Hiya
 
Posts: n/a
Default Carrier or Lennox ?

Replacement system. Down to a choice between Lennox 2 stage variable
speed propane furnace G61V 70,000 BTU+ 2 stage HPX19 three ton heat
pump or Carrier 2stage variable speed 58MVP 80,000 BTU furnace + two
stage 38DVB three ton heat pump.
There isn't $20 difference in the estimates. Trane guy priced a
comparable system way high at 1200 more than either Lennox or Carrier
so Trane is out.
Plus for Lennox: Very Quiet (units close to master bedroom)
Scroll Compressor - big advantage?

Plus for Carrier: Better control system

Efficiency is comparable.
Prices are comparable.
Warranty the same.

Anything else to consider?
  #2   Report Post  
Red Neckerson
 
Posts: n/a
Default


"Hiya" wrote

Replacement system. Down to a choice between Lennox 2 stage variable
speed propane furnace G61V 70,000 BTU+ 2 stage HPX19 three ton heat
pump or Carrier 2stage variable speed 58MVP 80,000 BTU furnace + two
stage 38DVB three ton heat pump.
There isn't $20 difference in the estimates. Trane guy priced a
comparable system way high at 1200 more than either Lennox or Carrier
so Trane is out.


This is what bugs the sh*t out of me:

People buy new cars and will spend $1500 to $10,000 on options. People will
spend over a quarter of a million dollars on a home. But when it comes to
putting a system in that will give them trouble free comfort in a place
where they LIVE, they will refuse to even consider a system because "it
costs too much". You turn down a Trane system because it is "way high at
$1200 more"? Heavens! You could put that towards those fancy wheel covers on
your next car!!!

I'm not saying you should go with a Trane over the other brands. A system is
as good as the contractor that installs it. But you need to look at the
efficiency ratings, warranties, service (who will work on it oince it's
installed) , etc. and base your decision on criteria other than price.


  #3   Report Post  
Hiya
 
Posts: n/a
Default

On Sat, 30 Oct 2004 15:06:52 GMT, "Red Neckerson"
wrote:


I'm not saying you should go with a Trane over the other brands. A system is
as good as the contractor that installs it. But you need to look at the
efficiency ratings, warranties, service (who will work on it oince it's
installed) , etc. and base your decision on criteria other than price.

If you read my post you know I did consider those things.
Like it or not, price is a discriminator and frankly it is goofy to
think otherwise. All systems under consideration were "top of the
line", all good products I consider fairly comparable. I see no
reason to give an extra $1200 for the name "Trane".
If you can show me that Trane is worth the extra $1200 over Carrier
and Lennox go right ahead. I'd be happy to learn why you think so.
  #4   Report Post  
m Ransley
 
Posts: n/a
Default

You will get a more efficient motor on the Carrier for the furnace
blower, I have the consumption sheets somewhere. It was apx 25% less on
the Carrier VS DC blower. The Carrier thermostat that allows fan speed
control at the stat is cheaper on Carrier by 1-200$. And I beleive has
more features. Get the 10 yr warranty. The variable speed motors
although redesigned do fail.

Get factory electric consumption sheets for both units for furnace and
heat pump to make your own decision. Ive decided on carrier. Also
because the secondary coil on the Lennox furnace looks to be impossible
to clean easily, by its design. On an older 3 yr Lennox Dimension

Be sure you have a load calc done in writing, upping AC efficiency can
often leave to much humidity if the unit is near to being oversized. If
3 is what you had and it was correct a new 3 ton has a higher seer, you
may only want 2.5 ton . This was my mistake. Also if you plan future
insulation or doors or windows figure this in now. Here again I made a
mistake and insulated afterwards and my AC is oversized now. I must run
2 dehumidifiers to really remove humidity.

Also for the furnace, does yours keep up or is it underpowered, I down
graded from 110000 btu to 47000 btu, now I get a more even comfortable
heat, but I could have gone even lower. The Carrier is made to run more
of the time at low fan speed. Here it is a matter of comfort and heat
eveness.

In the end it is the installer that counts. Being sure he is real good,
works with you and gets you the properly sized equipment. To small an
AC , you wont cool, to large you will be humid and clammy. To small a
furnace it will strugle, to large it will have heat swings, uneven heat
and short cycle.

Remember get a load calculation in writing, guessing is not going to
work.

  #5   Report Post  
m Ransley
 
Posts: n/a
Default

Trane doesnt compare to Lennox or Carrier furnaces on heat efficiency or
blower motor efficiency. On heat pumps I have no idea.



  #6   Report Post  
SQLit
 
Posts: n/a
Default


"Hiya" wrote in message
...
Replacement system. Down to a choice between Lennox 2 stage variable
speed propane furnace G61V 70,000 BTU+ 2 stage HPX19 three ton heat
pump or Carrier 2stage variable speed 58MVP 80,000 BTU furnace + two
stage 38DVB three ton heat pump.
There isn't $20 difference in the estimates. Trane guy priced a
comparable system way high at 1200 more than either Lennox or Carrier
so Trane is out.
Plus for Lennox: Very Quiet (units close to master bedroom)
Scroll Compressor - big advantage?

