Hello,

I have an engineering question: if a point load bears on the top plate
of a stud wall, does the stud wall spread out the load by the time it
reaches the bottom plate? My WAG is that it is spread over a width
equal to the height of the stud wall. In my application, the stud
wall is on a 4" concrete slab that (I think) can handle a wall load of
300 lbs/ft, so I'm trying to figure out whether I need to add a
footing.

Thanks,
Wayne


  #2   Report Post  
Tom
 
Posts: n/a
Default

I'm no expert here, but it seems like a case could arise where a single
vertical
stud would take virtually all the load from a point source (it's slightly
taller
than it's neighbors for example).

So the better question might be, can the concrete spread the load
effectively?
In compression, the concrete strength is likely to be 2500-3000 psi. So, the
question would be can the concrete effecitvely spread the load from that one
vertical stud out to the underlaying soil?

-- Tom


"Wayne Whitney" wrote in message
...
Hello,

I have an engineering question: if a point load bears on the top plate
of a stud wall, does the stud wall spread out the load by the time it
reaches the bottom plate? My WAG is that it is spread over a width
equal to the height of the stud wall. In my application, the stud
wall is on a 4" concrete slab that (I think) can handle a wall load of
300 lbs/ft, so I'm trying to figure out whether I need to add a
footing.

Thanks,
Wayne




  #3   Report Post  
B
 
Posts: n/a
Default

If the top plate was absolutely inflexible (not possible), and all studs
were of PERfectly equal height, the weight would distribute evenly. It would
have nothing to do with the height of the wall. I am not an engineer, but I
can tell you from framing a number of houses that every load must be carried
to the ground with sufficient stud width (a stud must be doubled or tripled
or quadrupled or quintupled based on the load it carries at that point, with
NO reliance on other studs in other parts of the wall. The one point on the
floor where the doubled (or tripled, ...) stud touches must be strong enough
to hold everything up. The top sill is not to carry weight. The top sill is
really something to stabilize the studs and something to nail the sheetrock
to. I don't think you should design this project yourself. Now ... put $75
in that little slot on your computer and press Send.
-B


"Wayne Whitney" wrote in message
...
Hello,

I have an engineering question: if a point load bears on the top plate
of a stud wall, does the stud wall spread out the load by the time it
reaches the bottom plate? My WAG is that it is spread over a width
equal to the height of the stud wall. In my application, the stud
wall is on a 4" concrete slab that (I think) can handle a wall load of
300 lbs/ft, so I'm trying to figure out whether I need to add a
footing.

Thanks,
Wayne




  #4   Report Post  
Wayne Whitney
 
Posts: n/a
Default

On 2004-11-04, B wrote:

I am not an engineer, but I can tell you from framing a number of
houses that every load must be carried to the ground with sufficient
stud width (a stud must be doubled or tripled or quadrupled or
quintupled based on the load it carries at that point, with NO
reliance on other studs in other parts of the wall.


OK, that makes sense. Now, does putting a solid header in the wall
spread out a point load, and how much?

The building code says that that a loadbearing wall above a floor
diaphragm and perpendicular to the joists can be offset up to one
joist depth from a loadbearing wall beneath the floor diaphragm. So
that would suggest that the load spreads out at 45 degrees through the
solid member.

On the other hand, it seems like the two nearest studs on either side
would pick up all the load.

I don't think you should design this project yourself.


Well, I'm trying to do as much of the design as I can, and then I'll
run it by a civil engineer if I end up with anything usual, like a
point load. Plus I like to understand how everything works.

Thanks,
Wayne

  #5   Report Post  
Wayne Whitney
 
Posts: n/a
Default

On 2004-11-04, Tom wrote:

So the better question might be, can the concrete spread the load
effectively? In compression, the concrete strength is likely to be
2500-3000 psi.


A discussion of the load bearing capabilities of concrete slabs I read
seemed to indicate that the critical property is the "flexural
strength" which is on the order of 500-700 psi. Anyone know the
difference?

