I'm in the process of wiring up a new (to me) lathe, which is currently set
up with a 7.5hp 3 phase 440v motor. It also has a coolant system, if that
makes any difference.

I have a new 220v circuit in place, and a 10hp phase converter. I'm under
the impression that the motor works at 220v as well as 440v with just a
wiring change, due to the motor placard on the lathe and from what the
seller told me.

What i'm unsure about is how the wiring is changed when going from 440v to
220v. I opened up the electrical panel and was at first somewhat worried
about all the 'stuff'' in there. Picture at

www.blastzone.com/newlathe/102_1645.jpg

After looking at it for a while I found what I believe needs to be changed
to go from 440v to 220v. The transformer, pictured at

www.blastzone.com/newlathe/102_1646.jpg

On the transformer face are 2 diagrams for how to wire it for 220v and 440v
(as seen in the picture above).

My question is this. Is re-wiring this transformer the only thing I need to
change? What is going to be damaged if there's something else? I'm a
little hesitant to power it all up since i'm not 100% sure on what i'm doing
here.

I did look inside where the motor itself is, but there isnt much to be seen
the

www.blastzone.com/newlathe/102_1649.jpg

Also, the actual wiring point on the outside has some pretty small wires
compared to what the 200v circuit and wiring from the phase converter is,
which also has me wondering.

www.blastzone.com/newlathe/102_1655.jpg

I appreciate the help i've gotten here so far, and look forward to what you
have to say. Thanks.

Greg Deputy
Bonney Lake, WA


  #2   Report Post  
Grady
 
Posts: n/a
Default

Cant quite read the va rating on the transformer, but more than likely the
transformer is just for all of the control circuitry. This would include any
pilot lights, coils for contactors, etc.I doubt that it is inteded for
anything else. When you say rewire the transformer, I am assuming that it is
on the primary side to convert you rew input voltage to the 220 volt you
have at your place. If you can successfully change the control transformer
primary to still have the same output it now requires, and rewire the motor
to accept 220 volt, you should be in good shape.


"Greg Deputy" wrote in message
...
Thanks in advance for any advice on my questions below.

I'm in the process of wiring up a new (to me) lathe, which is currently
set
up with a 7.5hp 3 phase 440v motor. It also has a coolant system, if that
makes any difference.

I have a new 220v circuit in place, and a 10hp phase converter. I'm under
the impression that the motor works at 220v as well as 440v with just a
wiring change, due to the motor placard on the lathe and from what the
seller told me.

What i'm unsure about is how the wiring is changed when going from 440v to
220v. I opened up the electrical panel and was at first somewhat worried
about all the 'stuff'' in there. Picture at

www.blastzone.com/newlathe/102_1645.jpg

After looking at it for a while I found what I believe needs to be changed
to go from 440v to 220v. The transformer, pictured at

www.blastzone.com/newlathe/102_1646.jpg

On the transformer face are 2 diagrams for how to wire it for 220v and
440v
(as seen in the picture above).

My question is this. Is re-wiring this transformer the only thing I need
to
change? What is going to be damaged if there's something else? I'm a
little hesitant to power it all up since i'm not 100% sure on what i'm
doing
here.

I did look inside where the motor itself is, but there isnt much to be
seen
the

www.blastzone.com/newlathe/102_1649.jpg

Also, the actual wiring point on the outside has some pretty small wires
compared to what the 200v circuit and wiring from the phase converter is,
which also has me wondering.

www.blastzone.com/newlathe/102_1655.jpg

I appreciate the help i've gotten here so far, and look forward to what
you
have to say. Thanks.

Greg Deputy
Bonney Lake, WA




  #3   Report Post  
Anthony
 
Posts: n/a
Default

"Greg Deputy" wrote in
:




Take note that the current needed will double when you go from 440V to
220V, so use appropriate sized feed wires to the transformer, and you may
have to change your fuses also.
Does the coolant pump run from this transformer?
If yes, no further change is needed relative to the coolant pump after
changing the transformer. If no, you will need to rewire the motor for
220V.
Does the spindle motor run from this transformer?
If yes, again, no change needed after fixing the transformer. If no, you
will need to re-wire the spindle motor for 220V.
I cannot read the transformer plate. As another poster noted, this may be
only a control transformer, and not feed any motors.