Plus for Carrier: Better control system

Efficiency is comparable.
Prices are comparable.
Warranty the same.

Anything else to consider?


Trane is offering attractive financing and an $1000.00 rebate here.
Does the Trane have an scroll compressor?

Scrolls are usually quieter than recips. I would ask each bidder for the
address of installations of the condenser units and phone numbers. I would
go listen to each.
I put an American Standard/Trane outside my bedroom window because I was
told I would never hear it. HE LIED. It took me almost 3 months to stop
waking up every time the condenser turned on.

Are the heating and cooling seer numbers the same? I would go with the
higher number for the biggest load you have. Heat or cool. Here I am not at
all concerned with heat numbers as I use the heat maybe 6 days a year.

As others have said the installer is the key, not the equipment.

Are you going to get your ducts cleaned??? I would


  #7   Report Post  
TURTLE
 
Posts: n/a
Default


"Hiya" wrote in message
...
Replacement system. Down to a choice between Lennox 2 stage variable
speed propane furnace G61V 70,000 BTU+ 2 stage HPX19 three ton heat
pump or Carrier 2stage variable speed 58MVP 80,000 BTU furnace + two
stage 38DVB three ton heat pump.
There isn't $20 difference in the estimates. Trane guy priced a
comparable system way high at 1200 more than either Lennox or Carrier
so Trane is out.
Plus for Lennox: Very Quiet (units close to master bedroom)
Scroll Compressor - big advantage?

Plus for Carrier: Better control system

Efficiency is comparable.
Prices are comparable.
Warranty the same.

Anything else to consider?


This is Turtle.

It would be hard to try to decide between a Carrier and a Lennox as to using the
equipment quality as a deciding tool. Your guess is good as mine here.

Now what you should be looking at here is what kind of installer is the two
dealer that are bidding on the equipment. Is the carrier or the lennox dealer
the better installer. A good installer is hard to find in this world of who will
do it for the least they can get by with. You need to do some research and fine
out about some of the job the two dealers has done and see who really installs
it correctly and not have any trouble afterwards. Get you 3 or 4 referrences
from the two and call them up and talk about their equipment and about it
running good afterwards.

Now one thing here have a scroll compressor on your unit for sure.

TURTLE


  #8   Report Post  
Hiya
 
Posts: n/a
Default

On Sat, 30 Oct 2004 11:22:23 -0500, (m Ransley)
wrote:

The Carrier thermostat that allows fan speed
control at the stat is cheaper on Carrier by 1-200$. And I beleive has
more features. Get the 10 yr warranty. The variable speed motors
although redesigned do fail.


Carrier does have better controls, I agree. I may go for extended
warranty, depends on price.

Also for the furnace, does yours keep up or is it underpowered, I down
graded from 110000 btu to 47000 btu, now I get a more even comfortable
heat, but I could have gone even lower. The Carrier is made to run more
of the time at low fan speed. Here it is a matter of comfort and heat
eveness.


Currently no furnace, heat strips only. Three guys did load calcs and
all came up with 70,000 BTU and three ton AC. One guy admitted he
thought it would be larger. It appears Carrier does not make a 70000
BTU furnace but I don't think 80000 is grossly oversized.

In the end it is the installer that counts. To small a
furnace it will strugle, to large it will have heat swings, uneven Being sure he is real good,
works with you and gets you the properly sized equipment.


Yeah, I eliminated a couple of guys right away. One was selling the
company and a "satisfaction guarantee" claiming I could get all of my
money back if not happy and comfortable. He could tell me almost
nothing about the equipment. He only sold "packages" at different
price points...$3.000, $5,000, $10,000. Dropped him like a hot rock.
Another sold Lennox but never looked at insulation, ductwork, sq.
foot or did a load calc. He admitted he took the size off exixting
equipment and used it. He had to go back to his office to "work up" a
proposal. He is mailing it. I think it will get lost in the mail.

Thanks for your input.
  #9   Report Post  
Hiya
 
Posts: n/a
Default

On Sat, 30 Oct 2004 09:55:38 -0700, "SQLit"
wrote:


Trane is offering attractive financing and an $1000.00 rebate here.
Does the Trane have an scroll compressor?


Up to $1000 depending on what you buy.
FYI so are Carrier and Lennox for a few more days.

Scrolls are usually quieter than recips. I would ask each bidder for the
address of installations of the condenser units and phone numbers. I would
go listen to each.
I put an American Standard/Trane outside my bedroom window because I was
told I would never hear it. HE LIED. It took me almost 3 months to stop
waking up every time the condenser turned on.


Yikes. Well Carrier still uses recip and the equipment is fairly
close to the master bedroom.

Are the heating and cooling seer numbers the same?

Yes, very close.

Are you going to get your ducts cleaned??? I would


Never thought about it. Why?