Thanks, Wayne



  #6   Report Post  
PrecisionMachinisT
 
Posts: n/a
Default


"Wayne Whitney" wrote in message
...
On 2004-11-04, Tom wrote:

So the better question might be, can the concrete spread the load
effectively? In compression, the concrete strength is likely to be
2500-3000 psi.


A discussion of the load bearing capabilities of concrete slabs I read
seemed to indicate that the critical property is the "flexural
strength" which is on the order of 500-700 psi. Anyone know the
difference?


See ASTM C 42 and ASTM C 78

--

SVL


  #7   Report Post  
 
Posts: n/a
Default

B wrote:

If the top plate was absolutely inflexible (not possible), and all studs
were of PERfectly equal height, the weight would distribute evenly.


And it it weren't, the weight would distribute fairly evenly.

It would have nothing to do with the height of the wall. I am not an engineer


We can tell.

but I
can tell you from framing a number of houses that every load must be carried
to the ground with sufficient stud width (a stud must be doubled or tripled
or quadrupled or quintupled based on the load it carries at that point, with
NO reliance on other studs in other parts of the wall. The one point on the
floor where the doubled (or tripled, ...) stud touches must be strong enough
to hold everything up.


You tried other techniques, and houses fell down? :-) Shark repellent works
well around here. Most houses are way overbuilt. One 2x4 stud can support
about 4000 pounds if it can't move sideways.

"Wayne Whitney" wrote:

I have an engineering question: if a point load bears on the top plate
of a stud wall, does the stud wall spread out the load by the time it
reaches the bottom plate?


How many pounds of point load? What kind of studs, on what centers?

My WAG is that it is spread over a width equal to the height of
the stud wall.


Maybe less.

In my application, the stud wall is on a 4" concrete slab that (I think)
can handle a wall load of 300 lbs/ft, so I'm trying to figure out whether
I need to add a footing.


300 lb/ft sounds weak. You might check that again.

Nick

  #9   Report Post  
 
Posts: n/a
Default

Wayne Whitney wrote:

...if a point load bears on the top plate of a stud wall, does the
stud wall spread out the load by the time it reaches the bottom plate?


How many pounds of point load? What kind of studs, on what centers?


In the scenario I was considering, a header would pick up
two 12' floor joists 16" on center


Like this, viewed in a fixed font like Courier?

| 16" |
floorfloorfloorfloorfloor
j j
o o
i i
s s
t t
headerheaderheaderheaderheader
s s
t t
u u
d d
. .
. .
. .

and one end would be supported by the stud wall.


One end of what? The joists? The header? Is the stud wall
parallel to or perpendicular to (as above) the joists?

As to the specifics of the stud wall, that is flexible. Anyway,
it is not a lot of weight, as 12' x 4' = 48 sq ft,


Where does the 4' come from?

but the end of the header only carries 1/4 of that,
so 12 sq ft @ 50 lb/sqft = 600 lbs.


Where do the 1/4 and 12 square feet come from?

P.S. I'm probably not going to go with this design, but I'm still
interested. It's been fun learning how to size beams.


Sizing beams is easy... W, L, M, f, S, b, d.
Figuring how they share loads can be harder.

Nick

  #10   Report Post  
Wayne Whitney
 
Posts: n/a
Default

On 2004-11-04,
wrote:

Wayne Whitney wrote:

In the scenario I was considering, a header would pick up
two 12' floor joists 16" on center


Like this, viewed in a fixed font like Courier?

| 16" |
floorfloorfloorfloorfloor
j j
o o
i i
s s
t t
headerheaderheaderheaderheader
s s
t t
u u
d d
. .
. .
. .


Close, sorry if my descriptions were not clear. The stud wall would
be parallel to the joists, so eliminate the lefthand "stud..." in your
diagram; the righthand "stud..." is the stud wall viewed on edge. If
I understand correctly, that's why the header presents a point load to
the stud wall; if the stud wall is perpendicular to the floor joists,
they present a distributed load to the stud wall.

and one end would be supported by the stud wall.


One end of what?


One end of the header would be supported by the stud wall.

As to the specifics of the stud wall, that is flexible. Anyway,
it is not a lot of weight, as 12' x 4' = 48 sq ft,


Where does the 4' come from?


