Hi,

I am having a problem with double light switch in my kitchen...and
would appreciate any advice before I call out an electrician.

In the kitchen I have a double switch (in a single gang faceplate) that
separately operates a ceiling light and a set of under cupboard lights.
The kitchen was rewired by an electrician about 6 years ago when we had
a kitchen fitted.

For a while this one switch has been playing up - depending on how
hard/fast you switched off the under cupboard lights would either blow
the lighting circuit fuse (5A) or possibly trip the whole house circuit
- I say possibly because I have recently fitted a plug in trip fuse for
the consumer unit (just on this lighting circuit) to avoid having to
fit a new 5A fuse in the dark each time the fuse went - and now the
house earth leakage circuit breaker trips out as well.

This week the switch has started tripping the electric almost every
time it is used.
There is some soot/ burning to the inside of the undercupboard switch.

The new fuse/trip device in the consumer unit is the only change.Thsi
repalced the old style 5Amp fuse holder at the consumer unit with a new
plug in trip type which was at 6A (Wylex to match consumer unit). This
was to avoid having to replace the fuse which used to go in the
lighting circuit when the undercupboard lights


On inspection of the switch wiring there are two cables entering the
switch backplate - both earths are connected to the metal back box. On
the switch for ceiling light cavle ones red and black wire are
connected to switch one COM and L1. There is a jumper wire from this
switch L1 to switch 2 L1. The 2nd incoming mains cable has the neutral
cable taped up (not connected) and the red cable enters switch 2 COM.

There is a junction box above the kitchen cupboard that the electrican
has used to extend the old switch cable to the current position. On
inspection the two switch cables (from switch back box) go to this
junction box and connect separately to two further cables that go to
the ceiling (upstairs floor ) - connections in this junction box are
cable1 neutral to neutral / cable 1 live to live ; and cable2 neutral
to neutral and cable2 live to live. Earths are all connected together.
This junction box looks to do no more than extend the switch cable run,


The cable to the ceiling light is just that - a junction box / ceiling
rose is not visible. When the kitchen was rewired the electrians had
the floor in the bedroom above the kitchen up so I presume any
junctions boxes are under the floorboards...and I haven't considered
removing the carpet / floorboards yet to look for them. .

I guess my questions are ...
- Does the cabling sound right (jumper etc from switch 1 to switch 2)
- Any ideas what would cause it to trip ...(this happens even if all
the undercupoard lights are turned off (they each have a built in
switch).
- Should I go back to the old style cartidge fuse ?

The trip unit on my house wiring is an earth leakage circuit breaker
(my earth comes from a ground rod) .

Many thanks...
Nick

  #2   Report Post  
Posted to uk.d-i-y
mitchd
 
Posts: n/a
Default Switch wiring question

wrote:
Hi,

I am having a problem with double light switch in my kitchen...and
would appreciate any advice before I call out an electrician.

In the kitchen I have a double switch (in a single gang faceplate) that
separately operates a ceiling light and a set of under cupboard lights.
The kitchen was rewired by an electrician about 6 years ago when we had
a kitchen fitted.

For a while this one switch has been playing up - depending on how
hard/fast you switched off the under cupboard lights would either blow
the lighting circuit fuse (5A) or possibly trip the whole house circuit
- I say possibly because I have recently fitted a plug in trip fuse for
the consumer unit (just on this lighting circuit) to avoid having to
fit a new 5A fuse in the dark each time the fuse went - and now the
house earth leakage circuit breaker trips out as well.

This week the switch has started tripping the electric almost every
time it is used.
There is some soot/ burning to the inside of the undercupboard switch.

The new fuse/trip device in the consumer unit is the only change.Thsi
repalced the old style 5Amp fuse holder at the consumer unit with a new
plug in trip type which was at 6A (Wylex to match consumer unit). This
was to avoid having to replace the fuse which used to go in the
lighting circuit when the undercupboard lights


On inspection of the switch wiring there are two cables entering the
switch backplate - both earths are connected to the metal back box. On
the switch for ceiling light cavle ones red and black wire are
connected to switch one COM and L1. There is a jumper wire from this
switch L1 to switch 2 L1. The 2nd incoming mains cable has the neutral
cable taped up (not connected) and the red cable enters switch 2 COM.

