Talk about sticking my foot in it!!
I think they really misunderstood where I was coming from on this. Thanks
for offering to help on this.
Can you give me any pointers on what to check.

Thanks
Derek

  #2   Report Post  
TURTLE
 
Posts: n/a
Default


"derek" wrote in message
.191...


Talk about sticking my foot in it!!
I think they really misunderstood where I was coming from on this. Thanks
for offering to help on this.
Can you give me any pointers on what to check.

Thanks
Derek


This is Turtle.

When you come here for to talk about hvac repair it is welcomed for a bunch of
the hvac group will come over here and answer when they will not at alt.hvac .

It sounds like you have a very simple problem of lack of air supply to the
furnace or a restriction of the vent pipe to roof. Before I can give you a good
answer. You will have to give me a Model and serial number of the furnace for me
to know what furnace I'm dealing with. You need a good air supply to come into
the furnace area from out doors and a very good supply opening to let the burnt
vapors out to the outter doors. When you get a sometime roll out, you have a
problem with this. It is very windy here in Louisiana and i would say it is very
windy in Fla. and I will say this because of it being windy in Fla.. Now there
is one that could be is if it is windy out doors, your roof vent cap or pipe is
not mounted high enough to not have a down draft to blow the flames out of the
fire chamber and burn the wires. Still this is concidered as a air supply
problem.

Now they do have a burn fuse used for roll out $.98 found at any appliance parts
houses and is used on all electic heater and even toasters. Put this fuse in the
24 volt supply voltage to the gas valve and it will cut it off before it has
time to burn the wires. Now you can go to a Goodman / Amana supply house and get
a roll out flame button for about $15.00 and it will have a reset button on it
to reset it evertime it trips.

Post the Model & Serial number and also the brand name if possible. I can go by
model number but sometime it's hard to tell on old models.

You have a simple Air supply problem.

TURTLE


  #3   Report Post  
derek
 
Posts: n/a
Default

Hi Turtle
its a tempomatic
model#1117-07-4
Style 131
ser# 7036777

Thanks
again
Derek
  #4   Report Post  
Zypher
 
Posts: n/a
Default

Derek;

It is likely the "click" you're hearing may be the "fan control" bringing on
the fan after the burners have been on awhile [normal.] But, if you have
left the blower door off, upside down in place, or even just open a little
bit [after changing your filter], you may have a condition where the blower
is 'sucking' all of the available air from the equipment closet [including
bringing any available fumes down the flu vent through the cold air
diverter]. This causes the flames to leave their respective home in the
burner compartment and come out. Sometimes [actually often] the cabinet is
starved for oxygen and the flames will 'roll' characterist having a 'whomp'
delayed ignition sound....

1) Make sure the furnace cabinet is sealed from the base by checking with a
flash light. [Remove the filter after opening the blower compartment, pass
the flashlight under the base and see if you notice any light coming through
any cracks in the floor base or where the furnace meets the floor base.

2) Make sure any combustion air inlet screens above and below the appliance
are clear of any insulation [there will be one located in the ceiling above
the furnace and one either in the wall close to the bottom of the furnace or
on the base with a metal enclosure going through to the crawl space if you
have one.] If they appear obstructed, clean them out.

3) Be sure the blower door is on the furnace compartment tight and correct.
Look for writing on the door to help you determine if the blower door is
facing the correct direction. There should not be any air leakage between
the door and blower compartment.

These suggestions are indicative of ALL furnace installation(s) in a closet
and are not 'brand specific' except for those that have "direct vent" or
"high efficiency" style appliance.

4) Call your local gas company and see if they'll send a APR [appliance
inspection] person for free - he'll give you a good inspection, [and won't
try to sell you something]and let you know if you need to call your friendly
local HVAC professional to check it.

--
Zyp
"derek" wrote in message
.191...
Hi Turtle
its a tempomatic
model#1117-07-4
Style 131
ser# 7036777

Thanks
again
Derek



  #5   Report Post  
TURTLE
 
Posts: n/a
Default


"derek" wrote in message
.191...
Hi Turtle
its a tempomatic
model#1117-07-4
Style 131
ser# 7036777

Thanks
again
Derek


This is Turtle.