Sorry, 4' is the header length, since it spans 4 joists (3 * 16"),
carrying the middle two. Actually, I guess I'm assuming it carries 3
joists if I use the 4' figure.

but the end of the header only carries 1/4 of that,
so 12 sq ft @ 50 lb/sqft = 600 lbs.


Where do the 1/4 and 12 square feet come from?


The 12' x 4' floor area I'm considering is supported on one short side
by a concrete retaining wall, and on the other short side by a header.
One end of the header bears on another concrete retaining wall; the
other end would bear on a stud wall. So the header carries half the
floor area, and the stud wall carries half of the header, hence 1/4.
12 square feet = 1/4 * 4' * 12'.

Anyway, this is not my current design, but a reality check on the
analysis is welcome. The original question was "does the stud wall
spread out the point load?". If the 4" conrete slab can support 300
lbs/foot, and if the point load from the header is 600 ft, then it
would be OK as long as the stud wall spread the point load out over at
least 2 feet.

Thanks, Wayne

P.S. In my current design, I just have beams big enough to carry
everything and bearing on the concrete retaining walls. The header
still presents a point load to the beam parallel to the joists, but
I've figured out how to do the analysis of a beam with a point load.



  #11   Report Post  
B
 
Posts: n/a
Default


"Wayne Whitney" wrote in message
...
On 2004-11-04,
wrote:

Wayne Whitney wrote:

In the scenario I was considering, a header would pick up
two 12' floor joists 16" on center


Like this, viewed in a fixed font like Courier?

| 16" |
floorfloorfloorfloorfloor
j j
o o
i i
s s
t t
headerheaderheaderheaderheader
s s
t t
u u
d d
. .
. .
. .


Close, sorry if my descriptions were not clear. The stud wall would
be parallel to the joists, so eliminate the lefthand "stud..." in your
diagram; the righthand "stud..." is the stud wall viewed on edge. If
I understand correctly, that's why the header presents a point load to
the stud wall; if the stud wall is perpendicular to the floor joists,
they present a distributed load to the stud wall.

and one end would be supported by the stud wall.


One end of what?


One end of the header would be supported by the stud wall.

As to the specifics of the stud wall, that is flexible. Anyway,
it is not a lot of weight, as 12' x 4' = 48 sq ft,


Where does the 4' come from?


Sorry, 4' is the header length, since it spans 4 joists (3 * 16"),
carrying the middle two. Actually, I guess I'm assuming it carries 3
joists if I use the 4' figure.

but the end of the header only carries 1/4 of that,
so 12 sq ft @ 50 lb/sqft = 600 lbs.


Where do the 1/4 and 12 square feet come from?


The 12' x 4' floor area I'm considering is supported on one short side
by a concrete retaining wall, and on the other short side by a header.
One end of the header bears on another concrete retaining wall; the
other end would bear on a stud wall. So the header carries half the
floor area, and the stud wall carries half of the header, hence 1/4.
12 square feet = 1/4 * 4' * 12'.

Anyway, this is not my current design, but a reality check on the
analysis is welcome. The original question was "does the stud wall
spread out the point load?". If the 4" conrete slab can support 300
lbs/foot, and if the point load from the header is 600 ft, then it
would be OK as long as the stud wall spread the point load out over at
least 2 feet.

Thanks, Wayne

P.S. In my current design, I just have beams big enough to carry
everything and bearing on the concrete retaining walls. The header
still presents a point load to the beam parallel to the joists, but
I've figured out how to do the analysis of a beam with a point load.