There is a junction box above the kitchen cupboard that the electrican
has used to extend the old switch cable to the current position. On
inspection the two switch cables (from switch back box) go to this
junction box and connect separately to two further cables that go to
the ceiling (upstairs floor ) - connections in this junction box are
cable1 neutral to neutral / cable 1 live to live ; and cable2 neutral
to neutral and cable2 live to live. Earths are all connected together.
This junction box looks to do no more than extend the switch cable run,

is there four twin and earth cables into this junction box?


The cable to the ceiling light is just that - a junction box / ceiling
rose is not visible. When the kitchen was rewired the electrians had
the floor in the bedroom above the kitchen up so I presume any
junctions boxes are under the floorboards...and I haven't considered
removing the carpet / floorboards yet to look for them. .

I guess my questions are ...
- Does the cabling sound right (jumper etc from switch 1 to switch 2)
- Any ideas what would cause it to trip ...(this happens even if all
the undercupoard lights are turned off (they each have a built in
switch).
- Should I go back to the old style cartidge fuse ?

The trip unit on my house wiring is an earth leakage circuit breaker
(my earth comes from a ground rod) .

Many thanks...
Nick


switch sounds ok, one of the black wire as a "switched"(Live) wire, have
the lights ever worked?if they have it prob a faulty light, have you
done/had done any work in kitchen that could have damaged a cable?

  #3   Report Post  
Posted to uk.d-i-y
 
Posts: n/a
Default Switch wiring question

wrote:

Hi,

I am having a problem with double light switch in my kitchen...and
would appreciate any advice before I call out an electrician.

In the kitchen I have a double switch (in a single gang faceplate) that
separately operates a ceiling light and a set of under cupboard lights.
The kitchen was rewired by an electrician about 6 years ago when we had
a kitchen fitted.

For a while this one switch has been playing up - depending on how
hard/fast you switched off the under cupboard lights would either blow
the lighting circuit fuse (5A) or possibly trip the whole house circuit
- I say possibly because I have recently fitted a plug in trip fuse for
the consumer unit (just on this lighting circuit) to avoid having to
fit a new 5A fuse in the dark each time the fuse went - and now the
house earth leakage circuit breaker trips out as well.

This week the switch has started tripping the electric almost every
time it is used.
There is some soot/ burning to the inside of the undercupboard switch.

The new fuse/trip device in the consumer unit is the only change.Thsi
repalced the old style 5Amp fuse holder at the consumer unit with a new
plug in trip type which was at 6A (Wylex to match consumer unit). This
was to avoid having to replace the fuse which used to go in the
lighting circuit when the undercupboard lights


On inspection of the switch wiring there are two cables entering the
switch backplate - both earths are connected to the metal back box. On
the switch for ceiling light cavle ones red and black wire are
connected to switch one COM and L1. There is a jumper wire from this
switch L1 to switch 2 L1. The 2nd incoming mains cable has the neutral
cable taped up (not connected) and the red cable enters switch 2 COM.

There is a junction box above the kitchen cupboard that the electrican
has used to extend the old switch cable to the current position. On
inspection the two switch cables (from switch back box) go to this
junction box and connect separately to two further cables that go to
the ceiling (upstairs floor ) - connections in this junction box are
cable1 neutral to neutral / cable 1 live to live ; and cable2 neutral
to neutral and cable2 live to live. Earths are all connected together.
This junction box looks to do no more than extend the switch cable run,


The cable to the ceiling light is just that - a junction box / ceiling
rose is not visible. When the kitchen was rewired the electrians had
the floor in the bedroom above the kitchen up so I presume any
junctions boxes are under the floorboards...and I haven't considered
removing the carpet / floorboards yet to look for them. .



any fitting with any signs of charring at all should be replaced,
however slight.


I guess my questions are ...
- Does the cabling sound right (jumper etc from switch 1 to switch 2)


that'll be the unswitched live

- Any ideas what would cause it to trip ...(this happens even if all
the undercupoard lights are turned off (they each have a built in
switch).


since both mcb and rcd trip, sounds like a toast situation. Find out
whats toasted and replace it before something catches fire.


