  #1   Report Post  
Mike Hall
 
Posts: n/a
Default Fixing loft boarding *through* insulation and derating cable.

I've been quoted £125 for supply and installation of 350mm loft
insulation in the roof of our 3 bed semi, (includes a grant based
discount). This seems like a remarkably good deal, and it doesn't
seem worth getting my hands dirty for this kind of money, (so much for
DIY!)
Before I proceed though, I've got a couple of questions that I hope
the collective massive can help me with:

The upstairs lighting cable needs replacing, (currently stranded
aluminium with no earth). I've seen this question asked before, but
have not found the answer as to; whether or not lighting cable fixed
to rafters on one side and then covered with loft insulation needs
derating. If so then I guess the derating factor is 0.5. My thoughts
are 'yes' that this counts as being totally enclosed in insulation,
but I have also seen it suggested that having the rafter on one side
means that it is *not* totally enclosed in insulation. - which is it?

Secondly, I will wish to board part of the loft after the insulation
is applied, and the insulation guy suggests putting the boards on the
insulation and screwing *through* the insulation to the joists. Does
this seem OK, or should I clear a path through to the joists for a
wood-on-wood joint? Also I read a lot of talk about vapour barriers
under the insulation, but am still unclear as to whether this is
really necessary or not!
  #2   Report Post  
Christian McArdle
 
Posts: n/a
Default Fixing loft boarding *through* insulation and derating cable.

The upstairs lighting cable needs replacing, (currently stranded
aluminium with no earth). I've seen this question asked before,
but have not found the answer as to; whether or not lighting
cable fixed to rafters on one side and then covered with loft
insulation needs derating. If so then I guess the derating factor
is 0.5.


Lighting cable is so overrated anyway, that 50% derating just isn't an
issue. Run in 1.5mm if you're really worried.

Secondly, I will wish to board part of the loft after the insulation
is applied, and the insulation guy suggests putting the boards on the
insulation and screwing *through* the insulation to the joists.


I don't see how that would work. Surely it would squash the insulation? I'm
assuming it is fibre, not Jablite or something, when you would might get
away with it, although it might start crushing above the joist lines. This
could be solved by insulating upto joist level, boarding, insulating the
rest and boarding again. Not cheap though, and I bet you're using fibre, not
Jablite.

Also I read a lot of talk about vapour barriers under the
insulation, but am still unclear as to whether this is really
necessary or not!


Definately install one, especially for fibre insulation. Just a sheet of
plastic over the joists and plasterboard would be fine.

Christian.



  #3   Report Post  
Set Square
 
Posts: n/a
Default Fixing loft boarding *through* insulation and derating cable.

In an earlier contribution to this discussion,
Mike Hall wrote:

I've been quoted £125 for supply and installation of 350mm loft
insulation in the roof of our 3 bed semi, (includes a grant based
discount). This seems like a remarkably good deal, and it doesn't
seem worth getting my hands dirty for this kind of money, (so much for
DIY!)
Before I proceed though, I've got a couple of questions that I hope
the collective massive can help me with:

The upstairs lighting cable needs replacing, (currently stranded
aluminium with no earth). I've seen this question asked before, but
have not found the answer as to; whether or not lighting cable fixed
to rafters on one side and then covered with loft insulation needs
derating. If so then I guess the derating factor is 0.5. My thoughts
are 'yes' that this counts as being totally enclosed in insulation,
but I have also seen it suggested that having the rafter on one side
means that it is *not* totally enclosed in insulation. - which is it?

Secondly, I will wish to board part of the loft after the insulation
is applied, and the insulation guy suggests putting the boards on the
insulation and screwing *through* the insulation to the joists. Does
this seem OK, or should I clear a path through to the joists for a
wood-on-wood joint? Also I read a lot of talk about vapour barriers
under the insulation, but am still unclear as to whether this is
really necessary or not!



I'll others to comment on the cable issues.

With regard to the insulation, how tall are the joists? If it's an old
house, they're probably no more than 100mm - if that. There's no point
whatsoever putting in 350mm of insulation if you are going to compress it
into 100mm. 350mm of insulation is only effective if it traps a 350mm layer
of air! Admittedly the boarding will add some insulation, but you really
need to pack the joists up as high as possible with something solid to
support the boards.

Having said that, I'm not sure what to suggest for packing - timber would
really be too heavy. Anyone know whether you can get aluminium (or maybe
rigid plastic) I-sections which are 50mm wide and maybe 250mm high?
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is Black Hole!