I don't know that brand well and can't tell the type system it has as to having
a vent fan blower or just gravity to pull the flames through the fire chamber.

I need to know if it has a vent fan on the fire chamber or not ?

Now Zypher did say about you got to have the blower door on it tight or you can
pull the flame out of the fire chamber by just having a little crack in it.
Check this out.

Now another thing here. Check to see if the burners are not clogged up and this
will let the flame roll out after a little time of running with ditry burners.

TURTLE




  #6   Report Post  
derek
 
Posts: n/a
Default

Hi Turtle
I got up in the attic and checked the air intake and it was wide open. I
could look down the pipe into the closet. I got up on the roof and
checked the exhaust and everything looked good as well. I can’t find any
kind of exhaust fan on the unit.
I posted some pictures he http://home.earthlink.net/~tig414/furnace/
What concerns me about this is why did a unit that operated for 30 years
suddenly develop a roll out problem. There have only been Three things
changed relating to the system. The thermostat, The main gas meter
outside the house, and the drive belt on the blower. The drive belt was
really old and slipping badly. I changed it out and I suppose I could
reason it out that the increase in draw with the extra rpms could make a
difference but that takes me back to why is it starting to happen now.
The closet door holds the filter and there is no sealing between the
filter frame and the furnace frame when it’s closed. I removed the filter
from the door and there is a 1’’ gap between the top of the filter frame
and the furnace. If I understand you correctly on how this is supposed
to operate then this can’t possibly be right.

I’m not going to do anything until I install the roll out protection I
also have some high tenp insulation blanket that I use in my kilns and
I’m going to protect the wires with that. I’m going to use an incremental
approach to solving this Starting with improving the safety system and
sealing up the filter frame to furnace connection.
I’m not an idiot and I’m not out to kill my family. I’ve built two kilns
that both run on gas and reach temps in excess of 1500 degrees for days
at a time. They have redundant safety systems and are temperature
controlled via microprocessor units that feed real time data to a
central server in my shop. I’ve built two metal melting crucible
furnaces that reach temps of 2500 degrees for melting bronze.
I know you’ve taken some flack for helping me on this and I really
appreciate your help.
The quality of service technicians and tradesmen in all industries
including mine has diminished over the years for various reasons and has
made me into the do it myself person that I am. Also I’m really broke
right now! There’s a difference between being cheap and being poor.
Thanks
Derek

  #7   Report Post  
Gary R. Lloyd
 
Posts: n/a
Default

On Sun, 28 Nov 2004 15:31:28 GMT, derek wrote:

Hi Turtle
I got up in the attic and checked the air intake and it was wide open. I
could look down the pipe into the closet. I got up on the roof and
checked the exhaust and everything looked good as well. I can’t find any
kind of exhaust fan on the unit.
I posted some pictures he http://home.earthlink.net/~tig414/furnace/
What concerns me about this is why did a unit that operated for 30 years
suddenly develop a roll out problem. There have only been Three things
changed relating to the system. The thermostat, The main gas meter
outside the house, and the drive belt on the blower.


As I understand it, the rollout occurred when the gas valve shut down.
Something to check would be the pressure coming from the new gas meter
to the furnace. Excessive inlet pressure can sometimes overwhelm the
gas valve. Max inlet pressure varies with the valve model and is often
marked on the valve, but generally it should be 5-10" WC for a
residential gas valve.

Gary R. Lloyd CMS
HVACR Troubleshooting Books/Software
http://www.techmethod.com

  #8   Report Post  
derek
 
Posts: n/a
Default

Could it be this simple
I looked carefully at the panels and noticed that the one on top was not
covering the exhaust completely. I then noticed that they are
interchangeable. It’s possible that when I had the unit inspected before we
bought the house (I wasn’t here) they mixed up the panels. With the long
one on the bottom there isn’t nearly the gap for air intake as with the
short panel.
Hmmmm.
Derek
  #9   Report Post  
TURTLE
 
Posts: n/a
Default


"derek" wrote in message
.191...
Could it be this simple
I looked carefully at the panels and noticed that the one on top was not
covering the exhaust completely. I then noticed that they are
interchangeable. It’s possible that when I had the unit inspected before we
bought the house (I wasn’t here) they mixed up the panels. With the long
one on the bottom there isn’t nearly the gap for air intake as with the
short panel.
Hmmmm.
Derek


This is Turtle.

