Ground current through water main/meter
Awl--
How much is acceptable? An amp-probe reveals between 2 and 6 amps, depending on how balanced the load is on each leg of the main panel. I'm hearing that the neutral from the panel is connected to a *steel* cable outside, while the hots are indeed connected to copper conductors. This would explain some current going through ground. If the water main connection is broken, no noticeable effect in the house--or so it seems. Mebbe I'll amp-probe some of my neighbors plumbing. -- Mr. P.V.'d (formerly Droll Troll), Yonkers, NY Stop Corruption in Congress & Send the Ultimate Message: Absolutely Vote, for *Anyone BUT* a Democrat or a Republican Ending Corruption in Congress is the Single Best Way to Materially Improve Your Life entropic3.14decay at optonline2.718 dot net; remove pi and e to reply--ie, all d'numbuhs |
#2
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
"Proctologically Violated©®" wrote:
Awl-- How much is acceptable? An amp-probe reveals between 2 and 6 amps, depending on how balanced the load is on each leg of the main panel. I'm hearing that the neutral from the panel is connected to a *steel* cable outside, while the hots are indeed connected to copper conductors. This would explain some current going through ground. If the water main connection is broken, no noticeable effect in the house--or so it seems. Mebbe I'll amp-probe some of my neighbors plumbing. -- Mr. P.V.'d (formerly Droll Troll), Yonkers, NY Stop Corruption in Congress & Send the Ultimate Message: Absolutely Vote, for *Anyone BUT* a Democrat or a Republican Ending Corruption in Congress is the Single Best Way to Materially Improve Your Life entropic3.14decay at optonline2.718 dot net; remove pi and e to reply--ie, all d'numbuhs Bonding straps are generally required across the water meter to prevent potential for electrocution of the water guy if he removes the meter while there is an electrical fault. As for what current is acceptable, in my book it's essentially zero, or at least very low milliamps. I'd carefully check all your neutral connections in your panel and meter socket and anywhere else accessible. Also check for current to your ground rod since you shouldn't be relying on just a water line for a ground. Pete C. |
#3
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
Proctologically Violated©® wrote:
Awl-- How much is acceptable? Nothing you can measure with an ampprobe. An amp-probe reveals between 2 and 6 amps, depending on how balanced the load is on each leg of the main panel. I'm hearing that the neutral from the panel is connected to a *steel* cable outside, while the hots are indeed connected to copper conductors. This would explain some current going through ground. Actually its pretty unlikely a steel cable would have been used. Are you sure it isn't bare *aluminum*? If the water main connection is broken, no noticeable effect in the house--or so it seems. Mebbe I'll amp-probe some of my neighbors plumbing. -- Mr. P.V.'d (formerly Droll Troll), Yonkers, NY Stop Corruption in Congress & Send the Ultimate Message: Absolutely Vote, for *Anyone BUT* a Democrat or a Republican Ending Corruption in Congress is the Single Best Way to Materially Improve Your Life entropic3.14decay at optonline2.718 dot net; remove pi and e to reply--ie, all d'numbuhs |
#4
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
In article , "Proctologically Violated©®" wrote:
Awl-- How much is acceptable? None. There's supposed to be a bonding jumper around it. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#5
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
You have a problem there. You should have nothing moving through there.
