
shed. Then you can ensure that everything is turned off without having to
brave the weather.

My earthing system is TN-S. I guess you'd advise that I would be better
served by a switch than a 100A/100mA time delay RCD at the incomer.


Yes.

So, with these modifications, you get:

1. B32A RCBO - Kitchen ring
2. B32A RCBO - Reception ring
3. B32A RCBO - Upstairs ring
4. B32A RCBO - Extension/utility ring
5. B32A MCB - Cooker
6. B20A RCBO - Outside
7. B16A MCB - Heating
8. B16A MCB - Fridge/Freezer
9. B6A MCB - Lighting A
10. B6A MCB - Lighting B
11. B6A MCB - Alarm

I make this 16 outgoing ways using double width RCBOs, or 11 outgoing ways
using single width RCBOs. You've probably got some overkill on the ring
mains and could combine some, too. For example, you might swap the Utility
RCBO for a 32A MCB for just the appliances and use the Reception ring RCBO
to cover the sockets in the extension. This would save you an RCBO (and give
you an extra way if using double width units). It also removes likely earth
leakage culprits (i.e. the washing machine and tumbler) from the general
purpose ring main.

Christian.


  #7   Report Post  
Andrew Gabriel
 
Posts: n/a
Default Typical domestic electrical circuits

In article ,
"Christian McArdle" writes:
OK.

Assuming that the RCBOs are double width, I guess that I need at least a


You can get single width ones, although it may depend on the make
of CU.

17-way consumer unit. Did you put your RCBOs side-by-side? I read

somewhere
on this NG that a RCBO can "trip" an adjacent RCBO.


You can put them side by side, no problem.


Check the manufacturer's spec. It varies, and isn't just related
to RCBO side-by-side -- in one case they can't be used with MCB
of 40A or more side-by-side IIRC.

--
Andrew Gabriel
  #8   Report Post  
Owain
 
Posts: n/a
Default Typical domestic electrical circuits

"Andrew Gabriel" wrote
| fire alarms = either wire from a regularly used lighting circuit,
| or give own small radial circuit (i.e. B6A or B3A MCB).
| There are some rules (which I don't remember, and didn't seem very
| sensible to me) about sharing smoke detectors with lighting circuits,
| and relate to the type of battery backup the smoke detectors have.
| In my case, the smoke detectors run off the alarm anyway, and use
| the alarm battery in the event of a mains failure.

IIRC if you use a lighting circuit (where you will probably notice a failure
fairly quickly) you have to have battery[1]-back-up smoke detectors, and if
you use a dedicated circuit (which would go faulty for weeks without being
noticed) you don't have to have battery-back-up.

Owain

[1] Although some have a whopping big capacitor these days, I think

  #9   Report Post  
Andrew Gabriel
 
Posts: n/a
Default Typical domestic electrical circuits

In article ,
"Owain" writes:
"Andrew Gabriel" wrote
| fire alarms = either wire from a regularly used lighting circuit,
| or give own small radial circuit (i.e. B6A or B3A MCB).
| There are some rules (which I don't remember, and didn't seem very
| sensible to me) about sharing smoke detectors with lighting circuits,
| and relate to the type of battery backup the smoke detectors have.
| In my case, the smoke detectors run off the alarm anyway, and use
| the alarm battery in the event of a mains failure.

IIRC if you use a lighting circuit (where you will probably notice a failure
fairly quickly) you have to have battery[1]-back-up smoke detectors, and if
you use a dedicated circuit (which would go faulty for weeks without being
noticed) you don't have to have battery-back-up.


Yes, that sounds familiar now you mention it ;-)

--
Andrew Gabriel
  #10   Report Post  
John Aston
 
Posts: n/a
Default Typical domestic electrical circuits


"Christian McArdle" wrote in message
. net...

As an example, my house has the following circuits installed into a 16
outgoing way Contactum CU. TN-S earthing, 100A DP switch incomer. (60A
cutout). RCBOs are double width, as they were the cheapest Type B RCBOs I
could find.


Some single width RCBOs are single pole only. Would you recommend a RCBO
that disconnects the neutral as well?




  #11   Report Post  
Chris Oates
 
Posts: n/a
Default Typical domestic electrical circuits


"John Aston" wrote in message
...

"Christian McArdle" wrote in message
. net...