--
Anthony

You can't 'idiot proof' anything....every time you try, they just make
better idiots.

Remove sp to reply via email
  #4   Report Post  
Greg Deputy
 
Posts: n/a
Default

Yeah, the transformer diagram indicates 110v out the secondary, and has 2
configurations for the primary, 440v or 220v.

So how would one normally go about rewiring the motor for 220v? Is it
likely i'm going to need direct access to the motor? As installed it is all
buried inside the cabinet, so i guess i'll have to pull the thing out.

"Grady" wrote in message
news:nO8Xd.733$Qz.470@okepread05...
Cant quite read the va rating on the transformer, but more than likely the
transformer is just for all of the control circuitry. This would include

any
pilot lights, coils for contactors, etc.I doubt that it is inteded for
anything else. When you say rewire the transformer, I am assuming that it

is
on the primary side to convert you rew input voltage to the 220 volt you
have at your place. If you can successfully change the control transformer
primary to still have the same output it now requires, and rewire the

motor
to accept 220 volt, you should be in good shape.


"Greg Deputy" wrote in message
...
Thanks in advance for any advice on my questions below.

I'm in the process of wiring up a new (to me) lathe, which is currently
set
up with a 7.5hp 3 phase 440v motor. It also has a coolant system, if

that
makes any difference.

I have a new 220v circuit in place, and a 10hp phase converter. I'm

under
the impression that the motor works at 220v as well as 440v with just a
wiring change, due to the motor placard on the lathe and from what the
seller told me.

What i'm unsure about is how the wiring is changed when going from 440v

to
220v. I opened up the electrical panel and was at first somewhat

worried
about all the 'stuff'' in there. Picture at

www.blastzone.com/newlathe/102_1645.jpg

After looking at it for a while I found what I believe needs to be

changed
to go from 440v to 220v. The transformer, pictured at

www.blastzone.com/newlathe/102_1646.jpg

On the transformer face are 2 diagrams for how to wire it for 220v and
440v
(as seen in the picture above).

My question is this. Is re-wiring this transformer the only thing I

need
to
change? What is going to be damaged if there's something else? I'm a
little hesitant to power it all up since i'm not 100% sure on what i'm
doing
here.

I did look inside where the motor itself is, but there isnt much to be
seen
the

www.blastzone.com/newlathe/102_1649.jpg

Also, the actual wiring point on the outside has some pretty small wires
compared to what the 200v circuit and wiring from the phase converter

is,
which also has me wondering.

www.blastzone.com/newlathe/102_1655.jpg

I appreciate the help i've gotten here so far, and look forward to what
you
have to say. Thanks.

Greg Deputy
Bonney Lake, WA






  #5   Report Post  
Greg Deputy
 
Posts: n/a
Default

Judging from the size of the transformer (small) and the fact it outputs
110v, i'm pretty sure it only drives the coolant pump, so i guess its time
to pull out the motor and look at how to rewire the thing.

Thanks.


"Anthony" wrote in message
...
"Greg Deputy" wrote in
:




Take note that the current needed will double when you go from 440V to
220V, so use appropriate sized feed wires to the transformer, and you may
have to change your fuses also.
Does the coolant pump run from this transformer?
If yes, no further change is needed relative to the coolant pump after
changing the transformer. If no, you will need to rewire the motor for
220V.
Does the spindle motor run from this transformer?
If yes, again, no change needed after fixing the transformer. If no, you
will need to re-wire the spindle motor for 220V.
I cannot read the transformer plate. As another poster noted, this may be
only a control transformer, and not feed any motors.


--
Anthony

You can't 'idiot proof' anything....every time you try, they just make
better idiots.