  #4   Report Post  
Alistair Riddell
 
Posts: n/a
Default Fixing loft boarding *through* insulation and derating cable.

On Wed, 7 Jan 2004, Mike Hall wrote:

The upstairs lighting cable needs replacing, (currently stranded
aluminium with no earth). I've seen this question asked before, but
have not found the answer as to; whether or not lighting cable fixed
to rafters on one side and then covered with loft insulation needs
derating. If so then I guess the derating factor is 0.5. My thoughts
are 'yes' that this counts as being totally enclosed in insulation,
but I have also seen it suggested that having the rafter on one side
means that it is *not* totally enclosed in insulation. - which is it?


The tables in the regs say that the current capacity of standard 1mm2
twin&earth enclosed in insulation is 11 Amps so you should have no problem
with normal lighting circuits.

--
Alistair Riddell - BOFH
IT Manager, George Watson's College, Edinburgh
Tel: +44 131 446 6070 Fax: +44 131 446 6090
Microsoft - because god hates us
  #5   Report Post  
Mike Hall
 
Posts: n/a
Default Fixing loft boarding *through* insulation and derating cable.

"Set Square" wrote in message ...
With regard to the insulation, how tall are the joists? If it's an old
house, they're probably no more than 100mm - if that.


It's a 1950's ex council house - I believe the joists are 100mm, and
the insulator guys were going to lay the insulation over the joists
(at right angles).

There's no point
whatsoever putting in 350mm of insulation if you are going to compress it
into 100mm. 350mm of insulation is only effective if it traps a 350mm layer
of air! Admittedly the boarding will add some insulation, but you really
need to pack the joists up as high as possible with something solid to
support the boards.


I absolutely agree with the physics of this, however from my point of
view I can get the whole insulation done in the next few weeks, and at
some point later in the year I can board over only a relatively small
portion of the loft, (around the hatch and tanks etc). So, 100mm of
compressed insulation is not as effective as 350mm uncompressed, but
taking that as given, and going back to my original question I still
wonder about the sensibility of screwing the boards to the joists
*through* the insulation, (which I am guessing will be compressed to
about 20-30mm at that point). I then end up with 20-30mm compressed
insulation *and* a board above a joist which has got to be better than
just the board alone????


  #6   Report Post  
Christian McArdle
 
Posts: n/a
Default Fixing loft boarding *through* insulation and derating cable.

I absolutely agree with the physics of this, however from my point
of view I can get the whole insulation done in the next few weeks,
and at some point later in the year I can board over only a
relatively small portion of the loft,


If you are only boarding a small section, then just crosslaying some 200mm
beams and attaching the boards to these should be pretty easy and will only
compress the insulation by 50mm or so. I wouldn't use it for medium-heavy
storage though. The self weight of the floor will already be high with the
extra wood, and boarding that the ceiling joists were not designed to
handle.

Christian.



  #7   Report Post  
Mike Hall
 
Posts: n/a
Default Fixing loft boarding *through* insulation and derating cable.

Alistair Riddell wrote in message . org.uk...

The tables in the regs say that the current capacity of standard 1mm2
twin&earth enclosed in insulation is 11 Amps so you should have no problem
with normal lighting circuits.


That's good news, thanks. Can someone who knows better please square
the above statement with what I was trying to calculate using the On
Site Guide:
I've got, (or rather intend to have by the end of today), 9 bayonet
fittings on the upstairs lighting circuit, (3 x bed, landing, 2 x
bathroom, 3 x loft + bathroom fan). This equates to a design current
of well less than 6A, so 6A TypeB MCB should be fine.
Now getting to the bit I am a little muddy on!
The cable is now protected for 6A, however as it will be under
insulation the On Site Guide says it needs derating by 0.5. Using
the formula they give this means that although the MCB is 6A the cable
needs to be rated for 12A, (right so far??)
So I look down the table of 'conventional circuits' and find that the
next biggest radial circuit above 10A is 15A which is wired with
2.5mm^2 T&E.
Have I gone wrong somewhere with my understanding of the derating
process?
  #8   Report Post  
Christian McArdle
 
Posts: n/a
Default Fixing loft boarding *through* insulation and derating cable.

Have I gone wrong somewhere with my understanding of the derating
process?


I'm not sure I quite follow you. However, in most circuits cable size is not
limited by the current carrying capacity of the cable, but voltage drop or
earth loop impedence.

Christian.


  #9   Report Post  
Owain
 
Posts: n/a
Default Fixing loft boarding *through* insulation and derating cable.