- Should I go back to the old style cartidge fuse ?


no

The trip unit on my house wiring is an earth leakage circuit breaker
(my earth comes from a ground rod) .



You need to find out where the fault is. Trips on switch off typically
result from a switch being in the neutral line. You can use a
multimeter (in most cases) to find what is conducting slightly when it
shouldnt be. Maybe switch, light fitting, or cable. With item under
test disconnected, measure from earth to L&N connected. Also measure L
to N with bulb removed. You should get no conduction anywhere if things
are ok.

Obviously turn supply power off before disconnecting anything, leave
alone if you dont know what youre doing etc.


But dont leave it like this, it sounds like a fire starter.


NT

  #4   Report Post  
Posted to uk.d-i-y
marble
 
Posts: n/a
Default Switch wiring question

On 7 Jan 2006 04:31:31 -0800, wrote:

Hi,

I am having a problem with double light switch in my kitchen...and
would appreciate any advice before I call out an electrician.

In the kitchen I have a double switch (in a single gang faceplate) that


I guesse you mean the faceplate is 2 gang and the back box is single
width.

separately operates a ceiling light and a set of under cupboard lights.
The kitchen was rewired by an electrician about 6 years ago when we had
a kitchen fitted.

For a while this one switch has been playing up - depending on how
hard/fast you switched off the under cupboard lights would either blow
the lighting circuit fuse (5A) or possibly trip the whole house circuit
- I say possibly because I have recently fitted a plug in trip fuse for
the consumer unit (just on this lighting circuit) to avoid having to
fit a new 5A fuse in the dark each time the fuse went - and now the
house earth leakage circuit breaker trips out as well.


You have a short to earth and as its taking out the mcb aswell its
probably from a live.


This week the switch has started tripping the electric almost every
time it is used.
There is some soot/ burning to the inside of the undercupboard switch.


The soot is the clue!

Have the earths got yellow/green sleeving over them??? If not then put
some on as this is probably the problem.

Otherwise replace the switch and make sure the wires are not lose ie
tighten the screw terminals and make sure the cables have not had the
core exposed maybe the electrician had accidentaly scrapped some off
the live wire when he was removing the outer sheathing, this could be
fixed with some insulation tape.



I guess my questions are ...
- Does the cabling sound right (jumper etc from switch 1 to switch 2)

Its OK
- Any ideas what would cause it to trip ...(this happens even if all
the undercupoard lights are turned off (they each have a built in
switch).


There is an earth short from the feed to the undercupboard lights -
that is the red wire that goes to the cable that has got its black
core taped up.

- Should I go back to the old style cartidge fuse ?


No, nothing wrong with the mcb, its telling you there is a problem.

  #5   Report Post  
Posted to uk.d-i-y
Sadly
 
Posts: n/a
Default Switch wiring question


wrote:
Hi,

I am having a problem with double light switch in my kitchen...and
would appreciate any advice before I call out an electrician.

In the kitchen I have a double switch (in a single gang faceplate) that
separately operates a ceiling light and a set of under cupboard lights.
The kitchen was rewired by an electrician about 6 years ago when we had
a kitchen fitted.

For a while this one switch has been playing up - depending on how
hard/fast you switched off the under cupboard lights would either blow
the lighting circuit fuse (5A) or possibly trip the whole house circuit
- I say possibly because I have recently fitted a plug in trip fuse for
the consumer unit (just on this lighting circuit) to avoid having to
fit a new 5A fuse in the dark each time the fuse went - and now the
house earth leakage circuit breaker trips out as well.

This week the switch has started tripping the electric almost every
time it is used.
There is some soot/ burning to the inside of the undercupboard switch.

The new fuse/trip device in the consumer unit is the only change.Thsi
repalced the old style 5Amp fuse holder at the consumer unit with a new
plug in trip type which was at 6A (Wylex to match consumer unit). This
was to avoid having to replace the fuse which used to go in the
lighting circuit when the undercupboard lights


On inspection of the switch wiring there are two cables entering the
switch backplate - both earths are connected to the metal back box. On
the switch for ceiling light cavle ones red and black wire are
connected to switch one COM and L1. There is a jumper wire from this
switch L1 to switch 2 L1. The 2nd incoming mains cable has the neutral
cable taped up (not connected) and the red cable enters switch 2 COM.

