Hi, All.
What is regarded as the acceptable tolerance for an RCD tripping current? Let's assume a 30mA RCD. I've read that the tollerance is that it must trip between 50% and 100% of the rated value. ( ie it may trip at 15mA and still be in spec ). I didn't trust the source of that quote too much, so I'd like a second opinion. Thanks -- Ron |
#2
Posted to uk.d-i-y
|
|||
|
|||
Tollerance on RCD trip current
"Ron Lowe" wrote in message
... Hi, All. What is regarded as the acceptable tolerance for an RCD tripping current? Let's assume a 30mA RCD. I've read that the tollerance is that it must trip between 50% and 100% of the rated value. ( ie it may trip at 15mA and still be in spec ). I didn't trust the source of that quote too much, so I'd like a second opinion. Thanks -- Ron The standard test is 0.5* trip current (at which it must stay closed) and then at 1* trip current (at which it must trip). Did one yesterday which went at 24mA (30mA type) which is typical using additional ramp test (i.e. exactly what current it trips at). So if it tripped at 15mA (0.5I) it would fail, but 16mA would pass. Mitch |
#3
Posted to uk.d-i-y
|
|||
|
|||
Tollerance on RCD trip current
Mitch wrote:
What is regarded as the acceptable tolerance for an RCD tripping current? Let's assume a 30mA RCD. I've read that the tollerance is that it must trip between 50% and 100% of the rated value. ( ie it may trip at 15mA and still be in spec ). I didn't trust the source of that quote too much, so I'd like a second opinion. The standard test is 0.5* trip current (at which it must stay closed) and then at 1* trip current (at which it must trip). Did one yesterday which went at 24mA (30mA type) which is typical using additional ramp test (i.e. exactly what current it trips at). So if it tripped at 15mA (0.5I) it would fail, but 16mA would pass. Mitch OK, Thanks for that. -- Ron |
#4
Posted to uk.d-i-y
|
|||
|
|||
Tollerance on RCD trip current
On 04/03/2010 18:53, Ron Lowe wrote:
Hi, All. What is regarded as the acceptable tolerance for an RCD tripping current? Let's assume a 30mA RCD. I've read that the tollerance is that it must trip between 50% and 100% of the rated value. ( ie it may trip at 15mA and still be in spec ). I didn't trust the source of that quote too much, so I'd like a second opinion. Thanks As Mitch said, the standard is that it must *not* trip at 15mA and it *must* trip at 30mA. It *must* trip at 150mA (5 * 30mA) within 40ms. In practice, if it trips close to 15mA then it will often be a nuisance, so manufacturers do tend to go for higher trip currents. However, the circuitry in an RCD is cruder than you might think, so any given RCD could be anywhere between (say) 17mA and 27mA trip threshold. Having said that, IME Hager RCDs consistently trip at or about 27mA-28mA, so are a good choice if you are replacing an RCD which is a little over sensitive. |
#5
Posted to uk.d-i-y
|
|||
|
|||
Tollerance on RCD trip current
On 5 Mar, 00:53, Dave Osborne wrote:
On 04/03/2010 18:53, Ron Lowe wrote: Hi, All. What is regarded as the acceptable tolerance for an RCD tripping current? Let's assume a 30mA RCD. I've read that the tollerance is that it must trip between 50% and 100% of the rated value. ( ie it may trip at 15mA and still be in spec ). I didn't trust the source of that quote too much, so I'd like a second opinion. Thanks As Mitch said, the standard is that it must *not* trip at 15mA and it *must* trip at 30mA. It *must* trip at 150mA (5 * 30mA) within 40ms. In practice, if it trips close to 15mA then it will often be a nuisance, so manufacturers do tend to go for higher trip currents. However, the circuitry in an RCD is cruder than you might think, so any given RCD could be anywhere between (say) 17mA and 27mA trip threshold. Having said that, IME Hager RCDs consistently trip at or about 27mA-28mA, so are a good choice if you are replacing an RCD which is a little over sensitive. FWIW every Hager 30mA RCD I have ramp tested seems to trip at 27mA |
#6
Posted to uk.d-i-y
|
|||
|
|||
Tollerance on RCD trip current
Dave Osborne wrote:
