Range pops circuit breaker
After a new electric range was installed the circuit breaker started to
pop every now and then when everything was turned on (oven+all burners). This indicated to me that the range was drawing a load that was right at the upper limit of the 50 amp circuit breaker rating. Checked the data plate on the range which reads 240V. & 54.2 amps. So, when the range is at peak load it apparently can draw 4.2 amps over the breaker capacity. The wiring is Aluminum 6 guage (6 Al on the sheath),. Can I safely go to the next size breaker (60 amp) to accomodate the additional 4-5 amps??? |
#2
Posted to alt.home.repair
|
|||
|
|||
Range pops circuit breaker
Russ,
The wire inside your walls must be large enough to support a bigger breaker before you should think about putting in a bigger breaker. So look at your wiring or have an electrician look at your wiring. Dave M. |
#3
Posted to alt.home.repair
|
|||
|
|||
Range pops circuit breaker
"David Martel" wrote in message
k.net... Russ, The wire inside your walls must be large enough to support a bigger breaker before you should think about putting in a bigger breaker. So look at your wiring or have an electrician look at your wiring. Did you read the post? He did. He said it's 6AWG Al wire. -Tim |
#4
Posted to alt.home.repair
|
|||
|
|||
Range pops circuit breaker
In article . com, "Russ" wrote:
After a new electric range was installed the circuit breaker started to pop every now and then when everything was turned on (oven+all burners). This indicated to me that the range was drawing a load that was right at the upper limit of the 50 amp circuit breaker rating. Checked the data plate on the range which reads 240V. & 54.2 amps. So, when the range is at peak load it apparently can draw 4.2 amps over the breaker capacity. The wiring is Aluminum 6 guage (6 Al on the sheath),. Can I safely go to the next size breaker (60 amp) to accomodate the additional 4-5 amps??? Probably NOT, but it depends on the temperature rating of the insulation on the conductors; this should also be indicated on the cable sheath -- if it is not indicated, assume it's 60 degrees C. With a 90-degree rating, yes, you can go up to 60 amps. If the rating is 75 degrees, you're limited to the 50 amps you're already at. And if it's only 60 degrees, you shouldn't have even a 50 amp breaker -- it's limited to 40 amps by Code. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#5
Posted to alt.home.repair
|
|||
|
|||
Range pops circuit breaker
Doug Miller wrote:
In article . com, "Russ" wrote: After a new electric range was installed the circuit breaker started to pop every now and then when everything was turned on (oven+all burners). This indicated to me that the range was drawing a load that was right at the upper limit of the 50 amp circuit breaker rating. Checked the data plate on the range which reads 240V. & 54.2 amps. So, when the range is at peak load it apparently can draw 4.2 amps over the breaker capacity. The wiring is Aluminum 6 guage (6 Al on the sheath),. Can I safely go to the next size breaker (60 amp) to accomodate the additional 4-5 amps??? Probably NOT, but it depends on the temperature rating of the insulation on the conductors; this should also be indicated on the cable sheath -- if it is not indicated, assume it's 60 degrees C. With a 90-degree rating, yes, you can go up to 60 amps. This is incorrect, if not a fire hazard. The temperature ratings of the lugs on the breaker and the range must be rated for 90 degrees C. I can assure you that they are NOT. The 90 degree C rating is used for derating conductors, such as for ambient temperature or more than three conductors in a conduit, etc. If one uses 90 degree C wire at the full rating, then one must also use 90 degree C lugs for terminating. Good luck finding a residential breaker rated for 90 degrees C. If the rating is 75 degrees, you're limited to the 50 amps you're already at. This will be true only if the terminals of the breaker and the range are rated for 75 degrees C. Some residential breakers are rated for 75 degrees C, some are _not_. And if it's only 60 degrees, you shouldn't have even a 50 amp breaker -- it's limited to 40 amps by Code. IIRC, a #4 copper THHN is rated for 70 amps at 60 degrees C. If using Romex, since Romex cannot be used over the 60 degree C rating, that would work with a 60 amp breaker with 60 or 75 degree C terminals. Bottom line, the OP needs to install a new circuit. |
