Ridge Vent or Box Vents?
 
I have heard that ridge vents only work well if there are wide soffits,
like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?

[email protected] April 8th 12 10:48 PM

Ridge Vent or Box Vents?
 
On Sun, 08 Apr 2012 17:42:42 -0400, DerbyDad03 wrote:

I have heard that ridge vents only work well if there are wide soffits,
like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


Don't see how the size of the soffits would matter. The area of the vents
(equivalent opening) certainly matters. While they're related they're not the
same. A 12" soffit isn't all that wide though.

DerbyDad03[_2_] April 8th 12 10:59 PM

Ridge Vent or Box Vents?
 
On 04/08/12 5:48 PM, zzzzzzzzzz wrote:
On Sun, 08 Apr 2012 17:42:42 -0400, wrote:

I have heard that ridge vents only work well if there are wide soffits,
like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


Don't see how the size of the soffits would matter. The area of the vents
(equivalent opening) certainly matters. While they're related they're not the
same. A 12" soffit isn't all that wide though.


It is compared to my 6" soffits.

12" or more was the number that a roofing estimator used when he
recommended box vents for my house.

He mentioned box vents, I asked why not a ridge vent, he said my soffits
are too narrow.

He then went on to explain that ridge vents only work well with wide
soffits, 12" or more.

[email protected][_2_] April 9th 12 12:11 AM

Ridge Vent or Box Vents?
 
On Apr 8, 5:59*pm, DerbyDad03 wrote:
On 04/08/12 5:48 PM, wrote:

On Sun, 08 Apr 2012 17:42:42 -0400, *wrote:


I have heard that ridge vents only work well if there are wide soffits,
like 12" or more.


On houses with narrow soffits, box vents are recommended.


Any truth to this?


Don't see how the size of the soffits would matter. *The area of the vents
(equivalent opening) certainly matters. *While they're related they're not the
same. *A 12" soffit isn't all that wide though.


It is compared to my 6" soffits.

12" or more was the number that a roofing estimator used when he
recommended box vents for my house.

He mentioned box vents, I asked why not a ridge vent, he said my soffits
are too narrow.

He then went on to explain that ridge vents only work well with wide
soffits, 12" or more.


The principle is that hot air rises. So, you want intakes
near the bottom and outlets near the top. Whether the
outlets are ridge or box vents isn't going to matter.
What's more important is the square footage of each.

As to needing soffit vents that are greater than 12" wide,
are we talking CONTINUOS soffit vents? If so, the
roofer is nuts. Vents even 3 or 4" wide, run continously,
are going to provide a lot of intake area.

I'd go with the ridge vent. And if the soffit vents aren't
big enough, then I'd enlarge them, if possible. Many
cases all it takes are one of the small cordless circular
saws run down the length. Plus ridge vents, IMO, look
a lot better.

Pat[_5_] April 9th 12 12:28 AM

Ridge Vent or Box Vents?
 

"DerbyDad03" wrote in message
...
I have heard that ridge vents only work well if there are wide soffits,
like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


Your roofer sees a problem with using ridge vents and isn't explaining why
very well. Perhaps you should talk to more roofers. If you have already
hired him perhaps you could get him to elaborate.



Bob F April 9th 12 12:29 AM

Ridge Vent or Box Vents?
 
wrote:
On Apr 8, 5:59 pm, DerbyDad03 wrote:
On 04/08/12 5:48 PM, wrote:

On Sun, 08 Apr 2012 17:42:42 -0400,
wrote:


I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.


On houses with narrow soffits, box vents are recommended.


Any truth to this?


Don't see how the size of the soffits would matter. The area of the
vents (equivalent opening) certainly matters. While they're related
they're not the same. A 12" soffit isn't all that wide though.


It is compared to my 6" soffits.

12" or more was the number that a roofing estimator used when he
recommended box vents for my house.

He mentioned box vents, I asked why not a ridge vent, he said my
soffits are too narrow.

He then went on to explain that ridge vents only work well with wide
soffits, 12" or more.


The principle is that hot air rises. So, you want intakes
near the bottom and outlets near the top. Whether the
outlets are ridge or box vents isn't going to matter.
What's more important is the square footage of each.

As to needing soffit vents that are greater than 12" wide,
are we talking CONTINUOS soffit vents? If so, the
roofer is nuts. Vents even 3 or 4" wide, run continously,
are going to provide a lot of intake area.

I'd go with the ridge vent. And if the soffit vents aren't
big enough, then I'd enlarge them, if possible. Many
cases all it takes are one of the small cordless circular
saws run down the length. Plus ridge vents, IMO, look
a lot better.


The goal should be to have free, clear venting in the soffits equal to the top
vent area. I can imagine no reason for needing wide siffits for that as long as
the isulation can be kept clear of the air flow space.



Larry Fishel April 9th 12 01:02 AM

Ridge Vent or Box Vents?
 
On Apr 8, 5:42*pm, DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide soffits,
like 12" or more.

On houses with narrow soffits, box vents are recommended.


