Looking at a mates ring circuit wiring, the original builder (1950's
bungalow) has wired the only ring final circuit up from the CU into the
loft space, done a lap of the loft and then back to the CU. At each
socket position there is a junction box, which takes off a single 2.5mm
sq unfused spur and drops it down a conduit to the socket 5' away.

The question is, is this style of wiring still permissible? It violates
the guideline of having no more spurs per circuit than there are actual
outlets directly on it, but I can't find anything in the regs that
explicitly forbids it.

(For various reasons, he is keen to rewire with as little disruption as
possible and is happy to accept the limted numbers of sockets etc he
currently has - so being able to reuse the conduit drops to the sockets
would be ideal, but they are only large enough for one cable, unless the
circuit is wired in singles and conduit added everywhere).



Background for those that are interested:

Got a call from my friend the other day to say that he just had a new
washing machine delivered, and his house nearly managed to electrocute
the delivery bod! Anyway we traced the problem to a disconnected earth
on the socket in question, capacitive filters on the appliance input,
and earthed pipes. Anyway we fixed that easy enough.

However a look at the general state of the wiring leads us to suspect
that it could probably do with a rewire PDQ. So I thought it prudent to
do some tests on it.

There are three/four [1] circuits in total, connected to to three
rewireable fuses. All the cable is rubber or PBJ insulated (inner and
outer), unearthed on the lighting circuit. Separate steel earth wire on
an ex-cooker point radial (this was the one that was disconnected), and
T&E construction on the ring circuit cable.

The Earth fault loop impedance was actually not bad considering (no
worse than 0.25 ohm in most places, rising to 0.7 on the end of several
cascaded 4 way trailing leads!). TN-S supply.

Insulation resistance on the lighting and ex-cooker point circuit was
also ok at 200M Ohm @ 500V (surprisingly!). The ring circuit however
was another matter. The best isolation between any pair of conductors
being 40K ohms! The (inner) cable insulation was visibly disintegrating
and would fall off if the wire was bent about much.


[1] The lighting circuit seems to have two cables terminating at the CU.
There is an open circuit between them, leading to the conclusion there
may in fact be two separate circuits (12 light fittings - so that would
also suggest more than one). For some reason however they are terminated
on one fuse, in spite of there being three spare ways in the CU complete
with unused 5A fuses!

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #2   Report Post  
Andrew Gabriel
 
Posts: n/a
Default

In article ,
John Rumm writes:

Looking at a mates ring circuit wiring, the original builder (1950's
bungalow) has wired the only ring final circuit up from the CU into the
loft space, done a lap of the loft and then back to the CU. At each
socket position there is a junction box, which takes off a single 2.5mm
sq unfused spur and drops it down a conduit to the socket 5' away.

The question is, is this style of wiring still permissible?


Yes.

It violates
the guideline of having no more spurs per circuit than there are actual
outlets directly on it, but I can't find anything in the regs that
explicitly forbids it.


The reason behind that is that rings normally have no spurs when
initially installed, and are extended with spurs. When you get to
the point where it's doubled in size with added spurs, then it's
time to reevaluate the adiquacy of the original design.

Given that this ring was not installed that way, then you need to
use your own judgement to decide if it's time to consider if the
ring is too big and needs splitting or has been hacked around so
much that it could do with reinstalling.

Background for those that are interested:

Got a call from my friend the other day to say that he just had a new
washing machine delivered, and his house nearly managed to electrocute
the delivery bod! Anyway we traced the problem to a disconnected earth
on the socket in question, capacitive filters on the appliance input,
and earthed pipes. Anyway we fixed that easy enough.


One issue with that would be you can't get two connections to each
socket for separate earth paths, not that this is required for just
a washing machine in any case.

The Earth fault loop impedance was actually not bad considering (no
worse than 0.25 ohm in most places, rising to 0.7 on the end of several
cascaded 4 way trailing leads!). TN-S supply.


That's one reason why extension cords are bad things, and daisy
chaining extension cords and/or multi-way socket blocks is a very
bad thing.

Insulation resistance on the lighting and ex-cooker point circuit was
also ok at 200M Ohm @ 500V (surprisingly!). The ring circuit however
was another matter. The best isolation between any pair of conductors
being 40K ohms! The (inner) cable insulation was visibly disintegrating
and would fall off if the wire was bent about much.


Rubber when it was in good condition actually has a higher insulation
resistance than PVC.