  #10   Report Post  
Hiya
 
Posts: n/a
Default

On Sun, 31 Oct 2004 00:29:12 -0500, "TURTLE"
wrote:


This is Turtle.

It would be hard to try to decide between a Carrier and a Lennox as to using the
equipment quality as a deciding tool. Your guess is good as mine here.

Now what you should be looking at here is what kind of installer is the two
dealer that are bidding on the equipment. Is the carrier or the lennox dealer
the better installer. A good installer is hard to find in this world of who will
do it for the least they can get by with. You need to do some research and fine
out about some of the job the two dealers has done and see who really installs
it correctly and not have any trouble afterwards. Get you 3 or 4 referrences
from the two and call them up and talk about their equipment and about it
running good afterwards.


Lennox guy is a local boy who has done work for me before. Everyone
will tell you his shop is good but expensive. Fact is he gave a
better price than most from the small city 15 miles away.

Don't know the other guy but if I go Carrier I will check a couple of
his installations.

Now one thing here have a scroll compressor on your unit for sure.


Well, that may decide the issue. Lennox uses scroll but Carrier does
not. Carrier claims a SEER as good as Lennox (maybe better) but many
say Carrier is not as quiet.

TURTLE


Thanks Turtle.



  #11   Report Post  
m Ransley
 
Posts: n/a
Default

With the equipment you are looking at , top of the line and all the
extras there is alot more to break, get the 10 yr full warranty, a VS DC
motor may be a 600 $ replacement.

You are looking at two stage gas, right. Carrier Mvp has a 49000 low
fire 75000 high fire model, a 61000 low fire-93000 high fire Btu model
and a 73000 low fire- 113000 high fire model . I dont know if these are
input or output ratings, I believe output . The 70000 Btu he gave you
is what you will need at the coldest temps. And is probably input btu.
with a VS 2 stage you only need the high fire in cold weather, or for
recovering from setback temps. You can use the 49000- 75000 unit, or
maybe even a smaller one if theses are output figures. Dont oversize,
you will get more even heat with a smaller unit, and short cycle less.
My unit is oversized and the second stage is only used to recover from
set back temps, not in normal operation. My next replacement will be a
size smaller in Btu.

AC Compressors- heat pumps, have Db sound ratings from the factory, a
standard is at 3 ft for testing, check ratings and at what distance the
testing was done.

Either way both units are good, so it is up to a real good instaler to
get you the right unit and proper instal.

  #12   Report Post  
TURTLE
 
Posts: n/a
Default


"Hiya" wrote in message
...
On Sun, 31 Oct 2004 00:29:12 -0500, "TURTLE"
wrote:


This is Turtle.

It would be hard to try to decide between a Carrier and a Lennox as to using
the
equipment quality as a deciding tool. Your guess is good as mine here.

Now what you should be looking at here is what kind of installer is the two
dealer that are bidding on the equipment. Is the carrier or the lennox dealer
the better installer. A good installer is hard to find in this world of who
will
do it for the least they can get by with. You need to do some research and
fine
out about some of the job the two dealers has done and see who really installs
it correctly and not have any trouble afterwards. Get you 3 or 4 referrences
from the two and call them up and talk about their equipment and about it
running good afterwards.


Lennox guy is a local boy who has done work for me before. Everyone
will tell you his shop is good but expensive. Fact is he gave a
better price than most from the small city 15 miles away.

Don't know the other guy but if I go Carrier I will check a couple of
his installations.

Now one thing here have a scroll compressor on your unit for sure.


Well, that may decide the issue. Lennox uses scroll but Carrier does
not. Carrier claims a SEER as good as Lennox (maybe better) but many
say Carrier is not as quiet.


This is Turtle.

Get you a scroll in there and if noise is a issue. Get you a sound blanket for
about $35.00 and put on the scroll compressor.

I didn't stutter here. Get you a scroll compressor on your stuff.

Now watch out here and get the installer that you know that has done good work
for you in the past and don't try out somebody new on the block. Go with the
installer that you know about and not one you WANT to know about.

TURTLE


Thanks Turtle.


Your Elkcome

TURTLE



  #13   Report Post  
davefr
 
Posts: n/a
Default

When it comes to HVAC, these qualities shouldn't be under estimated.
It would take a very compelling reason not to tip the scale in this
contractor's favor.


Hiya wrote in message . ..

Lennox guy is a local boy who has done work for me before.

Everyone
will tell you his shop is good but expensive. Fact is he gave a
better price than most from the small city 15 miles away.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Carrier variable speed gas furnace don h Home Repair 0 October 24th 04 10:54 PM
Carrier 58MPV vs Lenox G61MPV-363-070 comparrison? Jdmst Home Repair 10 August 20th 04 11:56 AM
Mechanical jamming problem with CD shuffle carrier mechanism Nigel Cook Electronics Repair 4 October 18th 03 03:20 PM


All times are GMT +1. The time now is 04:20 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"