It seems to me that there might be some failure to communicate here
(the forum). The OP is saying (taken literally) that his SOFFITS are
6", not his soffit VENTS. That leaves very little room for vents and
maybe the roofer thinks he will need fans to pull enough air through?
I don't know enough to offer an opinion on whether that would be
correct...

[email protected][_2_] April 9th 12 01:22 AM

Ridge Vent or Box Vents?
 
On Apr 8, 8:02*pm, Larry Fishel wrote:
On Apr 8, 5:42*pm, DerbyDad03 wrote:

I have heard that ridge vents only work well if there are wide soffits,
like 12" or more.


On houses with narrow soffits, box vents are recommended.


It seems to me that there might be some failure to communicate here
(the forum). The OP is saying (taken literally) that his SOFFITS are
6", not his soffit VENTS. That leaves very little room for vents and
maybe the roofer thinks he will need fans to pull enough air through?
I don't know enough to offer an opinion on whether that would be
correct...


Thanks for correcting that. Even with 6" soffits, if you ran a 2 or 3
inch wide continuous soffit down it, that adds up
to a lot of intake space, 24 or 36 sq inches per foot.
The only reason that wouldn't work is if there were
something in the construction blocking it. That something
in many cases is insulation that gets shoved too far, right
over the vents. To do it right, there should be plastic
baffles that you can get at HD that get stapled to the
underside of the sheating, at the soffits, that form an
open channel for a few feet from the soffit so that air
can flow.

A continuous soffit vent together with a continous ridge
vent, IMO is the optimal solution. The ridge vent is
typically a couple inches wide. A similar size opening
along the soffit and you're all set.

[email protected] April 9th 12 01:44 AM

Ridge Vent or Box Vents?
 
On Sun, 8 Apr 2012 16:29:15 -0700, "Bob F" wrote:

wrote:
On Apr 8, 5:59 pm, DerbyDad03 wrote:
On 04/08/12 5:48 PM, wrote:

On Sun, 08 Apr 2012 17:42:42 -0400,
wrote:

I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?

Don't see how the size of the soffits would matter. The area of the
vents (equivalent opening) certainly matters. While they're related
they're not the same. A 12" soffit isn't all that wide though.

It is compared to my 6" soffits.

12" or more was the number that a roofing estimator used when he
recommended box vents for my house.

He mentioned box vents, I asked why not a ridge vent, he said my
soffits are too narrow.

He then went on to explain that ridge vents only work well with wide
soffits, 12" or more.


The principle is that hot air rises. So, you want intakes
near the bottom and outlets near the top. Whether the
outlets are ridge or box vents isn't going to matter.
What's more important is the square footage of each.

As to needing soffit vents that are greater than 12" wide,
are we talking CONTINUOS soffit vents? If so, the
roofer is nuts. Vents even 3 or 4" wide, run continously,
are going to provide a lot of intake area.

I'd go with the ridge vent. And if the soffit vents aren't
big enough, then I'd enlarge them, if possible. Many
cases all it takes are one of the small cordless circular
saws run down the length. Plus ridge vents, IMO, look
a lot better.


The goal should be to have free, clear venting in the soffits equal to the top
vent area. I can imagine no reason for needing wide siffits for that as long as
the isulation can be kept clear of the air flow space.


That can be done with smaller soffits, too. My last house had 6" soffits and
a ridge vent. The soffit vent was continuous, however. It wasn't the
perforated aluminum that I see elsewhere, some of which only has 1/3
perforated.

HeyBub[_3_] April 9th 12 02:21 AM

Ridge Vent or Box Vents?
 
DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


Basic rule: You can't have too much soffit vents.

At a minimum, you should have one sq ft of soffit vent for each 150 sq ft of
floor space. This is one sq ft of unobstructed venting. Some screening
material consumes as much as 2/3rds of the space. Refigure accordingly.

If you have a 1500 sq ft house, you need 100 sq ft of soffits, minimum.
Assuming the screening material is hardware cloth or similar that consumes
less than 20% of the opening, you should plan on 120 sq ft of soffit
venting. Further, assuming small, six inch soffits on a 50 x 30' house, you
have 160 feet of perimeter. That means only 80 sq ft, maximum, for available
soffit vents.

Obviously this is woefully insufficient for the appropriate amount of
passive ventilation. You'll have to move up a step in addition to ridge
vents. Turbines are the next step and beyond that powered ventilators.





Mike Paulsen[_2_] April 9th 12 03:28 AM

Ridge Vent or Box Vents?
 
HeyBub wrote:
DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


Basic rule: You can't have too much soffit vents.

At a minimum, you should have one sq ft of soffit vent for each 150 sq ft of
floor space.


(snip)

Obviously this is woefully insufficient for the appropriate amount of
passive ventilation. You'll have to move up a step in addition to ridge
vents. Turbines are the next step and beyond that powered ventilators.


When, if ever, do you need to be concerned about having too much
negative pressure in the attic? You don't want to encourage air to come
up through the ceiling any more than necessary.

Home Guy April 9th 12 04:16 AM

Ridge Vent or Box Vents?
 
DerbyDad03 wrote:

He mentioned box vents, I asked why not a ridge vent, he said my
soffits are too narrow.