There is a junction box above the kitchen cupboard that the electrican
has used to extend the old switch cable to the current position. On
inspection the two switch cables (from switch back box) go to this
junction box and connect separately to two further cables that go to
the ceiling (upstairs floor ) - connections in this junction box are
cable1 neutral to neutral / cable 1 live to live ; and cable2 neutral
to neutral and cable2 live to live. Earths are all connected together.
This junction box looks to do no more than extend the switch cable run,


The cable to the ceiling light is just that - a junction box / ceiling
rose is not visible. When the kitchen was rewired the electrians had
the floor in the bedroom above the kitchen up so I presume any
junctions boxes are under the floorboards...and I haven't considered
removing the carpet / floorboards yet to look for them. .

I guess my questions are ...
- Does the cabling sound right (jumper etc from switch 1 to switch 2)
- Any ideas what would cause it to trip ...(this happens even if all
the undercupoard lights are turned off (they each have a built in
switch).
- Should I go back to the old style cartidge fuse ?

The trip unit on my house wiring is an earth leakage circuit breaker
(my earth comes from a ground rod) .

Many thanks...
Nick


Sounds a bit rum to me.

Normally a light switch gets a live in, and a switched live out.

If you are taking these in using a normal twin-and-earth cable the
black wire needs some red sleeving (or red tape) near the end to
signify that it caries live nor neutral.

When doing this it is usual to put the live on the red and the
switched-live on the black-with-red-bit.

For one thing it looks as if your setup has it the other way around.

Also, you seem to have live coming in via one cable only and switched
live going out in both. This is a bit strange, especially as the
junction box would be a great place to common together the lives if it
was not available up-stream for the under cupboard lights.

Why would the electricial have joined cable-2 neutral in the junction
box when he wasn't using it in the light switch? I wonder what is
connected to the other end of it!

I don't like the sound of this at all - a slightly odd wiring setup
that keeps blowing fuses. I would either check the whole lot myself
(including checking what is under that floor) or get in someone that
can be trusted to check it all for you. I wouldn't ask the original guy
back!



  #6   Report Post  
Posted to uk.d-i-y
 
Posts: n/a
Default Switch wiring question

Yes - 4 twin and earth into the junction box - but in two pairs .
Yes the lights have all worked - for atleast 5 years.
No work done in kitchen or anywhere else.
Ref faulty light - see below for it still tripping with lights
disconnected.

I have tried disconnecting all the under cupboard lights - the
electrician actually put in three drops from ceiling - which terminate
in junction boxes fixed to underside of wall units. The inidivual light
fittings (3) are connected to a separate junction box at the bottom of
each of the three cable drops.

The lights (link lights) are connected to the junction boxes - so I
have disconnected each light fitting in case one of these has gone bad
....but this didn't make a difference. The only thing I can think is
that one of the junction boxes under the wall cupboard has corroded
inside due to moisture ingress and when the switched live is applied
this trips the circuit ??

Additionally today I tried bypassing the two "extension" cables (both
twin and earth) that drop from this junction box to the wall switches.
For the main ceiling lights the twin and earth is suppling a live
(preumably looped in from a junction box under the upstairs floor) and
the black wire is as expected a switched live feed back to the light
(it's not marked with red tape though). A simple test joining the black
and red from cable one (which is all the switch one would do) and as
expected the ceiling lights are on (once power back on of course).

Based on the use of the jumper from switch 1 COM to switch 2 COM I
believe the second twin and earth is actually only supplying a switched
live back up to the junction box supplying the under cupboard lights.
If I join the red (this must have been acting as switched live before
as black wire is taped up unconnected in switch) from cable 2 to the
live red from cable one I would expect the under cupboard lights to be
on.....but this trips the earth leakage cicuit breaker the second the
power is restored.

I also tried going back to standard fuse on the circuit instead of the
MCB - no differnce apart from I'm now a gew 5A fuses down.


