Default Voltage in a switched off light fitting?

OK, we have a energy efficient lamp in the kitchen - normal ceiling
rose/pendant light fitting. The kitchen has two light switches for
this light, one at each door.

Strange thing was we noticed that the energy efficient lamp, once
warmed up, would flash (dimly) for some time after being switched off.

Stuck a multimeter into the pendant and there appears to be 50 volts
across the pins when switched off! Checked in the living room, which
also has two light switches, and it too had 50v across the pins!
Checked upstairs in a bedroom (one switch) and no voltage at all.

I take it this voltage presence is wrong? Anyone any pointer as to
what could be causing this?

Cheers,
Colin.

  #2   Report Post  
Christian McArdle
 
Posts: n/a
Default

Stuck a multimeter into the pendant and there appears to be 50 volts
across the pins when switched off!


A modern high impedence multimeter on a voltage range will give close to a
random reading when attached to an open circuit that has any length of
cabling. Any capacitive or inductive coupling will causing spurious voltage
readings.

Christian.



  #3   Report Post  
John Rumm
 
Posts: n/a
Default

wrote:

I take it this voltage presence is wrong? Anyone any pointer as to
what could be causing this?


A digital multimeter I take it?

If so the chances are you are seeing something called capacitive coupling.

Cable runs will have a small but detectable capacitance between the
conductors. This allows a tiny amount of current to flow between the
conductors even though when they are not connected to each other (and in
fact separated by insulation!). This allows some of the disconnected
sections of cable (i.e. switched off bits) to "charge up" toward some
fraction of mains voltage. A digital multimeter will tend to show this
since it places very little "load" on the cables when carrying out the
measurement. (Conventional meters place a higher load on the circuit
under test and this tends to discharge the cables).

You may well find the effect is more noticeable on two way switched
circuits since they will have longer runs of cable.

The flashing you can see with the CFL bulb is quite common, and seems to
be an extension of the same problem. The small leakage current due to
the capacitive coupling is also enough to charge capacitors in the input
circuitry of the lamp. Once these has accumulated a sufficient level of
charge, it is enough to momentarily "fire" the lamp. This discharges the
circuit, the lamp goes out and the process starts over.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd -
http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #4   Report Post  
 
Posts: n/a
Default

John Rumm wrote:
wrote:

I take it this voltage presence is wrong? Anyone any pointer as to
what could be causing this?


A digital multimeter I take it?


No - it's a 'mini' analogue needle multimeter - a few years old now
though.


If so the chances are you are seeing something called capacitive coupling.

Cable runs will have a small but detectable capacitance between the
conductors. This allows a tiny amount of current to flow between the
conductors even though when they are not connected to each other (and in
fact separated by insulation!). This allows some of the disconnected
sections of cable (i.e. switched off bits) to "charge up" toward some
fraction of mains voltage. A digital multimeter will tend to show this
since it places very little "load" on the cables when carrying out the
measurement. (Conventional meters place a higher load on the circuit
under test and this tends to discharge the cables).


I assume that this doesn't rule out the analogue meter also picking it
up though?

You may well find the effect is more noticeable on two way switched
circuits since they will have longer runs of cable.

The flashing you can see with the CFL bulb is quite common, and seems to
be an extension of the same problem. The small leakage current due to
the capacitive coupling is also enough to charge capacitors in the input
circuitry of the lamp. Once these has accumulated a sufficient level of
charge, it is enough to momentarily "fire" the lamp. This discharges the
circuit, the lamp goes out and the process starts over.


Thanks for this - it certainly sounds like a reasonable explanation to
me. (Don't need to call an electrician?) As long as we aren't
'seeping' electricity that we're having to pay for - or are we? I take
it that the amount lost in this way is so small as to be negligible?
:-)

Cheers,
Colin.

  #6   Report Post  
John Rumm
 
Posts: n/a
Default

wrote:

A digital multimeter I take it?



No - it's a 'mini' analogue needle multimeter - a few years old now
though.


I assume that this doesn't rule out the analogue meter also picking it
up though?


It is less common to see the effect with these since they load they
place on the circuit is higher, but it is still possible.

(The "load" of a meter is given by its "ohms per volt" spec. For AC
voltage measurement this is typically some "thousands" of ohms per volt.
A digital will usually be several million ohms/volt. So for example a 5k
ohm/volt meter on a 250V range will place a load of 250 x 5000 = 1.25
MOhm load on the circuit. This will pass a current of 240/1.25M = approx
0.2mA).

Have a look at your meter and see if you can see a rating for its
ohms/volt. Usually the higher the number the better (since it means the
less the meter is affecting the thing it is trying to measure), but it
also means that you can end up seeing stray voltages even where they are
of such a high impedance that they would quickly fade to nothing with
the merest hint of a load.

Thanks for this - it certainly sounds like a reasonable explanation to
me. (Don't need to call an electrician?)


I should not of thought so. If you stick an ordinary bulb in, the fact
that it goes off when you turn the switch off is a good indication there
is not really 50V there! (if there was it would still be glowing).

As long as we aren't
'seeping' electricity that we're having to pay for - or are we?


Well, every flash is coming from energy that you are paying for...

I take
it that the amount lost in this way is so small as to be negligible?
:-)


Chances are you are sinking micro amps here, so I would not be overly
worried if I were you!



--
Cheers,

John.

/================================================== ===============\
| Internode Ltd -
http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Survey on Newsgroup Behavior Jens Arndt Home Repair 27 November 2nd 04 02:45 PM
flush fitting light in bathroom Stephen Spinks UK diy 0 November 2nd 04 12:49 AM
changing a light bulb Joe Home Repair 6 March 8th 04 07:30 PM
Light bulb malfunction Oldylocks Home Repair 12 February 5th 04 02:51 PM
strange problem connecting light to dimmer John Hunter Home Repair 6 January 19th 04 08:57 PM


All times are GMT +1. The time now is 06:27 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"