As an example, my house has the following circuits installed into a 16
outgoing way Contactum CU. TN-S earthing, 100A DP switch incomer. (60A
cutout). RCBOs are double width, as they were the cheapest Type B RCBOs

I
could find.


Some single width RCBOs are single pole only. Would you recommend a RCBO
that disconnects the neutral as well?


there is no requirement
a standard CU has hard wired neutrals


  #12   Report Post  
John Aston
 
Posts: n/a
Default Typical domestic electrical circuits


"Chris Oates" none wrote in message
...

"John Aston" wrote in message
...

Some single width RCBOs are single pole only. Would you recommend a RCBO
that disconnects the neutral as well?


there is no requirement
a standard CU has hard wired neutrals


Could you use a single pole RCBO though to protect an outdoor circuit (or
any internal socket close to the back door to the garden)?

Looking though the catalogues, there is a much wider range of single pole
(solid neutral) RCBOs than there is for double pole RCBOs.


  #13   Report Post  
Christian McArdle
 
Posts: n/a
Default Typical domestic electrical circuits

Some single width RCBOs are single pole only. Would you recommend a RCBO
that disconnects the neutral as well?


A DP is nice, as it can act as an isolator for the circuit. Particularly
useful for maintainance, or if a neutral-earth short has caused the trip on
that circuit (will prevent other RCBOs tripping too). However, there is no
requirement, AIUI. After all, an MCB is single pole.

Christian.


  #14   Report Post  
John Aston
 
Posts: n/a
Default Typical domestic electrical circuits


Christian McArdle wrote in message
et...
Some single width RCBOs are single pole only. Would you recommend a RCBO
that disconnects the neutral as well?


A DP is nice, as it can act as an isolator for the circuit. Particularly
useful for maintainance, or if a neutral-earth short has caused the trip

on
that circuit (will prevent other RCBOs tripping too). However, there is no
requirement, AIUI. After all, an MCB is single pole.

Christian.


I guess, though, that I couldn't use a single pole RCBO though to protect
the circuit for the garden shed. I'll probably protect this circuit with a
MCB at the consumer unit and a RCD externally.



  #15   Report Post  
Lurch
 
Posts: n/a
Default Typical domestic electrical circuits

On Wed, 21 Jan 2004 09:52:58 -0000, "Christian McArdle"
wrote:

Some single width RCBOs are single pole only. Would you recommend a RCBO
that disconnects the neutral as well?


A DP is nice, as it can act as an isolator for the circuit. Particularly
useful for maintainance, or if a neutral-earth short has caused the trip on
that circuit (will prevent other RCBOs tripping too). However, there is no
requirement, AIUI. After all, an MCB is single pole.

I'd agree with that, nearly! A fault on one circuit wouldn't affect
other RCBO's unless they were upstream. If there is no upstream RCD
then SP would suffice but if there is then I would use DP.


SJW
A.C.S. Ltd.


  #16   Report Post  
Christian McArdle
 
Posts: n/a
Default Typical domestic electrical circuits

I'd agree with that, nearly! A fault on one circuit wouldn't affect
other RCBO's unless they were upstream.


No, it could affect an RCBO at the same level.

Consider two SP RCBO circuits in a CU, called A and B.

There is a neutral-earth short on circuit A.

A high current device on A draws some current. A small proportion of the
return current from this goes through the earth fault rather than the
neutral, tripping the RCBO. All well and good, exactly what you want.

However, now a device on circuit B draws some current. As RCBO A has only
cut the live, the neutral current from B could go into the A circuit neutral
and through the same neutral-earth short, causing B to trip also, even
though the earth fault is on a different circuit.

Had A been fitted with a DP RCBO, this neutral would have been cut, so B
wouldn't trip. It is possible that B would trip first whilst A is still
operating. However, once A had tripped or been manually pulled, B would not
repeat the experience.

Christian.


  #17   Report Post  
Christian McArdle
 
Posts: n/a
Default Typical domestic electrical circuits

A high current device on A draws some current. A small proportion of the
return current from this goes through the earth fault rather than the
neutral, tripping the RCBO. All well and good, exactly what you want.


Scratch that! I'm talking ********!

It won't take out RCBO B, will it. However, it will still have an
unnecessary earth fault, which could be detected by a 100mA device further
up.

Christian.