You apparently have a problem with a open or very poor neutral, The only flow of current should be through the neutral and the two power legs, Current and any kind through the ground is a fault. That needs to be addressed like yesterday, I can't imagine anyone using steel. Aluminum maybe, but not steel -- Joseph E. Meehan 26 + 6 = 1 It's Irish Math "Proctologically Violated©®" wrote in message ... Awl-- How much is acceptable? An amp-probe reveals between 2 and 6 amps, depending on how balanced the load is on each leg of the main panel. I'm hearing that the neutral from the panel is connected to a *steel* cable outside, while the hots are indeed connected to copper conductors. This would explain some current going through ground. If the water main connection is broken, no noticeable effect in the house--or so it seems. Mebbe I'll amp-probe some of my neighbors plumbing. -- Mr. P.V.'d (formerly Droll Troll), Yonkers, NY Stop Corruption in Congress & Send the Ultimate Message: Absolutely Vote, for *Anyone BUT* a Democrat or a Republican Ending Corruption in Congress is the Single Best Way to Materially Improve Your Life entropic3.14decay at optonline2.718 dot net; remove pi and e to reply--ie, all d'numbuhs |
#6
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
Proctologically Violated©® wrote:
Awl-- How much is acceptable? An amp-probe reveals between 2 and 6 amps, depending on how balanced the load is on each leg of the main panel. How did you use that amp-probe? Was it a clamp-on type placed around the pipe or around the ground conductor attached to the pipe? I think I understand your query, you are asking about copper and perhaps wondering about relative resistances of the two different metals. Despite what others here said about there requiring NO current in the ground lead connected to the water pipe..... If there's a significant imbalance in the loading of the 240 volt supply, there will be a hefty current in the neutral supply feed from the street and the drop that current creates in that feed will try and raise the potential of of the neutral and ground busses in your service panel higher than earth ground (likely by only a couple of volts). That potential could create a current flow in the grounding lead connected to the water pipe in your home. The situation gets more complicated to analyze when you have neighbors connected to the same line transformer's secondary. Then, their neutral feeds and their earth grounds can get involved in the whole current sharing network. Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) The speed of light is 1.8*10^12 furlongs per fortnight. |
#7
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
Proctologically Violated©® wrote:
Awl-- How much is acceptable? An amp-probe reveals between 2 and 6 amps, depending on how balanced the load is on each leg of the main panel. I'm hearing that the neutral from the panel is connected to a *steel* cable outside, while the hots are indeed connected to copper conductors. This would explain some current going through ground. If the water main connection is broken, no noticeable effect in the house--or so it seems. Mebbe I'll amp-probe some of my neighbors plumbing. -- Time to call the utility. An open or high-resistance neutral from pole to your home can cause the neutral unbalance current to flow via the copper water main piping to your neighbor's neutral and then back to the pole (as you suspected). In all likelihood it's the utility's responsibility, not yours. It's a serious issue because unexpected neutral currents can cause overheating of any of the parts in the "grounding" path. Jim |
#8
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
Both. I do have a bond/jump across the water meter (don't want any dead
plumbers on my conscience!), and can just slip the amprobe over the copper going into the street. IOW, f'sure I'm measuring the right current, and all of it. Yes, the load balance affects it. A cupla electricians around here say they see this all the time, and indeed a few plumbers got *really* jolted around town. And, the goddamm poles around here are older than Moses. Yeah, I know it would be *better* to have zero current going thru the cold water supply, but if it's the nature of the beast around here, I can live with it. As I said, if I break this cold water pipe circuit, doesn't seem to have noticeable effect, so mebbe it is just a matter of resistance. Mebbe I just have a superlative cold-water connection!! I may just check the connections at my weatherhead, and at the pole--when the wind dies down, and the rain stops. -- Mr. P.V.'d (formerly Droll Troll), Yonkers, NY Stop Corruption in Congress & Send the Ultimate Message: Absolutely Vote, for *Anyone BUT* a Democrat or a Republican Ending Corruption in Congress is the Single Best Way to Materially Improve Your Life entropic3.14decay at optonline2.718 dot net; remove pi and e to reply--ie, all d'numbuhs "Jeff Wisnia" wrote in message et... Proctologically Violated©® wrote: Awl-- How much is acceptable? An amp-probe reveals between 2 and 6 amps, depending on how balanced the load is on each leg of the main panel. How did you use that amp-probe? Was it a clamp-on type placed around the pipe or around the ground conductor attached to the pipe? I think I understand your query, you are asking about copper and perhaps wondering about relative resistances of the two different metals. Despite what others here said about there requiring NO current in the ground lead connected to the water pipe..... If there's a significant imbalance in the loading of the 240 volt supply, there will be a hefty current in the neutral supply feed from the street and the drop that current creates in that feed will try and raise the potential of of the neutral and ground busses in your service panel higher than earth ground (likely by only a couple of volts). That potential could create a current flow in the grounding lead connected to the water pipe in your home. The situation gets more complicated to analyze when you have neighbors connected to the same line transformer's secondary. Then, their neutral feeds and their earth grounds can get involved in the whole current sharing network. Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) The speed of light is 1.8*10^12 furlongs per fortnight. |
#9
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
On Mon, 30 Oct 2006 17:32:10 GMT, "Joseph Meehan"
wrote: You have a problem there. You should have nothing moving through there. You apparently have a problem with a open or very poor neutral, The only flow of current should be through the neutral and the two power legs, Current and any kind through the ground is a fault. That needs to be addressed like yesterday, Agreed- Fault may be located at the transformer/aerial feeder neutral connections. The power people will need to evaluate this. I can't imagine anyone using steel. Aluminum maybe, but not steel A very common type of aerial feeder triplex uses AL phase conductors with ACSR (aluminum conductor- steel reinforced) used for the bare (neutral). -- Mr.E |
#10
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
"Proctologically Violated©®" wrote in message ... Yeah, I know it would be *better* to have zero current going thru the cold water supply, but if it's the nature of the beast around here, I can live with it. Only until you our yours touches something they shouldn't. You've got a defective neutral. Here's what do: 1. Call your power company. 2. Act like the third monkey on Noah's gangplank. |
#11
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
In all likelihood it's the utility's responsibility, not yours. AFTER yopu d that try isolating the leak by tripping off breakers or groups of breakers to see if you can effect it |
#12
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
|
#14
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
0 is normal, if its 6a 120v its only costing you at .12kwh maybe 750$ a
year, GetR fixed |
#15
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
"Proctologically Violated©®" wrote in message ... Awl-- How much is acceptable? An amp-probe reveals between 2 and 6 amps, depending on how balanced the load is on each leg of the main panel. I'm hearing that the neutral from the panel is connected to a *steel* cable outside, while the hots are indeed connected to copper conductors. This would explain some current going through ground. If the water main connection is broken, no noticeable effect in the house--or so it seems. Mebbe I'll amp-probe some of my neighbors plumbing. -- Try measuring the current with your main breaker off. If you still have a current flow with no power going to your house, then the problem could be somewhere outside of your domain. I have heard stories of current flow coming from the neighbor's house going through a customer's grounding conductor and traveling back to the transformer via the overhead neutral. If you have no current flow with the main breaker off, you need to have all of your neutral connections tightened from the pole down to your main panel. If that doesn't correct the problem, it is possible that you have some leakage to ground from somewhere in your house such as a defective appliance. Not too long ago I had a customer with a circuit breaker that would repeatedly trip a little while after it was reset. It turned out to be an old defective sump pump leaking current into the water. |
#16
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
In article ,
Proctologically Violated©® wrote: Awl-- How much is acceptable? An amp-probe reveals between 2 and 6 amps, depending on how balanced the load is on each leg of the main panel. I'm hearing that the neutral from the panel is connected to a *steel* cable outside, while the hots are indeed connected to copper conductors. This would explain some current going through ground. If the water main connection is broken, no noticeable effect in the house--or so it seems. Mebbe I'll amp-probe some of my neighbors plumbing. -- If there really is that much current flowing through ground, it indicates a ground fault somewhere in the building wiring. -- For every complicated, difficult problem, there is a simple, easy solution that does not work. Larry Wasserman - Baltimore Maryland - |
#17
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
According to Jeff Wisnia :
wrote: It should be less than the utility neutral but beyond that it is unpredictable without knowing what is on the utility side of the water line. If this is all metal pipe, the ground electrode system might be as good a conductor as a perfect neutral wire. Bear in mind the utility grounds their side of the XO terminal of the transformer too. This makes the piping system a parallel path and there is nothing you can do about it. Just be sure you have a good amount of current on the neutral and that the phases have equal voltage referenced to neutral. At last, someone who understands parallel current paths and agrees with me. It ain't necessarily so that the the OP MUST have hot to neutral leakage somewhere in his home's electrical system. Consider this, then, while this conductor is indeed in parallel with the neutral to a certain extent, it's pretty much relying on the conductance of the dirt to move that 6A, at what's probably a pretty low neutral-ground voltage. Dirt generally isn't anywhere near as conductive as a copper wire. So a simple parallel current that high seems extremely unlikely. Furthermore, that amount of current is bound to greatly accelerate any galvanic corrosion (eg: of the pipe). It needs more investigation. I'd have it looked at. Experiment with flipping off the main breaker and individual ones. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#18
Posted to alt.home.repair
|
|||
|
|||
Ground current through water main/meter
According to :
On Tue, 31 Oct 2006 14:05:53 -0000, (Chris Lewis) wrote: Consider this, then, while this conductor is indeed in parallel with the neutral to a certain extent, it's pretty much relying on the conductance of the dirt to move that 6A, That all depends on whether the water system is all metal or plastic. Actually, I think it more depends on whether the local pole pig and your plumbing share a connection. In older cities with all metal piping the water system becomes the city wide ground electrode. In newer areas everything is plastic so you really are using dirt for your ground. I can't help but think that the waterworks doesn't like using the whole water grid as a ground. Can lead to nasties when someone has to cut a water main. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
AquaTherm Furnace - No Hot Water Issue | Home Repair | |||
Brown's gas?? | Metalworking | |||
Surface ground water problem | Home Repair | |||
electricity on my water pipes | Home Repair | |||
I need a little advice on running waterlines in an uninsulated crawlspace | Home Repair |