He then went on to explain that ridge vents only work well with
wide soffits, 12" or more.


That's a lot of horse ****.

I've installed a few ridge vents, and you usually cut maybe a 6 to 8"
wide gap in the decking at the very peak of a roof line (3 to 4 inches
on either side).

To theoretically balance out the size of that ridge opening with a
similar soffit opening, then a 6" fully-perforated soffit would work.

Also note that sometimes even a 2-foot-wide soffit isin't what it seems,
because the bottleneck will be the gap or opening between where the deck
passes over the wall header. Usually, the wider the soffit - the
lower-slope the roof is, making for a not-so-large header gap.

A ridge vent will give you a more even airflow pattern along the
underside of the decking compared to a few box vents.

JIMMIE April 9th 12 06:57 AM

Ridge Vent or Box Vents?
 
On Sunday, April 8, 2012 5:42:42 PM UTC-4, DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide soffits,
like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


Huh, if your vents arent big enough they arent big enough no matter which you use.
Soffit material is available that basically turns the whole soffit into a vent.

Jimmie

HeyBub[_3_] April 9th 12 12:29 PM

Ridge Vent or Box Vents?
 
Mike Paulsen wrote:
HeyBub wrote:
DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


Basic rule: You can't have too much soffit vents.

At a minimum, you should have one sq ft of soffit vent for each 150
sq ft of floor space.


(snip)

Obviously this is woefully insufficient for the appropriate amount of
passive ventilation. You'll have to move up a step in addition to
ridge vents. Turbines are the next step and beyond that powered
ventilators.


When, if ever, do you need to be concerned about having too much
negative pressure in the attic? You don't want to encourage air to
come up through the ceiling any more than necessary.


Excellent point! This could easily happen with aggressively powered fans and
insufficient, or no, soffit vents.



[email protected][_2_] April 9th 12 01:37 PM

Ridge Vent or Box Vents?
 
On Apr 8, 9:21*pm, "HeyBub" wrote:
DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.


On houses with narrow soffits, box vents are recommended.


Any truth to this?


Basic rule: You can't have too much soffit vents.

At a minimum, you should have one sq ft of soffit vent for each 150 sq ft of
floor space. This is one sq ft of unobstructed venting. Some screening
material consumes as much as 2/3rds of the space. Refigure accordingly.

If you have a 1500 sq ft house, you need 100 sq ft of soffits, minimum.
Assuming the screening material is hardware cloth or similar that consumes
less than 20% of the opening, you should plan on 120 sq ft of soffit
venting. Further, assuming small, six inch soffits on a 50 x 30' house, you
have 160 feet of perimeter. That means only 80 sq ft, maximum, for available
soffit vents.

Obviously this is woefully insufficient for the appropriate amount of
passive ventilation.


There is an error in your math. Assuming you need one sq ft of
venting per 100 sq ft of floor space, then a 1500
sq ft house needs 15 sq ft of venting, not 150. You're
off by a factor of 10. Following through with the
math, you'd then want 12 sq ft actual. If you did 2"
wide vents, you get .16 sq ft per linear foot. Which
in turn means those 2" wide vents down just the
long sides of the house would give you 16 sq ft total,
meeting the min reqt.

Also, technically, it's not floor space that
counts, but the attic area that is being vented. Some
houses don't have just one open continous attic area.


You'll have to move up a step in addition to ridge
vents. Turbines are the next step and beyond that powered ventilators.


Not when you redo the math.

Home Guy April 9th 12 01:41 PM

Ridge Vent or Box Vents?
 
HeyBub wrote:

When, if ever, do you need to be concerned about having too much
negative pressure in the attic?


What do you klowns think is happening?

You think there is some big vacuum cleaner sitting on your roof, sucking
air through your ceiling just because you have too much venting?

Excellent point!


Stupid point!

This could easily happen with aggressively powered
fans and insufficient, or no, soffit vents.


What are the odds that someone is going to have powered roof fans *and
no* soffit vents?

And think about this: Even IF you are somehow creating a negative
pressure in the attic that IS pulling air through the ceiling - SO
WHAT? This is going to be happening ONLY IN THE SUMMER. ITS NO BIG
DEAL IF IT HAPPENS IN THE SUMMER. It's in the winter when you don't
want that to happen, and who's going to turn on their roof fans in the
winter ????

bob haller April 9th 12 01:46 PM

Ridge Vent or Box Vents?
 
On Apr 9, 8:41*am, Home Guy wrote:
HeyBub wrote:
When, if ever, do you need to be concerned about having too much
negative pressure in the attic?


What do you klowns think is happening?

You think there is some big vacuum cleaner sitting on your roof, sucking
air through your ceiling just because you have too much venting?

Excellent point!


Stupid point!

This could easily happen with aggressively powered
fans and insufficient, or no, soffit vents.


What are the odds that someone is going to have powered roof fans *and
no* soffit vents?