On 04/03/2010 18:53, Ron Lowe wrote: Hi, All. What is regarded as the acceptable tolerance for an RCD tripping current? Let's assume a 30mA RCD. I've read that the tollerance is that it must trip between 50% and 100% of the rated value. ( ie it may trip at 15mA and still be in spec ). I didn't trust the source of that quote too much, so I'd like a second opinion. Thanks As Mitch said, the standard is that it must *not* trip at 15mA and it *must* trip at 30mA. It *must* trip at 150mA (5 * 30mA) within 40ms. In practice, if it trips close to 15mA then it will often be a nuisance, so manufacturers do tend to go for higher trip currents. However, the circuitry in an RCD is cruder than you might think, so any given RCD could be anywhere between (say) 17mA and 27mA trip threshold. Having said that, IME Hager RCDs consistently trip at or about 27mA-28mA, so are a good choice if you are replacing an RCD which is a little over sensitive. Very useful information. I have a Crabtree 30 mA trip which I am sure is at the bottom end of the tolerance. Trips quite often when things like PCs and laptop PSUs are switched on. Pain in the neck. I'll fit a Hager when the time comes. Peter Scott |
#7
Posted to uk.d-i-y
|
|||
|
|||
Tollerance on RCD trip current
On 5 Mar, 16:48, Peter Scott wrote:
Dave Osborne wrote: On 04/03/2010 18:53, Ron Lowe wrote: Hi, All. What is regarded as the acceptable tolerance for an RCD tripping current? Let's assume a 30mA RCD. I've read that the tollerance is that it must trip between 50% and 100% of the rated value. ( ie it may trip at 15mA and still be in spec ). I didn't trust the source of that quote too much, so I'd like a second opinion. Thanks As Mitch said, the standard is that it must *not* trip at 15mA and it *must* trip at 30mA. It *must* trip at 150mA (5 * 30mA) within 40ms. In practice, if it trips close to 15mA then it will often be a nuisance, so manufacturers do tend to go for higher trip currents. However, the circuitry in an RCD is cruder than you might think, so any given RCD could be anywhere between (say) 17mA and 27mA trip threshold. Having said that, IME Hager RCDs consistently trip at or about 27mA-28mA, so are a good choice if you are replacing an RCD which is a little over sensitive. Very useful information. I have a Crabtree 30 mA trip which I am sure is at the bottom end of the tolerance. Trips quite often when things like PCs and laptop PSUs are switched on. Pain in the neck. I'll fit a Hager when the time comes. Peter Scott- Hide quoted text - - Show quoted text - I'd suggest ramp testing your existing RCD - it may be tripping at a similar level to the Hager (or not) |
#8
Posted to uk.d-i-y
|
|||
|
|||
Tollerance on RCD trip current
cynic wrote:
On 5 Mar, 16:48, Peter Scott wrote: Dave Osborne wrote: On 04/03/2010 18:53, Ron Lowe wrote: Hi, All. What is regarded as the acceptable tolerance for an RCD tripping current? Let's assume a 30mA RCD. I've read that the tollerance is that it must trip between 50% and 100% of the rated value. ( ie it may trip at 15mA and still be in spec ). I didn't trust the source of that quote too much, so I'd like a second opinion. Thanks As Mitch said, the standard is that it must *not* trip at 15mA and it *must* trip at 30mA. It *must* trip at 150mA (5 * 30mA) within 40ms. In practice, if it trips close to 15mA then it will often be a nuisance, so manufacturers do tend to go for higher trip currents. However, the circuitry in an RCD is cruder than you might think, so any given RCD could be anywhere between (say) 17mA and 27mA trip threshold. Having said that, IME Hager RCDs consistently trip at or about 27mA-28mA, so are a good choice if you are replacing an RCD which is a little over sensitive. Very useful information. I have a Crabtree 30 mA trip which I am sure is at the bottom end of the tolerance. Trips quite often when things like PCs and laptop PSUs are switched on. Pain in the neck. I'll fit a Hager when the time comes. Peter Scott- Hide quoted text - - Show quoted text - I'd suggest ramp testing your existing RCD - it may be tripping at a similar level to the Hager (or not) Good idea. Peter Scott |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Current flow in main neutral vs. current through water meter | Home Repair | |||
Current flow in main neutral vs. current through water meter | Home Repair | |||
Current flow in main neutral vs. current through water meter | Home Repair | |||
trip to NYC | Woodturning | |||
MCB trip | UK diy |