Apart from the moisture what about mice eating throug a cable - I had
a brief look under floor upstairs today but no signs of any damage.

Thanks so far...
Nick

  #7   Report Post  
Posted to uk.d-i-y
 
Posts: n/a
Default Switch wiring question

wrote:

Hi,

I am having a problem with double light switch in my kitchen...and
would appreciate any advice before I call out an electrician.

In the kitchen I have a double switch (in a single gang faceplate) that
separately operates a ceiling light and a set of under cupboard lights.
The kitchen was rewired by an electrician about 6 years ago when we had
a kitchen fitted.

For a while this one switch has been playing up - depending on how
hard/fast you switched off the under cupboard lights would either blow
the lighting circuit fuse (5A) or possibly trip the whole house circuit
- I say possibly because I have recently fitted a plug in trip fuse for
the consumer unit (just on this lighting circuit) to avoid having to
fit a new 5A fuse in the dark each time the fuse went - and now the
house earth leakage circuit breaker trips out as well.

This week the switch has started tripping the electric almost every
time it is used.
There is some soot/ burning to the inside of the undercupboard switch.

The new fuse/trip device in the consumer unit is the only change.Thsi
repalced the old style 5Amp fuse holder at the consumer unit with a new
plug in trip type which was at 6A (Wylex to match consumer unit). This
was to avoid having to replace the fuse which used to go in the
lighting circuit when the undercupboard lights


On inspection of the switch wiring there are two cables entering the
switch backplate - both earths are connected to the metal back box. On
the switch for ceiling light cavle ones red and black wire are
connected to switch one COM and L1. There is a jumper wire from this
switch L1 to switch 2 L1. The 2nd incoming mains cable has the neutral
cable taped up (not connected) and the red cable enters switch 2 COM.

There is a junction box above the kitchen cupboard that the electrican
has used to extend the old switch cable to the current position. On
inspection the two switch cables (from switch back box) go to this
junction box and connect separately to two further cables that go to
the ceiling (upstairs floor ) - connections in this junction box are
cable1 neutral to neutral / cable 1 live to live ; and cable2 neutral
to neutral and cable2 live to live. Earths are all connected together.
This junction box looks to do no more than extend the switch cable run,


The cable to the ceiling light is just that - a junction box / ceiling
rose is not visible. When the kitchen was rewired the electrians had
the floor in the bedroom above the kitchen up so I presume any
junctions boxes are under the floorboards...and I haven't considered
removing the carpet / floorboards yet to look for them. .



any fitting with any signs of charring at all should be replaced,
however slight.


I guess my questions are ...
- Does the cabling sound right (jumper etc from switch 1 to switch 2)


that'll be the unswitched live

- Any ideas what would cause it to trip ...(this happens even if all
the undercupoard lights are turned off (they each have a built in
switch).


since both mcb and rcd trip, sounds like a toast situation. Find out
whats toasted and replace it before something catches fire.


- Should I go back to the old style cartidge fuse ?


no

The trip unit on my house wiring is an earth leakage circuit breaker
(my earth comes from a ground rod) .



You need to find out where the fault is. Trips on switch off typically
result from a switch being in the neutral line. You can use a
multimeter (in most cases) to find what is conducting slightly when it
shouldnt be. Maybe switch, light fitting, or cable. With item under
test disconnected, measure from earth to L&N connected. Also measure L
to N with bulb removed. You should get no conduction anywhere if things
are ok.

Obviously turn supply power off before disconnecting anything, leave
alone if you dont know what youre doing etc.


But dont leave it like this, it sounds like a fire starter.


NT

  #8   Report Post  
Posted to uk.d-i-y
 
Posts: n/a
Default Switch wiring question

wrote:

Hi,

I am having a problem with double light switch in my kitchen...and
would appreciate any advice before I call out an electrician.

In the kitchen I have a double switch (in a single gang faceplate) that
separately operates a ceiling light and a set of under cupboard lights.
The kitchen was rewired by an electrician about 6 years ago when we had
a kitchen fitted.

