The previous householders have re-used a 6mm^2(??) cable, (that I
presume was once used to feed an electric shower), to feed a power
shower pump and the (gas) heating system. (ie. low current draw
compared with the electric shower which I presume it used to feed).
The cable is protected by a 30A fuse in the consumer unit.

In order to make the wiring reach the power shower pump and the
heating system in the airing cupboard, they have extended the 6mm^2
with around 3metres of 2.5mm^2 using a junction box in the loft.

The current situation is clearly unsatisfactory as the 2.5mm^2 is
effectively (incorrectly) protected with a 30A protector.
I understand that the regs say that each reduction in cable size
should be appropriately protected, but I want to know if it is
acceptable just to place smaller fuse at the start of the whole
circuit in the CU. (ie. 16A).
[Working here on the principle that it just becomes a radial circuit
serving less than 50m^2 of floor area].
The alternative, if not, will be for me to replace the 3m of 2.5mm
with 6mm. Not a major issue, but I'm not sure about getting it into
the FCU's, (which incidentally have also been omitted by the previous
'installers')
  #2   Report Post  
BigWallop
 
Posts: n/a
Default Regs regarding Joining Smaller Cable with Bigger


"Mike Hall" wrote in message
om...
The previous householders have re-used a 6mm^2(??) cable, (that I
presume was once used to feed an electric shower), to feed a power
shower pump and the (gas) heating system. (ie. low current draw
compared with the electric shower which I presume it used to feed).
The cable is protected by a 30A fuse in the consumer unit.

In order to make the wiring reach the power shower pump and the
heating system in the airing cupboard, they have extended the 6mm^2
with around 3metres of 2.5mm^2 using a junction box in the loft.

The current situation is clearly unsatisfactory as the 2.5mm^2 is
effectively (incorrectly) protected with a 30A protector.
I understand that the regs say that each reduction in cable size
should be appropriately protected, but I want to know if it is
acceptable just to place smaller fuse at the start of the whole
circuit in the CU. (ie. 16A).
[Working here on the principle that it just becomes a radial circuit
serving less than 50m^2 of floor area].
The alternative, if not, will be for me to replace the 3m of 2.5mm
with 6mm. Not a major issue, but I'm not sure about getting it into
the FCU's, (which incidentally have also been omitted by the previous
'installers')


Depending on the load that is being drawn from the cable it would be safer
to drop the fuse rating in the consumer unit to cover it. The 30amp fuse
will protect the 6mm cable, but it is much to heavy to protect the thinner
gauge cables.

But do check what load is being drawn first so you get the correct fuse
rating and stop any nuisance tripping.


  #3   Report Post  
Lurch
 
Posts: n/a
Default Regs regarding Joining Smaller Cable with Bigger

On 14 Jan 2004 09:47:18 -0800,
(Mike Hall) wrote:

The previous householders have re-used a 6mm^2(??) cable, (that I
presume was once used to feed an electric shower), to feed a power
shower pump and the (gas) heating system. (ie. low current draw
compared with the electric shower which I presume it used to feed).
The cable is protected by a 30A fuse in the consumer unit.

In order to make the wiring reach the power shower pump and the
heating system in the airing cupboard, they have extended the 6mm^2
with around 3metres of 2.5mm^2 using a junction box in the loft.

The current situation is clearly unsatisfactory as the 2.5mm^2 is
effectively (incorrectly) protected with a 30A protector.
I understand that the regs say that each reduction in cable size
should be appropriately protected, but I want to know if it is
acceptable just to place smaller fuse at the start of the whole
circuit in the CU. (ie. 16A).
[Working here on the principle that it just becomes a radial circuit
serving less than 50m^2 of floor area].
The alternative, if not, will be for me to replace the 3m of 2.5mm
with 6mm. Not a major issue, but I'm not sure about getting it into
the FCU's, (which incidentally have also been omitted by the previous
'installers')


Either way would be fine, the easiest in your case would be to replace
the 30A fuse with a 16A.
For future reference you can get 6mm into fused spurs, 1 is easy
enough, two are tricky, but do-able with a little effort.


SJW
A.C.S. Ltd.
  #4   Report Post  
Capitol
 
Posts: n/a
Default Regs regarding Joining Smaller Cable with Bigger


As a single strand of 2.5mmsq cable is rated at 29A @ 35C, there isn't much
of a problem with cable ratings. I'd change the CU fuse to 16A or so, but
fit a local in line fuse @ 5A to protect against pump failure.
Regards
Capitol


  #5   Report Post  
PoP
 
Posts: n/a
Default Regs regarding Joining Smaller Cable with Bigger

On Wed, 14 Jan 2004 20:20:45 -0000, "Capitol"
wrote:

As a single strand of 2.5mmsq cable is rated at 29A @ 35C, there isn't much
of a problem with cable ratings.


Surely bad advice? Protecting a 29A rated cable with a 30A rated fuse
has to be bad karma. The 29A is max isn't it? And the 30A fuse could
take substantially more before it blows?

I'm not up to speed on this topic, but I'd certainly question it if I
came across it.

PoP

Sending email to my published email address isn't
guaranteed to reach me.


  #6   Report Post  
Lurch
 
Posts: n/a
Default Regs regarding Joining Smaller Cable with Bigger

On Wed, 14 Jan 2004 22:26:37 +0000, PoP wrote:

On Wed, 14 Jan 2004 20:20:45 -0000, "Capitol"
wrote:

As a single strand of 2.5mmsq cable is rated at 29A @ 35C, there isn't much
of a problem with cable ratings.


Surely bad advice? Protecting a 29A rated cable with a 30A rated fuse
has to be bad karma. The 29A is max isn't it? And the 30A fuse could
take substantially more before it blows?

