Default Why must ground & neutral be seperate in subpanel?

"Doug Miller" wrote in message
et...
In article , "The Streets"
wrote:

So, what is the proper way to connect a 220v sub-panel that has a single
bus bar for neutral and ground to a main panel with the neutral bar bonded
to the ground bar?


There isn't one.

To make a Code-compliant connection, you must install a second bar so that
you
can separate the neutral and ground conductors for the various circuits to
separate busses. The neutral bus must be electrically insulated from the
ground bus and from the panel chassis, and the ground bus must *not* be
insulated from the chassis.

*Also* you must connect the subpanel to the main panel using *four*
conductors, e.g. black, red, white, and bare (or green). White goes from
the
neutral bus bar in the main panel to the neutral bus bar in the subpanel.
Bare
(or green) goes from the ground bus bar in the main panel to the ground
bus
bar in the subpanel. Black and red go from the two lugs on the circuit
breaker
in the main panel which feeds the sub, to the lugs on the main breaker in
the
subpanel.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


Thanks for your help and advice.
I've located a grounding bar kit from the panel manufacturer and
will install it along with (4) wires from the main panel (white,
greeen and two black) so that the neutral and ground are separate.


  #42   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 455
Default good book on this? Why must ground & neutral be seperate in subpanel?

In article ,
Charles Schuler wrote:

wrote in message
oups.com...
I installed a subpanel when I switched from an electric stove to gas. I
used the 40A 220V breaker that formerly served the stove to power the
sub panel. The cable is #4 with two conductors and a ground. I have 6-
15 amp breakers in the panel providing branch circuits for my kitchen
and other areas of my house. The grounds and neutrals all share the
common bus bar in the sub panel. Everything has worked fine for years
now. Can someone explain why I read that ground and neutral are to be
isolated in the sub panel? Please don't answer because of the NEC since
that does not explain why. What is the risk of my current situation?


The neutral (white) is a return ... it carries the same current as the hot
wire (black). The ground wire is a non current-carrying safety wire (often
bare copper). The purpose of the ground wire is to reduce voltages in the
case of lightning or an accident (wires falling across other wires outside
of your home and raising the voltage with respect to ground to a dangerous
level). The ground wire only conducts current in the case of a fault.
Ground fault circuit interrupters need the ground wire to detect such faults
and open the circuit when they occur.

People are often shocked and even electrocuted with voltages with respect to
ground ... one is standing on a wet basement floor ... one is touching a
faucet ... one is in the tub or shower. The voltage with respect to ground
is the big issue here (for safety reasons).

An ungrounded electrical system in your home would allow voltages to rise to
thousands of volts above ground and fry you if you happened to be grounded
(in a tub or standing on a wet concrete floor).



Are there one or more books that actually coverf
*this* kind of stuff, ie that's being discussed in
*this* thread?

Not some home-improvement book you might find at HD,
but something that really, tutorially, gets down to
the depth of *this* stuff, this "more complex" stuff
than you usually see covered in the home-improvement-style
electrical-books.

Something so that when you finish a subject, you really
understand it, not so that you can merely "do" some
home-job, but even would let you (correctly!, and usefully)
contribute to eg this current thread.

Ideas?

Thanks!

David


PS: eons ago I took some EE courses in college, but of course
that knowledge was pretty useless for this current subject.





Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
.2 volts between neutral and ground Dave Botsch Electronics Repair 11 August 19th 06 11:47 PM
Neutral/ground issue Tuyen Home Repair 17 August 8th 06 01:32 AM
Neutral v Ground? LurfysMa Home Repair 14 April 8th 06 07:21 PM
Wiring subpanel - seperate ground / neutral DG Home Repair 6 April 2nd 06 06:47 AM
Why Ground AND Neutral? TURTLE Home Repair 13 September 23rd 05 05:35 AM


All times are GMT +1. The time now is 11:24 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"