--
Andrew Gabriel

  #3   Report Post  
Owain
 
Posts: n/a
Default

John Rumm wrote:
(For various reasons, he is keen to rewire with as little disruption as
possible and is happy to accept the limted numbers of sockets etc he
currently has


He might be, but IMHO it would be irresponsible to install a circuit
which would not be sufficient for the purpose by today's standards.

- so being able to reuse the conduit drops to the sockets
would be ideal, but they are only large enough for one cable, unless the
circuit is wired in singles and conduit added everywhere).


Would it be acceptable to go *down* one conduit to a socket,
horizontally along the wall (either chased or mini-trunking) with
intermediate sockets, to socket at another conduit and then back *up*?

If minitrunking, a bit of slack would offer the possibility of chasing
in at a later date. Horizontally between accessories is a permitted zone.

An alternative is to use radials, not rings. Then any additional sockets
required can be spurred off existing socket locations, without having to
do down-along-up to preserve continuity of a ring.

Another thought is MICC cable might be thin enough to get 2x down a
conduit. IIRC rings only need 1.5mm minimum in MICC, not 2.5mm? Would
involve some faffing and making good at the socket locations though to
accommodate the glands.

Owain


  #4   Report Post  
John Rumm
 
Posts: n/a
Default

Owain wrote:

He might be, but IMHO it would be irresponsible to install a circuit
which would not be sufficient for the purpose by today's standards.


Personally I would tend to agree, and would try to guide him toward a
slightly more elaborate setup (the whole house currently only has about
10 sockets (mostly doubles) in total). Having said that, I can also see
why he is keen to do the minimum possible since he only owns one third
of the house (was left to him and his sisters) so recouping the cost of
any work whe he sells is harder, and the sisters will just cop a bigger
CGT bill.

Would it be acceptable to go *down* one conduit to a socket,
horizontally along the wall (either chased or mini-trunking) with
intermediate sockets, to socket at another conduit and then back *up*?


Could be in some cases...

If minitrunking, a bit of slack would offer the possibility of chasing
in at a later date. Horizontally between accessories is a permitted zone.


Yup, I may suggest that for some areas.

An alternative is to use radials, not rings. Then any additional sockets
required can be spurred off existing socket locations, without having to
do down-along-up to preserve continuity of a ring.


I did think of that, but you don't gain much in this case since I don't
think you can get 4mm^2 cable down the conduit either, you would still
be limited to 2.5mm^2 conduit drops. So extension would still have to be
via a new drop rather than from an existing socket.

Another thought is MICC cable might be thin enough to get 2x down a
conduit. IIRC rings only need 1.5mm minimum in MICC, not 2.5mm? Would
involve some faffing and making good at the socket locations though to
accommodate the glands.


Would probably be simpler to go for singles in the conduit in that case
I would have thought?


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #5   Report Post  
John Rumm
 
Posts: n/a
Default

Andrew Gabriel wrote:

The reason behind that is that rings normally have no spurs when
initially installed, and are extended with spurs. When you get to
the point where it's doubled in size with added spurs, then it's
time to reevaluate the adiquacy of the original design.

Given that this ring was not installed that way, then you need to
use your own judgement to decide if it's time to consider if the
ring is too big and needs splitting or has been hacked around so
much that it could do with reinstalling.


This place is like a little island in time wrt wiring. Original install,
with practically no mods made to it since (one, possibly two extra
sockets added, and one cooker point converted to feed a socket).
Everything else seems much as it was when installed. (even the MK socket
faces which have four securing screws - two at the top and two at the
bottom).

Insulation resistance on the lighting and ex-cooker point circuit was
also ok at 200M Ohm @ 500V (surprisingly!). The ring circuit however
was another matter. The best isolation between any pair of conductors
being 40K ohms! The (inner) cable insulation was visibly disintegrating
and would fall off if the wire was bent about much.



Rubber when it was in good condition actually has a higher insulation
resistance than PVC.


I was quite supprised to find that a couple of the circuits were
basically ok even after all this time. I would guess that the story may
change if any of the cables were moved about too much or stepped on
(currently run loose in the loft - not even clipped to the joists - even
the JBs are not screwed down).


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #6   Report Post  
Christian McArdle
 
Posts: n/a
Default

The question is, is this style of wiring still permissible? It violates
the guideline of having no more spurs per circuit than there are actual
outlets directly on it, but I can't find anything in the regs that
explicitly forbids it.


It is likely to be a perfectly OK design.