I'm not up to speed on this topic, but I'd certainly question it if I
came across it.


Quite right. I'd note it on a periodic test as a failure.
As I have mentioned in another post tonight there is an answer which
states rules and regulations willy nilly without knowing what they
mean, or totally disregarding others directly related to the odd one
or two you happen to know. The regulations, BS7671, is not a diy guide
with a few pages of tips, it is a comprehenshive book of guidelines,
which, when coupled with years of interpreting and training can be
used safely.
There is the other type of answer which is based on experience, years
of training and a little of been there done that.
I think the first couple of answers covered it, no need for any more
randomly dangerous rubbish to be thrown in as well.


SJW
A.C.S. Ltd.
  #7   Report Post  
Christian McArdle
 
Posts: n/a
Default Regs regarding Joining Smaller Cable with Bigger

Surely bad advice? Protecting a 29A rated cable with a 30A rated fuse
has to be bad karma. The 29A is max isn't it? And the 30A fuse could
take substantially more before it blows?


No, it is fine, provided there is ONE fused connection unit at the end (or
ONE single or double socket). It is no different from an unfused spur run in
2.5mm on a 30A radial/ring circuit. Overload protection in the 2.5mm spur is
from the FCU/plug top fuse. Short circuit and earth fault protection for the
cable is provided by having sufficiently low earth loop impedence. As the
majority of the circuit is in 6mm and there is only 3m of 2.5mm, this is
unlikely to be a problem.

The fuse/MCB rating will cover any cable that has that rating. The cable is
designed to stand substantial overload for much longer than the protective
device.

However, there is no need for this circuit to be 32A. If it only runs the
central heating and a shower pump, I'd replace the MCB with a 16A or even
lower. I see no reason to have higher MCB ratings than necessary.

Another alternative is to replace the junction box with a 13A FCU, if it is
accessible for changing fuses and checking terminals.

Christian.

P.S. being paranoid, I tend to run shower pumps off an RCD, even when
plumbed in plastic.


  #8   Report Post  
Dave Plowman
 
Posts: n/a
Default Regs regarding Joining Smaller Cable with Bigger

In article ,
Christian McArdle wrote:
P.S. being paranoid, I tend to run shower pumps off an RCD, even when
plumbed in plastic.


But water is a poor conductor of electricity - especially over the
distance a pump would normally be from the shower. Wetting *skin* and
other materials increases their conductivity, but that's a different
argument.

--
*Men are from Earth, women are from Earth. Deal with it.

Dave Plowman London SW 12
RIP Acorn
  #9   Report Post  
Christian McArdle
 
Posts: n/a
Default Regs regarding Joining Smaller Cable with Bigger

P.S. being paranoid, I tend to run shower pumps off an RCD, even when
plumbed in plastic.


But water is a poor conductor of electricity - especially over the
distance a pump would normally be from the shower.


Indeed. Paranoia is an irrational fear, not a sensible one!

Christian.


  #10   Report Post  
Mike Hall
 
Posts: n/a
Default Regs regarding Joining Smaller Cable with Bigger

"Christian McArdle" wrote in message . net...
No, it is fine, provided there is ONE fused connection unit at the end (or
ONE single or double socket).


I will have two FCU's, (one for shower pump and one for CH), hence I
believe the 16A fuse at the CU will sort me out.

P.S. being paranoid, I tend to run shower pumps off an RCD, even when
plumbed in plastic.


Thats the next plan when I replace the CU over the next few weeks
(/months). At the moment I'm just laying in the groundwork.


  #11   Report Post  
Capitol
 
Posts: n/a
Default Regs regarding Joining Smaller Cable with Bigger

I think I should reply to my admirers.

1) Go out and read the 16th edition regulations IN DETAIL before committing
finger to keyboard. Together with the background clauses in the IEE
discussions.

2) Just to give you a clue, 2.5sqmm cable in free air WITH CONSTANT LOADING
can be adequately protected by a 30A fuse in a radial circuit.

3) The IEE regulations are a code of practice and not a Bible. The IEE
specifically states that the code is a guide.

4) Changing wire gauge is not bad practice. Sorry, but that is the real
world.

5) This application is an intermittent loading. Thus cable ratings change.

6) Both of the admirers I noticed had failed to look at the application in
sufficient detail to spot the really weak points in the installation.

a) If solid cable is used to connect to a vibrating pump( shower pumps
normally are on anti-vibration mountings), it shears! The pump should be
connected with stranded wire.
b) The fusing problem is not in the CU but locally. The pump should be
protected with a local 5A fuse.

7) If you ask what would I have done:

a2) Left the fuse @30A
b2) Split the 6mm feed in the loft into a 13A socket( for local convenience)
and a fused 13A spur using the local 2.5mm2 cable, both mounted in a surface
box.
c2) Terminate the 2.5mm2 adjacent to the pump in a 13A socket.
d2) Fit a 13A plug flexible lead to the pump fused @5A.

The inherent problem in the setup was the ability of the source to over
supply energy to the pump under failure conditions. A 15/16A CU fuse helps
in this respect but is not ideal, hence the preference for a local fuse @ 5A

Hope this explains the reasoning behind the statements.

Regards
Capitol


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pulling cable through with existing one / Clipping cable in loft Mike Hall UK diy 17 January 12th 04 12:52 PM
Joining co-axial cable outdoors Peter Crosland UK diy 45 September 17th 03 04:50 PM
Is it OK to put standard "twin & earth" cable directly into the cavity of a dwarf wall? Jon Weaver UK diy 20 August 8th 03 03:38 PM
Cable - pricing up NorwichLad UK diy 3 July 25th 03 12:59 PM
Routeing Electrical FTE cable pickerel UK diy 3 July 24th 03 12:43 AM


All times are GMT +1. The time now is 01:23 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"