"Mike Hall" wrote
| That's good news, thanks. Can someone who knows better please square
| the above statement with what I was trying to calculate using the On
| Site Guide:
| Now getting to the bit I am a little muddy on!
| The cable is now protected for 6A, however as it will be under
| insulation the On Site Guide says it needs derating by 0.5. Using
| the formula they give this means that although the MCB is 6A the
| cable needs to be rated for 12A, (right so far??)

Yes.

| So I look down the table of 'conventional circuits' and find that the
| next biggest radial circuit above 10A is 15A which is wired with
| 2.5mm^2 T&E.
| Have I gone wrong somewhere with my understanding of the derating
| process?

Yes. You don't change the circuit arrangement when you derate a cable. You
still run a 6A lighting circuit, you just have to use cable rated at 12A in
the applicable method of mounting.

A quick glance at Table 4.7 in Whitfield's electricians guide shows that
1.0mm in wall in thermal insulation has a rating of 11A which is not big
enough, so you will have to use 1.5mm at 14A. There should be no problem
using that with most lighting fittings.

Incidentally, if you were to use a 15A 2.5mm radial conventional circuit,
you would apply derating of 0.5 so your cable would have to be rated at 30A
in insulation. 2.5mm is only rated at 18.5A in insulation (compared to 27A
clipped direct), 4.0mm is rated at 25A in insulation, so you would have to
use 6.0mm at 32A for that radial circuit.

Whitfield has an example where that 15A radial circuit has not only thermal
insulation but ambient temperature and grouping factors apply, and ends up
with a 15A circuit run in 10mm cable, which would be impractical because the
switch terminals would be unlikely to accept the cable.

Owain


  #10   Report Post  
Mike Hall
 
Posts: n/a
Default Fixing loft boarding *through* insulation and derating cable.

"Owain" wrote in message ...
Yes. You don't change the circuit arrangement when you derate a cable. You
still run a 6A lighting circuit, you just have to use cable rated at 12A in
the applicable method of mounting.

A quick glance at Table 4.7 in Whitfield's electricians guide shows that
1.0mm in wall in thermal insulation has a rating of 11A which is not big
enough, so you will have to use 1.5mm at 14A. There should be no problem
using that with most lighting fittings.

Looks like I might need a copy of this Whitfield's as well as the 'On
Site Guide' - or is there really not a lot of difference between them?


  #11   Report Post  
Andy Hall
 
Posts: n/a
Default Fixing loft boarding *through* insulation and derating cable.

On 9 Jan 2004 03:01:19 -0800,
(Mike Hall) wrote:

"Owain" wrote in message ...
Yes. You don't change the circuit arrangement when you derate a cable. You
still run a 6A lighting circuit, you just have to use cable rated at 12A in
the applicable method of mounting.

A quick glance at Table 4.7 in Whitfield's electricians guide shows that
1.0mm in wall in thermal insulation has a rating of 11A which is not big
enough, so you will have to use 1.5mm at 14A. There should be no problem
using that with most lighting fittings.

Looks like I might need a copy of this Whitfield's as well as the 'On
Site Guide' - or is there really not a lot of difference between them?


The Whitfield book has a lot more info in it and commentary on what
the issues are. The OSG is more by way of extracts plus a bit of
information but not a lot of background info. The assumption it has
is that you know most of the stuff and just need tables and other
information to hand when on site or planning installations. It's
because the main IEE Wiring Regulations book is written in the way of
all standards. It is often quite difficult to find things in it
quickly.

You can find most of the Whitfield book on line at
www.tlc-direct.co.uk in the technical section, but I think it is worth
having a copy if you are doing a lot of electrical work, and
especially anything a bit unusual.



..andy

To email, substitute .nospam with .gl
  #12   Report Post  
Owain
 
Posts: n/a
Default Fixing loft boarding *through* insulation and derating cable.

"Mike Hall" wrote
| "Owain" wrote
| A quick glance at Table 4.7 in Whitfield's electricians guide
| Looks like I might need a copy of this Whitfield's as well as the
| On Site Guide' - or is there really not a lot of difference between
| them?

Whitfield says his book is intended for electricians who have to design
their own circuits, whereas the OSG tends to assume there is an electrical
engineer in the background doing the design work. Whitfield goes in a deep
pocket quite nicely.

Owain


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is it OK to put standard "twin & earth" cable directly into the cavity of a dwarf wall? Jon Weaver UK diy 20 August 8th 03 04:38 PM