Remove sp to reply via email





  #6   Report Post  
Robert Swinney
 
Posts: n/a
Default

There should be a name plate on the motor which shows the two wiring
configurations, for 220 v or 440 v. If in doubt I suggest you get help from
someone that knows about these things, say an electrician.

Bob Swinney
"Greg Deputy" wrote in message
...
Judging from the size of the transformer (small) and the fact it outputs
110v, i'm pretty sure it only drives the coolant pump, so i guess its time
to pull out the motor and look at how to rewire the thing.

Thanks.


"Anthony" wrote in message
...
"Greg Deputy" wrote in
:




Take note that the current needed will double when you go from 440V to
220V, so use appropriate sized feed wires to the transformer, and you may
have to change your fuses also.
Does the coolant pump run from this transformer?
If yes, no further change is needed relative to the coolant pump after
changing the transformer. If no, you will need to rewire the motor for
220V.
Does the spindle motor run from this transformer?
If yes, again, no change needed after fixing the transformer. If no, you
will need to re-wire the spindle motor for 220V.
I cannot read the transformer plate. As another poster noted, this may be
only a control transformer, and not feed any motors.


--
Anthony

You can't 'idiot proof' anything....every time you try, they just make
better idiots.

Remove sp to reply via email





  #7   Report Post  
carl mciver
 
Posts: n/a
Default


"Greg Deputy" wrote in message
...
| Thanks in advance for any advice on my questions below.
|
| I'm in the process of wiring up a new (to me) lathe, which is currently
set
| up with a 7.5hp 3 phase 440v motor. It also has a coolant system, if that
| makes any difference.
|
| I have a new 220v circuit in place, and a 10hp phase converter. I'm under
| the impression that the motor works at 220v as well as 440v with just a
| wiring change, due to the motor placard on the lathe and from what the
| seller told me.
|
| What i'm unsure about is how the wiring is changed when going from 440v to
| 220v. I opened up the electrical panel and was at first somewhat worried
| about all the 'stuff'' in there. Picture at
SNIP


You need to rewire both the control transformer and the motor. The
control transformer has been done already, likely, so the motor still has to
get rewired. If you can't find a local electrician, hit me up off list and
I'll try to put in words the diagrams I have so that you can do it yourself.
Perhaps visit your local library and see what they have in the way of
industrial electricity and motor controls. Ought to be the typical motor
wiring diagrams available if it isn't on the motor directly. I assume that
your phase converter is a delta configuration, which is the most common
motor arrangement, but delta and wye wire up differently, even more so for
different voltages.
The control transformer provides power to operate all the controls,
lights, relay/contactor/starter coils, and so forth. With the one wire in
the way and the lighting just so it's not very readable. The controls don't
care what voltage they switch for the motor, and as far as they are
concerned it has no bearing. They only see control voltage, which could be
12VAC to 240VAC or even 12VDC to 48VDC or more. You library will also have
some useful information.
Just from looking at the wiring you have there, there's a pair of motor
starters, one being a replacement. I thought at first that they were a
reversing setup (does yours have a switch to reverse the motor?) but it
might be for a soft start, which allows the lathe to come up to speed
without blowing any overloads. The black blob on the right side that got
cut off - is that another motor contactor/starter? Where is the overload
for it? Usually looks like three flat fuses sorta, and attached to the main
contactor/starter. I'm guessing that the rectifier is part of a DC brake.
If you apply DC to an AC motor it will come to a firm stop very quickly and
not rotate at all. That's one relay/starter, but it doesn't explain why
there would be two there. Soft starts take two, but there would be more
stuff there, unless I can't see it.
Before you turn everything on, you can disconnect the motor wiring
itself from the control panel and run the controls through their paces. If
you understand basic electricity, and can read a book, you ought to be able
to figure out what does what. It helps to create a wiring diagram for what
you have to help understand what's going on.

The controls have been used and abused over the years, with the normal
replacement of original parts no longer available, and this makes it a bit
hard to figure out what it all does just from looking at it in a photo.


  #8   Report Post  
PrecisionMachinisT
 
Posts: n/a
Default


"Robert Swinney" wrote in message
...


