A tenant of mine had an outlet start sparking after trying to plug a
lamp into it. There is an air conditioner on the same circuit as
well. The sparking was bad enough to melt the side of the outlet
where the wire get screwed in. Shouldn't the circuit breaker have
tripped? Do cicuit breakers go bad such that they do not trip when
they need to?
  #2   Report Post  
toller
 
Posts: n/a
Default

Circuit breakers do go bad and fail to trip on overloads, but it is unusual.
More commonly they trip unnecessarily when they fail.

But, they will not trip on arcs unless there is also an overload. Arc fault
circuit breakers were invented for precisely that reason; to protect against
arcs that did not involve overloads.
They outlet was probably damaged, and that is what caused the problem. The
breaker is "probably" okay, but unless you want to test it, you might rest
easier replacing the breaker. Hey, why not replace it with an arc fault
breaker?!


  #3   Report Post  
TURTLE
 
Posts: n/a
Default


"balboni" wrote in message
om...
A tenant of mine had an outlet start sparking after trying to plug a
lamp into it. There is an air conditioner on the same circuit as
well. The sparking was bad enough to melt the side of the outlet
where the wire get screwed in. Shouldn't the circuit breaker have
tripped? Do cicuit breakers go bad such that they do not trip when
they need to?


This is Turtle.

They sure do !

Replace the I.T.E. breaker for just good measure to be safe.

TURTLE


  #4   Report Post  
Childfree Scott
 
Posts: n/a
Default

I would also add that replacing the breaker might be a good idea if
it's very old. Older ones aren't as reliable as newer ones. They
sometimes go bad slowly with age.
  #5   Report Post  
SQLit
 
Posts: n/a
Default


"balboni" wrote in message
om...
A tenant of mine had an outlet start sparking after trying to plug a
lamp into it. There is an air conditioner on the same circuit as
well. The sparking was bad enough to melt the side of the outlet
where the wire get screwed in. Shouldn't the circuit breaker have
tripped? Do cicuit breakers go bad such that they do not trip when
they need to?


You can not afford to test an molded case circuit breaker. Here in Phoenix I
know of only one company that has MC CB testers. And they can not test every
brand.

Call a pro and have the circuit checked out. If you can "weld" with the
circuit there could be something wrong with the grounding for the circuit.

For the ~15 bucks replace the offending unit. When you replace it. Force all
of the breakers off and on a couple of times. Sometimes they will "freeze"
into an ON position.


---
Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.754 / Virus Database: 504 - Release Date: 9/6/2004




  #7   Report Post  
balboni
 
Posts: n/a
Default

"toller" wrote in message ...
Circuit breakers do go bad and fail to trip on overloads, but it is unusual.
More commonly they trip unnecessarily when they fail.

But, they will not trip on arcs unless there is also an overload. Arc fault
circuit breakers were invented for precisely that reason; to protect against
arcs that did not involve overloads.
They outlet was probably damaged, and that is what caused the problem. The
breaker is "probably" okay, but unless you want to test it, you might rest
easier replacing the breaker. Hey, why not replace it with an arc fault
breaker?!


Could the arc have been caused by bad wire? The outlet was only one
year old, but the wiring is very old. Someone suggested that the wire
is too old and needs to be replaced. If it is charred, can it just be
cut back and used again?
  #8   Report Post  
toller
 
Posts: n/a
Default



Could the arc have been caused by bad wire? The outlet was only one
year old, but the wiring is very old. Someone suggested that the wire
is too old and needs to be replaced. If it is charred, can it just be
cut back and used again?


Without seeing I can't really answer that, but it seems unlikely.
Since the arc happened when you plugged the light in (right?) the problem
had to either be the outlet or the connection between the outlet and the
wire. A defective hot wire does not need anything plugged in to short, and
a defective neutral should not short unless it is completely broken.
Did the person who installed the outlet know what they were doing? If the
outlet is a year old and not abused, a bad connection sounds like the
culprit. Was the wire attached to a screw terminal or pushed through a hole
in the back. The holes in the back are very prone to failure, at least on
the $0.99 outlets.
If there is no visible damage to the wire, and it is not overloaded, it
should be safe; though some 70 year old wiring looks pretty dicey.

If you have enough wire to cut it back to a sound section, it ought to be
okay, though again, I can't see the wire so it might be prudent to get
someone to see it if you have any doubt.


  #10   Report Post  
default
 
Posts: n/a
Default



Could the arc have been caused by bad wire? The outlet was only one
year old, but the wiring is very old. Someone suggested that the wire
is too old and needs to be replaced. If it is charred, can it just be
cut back and used again?


OP said it went when the tenant tried to plug something into it...
My bet would be improperly installed plaster-ears shifted when
the plugh got shoved in, and either cut something, or bridged
two screw-contacts.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
circuit is off, circuit breaker is on Massi Home Repair 1 July 4th 04 11:31 PM
circuit breaker question! barry martin Home Repair 0 May 2nd 04 08:12 PM
15A Circuit Breaker on a Power Tap Jajal Electronics 3 April 3rd 04 03:18 PM
Is it a radial or ring circuit? Paul UK diy 14 September 4th 03 04:48 PM
Help -- Power out in one area but circuit breaker not tripped Joseph Meehan Home Repair 0 June 27th 03 02:29 AM


All times are GMT +1. The time now is 05:33 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"