Forget about any "more spurs than sockets" rules of thumb. They are just
guidelines for mentally challenged electricians. The important things to
determine a

(a) That the end of the spurs have sufficiently low earth loop impedence for
a rapid disconnect on an earthlive fault. (Plus voltage drop calcs if
required.)

(b) That the ring itself is reasonably balanced, so that sockets and spur
connections are evenly placed around the rings, with sockets likely to have
heavy loads either moved off ring (preferably) or distributed around the
ring.

Christian.


  #7   Report Post  
 
Posts: n/a
Default

John Rumm wrote:

An alternative is to use radials, not rings. Then any additional sockets
required can be spurred off existing socket locations, without having to
do down-along-up to preserve continuity of a ring.


I did think of that, but you don't gain much in this case since I don't
think you can get 4mm^2 cable down the conduit either, you would still
be limited to 2.5mm^2 conduit drops. So extension would still have to be
via a new drop rather than from an existing socket.

Doesn't have to be 4mm^2, you can wire radials with 2.5mm^2 and use a
20amp MCB. This is what I have done for a lot of new circuits to the
study and places like that in our house. It's much easier in many
ways than a ring.

--
Chris Green

  #9   Report Post  
John Rumm
 
Posts: n/a
Default

Christian McArdle wrote:

Forget about any "more spurs than sockets" rules of thumb. They are just
guidelines for mentally challenged electricians. The important things to
determine a


Yup, ta for the confirmation... I was pretty sure it was only a
guidline, I just wanted to make sure it did not have some obscure regs
"heritage" that I had not spotted!

(a) That the end of the spurs have sufficiently low earth loop impedence for
a rapid disconnect on an earthlive fault. (Plus voltage drop calcs if
required.)


Based on my tests using the present wiring that should not be a problem.
(The incoming supply is also newish and has a well made earth connection
to the sheath - so Zs should be nicely low)

(b) That the ring itself is reasonably balanced, so that sockets and spur
connections are evenly placed around the rings, with sockets likely to have
heavy loads either moved off ring (preferably) or distributed around the
ring.


Again the house layout is also conducive to a nicely ballanced circuit.
The kitchen is also at the other end of the house from the CU, so you
get the load nicely spaced round the middle of the cable runs without
any bunching toward one end.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #10   Report Post  
Owain
 
Posts: n/a
Default

John Rumm wrote:
Yup, sorry I ommited part of my reasoning there... there is the same
conduit issue getting the wires from the CU to the loft as there is for
the socket drops. There is currently room for at best I would guess four
2.5s and it struck me that a 32A radial would be more use than a pair of
20A ones.


You may run into trouble both with conduit capacity factors and also
derating the cables for grouping.

If this guy is doing the place up to sell then

(a) the number of sockets must be adequate - inadequate electric sockets
is the sort of stating-the-bleeding-obvious to be picked up on survey.
If the job can't be done to current expectations of number of sockets,
perhaps better to leave it for the buyer to modernise.
(b) the place probably needs the decoration freshening anyway, whether
he wants to or not - so better to bite the bullet, chase in the cables
and re-emulsion. IIRC you said the sockets had old mounting holes, so
you'll probably have to break out the old back boxes from the conduit
anyway.
(c) if the sisters are getting 2/3rds of the profits from sale, perhaps
they should be prepared to chip in 2/3rds of the cost of the upgrade.

Owain



  #11   Report Post  
John Rumm
 
Posts: n/a
Default

Owain wrote:

You may run into trouble both with conduit capacity factors and also
derating the cables for grouping.


Possibly, but the one(s) with most load (CU to loft) are only 1m long

If this guy is doing the place up to sell then


Nope, he plans to stay there for the time being IIUC.

(a) the number of sockets must be adequate - inadequate electric sockets
is the sort of stating-the-bleeding-obvious to be picked up on survey.


I did suggest that, and expect that in reality one could add more with
very little disruption in some places (like the kitchen etc). There is
no point saving 500 now if it causes a future buyer to bargin you down 3K.

If the job can't be done to current expectations of number of sockets,
perhaps better to leave it for the buyer to modernise.


Given that he may be there for another 10 years, I would not be keen to
hang about with insulation in that sort of state though.

(b) the place probably needs the decoration freshening anyway, whether
he wants to or not - so better to bite the bullet, chase in the cables


Decoration was done recently alas (before mom departed)...

and re-emulsion. IIRC you said the sockets had old mounting holes, so
you'll probably have to break out the old back boxes from the conduit
anyway.


