I've been in my home almost 10 years and all of a sudden, a single
circuit in my home started to flicker and intermittently power on and
off (the breaker never tripped). I've done electrical work in the past
when I finished my basement. The first thing I thought of was to
replace the breaker. It's a Cutler Hammer twin (slimline) 15A breaker.

After replacing it, the problem still occurred (so it was unlikely it
was the breaker). After some diagnosising, I noticed that there was
some arching ocurring in one of the terminals on the neutral buss bar.
I tapped on the panel, and a small spark shot from the terminal. I
turned off the circuit in question, and the arching and spark ceased.
I then knew that the arching neutral belonged to the circuit in
question.

I found it odd that there are one or two ground wires on the neutral
buss bar. However, the neutral buss bar is right on top of the ground
buss bar. Don't they go to the same place anyway? Is this odd or OK? I
know I've seen some panels where the ground buss is totally separated
from the neutral buss.

This neutral wire is sharing the same screw terminal on the buss bar
with a ground wire from another circuit. I shut off the main breaker
and screwed down the terminal firmly which fixed the problem. However,
5 days later, it started happening again. No sparks fly when I tap on
the panel, but there is slight arching in that same termAinal.

Just eyeballing it, it looks like my neutral is a 14 gauge whilst the
ground in the same terminal might be a 12 gauge which would explain
why the neutral is not secured enough by the screw terminal. I am
going to to shut off the main breaker do some housekeeping on the
terminals making sure the same gauge wire is shared by neutrals in the
same terminal.

1. Does it look like I've diagnosed the problem and I'm taking the
correct measures to fix it?

2. Why would this happen all of sudden after 10 years of living in the
home? The terminal screw didn't seem all that loose when I tightened
it the first time. I barely got 1/16 to 1/8 of a turn on it.

3. Is it OK for neutrals and grounds to share the same terminal on the
neutral buss bar? Of different or same circuits?

4. Any other comments to add on what I've described?

Thanks,

Jason

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Flickering Lights and Buss Arching

In article .com, daokfella wrote:
I've been in my home almost 10 years and all of a sudden, a single
circuit in my home started to flicker and intermittently power on and
off (the breaker never tripped). I've done electrical work in the past
when I finished my basement. The first thing I thought of was to
replace the breaker. It's a Cutler Hammer twin (slimline) 15A breaker.

After replacing it, the problem still occurred (so it was unlikely it
was the breaker). After some diagnosising, I noticed that there was
some arching ocurring in one of the terminals on the neutral buss bar.
I tapped on the panel, and a small spark shot from the terminal. I
turned off the circuit in question, and the arching and spark ceased.
I then knew that the arching neutral belonged to the circuit in
question.


Sounds like that terminal is a bit loose. Did you tighten it?

And is this copper wire, or aluminum?

I found it odd that there are one or two ground wires on the neutral
buss bar. However, the neutral buss bar is right on top of the ground
buss bar. Don't they go to the same place anyway? Is this odd or OK? I
know I've seen some panels where the ground buss is totally separated
from the neutral buss.


It's OK, as long as this is your main panel. Neutral and ground are required
to be connected at the service entrance (main) panel, and required to *not* be
connected anywhere else.

This neutral wire is sharing the same screw terminal on the buss bar
with a ground wire from another circuit.


That is *not* OK unless the terminals are specifically listed for use with
more than one wire. If they are, it will say so on the label inside the panel
access door.

I shut off the main breaker
and screwed down the terminal firmly which fixed the problem. However,
5 days later, it started happening again. No sparks fly when I tap on
the panel, but there is slight arching in that same termAinal.

Just eyeballing it, it looks like my neutral is a 14 gauge whilst the
ground in the same terminal might be a 12 gauge which would explain
why the neutral is not secured enough by the screw terminal. I am
going to to shut off the main breaker do some housekeeping on the
terminals making sure the same gauge wire is shared by neutrals in the
same terminal.


Better still to use only one wire per terminal.

1. Does it look like I've diagnosed the problem and I'm taking the
correct measures to fix it?


Diagnosed the problem, yes. Correct measures to fix it, probably not. The best
fix is one wire per terminal (unless the terminals are specifically listed for
two wires).

