I've done a bit of testing this afternoon, and found a fault on a ring
main.
Continuity results:
E-E 0.40 ohms
N-N 0.19 ohms
L-L 37 ohms - clearly a fault here.

I checked the 4 sockets on the ring for loose connections, and found no
apparent fault.
So next I joined up opposite ends of L+E, and measured R1 + R2 at the
sockets: 0.42 ohms, 0.42, 0.48, and 0.51ohms.

Clearly the resistance goes up as the sockets get further away.

Muddled thinking got me nowhere.
After a while, I was thinking that the cable must be damaged between the
final socket and the return cable.
But, a resistance of 37 ohms? That doesnt seem to be enough to be a
damaged cable.
(Insulation resistance was checked, and all fine at 1k M ohms)

Any thoughts?
Ta
Alan.

--
To reply by e-mail, change the ' + ' to 'plus'.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,188
Default Sparkies - Ring fault?

On Jan 14, 5:55*pm, (A.Lee) wrote:
I've done a bit of testing this afternoon, and found a fault on a ring
main.
Continuity results:
E-E *0.40 ohms
N-N *0.19 ohms
L-L * *37 ohms * - *clearly a fault here.

I checked the 4 sockets on the ring for loose connections, and found no
apparent fault.
So next I joined up opposite ends of L+E, and measured R1 + R2 at the
sockets: *0.42 ohms, 0.42, 0.48, and 0.51ohms.

Clearly the resistance goes up as the sockets get further away.

Muddled thinking got me nowhere.
After a while, I was thinking that the cable must be damaged between the
final socket and the return cable.
But, a resistance of 37 ohms? That doesnt seem to be enough to be a
damaged cable.
(Insulation resistance was checked, and all fine at 1k M ohms)

Any thoughts?
Ta
Alan.

--
To reply by e-mail, change the ' + ' to 'plus'.


99% of faults are behind/on a socket. Are you sure you've found them
all. Have you removed the socket to test the cable, could be a faulty
socket switch?
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,766
Default Sparkies - Ring fault?

A.Lee explained on 14/01/2011 :
I've done a bit of testing this afternoon, and found a fault on a ring
main.
Continuity results:
E-E 0.40 ohms
N-N 0.19 ohms
L-L 37 ohms - clearly a fault here.


Connect to one end of the ring live with the ring parted, then work
your way along with a long wire with a 13amp plug fitted temporarily on
the end - check each socket in turn, until you find a sudden variation
in impedance. That should make localising it easier.

--
Regards,
Harry (M1BYT) (L)
http://www.ukradioamateur.co.uk


  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Sparkies - Ring fault?

A.Lee wrote:
I've done a bit of testing this afternoon, and found a fault on a ring
main.
Continuity results:
E-E 0.40 ohms
N-N 0.19 ohms
L-L 37 ohms - clearly a fault here.

I checked the 4 sockets on the ring for loose connections, and found
no apparent fault.
So next I joined up opposite ends of L+E, and measured R1 + R2 at the
sockets: 0.42 ohms, 0.42, 0.48, and 0.51ohms.

Clearly the resistance goes up as the sockets get further away.

Muddled thinking got me nowhere.
After a while, I was thinking that the cable must be damaged between
the final socket and the return cable.
But, a resistance of 37 ohms? That doesnt seem to be enough to be a
damaged cable.
(Insulation resistance was checked, and all fine at 1k M ohms)

Any thoughts?
Ta
Alan.



You have actually answered your own question.

Split the ring at all 4 sockets and use a fly lead of known resistance to
check both ends of r1 from the CU before adding sockets as you work to
confirm the topology of the circuit.

It is a damaged cable or an unknown juction box or socket that is at fault.

--
Adam




  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 249
Default Sparkies - Ring fault?

On Jan 14, 5:55 pm, (A.Lee) wrote:

But, a resistance of 37 ohms? That doesnt seem to be enough to be a
damaged cable.