You just fixed it for in the picture if that is they way you have it. You will
starve the burners for air by cutting off the air supply to it. The Doors was
your problem in the beginning. Get the Door right and it will not burn up the
burner area.

TURTLE


  #10   Report Post  
Zypher
 
Posts: n/a
Default

Derek;

After looking at your photo's [quite helpful]

1) The filter in the door is a 'pleated filter' and could be more
restrictive to air flow causing your furnace blower to suck from other
area's.

2) The filter housing in the door doesn't appear to seal well. I'm curious
about the white panel board on the door. Was that there when you bought the
house? It seems it prevents the door from sealing against the framing and
might cause a slight gap at the top of the filter just below the burner
area. This would cause a suction and bring the flames out. [Today code
doesn't allow for the return to be drawn through a door like the one you
have.]

3) I see there's very little clearance on the sides of your furnace, not
allowing for lower combustion as required by code.

4) Since you replaced the blower belt, you may have increased your chance
for the problem to become more evident.

5) The furnace has to be on the high side of 35 years old. Replace it with
a newer high efficiency model, and you will eliminate the possible hazards
to your family. The newer furnace will be smaller, thus allowing for code
corrections.

6) If I bought that house, I would have replaced that furnace yesterday.

--
Zyp
"derek" wrote in message
.191...
Hi Turtle
I got up in the attic and checked the air intake and it was wide open. I
could look down the pipe into the closet. I got up on the roof and
checked the exhaust and everything looked good as well. I can't find any
kind of exhaust fan on the unit.
I posted some pictures he http://home.earthlink.net/~tig414/furnace/
What concerns me about this is why did a unit that operated for 30 years
suddenly develop a roll out problem. There have only been Three things
changed relating to the system. The thermostat, The main gas meter
outside the house, and the drive belt on the blower. The drive belt was
really old and slipping badly. I changed it out and I suppose I could
reason it out that the increase in draw with the extra rpms could make a
difference but that takes me back to why is it starting to happen now.
The closet door holds the filter and there is no sealing between the
filter frame and the furnace frame when it's closed. I removed the filter
from the door and there is a 1'' gap between the top of the filter frame
and the furnace. If I understand you correctly on how this is supposed
to operate then this can't possibly be right.

I'm not going to do anything until I install the roll out protection I
also have some high tenp insulation blanket that I use in my kilns and
I'm going to protect the wires with that. I'm going to use an incremental
approach to solving this Starting with improving the safety system and
sealing up the filter frame to furnace connection.
I'm not an idiot and I'm not out to kill my family. I've built two kilns
that both run on gas and reach temps in excess of 1500 degrees for days
at a time. They have redundant safety systems and are temperature
controlled via microprocessor units that feed real time data to a
central server in my shop. I've built two metal melting crucible
furnaces that reach temps of 2500 degrees for melting bronze.
I know you've taken some flack for helping me on this and I really
appreciate your help.
The quality of service technicians and tradesmen in all industries
including mine has diminished over the years for various reasons and has
made me into the do it myself person that I am. Also I'm really broke
right now! There's a difference between being cheap and being poor.
Thanks
Derek





  #11   Report Post  
derek
 
Posts: n/a
Default

Thanks everyone for all your help on this. You guys are a credit to your
industry and if the techs that came to my house had this kind of knowledge
and attitude I probably wouldn’t have had to go through this. But I do know
an awful lot more about furnaces now.
I’m still going to install the roll out switch and start saving the dough
to get a new unit.
Thanks again
Derek

  #12   Report Post  
Bubba
 
Posts: n/a
Default

On Sun, 28 Nov 2004 14:08:09 -0600, "TURTLE"
wrote:


"derek" wrote in message
9.191...
Could it be this simple
I looked carefully at the panels and noticed that the one on top was not
covering the exhaust completely. I then noticed that they are
interchangeable. It’s possible that when I had the unit inspected before we
bought the house (I wasn’t here) they mixed up the panels. With the long
one on the bottom there isn’t nearly the gap for air intake as with the
short panel.
Hmmmm.
Derek


This is Turtle.