There should be a name plate on the motor which shows the two wiring
configurations, for 220 v or 440 v. If in doubt I suggest you get help

from
someone that knows about these things, say an electrician.


He will need to change out the heaters in any mag starters too...

--

SVL


  #9   Report Post  
PrecisionMachinisT
 
Posts: n/a
Default


"Greg Deputy" wrote in message
...
Yeah, the transformer diagram indicates 110v out the secondary, and has 2
configurations for the primary, 440v or 220v.


For low voltage operation you place the primary windings in series with one
another.


So how would one normally go about rewiring the motor for 220v? Is it
likely i'm going to need direct access to the motor? As installed it is

all
buried inside the cabinet, so i guess i'll have to pull the thing out.


Yup, you also gotta rewire the taps inside the motor's peckerhead for low
voltage operation--the connection diagrams should be on the motor's
data-plate.

--

SVL


  #10   Report Post  
Jerry Martes
 
Posts: n/a
Default


"PrecisionMachinisT" wrote in message
...

"Greg Deputy" wrote in message
...
Yeah, the transformer diagram indicates 110v out the secondary, and has 2
configurations for the primary, 440v or 220v.


For low voltage operation you place the primary windings in series with
one
another.


Woops -- I meant parallel

J








So how would one normally go about rewiring the motor for 220v? Is it
likely i'm going to need direct access to the motor? As installed it is

all
buried inside the cabinet, so i guess i'll have to pull the thing out.


Yup, you also gotta rewire the taps inside the motor's peckerhead for low
voltage operation--the connection diagrams should be on the motor's
data-plate.

--

SVL






  #11   Report Post  
PrecisionMachinisT
 
Posts: n/a
Default


"Jerry Martes" wrote in message
news:tjaXd.57472$EL5.52213@trnddc05...

"PrecisionMachinisT" wrote in message
...

"Greg Deputy" wrote in message
...
Yeah, the transformer diagram indicates 110v out the secondary, and has

2
configurations for the primary, 440v or 220v.


For low voltage operation you place the primary windings in series with
one
another.


Woops -- I meant parallel

J



Yup, that I did....

Thx.

--

SVL


  #12   Report Post  
Grady
 
Posts: n/a
Default

There should be a wiring diagram on the motor to show which leads to connect
where to change the voltage. Also, where does the coolant pump tie in at?
Hopefully it is on the 110 volt side of the transformer. Be sure you have
the correct size wire for the full load amp rating of unit at 220 volt.
Since you are going from 440 to 220 volts the current draw will double. What
is the full load amp rating on motor and what size wire do you have pulled
for this circuit?


"Greg Deputy" wrote in message
...
Yeah, the transformer diagram indicates 110v out the secondary, and has 2
configurations for the primary, 440v or 220v.

So how would one normally go about rewiring the motor for 220v? Is it
likely i'm going to need direct access to the motor? As installed it is
all
buried inside the cabinet, so i guess i'll have to pull the thing out.

"Grady" wrote in message
news:nO8Xd.733$Qz.470@okepread05...
Cant quite read the va rating on the transformer, but more than likely
the
transformer is just for all of the control circuitry. This would include

any
pilot lights, coils for contactors, etc.I doubt that it is inteded for
anything else. When you say rewire the transformer, I am assuming that it

is
on the primary side to convert you rew input voltage to the 220 volt you
have at your place. If you can successfully change the control
transformer
primary to still have the same output it now requires, and rewire the

motor
to accept 220 volt, you should be in good shape.


"Greg Deputy" wrote in message
...
Thanks in advance for any advice on my questions below.

I'm in the process of wiring up a new (to me) lathe, which is currently
set
up with a 7.5hp 3 phase 440v motor. It also has a coolant system, if

that
makes any difference.

I have a new 220v circuit in place, and a 10hp phase converter. I'm

under
the impression that the motor works at 220v as well as 440v with just a
wiring change, due to the motor placard on the lathe and from what the
seller told me.