Are you sure you disconnected *every* appliance on the ring? I once had a
very similar fault, and like you was puzzled at the measured loop
resistance of a few tens of ohms, but it went up to the expected
'infinity' when everything was properly disconnected. A wire had come
astray behind a socket outlet.

Richard.
http://www.rtrussell.co.uk/
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,188
Default Sparkies - Ring fault?

On Jan 14, 6:52*pm, Skipweasel wrote:
In article 7325a866-ef54-42c5-9586-
, says...

99% of faults are behind/on a socket. Are you sure you've found them
all. Have you removed the socket to test the cable, could be a faulty
socket switch?


How would a socket-switch affect the ring continuity?

--
Skipweasel - never knowingly understood.


He may not have removed the sockests from the wiring and be testing
from the front of the sockets.
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Sparkies - Ring fault?

harry wrote:
On Jan 14, 6:52 pm, Skipweasel wrote:
In article 7325a866-ef54-42c5-9586-
,
says...

99% of faults are behind/on a socket. Are you sure you've found them
all. Have you removed the socket to test the cable, could be a
faulty socket switch?


How would a socket-switch affect the ring continuity?

--
Skipweasel - never knowingly understood.


He may not have removed the sockests from the wiring and be testing
from the front of the sockets.


The clue is in the words "ring continuity":-)

You don't test that from the front of the socket!

--
Adam


  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,307
Default Sparkies - Ring fault?

ARWadsworth wrote:

Tried replying by email, but your address is dead:

Final-Recipient:
Action: failed
Status: 5.0.0 (permanent failure)
Remote-MTA: dns; [209.85.227.27]
Diagnostic-Code: smtp; 5.1.0 - Unknown address error 550-'5.2.1 The
email account that you tried to reach is disabled. 34si4611472wba.45'
(delivery attempts: 0)

You say "Clearly the resistance goes up as the sockets get further away."
and make it sound as if you did not expect that to happen.



Yes, I was trying to say it was like a radial where the resistance got
higher as I went along, but it did not go down as I progressed back
toward the CU, so the theory of the break between the last socket and
the CU holds some weight.
2 of the sockets have faulty outlets, so I'll change them on Tuesday
when I go back, and I'll do some further testing to pin down where the
fault is.
Thanks
Alan.

--
To reply by e-mail, change the ' + ' to 'plus'.


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Sparkies - Ring fault?

"A.Lee" wrote in message
...
ARWadsworth wrote:

Tried replying by email, but your address is dead:

Final-Recipient:
Action: failed
Status: 5.0.0 (permanent failure)
Remote-MTA: dns; [209.85.227.27]
Diagnostic-Code: smtp; 5.1.0 - Unknown address error 550-'5.2.1 The
email account that you tried to reach is disabled. 34si4611472wba.45'
(delivery attempts: 0)

You say "Clearly the resistance goes up as the sockets get further away."
and make it sound as if you did not expect that to happen.



Yes, I was trying to say it was like a radial where the resistance got
higher as I went along, but it did not go down as I progressed back
toward the CU, so the theory of the break between the last socket and
the CU holds some weight.


It certainly does, either that or an odd topology,

2 of the sockets have faulty outlets, so I'll change them on Tuesday
when I go back, and I'll do some further testing to pin down where the
fault is.


Well it will obviously be the last cable you test!
--
Adam


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
A question for the trading plumbers, gas fitters and sparkies? OT Bob[_42_] UK diy 5 January 19th 10 10:13 PM
OT ...one for the sparkies mark UK diy 31 February 21st 08 11:45 AM
Rewiring cost + any recommended sparkies? (South London, Croydon Area) Seri UK diy 7 November 29th 03 12:30 PM
Another sparkies question about generators Eric R Snow Metalworking 47 August 30th 03 05:36 AM
Sparkies question-theoretical voltage from homade generator Eric R Snow Metalworking 16 August 15th 03 03:38 AM


All times are GMT +1. The time now is 07:48 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"