Sockets are on standard metal back boxes from what I have seen - so no
problem with them. The light switches however have wood ones that will
not fit current switches, so some delicate work with the SDS will be
needed for them!

(c) if the sisters are getting 2/3rds of the profits from sale, perhaps
they should be prepared to chip in 2/3rds of the cost of the upgrade.


I think they may be prepared to cough up some contribution (although
they probably figure that letting brother live rent free in their
inheritance contributes a way toward it!). I don't think he was that
bothered by the cost, but just wanted to avoid too much disruption, and
hates the smell of paint!

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #12   Report Post  
Owain
 
Posts: n/a
Default

John Rumm wrote:
Sockets are on standard metal back boxes from what I have seen - so no
problem with them. The light switches however have wood ones that will
not fit current switches, so some delicate work with the SDS will be
needed for them!


Very delicate, if you want to sell them on Ebay afterwards :-)

Owain

  #13   Report Post  
John Rumm
 
Posts: n/a
Default

Owain wrote:

Very delicate, if you want to sell them on Ebay afterwards :-)


Is there a big aftermarket for (flush mount) wooden back boxes?



--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #14   Report Post  
Owain
 
Posts: n/a
Default

John Rumm wrote:
Owain wrote:
Very delicate, if you want to sell them on Ebay afterwards :-)

Is there a big aftermarket for (flush mount) wooden back boxes?


There is a smallish market for old electrical collectables, and I doubt
many wooden back boxes make it to Ebay, so you could make some sad
anorak happy, earn yourself a beer voucher, and reduce landfill.

Owain


  #15   Report Post  
John Rumm
 
Posts: n/a
Default

Owain wrote:

John Rumm wrote:

Owain wrote:

Very delicate, if you want to sell them on Ebay afterwards :-)


Is there a big aftermarket for (flush mount) wooden back boxes?



There is a smallish market for old electrical collectables, and I doubt
many wooden back boxes make it to Ebay, so you could make some sad
anorak happy, earn yourself a beer voucher, and reduce landfill.


Spose I could throw in the old switch as well ;-))


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #16   Report Post  
 
Posts: n/a
Default


John Rumm wrote:
Christian McArdle wrote:

Forget about any "more spurs than sockets" rules of thumb. They are just
guidelines for mentally challenged electricians. The important things to
determine a


Yup, ta for the confirmation... I was pretty sure it was only a
guidline, I just wanted to make sure it did not have some obscure regs
"heritage" that I had not spotted!


2 aspects come to mind:

Firstly, heritage is what it is.

15th ed IEE & (IIRC 14th & maybe earlier) had explicit rules for ring
circuits. These were moved to OSG after 16th ed published, so they are
now guidelines. The rule is now in OSG appendix 8 - Spurs page 149 in
my vintage 1998 yellow cover copy.

IIUIC you can't easily be fingered (part pee aside) if you follow OSG
to the letter, but you can depart if you are prepared to justify the
design.

Secondly, the original post said the circuit dated from the 50s. If so
it would most likely have been cabled in imperial 7/029 (earth
conductor (CPC)is 3/029 IIRC) - that is approx 3mmsq with 1.25mmsq
earth. 7/029 has a rating of about 30A on the same basis that modern
2.5mmsq has 27A. The whole installation would also have run off a
conventional (probably wired) fuse box.

In very broad terms, and leaving aside any derating for the cable being
run down the wall in conduit, each socket would have had the full
nominal 30A ring current available. Nowadays spur ratings are fiddled.
After maximum derating a 2.5mmsq spur cable is held to have a current
rating of 20A and the socket at the end, whether single or double 13A
is held to have a maximum demand of 13A.

Now that RCDs are in wide use and we have precise instruments to
measure fault currents and we are very aware of things like earth loop
impedances and so on, there would be a major quibble with a 3/029 (ie
1.27mmsq) CPC. It is a tad too small - in the 'standard' fault
condition this could leave a fault greater than the 50V maximum -
limiting the maximum cable run length. (Standard 2.5mmsq cable uses
1.5mmsq CPC & avoids the problem. Modern 4mmsq, with a 1.5mm CPC,
suffers from the same fault - which limits its popularity.

One cynical way of complying with OSG is simply to insert ghost 13A
sockets between each drop in the attic, though that might be queried by
pundits pointing to the requirement to evenly spread load around a
ring.

