Here is a general question, I am planning a project and will eventually get
all proper permits but I want some advice to determine if this step is
necessary

I am planning to install a steam room in a new bathroom and it requires a
35A, 220V dedicated breaker. My house has a 100A service panel with one 50A
to the range, one 35A to the drier and about a dozen 20A wall plug circuits.

The question is: Is it likly that I will need to simultaniously upgrade the
service panel to 150A when adding this circuit? What is the rule about the
maximum capacity of a service panel?

I know it depends on where I live (CA) etc. I am just looking for direction
before I go in for permits and get rejected for omitting something
important.


  #2   Report Post  
Travis Jordan
 
Posts: n/a
Default

AutoTracer wrote:
Here is a general question, I am planning a project and will
eventually get all proper permits but I want some advice to determine
if this step is necessary

I am planning to install a steam room in a new bathroom and it
requires a 35A, 220V dedicated breaker. My house has a 100A service
panel with one 50A to the range, one 35A to the drier and about a
dozen 20A wall plug circuits.

The question is: Is it likly that I will need to simultaniously
upgrade the service panel to 150A when adding this circuit? What is
the rule about the maximum capacity of a service panel?

I know it depends on where I live (CA) etc. I am just looking for
direction before I go in for permits and get rejected for omitting
something important.


The service load needs to be calculated per NEC 220-31. Add up the
numbers and see what you get.
220-31. Optional Calculation for Additional Loads in Existing Dwelling
Unit

For an existing dwelling unit presently being served by an existing
120/240-volt or 208Y/120-

volt, 3-wire service, it shall be permissible to compute load
calculations as follows:

Load (kVa) Percent of Load

First 8 kVA of load at 100

Remainder of load at 40

Load calculations shall include lighting at 3 volt-amperes/ft2 (0.093
m2); 1500 volt-amperes for

each 2-wire, small-appliance branch circuit and each laundry branch
circuit as specified in

Section 220-16; range or wall-mounted oven and counter-mounted cooking
unit; and other

appliances that are permanently connected or fastened in place, at
nameplate rating.

If air-conditioning equipment or electric space-heating equipment is to
be installed, the following

formula shall be applied to determine if the existing service is of
sufficient size.

Air-conditioning equipment* 100%

Central electric space heating* 100%

Less than four separately controlled space-heating units* 100%

First 8 kVA of all other loads 100%

Remainder of all other loads 40%

*Use larger connected load of air conditioning and space heating, but
not both.

Other loads shall include the following:

1. 1500 volt-amperes for each 20-ampere appliance circuit

2. Lighting and portable appliances at 3 volt-amperes/ft2 (0.093 m2)

3. Household range or wall-mounted oven and counter-mounted cooking unit

4. All other appliances fastened in place, including four or more
separately controlled spaceheating

units, at nameplate rating


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Metal Working Machinery New and Used in Australia and for Export [email protected] Metalworking 0 February 23rd 05 02:54 AM
Popping circuit breaker w/ TS Don97623 Woodworking 14 December 1st 04 01:49 AM
Circuit breaker tester maps to wrong breaker!! Joe Doe Home Repair 7 November 30th 04 01:47 AM
Electric circuit breaker barry martin Home Repair 1 December 26th 03 04:41 AM
Is it a radial or ring circuit? Paul UK diy 14 September 4th 03 04:48 PM


All times are GMT +1. The time now is 02:50 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"