And think about this: *Even IF you are somehow creating a negative
pressure in the attic that IS pulling air through the ceiling - SO
WHAT? *This is going to be happening ONLY IN THE SUMMER. *ITS NO BIG
DEAL IF IT HAPPENS IN THE SUMMER. *It's in the winter when you don't
want that to happen, and who's going to turn on their roof fans in the
winter ????


in the summer with AC sucking cooled air from the air conditioned
space is a poor choice, but at the same time its when having a cool
attic is most important....

beyond which sucking on the living part of the home will create paths
for the air from the living area to follow all the time.....

a real lose lose kinda situation.

roof fans in the winter help keep the humidity low in the attic which
helps prevent mold growth

Home Guy April 9th 12 02:07 PM

Ridge Vent or Box Vents?
 
bob haller wrote:

in the summer with AC sucking cooled air from the air conditioned
space is a poor choice, but at the same time its when having a
cool attic is most important....

beyond which sucking on the living part of the home will create
paths for the air from the living area to follow all the time...


In the summer, if I had a choice between:

a) pulling 1000 cfm of air out of my attic using powered vents - with
950 cfm coming from the soffits (and/or gable-end vents) and 50 cfm
coming from ceiling leaks - or

b) having NO powered vents (only passive vents) and therefore only
getting 200 cfm of passive air movement out of the attic (and 0 cfm from
ceiling air leaks) -

It's a no -brainer which one is better for the house and the roof.

And if I can pull more than 50 cfm from ceiling leaks, then the answer
is NOT to turn off the fans. The answer is to fix the ceiling leaks (or
just live with them) - not sacrifice the life of the shingles by letting
attic temperatures soar.

roof fans in the winter help keep the humidity low in the
attic which helps prevent mold growth


I would bet that the vast majority of roof fans don't have humidity
sensors - only thermostats (which means they only come on in the
summer).

I know the theory of ventilating the attic in the winter to prevent
mold, but explain to me how discharging cold, humid air from the attic
and replacing it with cold, humid air from the outside is going to
change anything.

If the air in the attic is more humid than outside air in the winter,
it's because you have ceiling air leaks (or you're venting bathroom and
kitchen exhaust fans directly into the attic). It's a no-brainer that
you fix those situations first, eliminating the need for winter attic
ventilation in the first place.

Bob F April 9th 12 03:34 PM

Ridge Vent or Box Vents?
 
Home Guy wrote:
bob haller wrote:

in the summer with AC sucking cooled air from the air conditioned
space is a poor choice, but at the same time its when having a
cool attic is most important....

beyond which sucking on the living part of the home will create
paths for the air from the living area to follow all the time...


In the summer, if I had a choice between:

a) pulling 1000 cfm of air out of my attic using powered vents - with
950 cfm coming from the soffits (and/or gable-end vents) and 50 cfm
coming from ceiling leaks - or

b) having NO powered vents (only passive vents) and therefore only
getting 200 cfm of passive air movement out of the attic (and 0 cfm
from ceiling air leaks) -

It's a no -brainer which one is better for the house and the roof.


As long as you don't care what it costs to run the A/C. Trying to cool an extra
50 cfm of exterior air continuously is going to COST.



Home Guy April 9th 12 04:24 PM

Ridge Vent or Box Vents?
 
Bob F wrote:

In the summer, if I had a choice between:

a) pulling 1000 cfm of air out of my attic using powered vents -
with 950 cfm coming from the soffits (and/or gable-end vents) and
50 cfm coming from ceiling leaks - or

b) having NO powered vents (only passive vents) and therefore
only getting 200 cfm of passive air movement out of the attic
(and 0 cfm from ceiling air leaks) -

It's a no -brainer which one is better for the house and the roof.


As long as you don't care what it costs to run the A/C. Trying to
cool an extra 50 cfm of exterior air continuously is going to
COST.


That cost might be more than offset by the heat load I'm taking away
from the interior ceiling area by ventilating the attic with 950 cfm of
outside air vs 200 cfm of passive air.

Numbers like 1000, 200 and 50 (cfm) are all just hypothetical, but I
still assert that interior air leaks into the attic are trivial (for any
home built in the last 50 years) - not counting any bad practices like
venting bathroom or kitchen fans into the attic.

gonjah April 9th 12 04:51 PM

Ridge Vent or Box Vents?
 
On 4/8/2012 4:42 PM, DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


I'd ask why?

Seems to make no sense to me.

Sounds like he's saying you need larger intake vents regardless and he
likes box vents. Maybe that's all he knows how to install?

Weird

HeyBub[_3_] April 9th 12 08:22 PM

Ridge Vent or Box Vents?
 
wrote:
On Apr 8, 9:21 pm, "HeyBub" wrote:
DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.


On houses with narrow soffits, box vents are recommended.


Any truth to this?


Basic rule: You can't have too much soffit vents.

At a minimum, you should have one sq ft of soffit vent for each 150
sq ft of floor space. This is one sq ft of unobstructed venting.
Some screening material consumes as much as 2/3rds of the space.
Refigure accordingly.

If you have a 1500 sq ft house, you need 100 sq ft of soffits,
minimum. Assuming the screening material is hardware cloth or
similar that consumes less than 20% of the opening, you should plan
on 120 sq ft of soffit venting. Further, assuming small, six inch
soffits on a 50 x 30' house, you have 160 feet of perimeter. That
means only 80 sq ft, maximum, for available soffit vents.