#6
Posted to alt.home.repair
|
|||
|
|||
Range pops circuit breaker
Russ wrote: After a new electric range was installed the circuit breaker started to pop every now and then when everything was turned on (oven+all burners). This indicated to me that the range was drawing a load that was right at the upper limit of the 50 amp circuit breaker rating. Checked the data plate on the range which reads 240V. & 54.2 amps. So, when the range is at peak load it apparently can draw 4.2 amps over the breaker capacity. The wiring is Aluminum 6 gauge (6 Al on the sheath),. Can I safely go to the next size breaker (60 amp) to accommodate the additional 4-5 amps??? .. Personally a bit surprised that it trips breaker, never having it happen with a number of different stoves over a number of years. I think ours is wired with #8 AWG copper at least 35 feet from circuit breaker. Wiring has been in place for some 35 years. Ours stoves have always been regular North American domestic 30 inch often with two smaller and two larger burners on top. But unless you turn everything on from cold simultaneously it would seem unlikely you would draw maximum current anyway? After while one burner or another my be turning off and or the oven thermostat would switch off/on the oven cooking element etc. However when one first turns on the oven, in some models, the upper and lower heating elements both come on for a while; presumably to speed up the initial heat-up of the oven. Once up to an initial temperature the oven cooks using the bottom element only under control of the oven heat control thermostat a set by the user! |
#7
Posted to alt.home.repair
|
|||
|
|||
Range pops circuit breaker
"terry" wrote in message ups.com... But unless you turn everything on from cold simultaneously it would seem unlikely you would draw maximum current anyway? OP's issue is he's tripping the breaker, so however unlikely, he's seeing the problem. -Tim |
#8
Posted to alt.home.repair
|
|||
|
|||
Range pops circuit breaker
In article .com, "volts500" wrote:
Doug Miller wrote: In article . com, "Russ" wrote: After a new electric range was installed the circuit breaker started to pop every now and then when everything was turned on (oven+all burners). This indicated to me that the range was drawing a load that was right at the upper limit of the 50 amp circuit breaker rating. Checked the data plate on the range which reads 240V. & 54.2 amps. So, when the range is at peak load it apparently can draw 4.2 amps over the breaker capacity. The wiring is Aluminum 6 guage (6 Al on the sheath),. Can I safely go to the next size breaker (60 amp) to accomodate the additional 4-5 amps??? Probably NOT, but it depends on the temperature rating of the insulation on the conductors; this should also be indicated on the cable sheath -- if it is not indicated, assume it's 60 degrees C. With a 90-degree rating, yes, you can go up to 60 amps. This is incorrect, if not a fire hazard. The temperature ratings of the lugs on the breaker and the range must be rated for 90 degrees C. I can assure you that they are NOT. The 90 degree C rating is used for derating conductors, such as for ambient temperature or more than three conductors in a conduit, etc. If one uses 90 degree C wire at the full rating, then one must also use 90 degree C lugs for terminating. Good luck finding a residential breaker rated for 90 degrees C. I stand corrected. Thank you. If the rating is 75 degrees, you're limited to the 50 amps you're already at. This will be true only if the terminals of the breaker and the range are rated for 75 degrees C. Some residential breakers are rated for 75 degrees C, some are _not_. Ditto. And if it's only 60 degrees, you shouldn't have even a 50 amp breaker -- it's limited to 40 amps by Code. IIRC, a #4 copper THHN is rated for 70 amps at 60 degrees C. If using Romex, since Romex cannot be used over the 60 degree C rating, that would work with a 60 amp breaker with 60 or 75 degree C terminals. Yep. Bottom line, the OP needs to install a new circuit. Sounds like it. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Circuit Breaker Seems to Trip but Stays in On Position | Home Repair | |||
Locating Circuit Breaker( | Home Repair | |||
circuit breaker question! | Home Repair | |||
2-pole GFCI breaker for Edison (shared neutral) circuit | Home Ownership | |||
Dryer flips main circuit breaker occasionally | Home Repair |