HTH

  #17   Report Post  
John Rumm
 
Posts: n/a
Default

wrote:

Yup, ta for the confirmation... I was pretty sure it was only a
guidline, I just wanted to make sure it did not have some obscure regs
"heritage" that I had not spotted!



2 aspects come to mind:

Firstly, heritage is what it is.

15th ed IEE & (IIRC 14th & maybe earlier) had explicit rules for ring
circuits. These were moved to OSG after 16th ed published, so they are
now guidelines. The rule is now in OSG appendix 8 - Spurs page 149 in
my vintage 1998 yellow cover copy.


Yup, page 150 Annex 8 in the current one, with the specific bit on spurs
on page 153 now.

IIUIC you can't easily be fingered (part pee aside) if you follow OSG
to the letter, but you can depart if you are prepared to justify the
design.


Tis what I figured. I could not find any technical / moral reason for
not using the same layout as is used currently, but thought I would
check the collective memory banks to see if there was a reg I had
missed! ;-)

Secondly, the original post said the circuit dated from the 50s. If so
it would most likely have been cabled in imperial 7/029 (earth
conductor (CPC)is 3/029 IIRC) - that is approx 3mmsq with 1.25mmsq
earth. 7/029 has a rating of about 30A on the same basis that modern
2.5mmsq has 27A. The whole installation would also have run off a
conventional (probably wired) fuse box.


Yup certainly imperial sizes (and stranded). I did not actually measure
the cross section of the wire other than approximately by eye... did not
seem much point since it all needs to go really.

Now that RCDs are in wide use and we have precise instruments to
measure fault currents and we are very aware of things like earth loop
impedances and so on, there would be a major quibble with a 3/029 (ie
1.27mmsq) CPC. It is a tad too small - in the 'standard' fault


It would be a problem on a long spur, but as a short "finger" from a
ring it probably still copes.

condition this could leave a fault greater than the 50V maximum -
limiting the maximum cable run length. (Standard 2.5mmsq cable uses
1.5mmsq CPC & avoids the problem. Modern 4mmsq, with a 1.5mm CPC,
suffers from the same fault - which limits its popularity.


That and it is harder to work with anyway...


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd -
http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #18   Report Post  
 
Posts: n/a
Default


John Rumm wrote:
wrote:

Yup, ta for the confirmation... I was pretty sure it was only a
guidline, I just wanted to make sure it did not have some obscure regs
"heritage" that I had not spotted!


snip

Now that RCDs are in wide use and we have precise instruments to
measure fault currents and we are very aware of things like earth loop
impedances and so on, there would be a major quibble with a 3/029 (ie
1.27mmsq) CPC. It is a tad too small - in the 'standard' fault


It would be a problem on a long spur, but as a short "finger" from a
ring it probably still copes.



or perhaps not, IIRC when I tried out various designs for this place
(sometime ago now), ISTR that I discovered suggested/standard circuits
in OSG are generally limited by voltage drop. Interestingly no 4mmsq
circuits are listed.

When you do the calcs using 4mmsq you find that (depending on open loop
supply impedance and cicuit length) the potential fault voltage at the
point where there is a live to earth fault can be over 50V. This is due
to the small dia of the CPC. SFAIUI 50V is generally considered the
max safe permissable voltage at a fault point, as you might touch an
earthed item near the fault. ie the length of a 4mmsq cct in those
circumstances is limited not by voltage drop, but by fault voltage.

Without doing the calcs my gut feeling is that 7/029 is likely to give
similar results as 4mmsq, as the CPC dia is less than that of 2.5mmsq
cable. IIRC the conductor & CPC sizes in 2.5mmsq FT&E means volt drop
just scrapes home as the premier limiting length factor.

IMHO even if the new ring circuit uses 2.5mmsq, it should be checked by
calculation for 2 or 3 typical spurs drawing 30A - in varying
proportions - between them. The calc should be a doddle with a
spreadsheet.


HTH

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Kitchen lights on ring circuit antgel UK diy 6 June 13th 05 09:40 AM
Ring Circuit - steel knockout boxes/grommets Perry Gunn UK diy 15 June 8th 05 11:03 AM
Unique Spoon Ring *please help!* J Metalworking 2 January 8th 04 05:06 PM
Commissioning a ring circuit David W.E. Roberts UK diy 35 November 4th 03 10:52 PM
Testing ring circuit John Greenwood UK diy 6 August 4th 03 03:45 PM


All times are GMT +1. The time now is 05:04 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"