  #1   Report Post  
Michael Roback
 
Posts: n/a
Default Finishing Electrical Panel (Questions)


The guy that installed the subpanel (Siemens) left the panel door off and
must have lost the screws. The screw holes on the box are slighly smaller
than a 10-32. Do I rethread and use 10-32 screws or is there a special
screw used to mount panel door onto the box.

Also there is a bolt missing that holds down the neutral strap that runs
from one bar to the other. So it is not connected accross. Anyone know the
size of that bolt so that I can install it properly.

A few lights in the house periodically will go off and them come back on?
Is this the bulb? The breaker never trips!

Anyone know what kind of voltage comes through the service cables into a
subpanel? It is a 200 AMP panel.

  #2   Report Post  
RBM
 
Posts: n/a
Default

If this is in fact a subpanel, the two sides of the "neutral" bars may have
been separated for a reason, isolating equipment grounds from neutrals. You
may want to have an electrician look at it to be sure. The voltage is
120/240 and the screws may not be machine,but possibly a fine threat sheet
metal screw
"Michael Roback" wrote in message
...

The guy that installed the subpanel (Siemens) left the panel door off and
must have lost the screws. The screw holes on the box are slighly smaller
than a 10-32. Do I rethread and use 10-32 screws or is there a special
screw used to mount panel door onto the box.

Also there is a bolt missing that holds down the neutral strap that runs
from one bar to the other. So it is not connected accross. Anyone know
the
size of that bolt so that I can install it properly.

A few lights in the house periodically will go off and them come back on?
Is this the bulb? The breaker never trips!

Anyone know what kind of voltage comes through the service cables into a
subpanel? It is a 200 AMP panel.



  #3   Report Post  
toller
 
Posts: n/a
Default


"Michael Roback" wrote in message
...

The guy that installed the subpanel (Siemens) left the panel door off and
must have lost the screws. The screw holes on the box are slighly smaller
than a 10-32. Do I rethread and use 10-32 screws or is there a special
screw used to mount panel door onto the box.

I needed two screws for my Sylvania box. The ones HD had were completely
different from mine, but the clerk said they fit all boxes. Amazingly, they
fit. Worth a try.

Also there is a bolt missing that holds down the neutral strap that runs
from one bar to the other. So it is not connected accross. Anyone know
the
size of that bolt so that I can install it properly.

Do you mean the neutral bus and ground bus are not connected? If it is a
subpanel, that is proper.
If the problem is different that this, please elaborate.

A few lights in the house periodically will go off and them come back on?
Is this the bulb? The breaker never trips!

You have a loose connection somewhere. Could be the lamp socket, the
breaker, or anywhere inbetween.
I have a lamp that is built into a headboard that does this. Haven't found
a good solution and can't replace it; but at least I know it is the lamp
socket.

Anyone know what kind of voltage comes through the service cables into a
subpanel? It is a 200 AMP panel.

You have two 120v wires, with 240v between them. 200a is a pretty big
subpanel; is that actually what you meant?


  #4   Report Post  
Percival P. Cassidy
 
Posts: n/a
Default

Our previous home had 60A main fuses, and we blew one every now and
again until we rearranged some circuits between "legs."

Our current home has a 100A panel, and we have never tripped a breaker,
but many of the books I've read say that 200A is becoming more common.

I'm probably going to replace our subpanel in the basement by a 200A one
(mainly for the additional spaces: 32 instead of 20). Although it's a
SUBpanel (because the main panel is in the garage with only the main
breaker and a breaker for the garage circuit), it needs a large capacity
because everything but the garage is fed through it.

Perce


On 01/23/05 03:31 pm toller tossed the following ingredients into the
ever-growing pot of cybersoup:

Anyone know what kind of voltage comes through the service cables into a
subpanel? It is a 200 AMP panel.


You have two 120v wires, with 240v between them. 200a is a pretty big
subpanel; is that actually what you meant?

  #5   Report Post  
Michael Roback
 
Posts: n/a
Default



Yeah, you are right. The Neutral and Ground bus are not connected, however
the guy left the bar bolted into the neutral bus and left the other side
hanging without a bolt. Basically, he did not bolt the bar down onto the
ground bus. When the electrician that I currently have looked at it, he
said that it needed to be connected and stated what the correct bolt size
for it would be but I cannot remember. It is a subpanel. The main panel
with a main breaker sits out in front of my house and the subpanel is inside
with all of the individual circuit breakers in it, in additon to the main
for that panel.

The old electrician who was a builder/electrician who did the remodel also
left notes saying that an future electrician should split the 3 and five
wire branch circuits to each leg of the incoming power and panel bus to
prevent overload on the neutrals. The new electrician who is a master
electrician, head of a local electrical union said that this doens't really
make sense. Does it make sense to you?

I also know that the city likes to have all neutral circuits split up at the
device locations and to avoid tying all neutrals together. The new
electrician said that this is not really necessary but would do it if I
wanted him to. Does this make sense to you.





  #6   Report Post  
Tekkie
 
Posts: n/a
Default

Percival P. Cassidy posted for all of us....

Our previous home had 60A main fuses, and we blew one every now and
again until we rearranged some circuits between "legs."

Our current home has a 100A panel, and we have never tripped a breaker,
but many of the books I've read say that 200A is becoming more common.

I'm probably going to replace our subpanel in the basement by a 200A one
(mainly for the additional spaces: 32 instead of 20). Although it's a
SUBpanel (because the main panel is in the garage with only the main
breaker and a breaker for the garage circuit), it needs a large capacity
because everything but the garage is fed through it.

Perce


On 01/23/05 03:31 pm toller tossed the following ingredients into the
ever-growing pot of cybersoup:

Anyone know what kind of voltage comes through the service cables into a
subpanel? It is a 200 AMP panel.


You have two 120v wires, with 240v between them. 200a is a pretty big
subpanel; is that actually what you meant?


And this relates to the original post HOW?
--
Tekkie
  #7   Report Post  
Percival P. Cassidy
 
Posts: n/a
Default

I was responding to toller's comment that 200A was a lot for a subpanel.
The point is that even 200A may not be excessive for what is technically
a SUBpanel. Our SUBpanel handles everything except the garage circuit.
Perhaps the OP has a similar situation and *needs* a 200A subpanel.

Perce


On 01/24/05 07:57 pm Tekkie tossed the following ingredients into the
ever-growing pot of cybersoup:

Our previous home had 60A main fuses, and we blew one every now and
again until we rearranged some circuits between "legs."

Our current home has a 100A panel, and we have never tripped a breaker,
but many of the books I've read say that 200A is becoming more common.

I'm probably going to replace our subpanel in the basement by a 200A one
(mainly for the additional spaces: 32 instead of 20). Although it's a
SUBpanel (because the main panel is in the garage with only the main
breaker and a breaker for the garage circuit), it needs a large capacity
because everything but the garage is fed through it.


You have two 120v wires, with 240v between them. 200a is a pretty big
subpanel; is that actually what you meant?


And this relates to the original post HOW?

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Panel Question James \Cubby\ Culbertson Home Repair 21 January 10th 05 06:14 AM
Amana Fridge/Freezer - Control Panel Is Dead? [email protected] Electronics Repair 2 August 30th 04 04:49 AM
More Questions - Electrical sockets Stephen Gilkes UK diy 10 February 23rd 04 08:10 PM
Hot tub wiring questions Jason Home Repair 2 December 6th 03 06:05 AM
Overhead electrical service to a storage shed Timothy J. Trace Home Repair 3 December 3rd 03 04:21 AM


All times are GMT +1. The time now is 04:41 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"