For a while this one switch has been playing up - depending on how
hard/fast you switched off the under cupboard lights would either blow
the lighting circuit fuse (5A) or possibly trip the whole house circuit
- I say possibly because I have recently fitted a plug in trip fuse for
the consumer unit (just on this lighting circuit) to avoid having to
fit a new 5A fuse in the dark each time the fuse went - and now the
house earth leakage circuit breaker trips out as well.

This week the switch has started tripping the electric almost every
time it is used.
There is some soot/ burning to the inside of the undercupboard switch.

The new fuse/trip device in the consumer unit is the only change.Thsi
repalced the old style 5Amp fuse holder at the consumer unit with a new
plug in trip type which was at 6A (Wylex to match consumer unit). This
was to avoid having to replace the fuse which used to go in the
lighting circuit when the undercupboard lights


On inspection of the switch wiring there are two cables entering the
switch backplate - both earths are connected to the metal back box. On
the switch for ceiling light cavle ones red and black wire are
connected to switch one COM and L1. There is a jumper wire from this
switch L1 to switch 2 L1. The 2nd incoming mains cable has the neutral
cable taped up (not connected) and the red cable enters switch 2 COM.

There is a junction box above the kitchen cupboard that the electrican
has used to extend the old switch cable to the current position. On
inspection the two switch cables (from switch back box) go to this
junction box and connect separately to two further cables that go to
the ceiling (upstairs floor ) - connections in this junction box are
cable1 neutral to neutral / cable 1 live to live ; and cable2 neutral
to neutral and cable2 live to live. Earths are all connected together.
This junction box looks to do no more than extend the switch cable run,


The cable to the ceiling light is just that - a junction box / ceiling
rose is not visible. When the kitchen was rewired the electrians had
the floor in the bedroom above the kitchen up so I presume any
junctions boxes are under the floorboards...and I haven't considered
removing the carpet / floorboards yet to look for them. .



any fitting with any signs of charring at all should be replaced,
however slight.


I guess my questions are ...
- Does the cabling sound right (jumper etc from switch 1 to switch 2)


that'll be the unswitched live

- Any ideas what would cause it to trip ...(this happens even if all
the undercupoard lights are turned off (they each have a built in
switch).


since both mcb and rcd trip, sounds like a toast situation. Find out
whats toasted and replace it before something catches fire.


- Should I go back to the old style cartidge fuse ?


no

The trip unit on my house wiring is an earth leakage circuit breaker
(my earth comes from a ground rod) .



You need to find out where the fault is. Trips on switch off typically
result from a switch being in the neutral line. You can use a
multimeter (in most cases) to find what is conducting slightly when it
shouldnt be. Maybe switch, light fitting, or cable. With item under
test disconnected, measure from earth to L&N connected. Also measure L
to N with bulb removed. You should get no conduction anywhere if things
are ok.

Obviously turn supply power off before disconnecting anything, leave
alone if you dont know what youre doing etc.


But dont leave it like this, it sounds like a fire starter.


NT

  #9   Report Post  
Posted to uk.d-i-y
marble
 
Posts: n/a
Default Switch wiring question

On 8 Jan 2006 17:09:57 -0800, wrote:

Yes - 4 twin and earth into the junction box - but in two pairs .
Yes the lights have all worked - for atleast 5 years.
No work done in kitchen or anywhere else.
Ref faulty light - see below for it still tripping with lights
disconnected.

I have tried disconnecting all the under cupboard lights - the
electrician actually put in three drops from ceiling - which terminate
in junction boxes fixed to underside of wall units. The inidivual light
fittings (3) are connected to a separate junction box at the bottom of
each of the three cable drops.

The lights (link lights) are connected to the junction boxes - so I
have disconnected each light fitting in case one of these has gone bad
...but this didn't make a difference. The only thing I can think is
that one of the junction boxes under the wall cupboard has corroded
inside due to moisture ingress and when the switched live is applied
this trips the circuit ??


Junction boxes dont corrode, they are plastic and brass. Why havn't
you looked inside them yet?

Additionally today I tried bypassing the two "extension" cables (both
twin and earth) that drop from this junction box to the wall switches.
For the main ceiling lights the twin and earth is suppling a live
(preumably looped in from a junction box under the upstairs floor) and
the black wire is as expected a switched live feed back to the light
(it's not marked with red tape though). A simple test joining the black
and red from cable one (which is all the switch one would do) and as
expected the ceiling lights are on (once power back on of course).

Based on the use of the jumper from switch 1 COM to switch 2 COM I
believe the second twin and earth is actually only supplying a switched
live back up to the junction box supplying the under cupboard lights.
If I join the red (this must have been acting as switched live before
as black wire is taped up unconnected in switch) from cable 2 to the
live red from cable one I would expect the under cupboard lights to be
on.....but this trips the earth leakage cicuit breaker the second the
power is restored.

I also tried going back to standard fuse on the circuit instead of the
MCB - no differnce apart from I'm now a gew 5A fuses down.


Apart from the moisture what about mice eating throug a cable - I had
a brief look under floor upstairs today but no signs of any damage.


Can you get access to the junction box now? Its going to be crowded in
there with the 3 feeds to the other junction boxes, maybe the switched
live has come lose in this one or one of the others and is touching an
earth.

If there is a fault in the cable that caries the switched live you
could maybe use the currently tapped over core to be the switched live
if it turns out the short is in between the red core and earth.


Thanks so far...
Nick

  #10   Report Post  
Posted to uk.d-i-y
mitchd
 
Posts: n/a
Default Switch wiring question

wrote:
Yes - 4 twin and earth into the junction box - but in two pairs .
Yes the lights have all worked - for atleast 5 years.
No work done in kitchen or anywhere else.
Ref faulty light - see below for it still tripping with lights
disconnected.

I have tried disconnecting all the under cupboard lights - the
electrician actually put in three drops from ceiling - which terminate
in junction boxes fixed to underside of wall units. The inidivual light
fittings (3) are connected to a separate junction box at the bottom of
each of the three cable drops.

The lights (link lights) are connected to the junction boxes - so I
have disconnected each light fitting in case one of these has gone bad
...but this didn't make a difference. The only thing I can think is
that one of the junction boxes under the wall cupboard has corroded
inside due to moisture ingress and when the switched live is applied
this trips the circuit ??

Additionally today I tried bypassing the two "extension" cables (both
twin and earth) that drop from this junction box to the wall switches.
For the main ceiling lights the twin and earth is suppling a live
(preumably looped in from a junction box under the upstairs floor) and
the black wire is as expected a switched live feed back to the light
(it's not marked with red tape though). A simple test joining the black
and red from cable one (which is all the switch one would do) and as
expected the ceiling lights are on (once power back on of course).

Based on the use of the jumper from switch 1 COM to switch 2 COM I
believe the second twin and earth is actually only supplying a switched
live back up to the junction box supplying the under cupboard lights.
If I join the red (this must have been acting as switched live before
as black wire is taped up unconnected in switch) from cable 2 to the
live red from cable one I would expect the under cupboard lights to be
on.....but this trips the earth leakage cicuit breaker the second the
power is restored.

I also tried going back to standard fuse on the circuit instead of the
MCB - no differnce apart from I'm now a gew 5A fuses down.


Apart from the moisture what about mice eating throug a cable - I had
a brief look under floor upstairs today but no signs of any damage.

Thanks so far...
Nick


stick with the mcb, you defo have a short on cable to undershelf lights
best way to test is with a 500v insulation tester, prob light switch is
now faulty, don't try to switch on again until fault fixed, will damage
mcb next, fault is prob under flooring somewhere, maybe cable trapped
under floorboard? best to lift flooring and try to trace route of cable,
really you should now get a electricin in tho

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Re-Post for Wall Switch Harry Home Repair 1 July 27th 05 06:56 PM
Electrical question about a switch D. J. Dorn Woodworking 9 January 21st 05 01:29 PM
Wiring a two-way dimmer switch - am I dim? [email protected] UK diy 10 October 17th 04 02:58 PM
Duplex Switch Wiring Help Patrick Gillette Home Repair 8 January 23rd 04 05:21 PM
Help with Wiring an On/Off Switch Glen Electronics 0 August 14th 03 04:14 AM


All times are GMT +1. The time now is 09:04 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"