Obviously this is woefully insufficient for the appropriate amount of
passive ventilation.


There is an error in your math. Assuming you need one sq ft of
venting per 100 sq ft of floor space, then a 1500
sq ft house needs 15 sq ft of venting, not 150. You're
off by a factor of 10. Following through with the
math, you'd then want 12 sq ft actual. If you did 2"
wide vents, you get .16 sq ft per linear foot. Which
in turn means those 2" wide vents down just the
long sides of the house would give you 16 sq ft total,
meeting the min reqt.

Also, technically, it's not floor space that
counts, but the attic area that is being vented. Some
houses don't have just one open continous attic area.



Yep, you're right. My bad.

I appreciate the correction and congratulate you for preventing someone from
making a grievous error based on my calculations.

Still, my answer was closer to being right than someone who announces
"purple" as the solution.



Bob F April 10th 12 12:51 AM

Ridge Vent or Box Vents?
 
gonjah wrote:
On 4/8/2012 4:42 PM, DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


I'd ask why?

Seems to make no sense to me.

Sounds like he's saying you need larger intake vents regardless and he
likes box vents. Maybe that's all he knows how to install?


Box vents are way easier to install neatly than soffit vents.



gonjah April 10th 12 01:09 AM

Ridge Vent or Box Vents?
 
On 4/9/2012 6:51 PM, Bob F wrote:
gonjah wrote:
On 4/8/2012 4:42 PM, DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?

I'd ask why?

Seems to make no sense to me.

Sounds like he's saying you need larger intake vents regardless and he
likes box vents. Maybe that's all he knows how to install?

Box vents are way easier to install neatly than soffit vents.



So you're saying ignore the problem with the fact there isn't enough
total attic airflow? Sorry, I'm a bit new to pitched roofs.


DerbyDad03[_2_] April 10th 12 01:09 AM

Ridge Vent or Box Vents?
 
On 04/09/12 11:24 AM, Home Guy wrote:
Bob F wrote:

In the summer, if I had a choice between:

a) pulling 1000 cfm of air out of my attic using powered vents -
with 950 cfm coming from the soffits (and/or gable-end vents) and
50 cfm coming from ceiling leaks - or

b) having NO powered vents (only passive vents) and therefore
only getting 200 cfm of passive air movement out of the attic
(and 0 cfm from ceiling air leaks) -

It's a no -brainer which one is better for the house and the roof.


As long as you don't care what it costs to run the A/C. Trying to
cool an extra 50 cfm of exterior air continuously is going to
COST.


That cost might be more than offset by the heat load I'm taking away
from the interior ceiling area by ventilating the attic with 950 cfm of
outside air vs 200 cfm of passive air.

Numbers like 1000, 200 and 50 (cfm) are all just hypothetical, but I
still assert that interior air leaks into the attic are trivial (for any
home built in the last 50 years) - not counting any bad practices like
venting bathroom or kitchen fans into the attic.



House was built 56 years ago.

There's a pull-down attic staircase in the hallway.

DerbyDad03[_2_] April 10th 12 01:20 AM

Ridge Vent or Box Vents?
 
On 04/09/12 7:51 PM, Bob F wrote:
gonjah wrote:
On 4/8/2012 4:42 PM, DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


I'd ask why?

Seems to make no sense to me.

Sounds like he's saying you need larger intake vents regardless and he
likes box vents. Maybe that's all he knows how to install?


Box vents are way easier to install neatly than soffit vents.



The discussion isn't about box vents vs. soffit vents, it's about box
vents vs. a ridge vent.

There are currently no soffit vents now, just 3 gable end vents and 4
box vents (there's 2 sections of roof)

The estimate includes:

SOFFIT VENTS
Install ten (10), 6" x 16" size, in client selected color screened
soffit vents in overhangs.

ROOF VENTS
Install six (6) Lomanco Model 750 aluminum slant back box vents in roof
just below ridge line of roof in color selected by client.

(That would be 4 on the big section of roof and 2 on the smaller section)



DerbyDad03[_2_] April 10th 12 01:23 AM

Ridge Vent or Box Vents?
 
On 04/09/12 11:51 AM, gonjah wrote:
On 4/8/2012 4:42 PM, DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


I'd ask why?

Seems to make no sense to me.

Sounds like he's saying you need larger intake vents regardless and he
likes box vents. Maybe that's all he knows how to install?

Weird


It's a given that I need more intake.

There are currently no soffit vents now, just 3 gable end vents and 4
box vents (there's 2 sections of roof)

The estimate includes:

SOFFIT VENTS
Install ten (10), 6" x 16" size, in client selected color screened
soffit vents in overhangs.

ROOF VENTS
Install six (6) Lomanco Model 750 aluminum slant back box vents in roof
just below ridge line of roof in color selected by client.

(That would be 4 on the big section of roof and 2 on the smaller section)


Home Guy April 10th 12 02:02 AM

Ridge Vent or Box Vents?
 