What i'm unsure about is how the wiring is changed when going from 440v

to
220v. I opened up the electrical panel and was at first somewhat

worried
about all the 'stuff'' in there. Picture at

www.blastzone.com/newlathe/102_1645.jpg

After looking at it for a while I found what I believe needs to be

changed
to go from 440v to 220v. The transformer, pictured at

www.blastzone.com/newlathe/102_1646.jpg

On the transformer face are 2 diagrams for how to wire it for 220v and
440v
(as seen in the picture above).

My question is this. Is re-wiring this transformer the only thing I

need
to
change? What is going to be damaged if there's something else? I'm a
little hesitant to power it all up since i'm not 100% sure on what i'm
doing
here.

I did look inside where the motor itself is, but there isnt much to be
seen
the

www.blastzone.com/newlathe/102_1649.jpg

Also, the actual wiring point on the outside has some pretty small
wires
compared to what the 200v circuit and wiring from the phase converter

is,
which also has me wondering.

www.blastzone.com/newlathe/102_1655.jpg

I appreciate the help i've gotten here so far, and look forward to what
you
have to say. Thanks.

Greg Deputy
Bonney Lake, WA








  #13   Report Post  
Grant Erwin
 
Posts: n/a
Default

Greg, you've got a real can of worms here. One thing you may not have
considered yet is to generate sufficient 220 3phase and just convert it
to 440 3phase using a (biggish) transformer. Or, you can convert 220
single phase to 440 single phase and then make a 440 phase converter.

A guy in our area recently did just that. Big transformers sometimes show
up but they often aren't cheap. I have one that might be big enough for you,
and might be cheap enough for you, but it's in LA and I won't be running
a vehicle down there until spring break which is a few weeks away. I don't
have the specs on hand, either. I do have 'em somewhere, though.

To email me, either use or go to the link:
http://www.tinyisland.com/email.html

Grant Erwin
Kirkland, Washington

  #14   Report Post  
Greg Deputy
 
Posts: n/a
Default

Just looked at the motor placard on the outside of the machine again. It
appears its not a 7.5hp, but a 5hp after all. I guess that means I've got
overkill for a phase converter (10hp), but better to much than not enough,
right?

The plate says 8/16 Amps, so I guess 16 amps is the rating. I've got 6
gauge wire run from the box for the circuit, and a 50 amp fuse.

"Grady" wrote in message
news:zEfXd.755$Qz.587@okepread05...
There should be a wiring diagram on the motor to show which leads to

connect
where to change the voltage. Also, where does the coolant pump tie in at?
Hopefully it is on the 110 volt side of the transformer. Be sure you have
the correct size wire for the full load amp rating of unit at 220 volt.
Since you are going from 440 to 220 volts the current draw will double.

What
is the full load amp rating on motor and what size wire do you have pulled
for this circuit?


"Greg Deputy" wrote in message
...
Yeah, the transformer diagram indicates 110v out the secondary, and has

2
configurations for the primary, 440v or 220v.

So how would one normally go about rewiring the motor for 220v? Is it
likely i'm going to need direct access to the motor? As installed it is
all
buried inside the cabinet, so i guess i'll have to pull the thing out.

"Grady" wrote in message
news:nO8Xd.733$Qz.470@okepread05...
Cant quite read the va rating on the transformer, but more than likely
the
transformer is just for all of the control circuitry. This would

include
any
pilot lights, coils for contactors, etc.I doubt that it is inteded for
anything else. When you say rewire the transformer, I am assuming that

it
is
on the primary side to convert you rew input voltage to the 220 volt

you
have at your place. If you can successfully change the control
transformer
primary to still have the same output it now requires, and rewire the

motor
to accept 220 volt, you should be in good shape.


"Greg Deputy" wrote in message
...
Thanks in advance for any advice on my questions below.

I'm in the process of wiring up a new (to me) lathe, which is

currently
set
up with a 7.5hp 3 phase 440v motor. It also has a coolant system, if

that
makes any difference.

I have a new 220v circuit in place, and a 10hp phase converter. I'm

under
the impression that the motor works at 220v as well as 440v with just

a
wiring change, due to the motor placard on the lathe and from what

the
seller told me.

What i'm unsure about is how the wiring is changed when going from

440v
to
220v. I opened up the electrical panel and was at first somewhat

worried
about all the 'stuff'' in there. Picture at

www.blastzone.com/newlathe/102_1645.jpg

After looking at it for a while I found what I believe needs to be

changed
to go from 440v to 220v. The transformer, pictured at

www.blastzone.com/newlathe/102_1646.jpg

On the transformer face are 2 diagrams for how to wire it for 220v

and
440v
(as seen in the picture above).

My question is this. Is re-wiring this transformer the only thing I

need
to
change? What is going to be damaged if there's something else? I'm

a
little hesitant to power it all up since i'm not 100% sure on what

i'm
doing
here.

I did look inside where the motor itself is, but there isnt much to

be
seen
the

www.blastzone.com/newlathe/102_1649.jpg

Also, the actual wiring point on the outside has some pretty small
wires
compared to what the 200v circuit and wiring from the phase converter

is,
which also has me wondering.

www.blastzone.com/newlathe/102_1655.jpg

I appreciate the help i've gotten here so far, and look forward to

what
you
have to say. Thanks.

Greg Deputy
Bonney Lake, WA










  #15   Report Post  
Greg Deputy
 
Posts: n/a
Default

I think i've got it covered. I'm going to rewire the transformer per the
diagram, which is for the coolant pump as far as i can tell.

For the motor, i'm going to have to pull it out of the cabinet to rewire it.
I cant get to its wires the way its tucked up inside the machine. I'll take
the opportunity to clean it up and the inside of the cabinet, its pretty
oily and nasty in there anyways.

I've already got a 220v 10hp phase converter, and the motor is a 220v/440v
so i'm going to rewire it and go that route rather than add in a
transformer.

Thanks for all the help, wish me luck!


"Grant Erwin" wrote in message
...
Greg, you've got a real can of worms here. One thing you may not have
considered yet is to generate sufficient 220 3phase and just convert it
to 440 3phase using a (biggish) transformer. Or, you can convert 220
single phase to 440 single phase and then make a 440 phase converter.

A guy in our area recently did just that. Big transformers sometimes show
up but they often aren't cheap. I have one that might be big enough for

you,
and might be cheap enough for you, but it's in LA and I won't be running
a vehicle down there until spring break which is a few weeks away. I don't
have the specs on hand, either. I do have 'em somewhere, though.

To email me, either use or go to the link:
http://www.tinyisland.com/email.html

Grant Erwin
Kirkland, Washington





  #16   Report Post  
Wayne Cook
 
Posts: n/a
Default

On Tue, 8 Mar 2005 08:23:06 -0800, "Greg Deputy"
wrote:

I think i've got it covered. I'm going to rewire the transformer per the
diagram, which is for the coolant pump as far as i can tell.

I seriously doubt that transformer is for the coolant pump. It looks
like a standard control transformer to me and is probably just big
enough to run the controls. By controls I mean the windings in the
motor contactors.

I'd definitely check the coolant pump closely. I'm betting it's 3
phase and is either wired for 440 or is straight 440.

Wayne Cook
Shamrock, TX
http://members.dslextreme.com/users/waynecook
  #17   Report Post  
Grady
 
Posts: n/a
Default

The 6 gauge wire will more than handle the 16 amp load of the motor. 12
guage wire is rated to 20 amp, 10 guage to 30. I dont know about the phase
converter stuff, what kind of load it pulls, so I cannot say as to the fuse
size. Someone else in the group can probably better serve this need then
myself. As a side note, since you are changing the voltage to the motor, if
your contactor has some type of thermal overload, you will need to resize it
appropriately as it will trip first rattle out of the box. It was set up to
run at half the current it will be drawing. See if it has an overload trip
unit and what brand it is.


"Greg Deputy" wrote in message
...
Just looked at the motor placard on the outside of the machine again. It
appears its not a 7.5hp, but a 5hp after all. I guess that means I've got
overkill for a phase converter (10hp), but better to much than not enough,
right?

The plate says 8/16 Amps, so I guess 16 amps is the rating. I've got 6
gauge wire run from the box for the circuit, and a 50 amp fuse.

"Grady" wrote in message
news:zEfXd.755$Qz.587@okepread05...
There should be a wiring diagram on the motor to show which leads to

connect
where to change the voltage. Also, where does the coolant pump tie in at?
Hopefully it is on the 110 volt side of the transformer. Be sure you have
the correct size wire for the full load amp rating of unit at 220 volt.
Since you are going from 440 to 220 volts the current draw will double.

What
is the full load amp rating on motor and what size wire do you have
pulled
for this circuit?


"Greg Deputy" wrote in message
...
Yeah, the transformer diagram indicates 110v out the secondary, and has

2
configurations for the primary, 440v or 220v.

So how would one normally go about rewiring the motor for 220v? Is it
likely i'm going to need direct access to the motor? As installed it
is
all
buried inside the cabinet, so i guess i'll have to pull the thing out.

"Grady" wrote in message
news:nO8Xd.733$Qz.470@okepread05...
Cant quite read the va rating on the transformer, but more than likely
the
transformer is just for all of the control circuitry. This would

include
any
pilot lights, coils for contactors, etc.I doubt that it is inteded for
anything else. When you say rewire the transformer, I am assuming that

it
is
on the primary side to convert you rew input voltage to the 220 volt

you
have at your place. If you can successfully change the control
transformer
primary to still have the same output it now requires, and rewire the
motor
to accept 220 volt, you should be in good shape.


"Greg Deputy" wrote in message
...
Thanks in advance for any advice on my questions below.

I'm in the process of wiring up a new (to me) lathe, which is

currently
set
up with a 7.5hp 3 phase 440v motor. It also has a coolant system,
if
that
makes any difference.

I have a new 220v circuit in place, and a 10hp phase converter. I'm
under
the impression that the motor works at 220v as well as 440v with
just

a
wiring change, due to the motor placard on the lathe and from what

the
seller told me.

What i'm unsure about is how the wiring is changed when going from

440v
to
220v. I opened up the electrical panel and was at first somewhat
worried
about all the 'stuff'' in there. Picture at

www.blastzone.com/newlathe/102_1645.jpg

After looking at it for a while I found what I believe needs to be
changed
to go from 440v to 220v. The transformer, pictured at

www.blastzone.com/newlathe/102_1646.jpg

On the transformer face are 2 diagrams for how to wire it for 220v

and
440v
(as seen in the picture above).

My question is this. Is re-wiring this transformer the only thing I
need
to
change? What is going to be damaged if there's something else? I'm

a
little hesitant to power it all up since i'm not 100% sure on what

i'm
doing
here.

I did look inside where the motor itself is, but there isnt much to

be
seen
the

www.blastzone.com/newlathe/102_1649.jpg

Also, the actual wiring point on the outside has some pretty small
wires
compared to what the 200v circuit and wiring from the phase
converter
is,
which also has me wondering.

www.blastzone.com/newlathe/102_1655.jpg

I appreciate the help i've gotten here so far, and look forward to

what
you
have to say. Thanks.

Greg Deputy
Bonney Lake, WA












Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wiring a 480V Single Phase Circuit Joshua Home Repair 58 June 8th 20 03:39 PM
Wiring 3 phase switch for 2 phase power Dan Miller Metalworking 37 June 14th 04 10:29 PM
Electrical Wiring FAQ (Part 1 of 2) Myron Samila Home Repair 1 March 15th 04 08:27 PM
wiring a 3 phase compressor motor question wallster Metalworking 32 March 15th 04 02:11 PM
Phase converter balancing Karl Townsend Metalworking 7 July 13th 03 01:48 AM


All times are GMT +1. The time now is 09:08 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"