Old July 13th 10, 09:05 PM posted to uk.d-i-y
external usenet poster
 
Posts: 164
Default RCD test button not tripping the RCD.

Hi all
After working OK since it was installed a couple of months ago the RCD
started tripping whenever anything was switched on.
After failing to isolate the problem by disconnecting circuits we (the
installer and I) realised that the RCD test button doesn't work, so
after a quick dash to Screwfix we got an identical one and installed
it but it's exactly the same! pressing the yellow test button does
nothing. Could it be we have two faulty RCD's or is there something
we're obviously missing?

Ads
  #2  
Old July 13th 10, 09:26 PM posted to uk.d-i-y
external usenet poster
 
Posts: 9,114
Default RCD test button not tripping the RCD.

In article ,
Rednadnerb writes:
Hi all
After working OK since it was installed a couple of months ago the RCD
started tripping whenever anything was switched on.
After failing to isolate the problem by disconnecting circuits we (the
installer and I) realised that the RCD test button doesn't work, so
after a quick dash to Screwfix we got an identical one and installed
it but it's exactly the same! pressing the yellow test button does
nothing. Could it be we have two faulty RCD's or is there something
we're obviously missing?


Does the RCD have an earth connection? (Most don't, but a few do.)
If it does, I might guess the earth connection is faulty.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #3  
Old July 13th 10, 09:27 PM posted to uk.d-i-y
external usenet poster
 
Posts: 5,416
Default RCD test button not tripping the RCD.

In article .
com, Rednadnerb scribeth thus
Hi all
After working OK since it was installed a couple of months ago the RCD
started tripping whenever anything was switched on.
After failing to isolate the problem by disconnecting circuits we (the
installer and I) realised that the RCD test button doesn't work, so
after a quick dash to Screwfix we got an identical one and installed
it but it's exactly the same! pressing the yellow test button does
nothing. Could it be we have two faulty RCD's or is there something
we're obviously missing?


I might be wrong but you haven't got the input and output's reversed?.

Or a Neutral to Earth short?...
--
Tony Sayer


  #4  
Old July 16th 10, 06:03 PM posted to uk.d-i-y
external usenet poster
 
Posts: 164
Default RCD test button not tripping the RCD.

You got it, a neutral to earth short.
We weren't thorough with our checks, it turned out to be a neutral
wire trapped between the faceplate and the backbox.
Thanks to you both.

Brendan.
  #5  
Old July 17th 10, 01:02 AM posted to uk.d-i-y
external usenet poster
 
Posts: 1,685
Default RCD test button not tripping the RCD.

Do test RCD (or RCBO often).

I nearly got caught out in April 2009 when I cut through an outdoor
cable.
My spine is usually rough (left front quadrant spinal muscle is
essentially missing on an MR scan) so I will drop anything if I sense
problems. On that day I did drop some aluminium, severing a cable, the
RCBO did not trip. I only knew because the cable steamed the puddle I
was standing in. The RCBO would not trip by test button, it had been
tested one year before and all figures were exactly in line with
others & expectations).

Aside - having seen similar RCBO failures, they all ran signficantly
warmer to those nearby. To the extent that a palm run along the top of
the RCBO body (CU lid on) was "point hot". Terminal tightness was not
an issue, nor load (unloaded).
 




Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI test button fails, but tester works? Tim Smith Home Repair 9 April 15th 07 07:44 PM
GFCI test button fails, but tester works? Malissa Baldwin Electronics Repair 0 April 15th 07 07:44 PM
GFCI test button fails, but tester works? Malissa Baldwin Electronics Repair 0 April 15th 07 07:42 PM
GFCI test button fails, but tester works? Malissa Baldwin Electronics Repair 0 April 15th 07 07:41 PM
RCCB not tripping when test button pushed James W UK diy 9 September 27th 03 12:14 AM


All times are GMT +1. The time now is 03:15 PM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.SEO by vBSEO ©2010, Crawlability, Inc.
Copyright 2004-2014 DIYbanter.
The comments are property of their posters.