2. Why would this happen all of sudden after 10 years of living in the
home? The terminal screw didn't seem all that loose when I tightened
it the first time. I barely got 1/16 to 1/8 of a turn on it.


Copper or aluminum wire? This is VERY important.

3. Is it OK for neutrals and grounds to share the same terminal on the
neutral buss bar? Of different or same circuits?


As long as we're talking about a main panel, not a subpanel, and the terminals
are listed for use with two or more wires, that's fine. Since the neutral and
ground are electrically continuous in the main panel, there's no problem
electrically. Mechanically, you may have a problem attaching multiple wires
securely.

4. Any other comments to add on what I've described?


If this is aluminum wire, you have to be *very* careful not to overtighten the
connections.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default Flickering Lights and Buss Arching

Thanks Doug,

This is copper wiring. I do notice on the buss bar that there are two
sizes of screw terminals. The ones containing two wires are of the
larger size. However, the point is taken. When I do my "housekeeping"
on the panel, I will try to keep it one wire per terminal. It does
look like, however, that there may not be enough terminals for each
circuit to be in it's own, but I'll get a closer look. The last time I
worked closely with the panel is when I installed a 50A breaker and
wired in a sub-panel for my finished basement.

It definitely seems like a poor connection on the buss since it worked
fine for a week after tightening it. However, this morning it was back
to flickering and arching.

Thanks for your help.

  #4   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Flickering Lights and Buss Arching

daokfella wrote:
I've been in my home almost 10 years and all of a sudden, a single
circuit in my home started to flicker and intermittently power on and
off (the breaker never tripped). I've done electrical work in the past
when I finished my basement. The first thing I thought of was to
replace the breaker. It's a Cutler Hammer twin (slimline) 15A breaker.

After replacing it, the problem still occurred (so it was unlikely it
was the breaker). After some diagnosising, I noticed that there was
some arching ocurring in one of the terminals on the neutral buss bar.
I tapped on the panel, and a small spark shot from the terminal. I
turned off the circuit in question, and the arching and spark ceased.
I then knew that the arching neutral belonged to the circuit in
question.

I found it odd that there are one or two ground wires on the neutral
buss bar. However, the neutral buss bar is right on top of the ground
buss bar. Don't they go to the same place anyway? Is this odd or OK? I
know I've seen some panels where the ground buss is totally separated
from the neutral buss.

This neutral wire is sharing the same screw terminal on the buss bar
with a ground wire from another circuit. I shut off the main breaker
and screwed down the terminal firmly which fixed the problem. However,
5 days later, it started happening again. No sparks fly when I tap on
the panel, but there is slight arching in that same termAinal.

Just eyeballing it, it looks like my neutral is a 14 gauge whilst the
ground in the same terminal might be a 12 gauge which would explain
why the neutral is not secured enough by the screw terminal. I am
going to to shut off the main breaker do some housekeeping on the
terminals making sure the same gauge wire is shared by neutrals in the
same terminal.

1. Does it look like I've diagnosed the problem and I'm taking the
correct measures to fix it?

2. Why would this happen all of sudden after 10 years of living in the
home? The terminal screw didn't seem all that loose when I tightened
it the first time. I barely got 1/16 to 1/8 of a turn on it.

3. Is it OK for neutrals and grounds to share the same terminal on the
neutral buss bar? Of different or same circuits?

4. Any other comments to add on what I've described?


What Doug said plus...

2. Time is the key along w/ load cycling and relaxation/compression of
the conductors. Things gradually tend to loosen some over time.
Particularly, if a small amount of corrosion begins, that acts as a
small heater and then it is a progressive thing w/ a positive
feedback--more heat leads to more thermal expansion/contraction and
corrosion which causes more loosening and so on. Very slow initially,
but eventually troubles become apparent.

4. As Doug says, depends a lot on whether this is copper or aluminum
wiring.

Either way, my recommendation would be to also turn power off and take
the affected circuit(s) neutrals free from the bar and check carefully
for signs of oxidation/corrosion on both the wire end(s) and the
connections and the screw. Shine 'em up a little can't hurt.

If it's Al, connections need to be made w/ anti-oxidant lube--I'm
assuming probably aren't or would have been mentioned, but if are,
that's critical as Doug says.

I would also do a routine check for tightness of all connections in the
box at the same time -- you might find a couple of others that aren't as
tight as they might be.