DerbyDad03 wrote:


The discussion isn't about box vents vs. soffit vents, it's about box
vents vs. a ridge vent.


If you ask me, box vents are more fussy to install (and shingle around)
vs ridge vents, and they don't give you as much ventilation area as you
think. In your case, the box vents you're being quoted for actually
have a circular opening of about 8" diameter (on the bottom) and the
perforated area on the outer side may not add up to a whole lot of
actual ventilation area.

http://www.lomanco.com/index.php/ven...tic-roof-vents

Your vents have a specified ventilation opening or area of 50 square
inches. Every running foot of ridge venting will give you between about
24 quare inches ventilation (about an inch worth on two sides) and be
faster to install - but I don't know about the cost of ridge venting.

Your aluminum Lorenco vents come in a box of 6, and can be had for as
little as $20 for a box if this ebay vendor is any example:

http://www.ebay.com/itm/140627349384

Bottom line is that a ridge vent is very easy to install, and gives more
ventilation capability and more even ventilation than box vents.

However, be aware of this:

Summer is notorious for having hot days WITH LITTLE OR NO WIND.

Any passive vent system really needs a good wind to help ventilate your
roof. So you might (or should) consider not having too much passive
venting AND have some power vent fans.

Going with the lightest-colored shingles you can manage is also better
than dark shingles.

Home Guy April 10th 12 02:04 AM

Ridge Vent or Box Vents?
 
DerbyDad03 wrote:

The discussion isn't about box vents vs. soffit vents, it's about
box vents vs. a ridge vent.


If you ask me, box vents are more fussy to install (and shingle around)
vs ridge vents, and they don't give you as much ventilation area as you
think. In your case, the box vents you're being quoted for actually
have a circular opening of about 8" diameter (on the bottom) and the
perforated area on the outer side may not add up to a whole lot of
actual ventilation area.

http://www.lomanco.com/index.php/ven...tic-roof-vents

Your vents have a specified ventilation opening or area of 50 square
inches. Every running foot of ridge venting will give you between about
24 quare inches ventilation (about an inch worth on two sides) and be
faster to install - but I don't know about the cost of ridge venting.

Your aluminum Lorenco vents come in a box of 6, and can be had for as
little as $20 for a box if this ebay vendor is any example:

http://www.ebay .com/itm/140627349384

Bottom line is that a ridge vent is very easy to install, and gives more
ventilation capability and more even ventilation than box vents.

However, be aware of this:

Summer is notorious for having hot days WITH LITTLE OR NO WIND.

Any passive vent system really needs a good wind to help ventilate your
roof. So you might (or should) consider not having too much passive
venting AND have some power vent fans.

Going with the lightest-colored shingles you can manage is also better
than dark shingles.

gonjah April 10th 12 03:01 AM

Ridge Vent or Box Vents?
 
On 4/9/2012 7:23 PM, DerbyDad03 wrote:
On 04/09/12 11:51 AM, gonjah wrote:
On 4/8/2012 4:42 PM, DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


I'd ask why?

Seems to make no sense to me.

Sounds like he's saying you need larger intake vents regardless and he
likes box vents. Maybe that's all he knows how to install?

Weird


It's a given that I need more intake.

There are currently no soffit vents now, just 3 gable end vents and 4
box vents (there's 2 sections of roof)

The estimate includes:

SOFFIT VENTS
Install ten (10), 6" x 16" size, in client selected color screened
soffit vents in overhangs.

ROOF VENTS
Install six (6) Lomanco Model 750 aluminum slant back box vents in
roof just below ridge line of roof in color selected by client.

(That would be 4 on the big section of roof and 2 on the smaller section)


I'm wondering why he prefers boxes? I had my ridge vent installed when
they tore off the old shingles. Maybe it's easier then?

gonjah April 10th 12 03:09 AM

Ridge Vent or Box Vents?
 
On 4/9/2012 8:02 PM, Home Guy wrote:
DerbyDad03 wrote:


The discussion isn't about box vents vs. soffit vents, it's about box
vents vs. a ridge vent.

If you ask me, box vents are more fussy to install (and shingle around)
vs ridge vents, and they don't give you as much ventilation area as you
think. In your case, the box vents you're being quoted for actually
have a circular opening of about 8" diameter (on the bottom) and the
perforated area on the outer side may not add up to a whole lot of
actual ventilation area.

http://www.lomanco.com/index.php/ven...tic-roof-vents

Your vents have a specified ventilation opening or area of 50 square
inches. Every running foot of ridge venting will give you between about
24 quare inches ventilation (about an inch worth on two sides) and be
faster to install - but I don't know about the cost of ridge venting.

Your aluminum Lorenco vents come in a box of 6, and can be had for as
little as $20 for a box if this ebay vendor is any example:

http://www.ebay.com/itm/140627349384

Bottom line is that a ridge vent is very easy to install, and gives more
ventilation capability and more even ventilation than box vents.

However, be aware of this:

Summer is notorious for having hot days WITH LITTLE OR NO WIND.