You just fixed it for in the picture if that is they way you have it. You will
starve the burners for air by cutting off the air supply to it. The Doors was
your problem in the beginning. Get the Door right and it will not burn up the
burner area.

TURTLE


hehe. Too funny. Lloyd gives out gas pressure info (10"WC) that could
be confused by the 3.5" WC on the outlet side. I could just see this
guy cranking up his outlet pressure trying to reach 10"WC. Remember,
this is a guy that puts a door panel in the wrong place and starves
the burner for air.
Then Zypher starts guessing at everything then tells him he needs a
new furnace. That freakin Williamson will probably be there another 35
years. Those have heat exchangers made like a tank. This, for a guy
that didnt need to spend a penny and only needed to put the door on
properly. Although that new belt, without checking amperage draw, may
burn up your motor now.
Im not trying to chew on your asses (Lloyd or Zypher) but you've gotta
realize that you have no way of knowing what the poster is or isnt
capable of. Something as simple as a door on wrong can kill. Its going
to get someone hurt.
Derek, just remember, there are rocket scientists and engineers out
there and I wouldnt dare let them near my furnace.
Your kiln building means nothing in the hvac world. Two completly
different animals
clip, clomp, clomp (stepping down off the soap box)
Bubba

  #13   Report Post  
Gary R. Lloyd
 
Posts: n/a
Default

On Mon, 29 Nov 2004 00:29:14 GMT, Bubba
wrote:

On Sun, 28 Nov 2004 14:08:09 -0600, "TURTLE"
wrote:


"derek" wrote in message
89.191...
Could it be this simple
I looked carefully at the panels and noticed that the one on top was not
covering the exhaust completely. I then noticed that they are
interchangeable. It’s possible that when I had the unit inspected before we
bought the house (I wasn’t here) they mixed up the panels. With the long
one on the bottom there isn’t nearly the gap for air intake as with the
short panel.
Hmmmm.
Derek


This is Turtle.

You just fixed it for in the picture if that is they way you have it. You will
starve the burners for air by cutting off the air supply to it. The Doors was
your problem in the beginning. Get the Door right and it will not burn up the
burner area.

TURTLE


hehe. Too funny. Lloyd gives out gas pressure info (10"WC) that could
be confused by the 3.5" WC on the outlet side. I could just see this
guy cranking up his outlet pressure trying to reach 10"WC. Remember,
this is a guy that puts a door panel in the wrong place and starves
the burner for air.
Then Zypher starts guessing at everything then tells him he needs a
new furnace. That freakin Williamson will probably be there another 35
years. Those have heat exchangers made like a tank. This, for a guy
that didnt need to spend a penny and only needed to put the door on
properly. Although that new belt, without checking amperage draw, may
burn up your motor now.
Im not trying to chew on your asses (Lloyd or Zypher) but you've gotta
realize that you have no way of knowing what the poster is or isnt
capable of. Something as simple as a door on wrong can kill. Its going
to get someone hurt.
Derek, just remember, there are rocket scientists and engineers out
there and I wouldnt dare let them near my furnace.
Your kiln building means nothing in the hvac world. Two completly
different animals
clip, clomp, clomp (stepping down off the soap box)
Bubba


As I see it, he was clever enough to figure out the door thing. I
don't think I have misjudged his capabilities at all.

But why criticize in here? This is alt.home.repair, Advice is free,
and worth every penny.

Gary R. Lloyd CMS
HVACR Troubleshooting Books/Software
https://www.merchantamerica.com/tmethod/

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace Problem Doug Miller Home Repair 3 November 7th 04 02:09 PM
Furnace Problem Doug Miller Home Ownership 3 November 7th 04 02:09 PM
Lincoln SP-135T feed problem jessem Metalworking 8 May 27th 04 03:49 PM
ok, my problem seems to be with the furnace fan constantly running Mr. Mark Home Repair 29 August 25th 03 04:20 PM
New furnace blower noise problem Lenine Home Repair 5 July 25th 03 12:58 PM


All times are GMT +1. The time now is 09:19 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"