And, of course, examine all wire ends for any signs of excessive heat
just as a precaution since you're in there anyway...

--
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,586
Default Flickering Lights and Buss Arching

daokfella wrote:
I've been in my home almost 10 years and all of a sudden, a single
circuit in my home started to flicker and intermittently power on and
off (the breaker never tripped). I've done electrical work in the past
when I finished my basement. The first thing I thought of was to
replace the breaker. It's a Cutler Hammer twin (slimline) 15A breaker.

After replacing it, the problem still occurred (so it was unlikely it
was the breaker). After some diagnosising, I noticed that there was
some arching ocurring in one of the terminals on the neutral buss bar.
I tapped on the panel, and a small spark shot from the terminal. I
turned off the circuit in question, and the arching and spark ceased.
I then knew that the arching neutral belonged to the circuit in
question.

I found it odd that there are one or two ground wires on the neutral
buss bar. However, the neutral buss bar is right on top of the ground
buss bar. Don't they go to the same place anyway? Is this odd or OK? I
know I've seen some panels where the ground buss is totally separated
from the neutral buss.

This neutral wire is sharing the same screw terminal on the buss bar
with a ground wire from another circuit. I shut off the main breaker
and screwed down the terminal firmly which fixed the problem. However,
5 days later, it started happening again. No sparks fly when I tap on
the panel, but there is slight arching in that same termAinal.

Just eyeballing it, it looks like my neutral is a 14 gauge whilst the
ground in the same terminal might be a 12 gauge which would explain
why the neutral is not secured enough by the screw terminal. I am
going to to shut off the main breaker do some housekeeping on the
terminals making sure the same gauge wire is shared by neutrals in the
same terminal.

1. Does it look like I've diagnosed the problem and I'm taking the
correct measures to fix it?

2. Why would this happen all of sudden after 10 years of living in the
home? The terminal screw didn't seem all that loose when I tightened
it the first time. I barely got 1/16 to 1/8 of a turn on it.

3. Is it OK for neutrals and grounds to share the same terminal on the
neutral buss bar? Of different or same circuits?

4. Any other comments to add on what I've described?

Thanks,

Jason

Hmmm,
First thing you'd do is checking for loose wire(hot, neutral, ground)
for that circuit. At the panel neutral and ground is same.


  #6   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Flickering Lights and Buss Arching

daokfella wrote:
Thanks Doug,

This is copper wiring. I do notice on the buss bar that there are two
sizes of screw terminals. The ones containing two wires are of the
larger size. However, the point is taken. When I do my "housekeeping"
on the panel, I will try to keep it one wire per terminal. It does
look like, however, that there may not be enough terminals for each
circuit to be in it's own, but I'll get a closer look. The last time I
worked closely with the panel is when I installed a 50A breaker and
wired in a sub-panel for my finished basement.

It definitely seems like a poor connection on the buss since it worked
fine for a week after tightening it. However, this morning it was back
to flickering and arching.


That may be indication of other connections on the circuit having
similar problems, too (although I guess you're seeing arcing at that
same neutral in the box so that would definitely be a problem).

See my other response on cleaning terminals and wires to remove
corrosion/oxidation. If the wires have been flattened by previous
connection might snip off to a new end if have a little slack. Moving
one or more to alternate location on the neutral bar is a possibility
although shouldn't be necessary unless the arcing has significantly
damaged that connection location. It is likely that if there has been
sufficient arcing you have seen it that it has caused some oxidation of
the surfaces. If so, may not be making good contact even if you did
retighten connections.

Whatever, don't give up until resolve it as (I'm sure you're well aware)
this ain't good...

--
  #7   Report Post  
Posted to alt.home.repair
EXT EXT is offline
external usenet poster
 
Posts: 1,661
Default Flickering Lights and Buss Arching

If you have to put two wires into the same terminal, either try to keep the
wire gauge the same so that the pressure is the same on both wires, or twist
the wires together before inserting into the terminal, which may be
difficult to insert the twisted wires without them untwisting, but you will
get a much better connection with equal pressure on both wires.


"daokfella" wrote in message
oups.com...
Thanks Doug,

This is copper wiring. I do notice on the buss bar that there are two
sizes of screw terminals. The ones containing two wires are of the
larger size. However, the point is taken. When I do my "housekeeping"
on the panel, I will try to keep it one wire per terminal. It does
look like, however, that there may not be enough terminals for each
circuit to be in it's own, but I'll get a closer look. The last time I
worked closely with the panel is when I installed a 50A breaker and
wired in a sub-panel for my finished basement.

It definitely seems like a poor connection on the buss since it worked
fine for a week after tightening it. However, this morning it was back
to flickering and arching.

Thanks for your help.



  #8   Report Post  
Posted to alt.home.repair
Joe Joe is offline
external usenet poster
 
Posts: 2,837
Default Flickering Lights and Buss Arching


daokfella wrote:

snip


4. Any other comments to add on what I've described?

Thanks,

Jason


One terminal, one wire is the rule. Go to an electrical distributor
outlet and buy an additional buss bar for your panel. There are often
pre-tapped mounting holes for the new bar in the enclosure. Mount and
bond it to the other busses, then segregate your neutral and ground
wires to single occupancy. Cost should be under $10 unless you're
driving a giant SUV to the store. HTH

Joe

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10,530
Default Flickering Lights and Buss Arching

Electricity should never arch. It should spark in a straight
line, not arched. If your electricity is arching, that's not
good. Curved like the golden arches (McDonalds) isn't normal.
Have you checked to see if the power company is selling you
straight electricity, or the new curved kind?

As to resolving the arcing, since you're already in the panel
box, how about shut off the breaker, and put the neutral into a
different hole, in the neutral bar? Then, screw it down snugly
and see if that helps.

--

Christopher A. Young
You can't shout down a troll.
You have to starve them.
..

"daokfella" wrote in message
oups.com...
: I've been in my home almost 10 years and all of a sudden, a
single
: circuit in my home started to flicker and intermittently power
on and
: off (the breaker never tripped). I've done electrical work in
the past
: when I finished my basement. The first thing I thought of was
to
: replace the breaker. It's a Cutler Hammer twin (slimline) 15A
breaker.
:
: After replacing it, the problem still occurred (so it was
unlikely it
: was the breaker). After some diagnosising, I noticed that there
was
: some arching ocurring in one of the terminals on the neutral
buss bar.
: I tapped on the panel, and a small spark shot from the
terminal. I
: turned off the circuit in question, and the arching and spark
ceased.
: I then knew that the arching neutral belonged to the circuit in
: question.
:
: I found it odd that there are one or two ground wires on the
neutral
: buss bar. However, the neutral buss bar is right on top of the
ground
: buss bar. Don't they go to the same place anyway? Is this odd
or OK? I
: know I've seen some panels where the ground buss is totally
separated
: from the neutral buss.
:
: This neutral wire is sharing the same screw terminal on the
buss bar
: with a ground wire from another circuit. I shut off the main
breaker
: and screwed down the terminal firmly which fixed the problem.
However,
: 5 days later, it started happening again. No sparks fly when I
tap on
: the panel, but there is slight arching in that same termAinal.
:
: Just eyeballing it, it looks like my neutral is a 14 gauge
whilst the
: ground in the same terminal might be a 12 gauge which would
explain
: why the neutral is not secured enough by the screw terminal. I
am
: going to to shut off the main breaker do some housekeeping on
the
: terminals making sure the same gauge wire is shared by neutrals
in the
: same terminal.
:
: 1. Does it look like I've diagnosed the problem and I'm taking
the
: correct measures to fix it?
:
: 2. Why would this happen all of sudden after 10 years of living
in the
: home? The terminal screw didn't seem all that loose when I
tightened
: it the first time. I barely got 1/16 to 1/8 of a turn on it.
:
: 3. Is it OK for neutrals and grounds to share the same terminal
on the
: neutral buss bar? Of different or same circuits?
:
: 4. Any other comments to add on what I've described?
:
: Thanks,
:
: Jason
:


  #10   Report Post  
Posted to alt.home.repair
M Q M Q is offline
external usenet poster
 
Posts: 257
Default Flickering Lights and Buss Arching

Stormin Mormon wrote:

Electricity should never arch. It should spark in a straight
line, not arched.

....