  #12   Report Post  
B
 
Posts: n/a
Default

This is a warning, friends. You are speculating the hell out of some tried
and true building techniques that are covered by very specific building
codes. Building codes cover the minimal standards so that you or your
children will not get killed when there's snow on the roof, or water, or a
worker, or some other exceptional (or normal) condition. There are standards
on the depth and width of footings, and you can't build much of anything on
a 4'' slab. There are standard on the number of studs and where they must go
to hold up such and such a type of ceiling or whatever. I can see the code
book from where I sit at this desk, but I'm not going to offer any more
specifics because I don't want to wonder whether you get killed, or even if
your 4-inch slab cracks and the studs settle and cause your house to crack.
-B

"Wayne Whitney" wrote in message
...
On 2004-11-04,
wrote:

Wayne Whitney wrote:

In the scenario I was considering, a header would pick up
two 12' floor joists 16" on center


Like this, viewed in a fixed font like Courier?

| 16" |
floorfloorfloorfloorfloor
j j
o o
i i
s s
t t
headerheaderheaderheaderheader
s s
t t
u u
d d
. .
. .
. .


Close, sorry if my descriptions were not clear. The stud wall would
be parallel to the joists, so eliminate the lefthand "stud..." in your
diagram; the righthand "stud..." is the stud wall viewed on edge. If
I understand correctly, that's why the header presents a point load to
the stud wall; if the stud wall is perpendicular to the floor joists,
they present a distributed load to the stud wall.

and one end would be supported by the stud wall.


One end of what?


One end of the header would be supported by the stud wall.

As to the specifics of the stud wall, that is flexible. Anyway,
it is not a lot of weight, as 12' x 4' = 48 sq ft,


Where does the 4' come from?


Sorry, 4' is the header length, since it spans 4 joists (3 * 16"),
carrying the middle two. Actually, I guess I'm assuming it carries 3
joists if I use the 4' figure.

but the end of the header only carries 1/4 of that,
so 12 sq ft @ 50 lb/sqft = 600 lbs.


Where do the 1/4 and 12 square feet come from?


The 12' x 4' floor area I'm considering is supported on one short side
by a concrete retaining wall, and on the other short side by a header.
One end of the header bears on another concrete retaining wall; the
other end would bear on a stud wall. So the header carries half the
floor area, and the stud wall carries half of the header, hence 1/4.
12 square feet = 1/4 * 4' * 12'.

Anyway, this is not my current design, but a reality check on the
analysis is welcome. The original question was "does the stud wall
spread out the point load?". If the 4" conrete slab can support 300
lbs/foot, and if the point load from the header is 600 ft, then it
would be OK as long as the stud wall spread the point load out over at
least 2 feet.

Thanks, Wayne

P.S. In my current design, I just have beams big enough to carry
everything and bearing on the concrete retaining walls. The header
still presents a point load to the beam parallel to the joists, but
I've figured out how to do the analysis of a beam with a point load.



  #13   Report Post  
Wayne Whitney
 
Posts: n/a
Default

On 2004-11-05, B wrote:

I can see the code book from where I sit at this desk, but I'm not
going to offer any more specifics because I don't want to wonder
whether you get killed, or even if your 4-inch slab cracks and the
studs settle and cause your house to crack.


Doom and gloom is not very informative. I believe there is a place
for "why can or can't I do this?"

Yours, Wayne

  #14   Report Post  
Nate
 
Posts: n/a
Default


"B"

This is a warning, friends. You are speculating the hell out of some tried
and true building techniques


That's an understatement. Wanking seems like a closer representation.

I am an engineer, with the facilities on this machine and experience to
prove out or arrive at any framing code in the books. In fact, framed
structures and beams are a relatively trivial, 101 level analysis. But I
don't do construction. I do small metal parts. That said, I know there are
so many freak'n variables in the loading and material equations (snow, wood
types, wind loads, yada, yada, yada.) these guys use that I don't have a
chance in heck of getting the right answer without an exhausting amount
homework and research into something someone else has already figured out
and tested across millions of homes over 100's of years - so I read the code
book. It makes the exercise trivial. Go buy a codebook. If you can't
understand a codebook, do the next owner of your house a HUGE favor and
immediately return your Stanley hammer to Home Depot.


- Nate



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Load bearing wall John Covington Home Repair 3 March 19th 04 09:25 PM
Concrete retaining wall issue revisited. Pat Keith Home Repair 14 August 20th 03 09:35 PM
Building an internal wall - brick or stud? steve UK diy 6 July 24th 03 09:40 AM


All times are GMT +1. The time now is 12:00 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"