Any passive vent system really needs a good wind to help ventilate your
roof. So you might (or should) consider not having too much passive
venting AND have some power vent fans.

Going with the lightest-colored shingles you can manage is also better
than dark shingles.


Should I still be using my attic fan during still periods? I thought
they were not cost effective. I have a 1500 sf house. How many sf should
I have in

soffit vents?

Jim


Pat[_5_] April 10th 12 04:04 AM

Ridge Vent or Box Vents?
 

The estimate includes:

SOFFIT VENTS
Install ten (10), 6" x 16" size, in client selected color screened soffit
vents in overhangs.


Nowadays 16" or more attic insulation is required by code. It may be
difficult to prevent the insulation from blocking the air flow from soffit
vents. If you install baffles to hold the insulation back you may be
putting a flow of cold air next to your ceiling. A cold spot on your
ceiling allows mold to grow. Might be better to install roof vents just
above the insulation at the bottom of the roof and again at the top. When
you have continuous venting at the soffit and ridge the venting can be
reduced by 50%. Since you do not have continuous soffit venting a ridge
vent may be undersized by 50%.



Home Guy April 10th 12 04:29 AM

Ridge Vent or Box Vents?
 
gonjah wrote:

Should I still be using my attic fan during still periods?
I thought they were not cost effective.


I try to not have my attic temperature exceed 100 degrees F.

So I'll turn on my attic fan when-ever the temp hits 100, wind or no
wind.

I have a 1500 sf house. How many sf should I have in

soffit vents?


You should have a soffit vent hole between every rafter joist.

If you have aluminum soffit, there's no excuse for not having perforated
aluminum soffit along the entire length of the eves. If you have mostly
(or totally) solid aluminum soffit, take it all down and replace with
100% perforated soffit:

http://www.biytoday.com/Soffit2.jpg

Just cut a hole the size of your hand with a jig saw in the existing
plywood soffit every 16" before you install the perforated soffit.

And remember that anything you do to improve soffit ventilation is
wasted if you have attic insulation jammed into the eves blocking air
flow.

gonjah April 10th 12 04:45 AM

Ridge Vent or Box Vents?
 
On 4/9/2012 10:29 PM, Home Guy wrote:
gonjah wrote:

Should I still be using my attic fan during still periods?
I thought they were not cost effective.

I try to not have my attic temperature exceed 100 degrees F.

So I'll turn on my attic fan when-ever the temp hits 100, wind or no
wind.


I have one of those fans that blows out the vent under the gable. I
think that's the right term. Wouldn't it just pull right from the ridge
vent directly above it making it practically useless?

BTW: We had 42 days of +100 degrees last year. All time record.


I have a 1500 sf house. How many sf should I have in

soffit vent

You should have a soffit vent hole between every rafter joist.

If you have aluminum soffit, there's no excuse for not having perforated
aluminum soffit along the entire length of the eves. If you have mostly
(or totally) solid aluminum soffit, take it all down and replace with
100% perforated soffit:

http://www.biytoday.com/Soffit2.jpg

Just cut a hole the size of your hand with a jig saw in the existing
plywood soffit every 16" before you install the perforated soffit.

And remember that anything you do to improve soffit ventilation is
wasted if you have attic insulation jammed into the eves blocking air
flow.e to


Not good. It's ply-board and the vents (about 6" x 12") are a good 5'
apart. Replacing some of the ply-board will be difficult.

gonjah April 10th 12 04:47 AM

Ridge Vent or Box Vents?
 
On 4/9/2012 7:23 PM, DerbyDad03 wrote:
On 04/09/12 11:51 AM, gonjah wrote:
On 4/8/2012 4:42 PM, DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?


I'd ask why?

Seems to make no sense to me.

Sounds like he's saying you need larger intake vents regardless and he
likes box vents. Maybe that's all he knows how to install?

Weird


It's a given that I need more intake.

There are currently no soffit vents now, just 3 gable end vents and 4
box vents (there's 2 sections of roof)

The estimate includes:

SOFFIT VENTS
Install ten (10), 6" x 16" size, in client selected color screened
soffit vents in overhangs.

ROOF VENTS
Install six (6) Lomanco Model 750 aluminum slant back box vents in
roof just below ridge line of roof in color selected by client.

(That would be 4 on the big section of roof and 2 on the smaller section)


Pat: How much are you being charged per vent? What is the soffit made of?

gonjah April 10th 12 04:52 AM

Ridge Vent or Box Vents?
 
On 4/9/2012 10:47 PM, gonjah wrote:
On 4/9/2012 7:23 PM, DerbyDad03 wrote:
On 04/09/12 11:51 AM, gonjah wrote:
On 4/8/2012 4:42 PM, DerbyDad03 wrote:
I have heard that ridge vents only work well if there are wide
soffits, like 12" or more.

On houses with narrow soffits, box vents are recommended.

Any truth to this?

I'd ask why?

Seems to make no sense to me.

Sounds like he's saying you need larger intake vents regardless and he
likes box vents. Maybe that's all he knows how to install?

Weird


It's a given that I need more intake.