Oh, yeah?
Check out:
http://www.fugly.com/videos/1342/Lugo_SWR.html
or

http://bumracing.com/v-web/gallery/v...02&id=Lugo_SWR



  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default Flickering Lights and Buss Arching

Doug Miller wrote:


This neutral wire is sharing the same screw terminal on the buss bar
with a ground wire from another circuit.


That is *not* OK unless the terminals are specifically listed for use with
more than one wire. If they are, it will say so on the label inside the panel
access door.


Neutrals must be 1 per terminal - 408.41.
[From an RBM post]

--
bud--
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,040
Default Flickering Lights and Buss Arching

In article Ylbhi.23$q12.10@trnddc08,
M Q wrote:

Stormin Mormon wrote:

Electricity should never arch. It should spark in a straight
line, not arched.

...

Oh, yeah?
Check out:
http://www.fugly.com/videos/1342/Lugo_SWR.html
or

http://bumracing.com/v-web/gallery/v...album02&id=Lug
o_SWR


Holy Crap! I hope *that* isn't going on inside the OP's breaker box.
  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Flickering Lights and Buss Arching

In article , Bud-- wrote:
Doug Miller wrote:

This neutral wire is sharing the same screw terminal on the buss bar
with a ground wire from another circuit.


That is *not* OK unless the terminals are specifically listed for use with
more than one wire. If they are, it will say so on the label inside the panel
access door.

Neutrals must be 1 per terminal - 408.41.
[From an RBM post]

Didn't know that. Thanks.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 49
Default Flickering Lights and Buss Arching

Smitty Two wrote:
In article Ylbhi.23$q12.10@trnddc08,
M Q wrote:

Stormin Mormon wrote:

Electricity should never arch. It should spark in a straight
line, not arched.

...

Oh, yeah?
Check out:
http://www.fugly.com/videos/1342/Lugo_SWR.html
or

http://bumracing.com/v-web/gallery/v...album02&id=Lug
o_SWR


Holy Crap! I hope *that* isn't going on inside the OP's breaker box.


Ah, there's a nice Jabob's Ladder effect going there...

Yours aye,
W. Underhill

--
"Take sides! Always take sides! You may sometimes be wrong - but the man
who refuses to take sides must *always* be wrong! Heaven save us from
poltroons who fear to make a choice!" R.A. Heinlein, "Double Star"
--
Main homepage: http://members.shaw.ca/fog.locker/
SCA homepage: http://members.shaw.ca/uilliam/
LiveJournal: http://www.livejournal.com/users/jackytar/
  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default Flickering Lights and Buss Arching

Doug Miller wrote:
In article , Bud-- wrote:

Doug Miller wrote:

This neutral wire is sharing the same screw terminal on the buss bar
with a ground wire from another circuit.

That is *not* OK unless the terminals are specifically listed for use with
more than one wire. If they are, it will say so on the label inside the panel
access door.


Neutrals must be 1 per terminal - 408.41.
[From an RBM post]


Didn't know that. Thanks.


Grounds, however, may be more than one (three I think?)

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel


  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default Flickering Lights and Buss Arching

Nate Nagel wrote:
Doug Miller wrote:
In article , Bud--
wrote:

Doug Miller wrote:

This neutral wire is sharing the same screw terminal on the buss bar
with a ground wire from another circuit.

That is *not* OK unless the terminals are specifically listed for
use with more than one wire. If they are, it will say so on the
label inside the panel access door.


Neutrals must be 1 per terminal - 408.41.
[From an RBM post]


Didn't know that. Thanks.


I didn't know until I read RBM's post. Amazing what is lurking in the
NEC. In any case, as you said, the panel label will indicate what is
allowed.


Grounds, however, may be more than one (three I think?)


RBM also wrote:
"UL Std. 67 (Panelboard Standard) permits up to three 10 AWG equipment
grounding conductors to terminate on a single terminal, if the terminal
is marked for this purpose."

--
bud--
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Lights flickering John UK diy 6 January 1st 07 07:20 AM
Flickering Lights [email protected] Home Repair 12 April 21st 06 11:48 PM
Flickering lights barry martin Home Repair 1 December 16th 04 02:15 AM
Flickering lights MPost Home Repair 5 December 15th 04 03:00 AM
Flickering lights Peter Smithson UK diy 1 November 28th 04 08:49 PM


All times are GMT +1. The time now is 12:02 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"