Can anyone tell me the maximum line-of-site distance that a breaker box
sited outside an A/C compressor can be from the A/C unit? I want to put a
breaker box about 15' from the unit (line-of-site), but I'm not quite sure
it is to code (Virginia).

Thanks.

H


  #2   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Distance from outside breaker box to A/C Unit

Nec requires three foot in front and I believe it's 30 inches wide area
without obstruction.

"H" wrote in message
news:kxTci.161$%t6.67@trnddc02...
Can anyone tell me the maximum line-of-site distance that a breaker box
sited outside an A/C compressor can be from the A/C unit? I want to put a
breaker box about 15' from the unit (line-of-site), but I'm not quite sure
it is to code (Virginia).

Thanks.

H



  #3   Report Post  
Posted to alt.home.repair
H H is offline
external usenet poster
 
Posts: 39
Default Distance from outside breaker box to A/C Unit

Is that minimum 3'? Is there a maximum?


"RBM" rbm2(remove wrote in message
...
Nec requires three foot in front and I believe it's 30 inches wide area
without obstruction.

"H" wrote in message
news:kxTci.161$%t6.67@trnddc02...
Can anyone tell me the maximum line-of-site distance that a breaker box
sited outside an A/C compressor can be from the A/C unit? I want to put
a breaker box about 15' from the unit (line-of-site), but I'm not quite
sure it is to code (Virginia).

Thanks.

H





  #4   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Distance from outside breaker box to A/C Unit

Yes, you need a minimum of 3' X30" working space. No maximum



"H" wrote in message
news:G3Uci.281$lY5.113@trnddc07...
Is that minimum 3'? Is there a maximum?


"RBM" rbm2(remove wrote in message
...
Nec requires three foot in front and I believe it's 30 inches wide area
without obstruction.

"H" wrote in message
news:kxTci.161$%t6.67@trnddc02...
Can anyone tell me the maximum line-of-site distance that a breaker box
sited outside an A/C compressor can be from the A/C unit? I want to put
a breaker box about 15' from the unit (line-of-site), but I'm not quite
sure it is to code (Virginia).

Thanks.

H







  #5   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Distance from outside breaker box to A/C Unit

I think I'm misunderstanding your question. If you want to know the maximum
distance an A/C disconnect can be from the condenser, that's something else.
It must be "in sight from" which means in sight of and within 50 feet.



"H" wrote in message
news:kxTci.161$%t6.67@trnddc02...
Can anyone tell me the maximum line-of-site distance that a breaker box
sited outside an A/C compressor can be from the A/C unit? I want to put a
breaker box about 15' from the unit (line-of-site), but I'm not quite sure
it is to code (Virginia).

Thanks.

H





  #6   Report Post  
Posted to alt.home.repair
H H is offline
external usenet poster
 
Posts: 39
Default Distance from outside breaker box to A/C Unit

That's what I need....Thanks.


"RBM" rbm2(remove wrote in message
...
I think I'm misunderstanding your question. If you want to know the maximum
distance an A/C disconnect can be from the condenser, that's something
else. It must be "in sight from" which means in sight of and within 50
feet.



"H" wrote in message
news:kxTci.161$%t6.67@trnddc02...
Can anyone tell me the maximum line-of-site distance that a breaker box
sited outside an A/C compressor can be from the A/C unit? I want to put
a breaker box about 15' from the unit (line-of-site), but I'm not quite
sure it is to code (Virginia).

Thanks.

H





  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Distance from outside breaker box to A/C Unit

On Jun 16, 12:58?pm, "H" wrote:
That's what I need....Thanks.

"RBM" rbm2(remove wrote in message

...



I think I'm misunderstanding your question. If you want to know the maximum
distance an A/C disconnect can be from the condenser, that's something
else. It must be "in sight from" which means in sight of and within 50
feet.


"H" wrote in message
news:kxTci.161$%t6.67@trnddc02...
Can anyone tell me the maximum line-of-site distance that a breaker box
sited outside an A/C compressor can be from the A/C unit? I want to put
a breaker box about 15' from the unit (line-of-site), but I'm not quite
sure it is to code (Virginia).


Thanks.


H- Hide quoted text -


- Show quoted text -


why not locate it at the compressor?

  #8   Report Post  
Posted to alt.home.repair
H H is offline
external usenet poster
 
Posts: 39
Default Distance from outside breaker box to A/C Unit

The current box has about 12" in front of it. It was installed about 40
years ago before the code said that there needs to be 3' of cleared space in
front of it.