There are currently no soffit vents now, just 3 gable end vents and 4
box vents (there's 2 sections of roof)

The estimate includes:

SOFFIT VENTS
Install ten (10), 6" x 16" size, in client selected color screened
soffit vents in overhangs.

ROOF VENTS
Install six (6) Lomanco Model 750 aluminum slant back box vents in
roof just below ridge line of roof in color selected by client.

(That would be 4 on the big section of roof and 2 on the smaller
section)


Pat: How much are you being charged per vent? What is the soffit made of?


Oops! Make that DerbyDad.

HeyBub[_3_] April 10th 12 01:13 PM

Ridge Vent or Box Vents?
 
gonjah wrote:

Should I still be using my attic fan during still periods? I thought
they were not cost effective. I have a 1500 sf house. How many sf
should I have in

soffit vents?


According to my corrected calculations, you need one sq ft of soffit vents
per 150 sq ft of floor space, or 10 sq ft.

This is ten UNRESTRICTED sq ft. Some of the screening on soffit vents take
up a considerable amount of space, so figure on 20-50% more actual venting.
Looking at the commercially available vent covers, I decided to make my own.

Here's what I did.

1. I got a roll of gutter screening. Plastic, 6"wide. Actually, several
rolls.
2. Using 1/2 x 2 furring strips, I constructed a number of 4' long frames to
hold the screening. A pneumatic staple gun is a great labor-saver here.
3. After trying all manner of saws, I ended up using a pruning chain saw(!)
to cut the 5" by 4' sections out of my 1/4" plywood soffits.
4. I installed the aforementioned frames with sheet metal screws. The soffit
screens were painted before installation*.
5. I installed a LOT of these home-made soffit screens. The perimeter of my
house is about 200'. At least 100' of that contains soffit vents. That works
out to 2.5 times the recommended minimum.

Of course I live in a hot, humid, town (Houston), so my needs may greatly
exceed yours.

--------
* Before painting my house the last time, I investigated the available
colors of spray paint available at the box store. I found one that was
acceptable ("Camouflage") and bought several cans. I then painted the tip of
a wood paint stir-stick with the spray paint and asked the paint department
to match the color with several gallons of exterior paint. Now, when a bit
of the house needs a touch-up, I spray it.

Anyway, the spray cans came in handy when painting the soffit screens...



Home Guy April 10th 12 01:45 PM

Ridge Vent or Box Vents?
 
gonjah wrote:

So I'll turn on my attic fan when-ever the (attic) temp hits 100,
wind or no wind.


I have one of those fans that blows out the vent under the gable.
I think that's the right term.


You mean you have a fan like this:

http://woodheatstoves.com/images/solarstar_gable.jpg

Wouldn't it just pull right from the ridge vent directly
above it making it practically useless?


Yes - that's the problem someone could have if they have a lot of
passive roof venting near the fan. I don't have ridge vents on my house
(I don't have enough of a ridge line to make it worth while).

BTW: We had 42 days of +100 degrees last year. All time record.


Yea, that's a killer for shingles.

Not good. It's ply-board and the vents (about 6" x 12") are a
good 5' apart. Replacing some of the ply-board will be difficult.


So you don't already have aluminum-clad soffits then... ?

gonjah April 10th 12 01:54 PM

Ridge Vent or Box Vents?
 
On 4/10/2012 7:45 AM, Home Guy wrote:
gonjah wrote:

So I'll turn on my attic fan when-ever the (attic) temp hits 100,
wind or no wind.

I have one of those fans that blows out the vent under the gable.
I think that's the right term.

You mean you have a fan like this:

http://woodheatstoves.com/images/solarstar_gable.jpg


Yup. It's unplugged and will probably stay that way.

Wouldn't it just pull right from the ridge vent directly
above it making it practically useless?

Yes - that's the problem someone could have if they have a lot of
passive roof venting near the fan. I don't have ridge vents on my house
(I don't have enough of a ridge line to make it worth while).

BTW: We had 42 days of +100 degrees last year. All time record.

Yea, that's a killer for shingles.

Not good. It's ply-board and the vents (about 6" x 12") are a
good 5' apart. Replacing some of the ply-board will be difficult.

So you don't already have aluminum-clad soffits then... ?


Looks like this w/o all the dirt

http://www.radiantbarrierguru.com/wp...offit-vent.jpg

Home Guy April 10th 12 01:57 PM

Ridge Vent or Box Vents?
 
HeyBub wrote:

I have a 1500 sf house. How many sf should I have in soffit vents?


According to my corrected calculations, (...)


I think it's a complete waste of time to mess around with calculations
for roof venting that is probably based on ad-hoc forumulas to begin
with.

Rule #1 for roofs/attics is that you can't have too much ventilation.

Beyond that, assuming that you have eves in the first place, any
logically-designed roof and eve system will have an eve vent-hole
located between every roof joist (assuming the eves were originally
finished with plywood on their underside instead of aluminum).

Now it's probably the case for new construction (new = anything younger
than 20 years) that the eves were not finished with solid plywood but
instead were simply clad in aluminum - and if so it should have been
100% perforated aluminum.


All times are GMT +1. The time now is 02:38 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter