Hi
I've installed some 12V halogen lights in some shelves, such that I have to mount the transformer remotely. I used 3m of normal 1.5mm^2 lighting cable to connect the transformer to the lights, having calculated a 300mV drop across the cable (30mV/A/m x 3.3A x 3m) However in practise I'm losing around 6V in the cable, and have discovered that the transformer output is 125kHz, not 50Hz, explaining the bad attenuation in the cable So my question is - do all compact dimmable 12V transformers have high frequency outputs? I don't have space for an old-fashioned 50Hz transformer Cheers -- Ben Mack Watchfront Electronics - Bespoke R&D - http://www.watchfront.co.uk/ Watchfront Internet - ADSL, Colo - http://www.watchfront.net/ Are you bricking it? - Firewalls - http://www.firebrick.co.uk/ |
| Ads | |
|
#2
|
|||
|
|||
|
In article , Ben Mack
writes Hi I've installed some 12V halogen lights in some shelves, such that I have to mount the transformer remotely. I used 3m of normal 1.5mm^2 lighting cable to connect the transformer to the lights, having calculated a 300mV drop across the cable (30mV/A/m x 3.3A x 3m) However in practise I'm losing around 6V in the cable, and have discovered that the transformer output is 125kHz, not 50Hz, explaining the bad attenuation in the cable Look for another cause to the problem, 100pF/m for the T/E over 3m still gives 4k impedance at 125kHz so unlikely to be causing your 6V problem. Look at minimum load, maximum load, wiring faults & faulty transformer. -- fred Plusnet - I hope you like vanilla |
|
#3
|
|||
|
|||
|
In article ,
Ben Mack wrote: I've installed some 12V halogen lights in some shelves, such that I have to mount the transformer remotely. I used 3m of normal 1.5mm^2 lighting cable to connect the transformer to the lights, having calculated a 300mV drop across the cable (30mV/A/m x 3.3A x 3m) However in practise I'm losing around 6V in the cable, and have discovered that the transformer output is 125kHz, not 50Hz, explaining the bad attenuation in the cable So my question is - do all compact dimmable 12V transformers have high frequency outputs? I don't have space for an old-fashioned 50Hz transformer TLC have a cable calculator for LV lamps. Dunno if it will help with your problem. http://www.tlc-direct.co.uk/Technica...ltageDrop.html -- *You sound reasonable......time to up my medication Dave Plowman London SW To e-mail, change noise into sound. |
|
#4
|
|||
|
|||
|
fred wrote:
In article , Ben Mack writes Hi I've installed some 12V halogen lights in some shelves, such that I have to mount the transformer remotely. I used 3m of normal 1.5mm^2 lighting cable to connect the transformer to the lights, having calculated a 300mV drop across the cable (30mV/A/m x 3.3A x 3m) However in practise I'm losing around 6V in the cable, and have discovered that the transformer output is 125kHz, not 50Hz, explaining the bad attenuation in the cable Look for another cause to the problem, 100pF/m for the T/E over 3m still gives 4k impedance at 125kHz so unlikely to be causing your 6V problem. Look at minimum load, maximum load, wiring faults & faulty transformer. http://en.wikipedia.com/wiki/skin%20effect |
|
#5
|
|||
|
|||
|
Ben Mack wrote:
Hi I've installed some 12V halogen lights in some shelves, such that I have to mount the transformer remotely. I used 3m of normal 1.5mm^2 lighting cable to connect the transformer to the lights, having calculated a 300mV drop across the cable (30mV/A/m x 3.3A x 3m) However in practise I'm losing around 6V in the cable, and have discovered that the transformer output is 125kHz, not 50Hz, explaining the bad attenuation in the cable it doesnt at all. Look for a bad connection or too many bulb watts for the transformer. Bear in mind multimeters may read the 12v wrong if its not sine wave. So my question is - do all compact dimmable 12V transformers have high frequency outputs? I don't have space for an old-fashioned 50Hz transformer tronic TFs are high frequency, toroidals are 50Hz. NT |
|
#6
|
|||
|
|||
|
|
|
#7
|
|||
|
|||
|
Andy Wade wrote:
wrote: it doesnt at all. Look for a bad connection or too many bulb watts for the transformer. Bear in mind multimeters may read the 12v wrong if its not sine wave. The problem here is caused by the inductance of the cable, which I figure will be roughly 0.9 uH per metre. For a 3 m run that's a reactance of about 2 ohms at 125 kHz, so with the 3 A load current mentioned the voltage drop will be about 6 V - more or less as observed :-) The only solutions are to get the electronic 'transformer' nearer to the luminaires, or use a real 50 Hz (iron-cored) transformer. if its 2 core cable the L shuold be vanishingly small, as i is flowing in opposite directions in each core. How do you get your 0,9uH figure? NT |
|
#8
|
|||
|
|||
|
In article , Ian
Stirling writes fred wrote: In article , Ben Mack writes Hi I've installed some 12V halogen lights in some shelves, such that I have to mount the transformer remotely. I used 3m of normal 1.5mm^2 lighting cable to connect the transformer to the lights, having calculated a 300mV drop across the cable (30mV/A/m x 3.3A x 3m) However in practise I'm losing around 6V in the cable, and have discovered that the transformer output is 125kHz, not 50Hz, explaining the bad attenuation in the cable Look for another cause to the problem, 100pF/m for the T/E over 3m still gives 4k impedance at 125kHz so unlikely to be causing your 6V problem. Look at minimum load, maximum load, wiring faults & faulty transformer. http://en.wikipedia.com/wiki/skin%20effect Only 5% increase in impedance on 1.5mm2 @ 125k -- fred Plusnet - I hope you like vanilla |
|
#9
|
|||
|
|||
|
|
|
#10
|
|||
|
|||
|
fred wrote:
Only 5% increase in impedance on 1.5mm2 @ 125k Only 5% increase in *resistance* due to skin effect, perhaps, but a huge increase in *impedance* due to the inductive reactance... -- Andy |
| Thread Tools | |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Low Voltage Lighting (MoonRays) + Swimming Pool? | Bob | Home Repair | 0 | April 21st 06 04:37 PM |
| Toshiba high voltage problem | Bobby Villamor | Electronics Repair | 4 | November 22nd 04 11:40 PM |
| Which is the advantage of low voltage lighting? | Faustino Dina | Home Repair | 12 | January 31st 04 09:18 PM |
| 12 volt lighting transformer tips | Paul Furman | Home Repair | 8 | December 8th 03 09:56 PM |
| Low Voltage Lighting | MLB | Home Repair | 0 | July 3rd 03 09:34 PM |