  #18   Report Post  
Lurch
 
Posts: n/a
Default Typical domestic electrical circuits

On Wed, 21 Jan 2004 11:56:00 -0000, "Christian McArdle"
wrote:

A high current device on A draws some current. A small proportion of the
return current from this goes through the earth fault rather than the
neutral, tripping the RCBO. All well and good, exactly what you want.


Scratch that! I'm talking ********!

It won't take out RCBO B, will it. However, it will still have an
unnecessary earth fault, which could be detected by a 100mA device further
up.

Christian.


This one makes more sense.
I think that's what I said originally!! ;-)


SJW
A.C.S. Ltd.
  #19   Report Post  
Christian McArdle
 
Posts: n/a
Default Typical domestic electrical circuits

This one makes more sense.
I think that's what I said originally!! ;-)


Indeed. I've already said 40 Hail Marys.

Christian.


  #20   Report Post  
Chris Oates
 
Posts: n/a
Default Typical domestic electrical circuits


"Christian McArdle" wrote in message
et...
Some single width RCBOs are single pole only. Would you recommend a RCBO
that disconnects the neutral as well?


A DP is nice, as it can act as an isolator for the circuit. Particularly
useful for maintainance, or if a neutral-earth short has caused the trip

on
that circuit (will prevent other RCBOs tripping too). However, there is no
requirement, AIUI. After all, an MCB is single pole.


easy way to do this if short of space is to run
the circuit through ab RCD switch as found
in consumer units but mounted in a 2 width box
like this
http://tinyurl.com/23yzw




  #21   Report Post  
Lurch
 
Posts: n/a
Default Typical domestic electrical circuits

On Wed, 21 Jan 2004 14:41:15 -0000, "Christian McArdle"
wrote:

This one makes more sense.
I think that's what I said originally!! ;-)


Indeed. I've already said 40 Hail Marys.

Christian.


I'll let you off, we all have bad days. I'm having one today actually!
Could be a bad year though, the bad days seem to have merged since 1st
Jan!!


SJW
A.C.S. Ltd.
  #22   Report Post  
Lurch
 
Posts: n/a
Default Typical domestic electrical circuits

On Tue, 20 Jan 2004 16:42:36 -0000, "John Aston"
wrote:


Christian McArdle wrote in message
.net...

snip

Technically, you have a maximum of 100m2 for a ring circuit. However, it

is
better to anticipate the likely load and use this as maximum. In

particular,
a well stocked kitchen often has more equipment than should be installed

on
a single ring main, especially if, like me, you cycle the machines all
simultaneously whilst cooking.

extended snip


Thanks for such a comprehensive reply.

Based on your excellent response and a bit of background reading, I have
pencilled in the following circuits (and protection) for my house:

Ring Main A ...32A RCBO
G/F Kitchen (incl. fridge/freezer)

Ring Main B ...32A RCBO
G/F Dining Room, Lounge, Hall

Ring Main C ...32A RCBO
1/F Bedrooms, Bathroom, Landing

Ring Main D ...32A RCBO
Extension: Playroom, Utilities (washer/dryer), Study

Radial A ...6A MCB
Lights on east side of house

Radial B ...6A MCB
Lights on west side of house

Radial C ...6A MCB
Lights in extension

Radial D ...32A MCB
Cooker

Radial E ...16A RCBO
Immersion Heater/boiler controls/pumps

Radial F ...6A MCB
Fire/Security alarms

Radial G ...20A RCBO
Garden sockets & lights

Assuming that the RCBOs are double width, I guess that I need at least a
17-way consumer unit.


Hager do single module RCBO's in a double pole flavour. Cant remember
what the numbers were off the top off my head, I'm thinking AD010B but
don't rely on that as correct!
Bear in mind you want some spare capacity, around 20-30% I usaually
allow.
If you were to use Hager then a 14 way board would be ample.



SJW
A.C.S. Ltd.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Arrghhh! My brain hurts. Electrical trouble with new cooker. Tim Downie UK diy 3 November 18th 03 08:48 PM
Upgrade to a three phase domestic supply? Pandora UK diy 32 October 5th 03 02:33 AM
How much does a typical house cost to rewire? Andy Hall UK diy 1 August 13th 03 10:01 AM
Forthcoming Building Regulations on electrical work (Part P) Andrew McKay UK diy 42 July 30th 03 08:05 AM
Electrical Wiring Grouping Factors in IEE Regs pickerel UK diy 5 July 14th 03 01:26 AM


All times are GMT +1. The time now is 03:05 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"