If I replaced the box near the compressor, there would be too many bends in
the wire to be to code. If I put it 15' away, there would be three bends
between the breaker box and the a/c, and 3 bends between the breaker box and
the electrical panel.

H

wrote in message
oups.com...
On Jun 16, 12:58?pm, "H" wrote:
That's what I need....Thanks.

"RBM" rbm2(remove wrote in message

...



I think I'm misunderstanding your question. If you want to know the
maximum
distance an A/C disconnect can be from the condenser, that's something
else. It must be "in sight from" which means in sight of and within 50
feet.


"H" wrote in message
news:kxTci.161$%t6.67@trnddc02...
Can anyone tell me the maximum line-of-site distance that a breaker
box
sited outside an A/C compressor can be from the A/C unit? I want to
put
a breaker box about 15' from the unit (line-of-site), but I'm not
quite
sure it is to code (Virginia).


Thanks.


H- Hide quoted text -


- Show quoted text -


why not locate it at the compressor?



  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 663
Default Distance from outside breaker box to A/C Unit

On Wed, 20 Jun 2007 22:55:19 GMT, "H" wrote:

The current box has about 12" in front of it. It was installed about 40
years ago before the code said that there needs to be 3' of cleared space in
front of it.

If I replaced the box near the compressor, there would be too many bends in
the wire to be to code. If I put it 15' away, there would be three bends
between the breaker box and the a/c, and 3 bends between the breaker box and
the electrical panel.

There is no maximum bends for cable. Conduit would limit the number
of bends, but this does not apply to romex.

If you do have conduit, you are allowed to put a box at the existing
location. The requirement is between pull points, not the breaker
box. This can be no more than 360 degrees.

Everything outside should be weatherproof.



  #10   Report Post  
Posted to alt.home.repair
H H is offline
external usenet poster
 
Posts: 39
Default Distance from outside breaker box to A/C Unit


"Terry" wrote in message
...
On Wed, 20 Jun 2007 22:55:19 GMT, "H" wrote:

The current box has about 12" in front of it. It was installed about 40
years ago before the code said that there needs to be 3' of cleared space
in
front of it.

If I replaced the box near the compressor, there would be too many bends
in
the wire to be to code. If I put it 15' away, there would be three bends
between the breaker box and the a/c, and 3 bends between the breaker box
and
the electrical panel.

There is no maximum bends for cable. Conduit would limit the number
of bends, but this does not apply to romex.

If you do have conduit, you are allowed to put a box at the existing
location. The requirement is between pull points, not the breaker
box. This can be no more than 360 degrees.

Everything outside should be weatherproof.

Terry,

Thanks for the clarification. Since this is outside, there will be conduit,
so the 360 degree rule will apply.




  #11   Report Post  
Posted to alt.home.repair
mm mm is offline
external usenet poster
 
Posts: 7,824
Default Distance from outside breaker box to A/C Unit

On Wed, 20 Jun 2007 23:35:04 GMT, "H" wrote:


There is no maximum bends for cable. Conduit would limit the number
of bends, but this does not apply to romex.

If you do have conduit, you are allowed to put a box at the existing
location. The requirement is between pull points, not the breaker
box. This can be no more than 360 degrees.

Everything outside should be weatherproof.

Terry,

Thanks for the clarification. Since this is outside, there will be conduit,


Lots of people use Romex designed for outside, outside. For ACs. No
need for conduit. In Virginia too, I'm sure.

so the 360 degree rule will apply.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric BBQ breaks GFI 20 Amp breaker yet works fine with non-GFI breaker. BoyntonStu Home Repair 10 May 26th 07 07:56 PM
Furnace Comes On When Circuit Breaker Turned On To Central Unit nowforsale Home Repair 6 September 13th 06 05:12 AM
A/C Unit Keeps Tripping Circuit Breaker - How to test breaker before calling repair man? C5Ya Home Repair 10 August 26th 05 08:34 PM
central air conditioner trips breaker/ need to replace outside unit domestic engineer Home Repair 16 August 24th 05 04:03 AM
Safe Distance Between Phone Wiring and Power Breaker Panel? [email protected] Home Repair 7 January 7th 05 08:40 PM


All times are GMT +1. The time now is 08:05 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"