I have a fluorescent light plugged into and outlet that comes BEFORE a GFCI
outlet on a circuit.
About 5% of the time I turn the light off (I have a switch leg going to that
outlet) the GFCI trips.
It only happens when I have an air filter turned on that is plugged into the
GFCI.

It is not clear to me why turning off the light would affect the GFCI coming
after it. (Yes, I do have the GFCI installed correctly; not backwards.)
Even if there was a ground fault, and I can't see why there should be one,
the GFCI wouldn't see it.

Any ideas?


  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 49
Default Turning off fluorescent light trip GFCI on different ?

May have something to do with the starting on the ballast. Rapid start
or instant start. A ballast in a fixture is essentially a transformer.
A transformer with an inductive load.

Reference.


http://www.safeelectricity.org/results.asp?ID=213

What is nuisance tripping of a GFCI?
It takes only 5 mA (0.005 A) of current leakage from the hot wire to
the ground to cause a GFCI to trip. A small amount of leakage current
may be difficult to avoid in some normal circuits. Hand-held power
tools do not cause a tripping problem if the tool is maintained in
good condition. Some stationary motors, such as a bathroom vent fan or
fluorescent lighting fixtures, may produce enough leakage to cause
nuisance tripping. Another problem may be a long circuit with many
splices. If possible, keep GFCI circuits less than 100 feet long. To
avoid nuisance tripping, a GFCI should not supply:

Circuits longer than 100 feet
Fluorescent or other types of electric-discharge lighting fixtures
Permanently installed electric motors



On Mon, 16 Oct 2006 03:11:21 GMT, "Toller" wrote:

I have a fluorescent light plugged into and outlet that comes BEFORE a GFCI
outlet on a circuit.
About 5% of the time I turn the light off (I have a switch leg going to that
outlet) the GFCI trips.
It only happens when I have an air filter turned on that is plugged into the
GFCI.

It is not clear to me why turning off the light would affect the GFCI coming
after it. (Yes, I do have the GFCI installed correctly; not backwards.)
Even if there was a ground fault, and I can't see why there should be one,
the GFCI wouldn't see it.

Any ideas?

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,617
Default Turning off fluorescent light trip GFCI on different ?

But if the light is before the GFCI, it wouldn't matter what happened to the
current going through the ballast since it wouldn't affect the GFCI. Would
it?

"Tazz" wrote in message
news
May have something to do with the starting on the ballast. Rapid start
or instant start. A ballast in a fixture is essentially a transformer.
A transformer with an inductive load.

Reference.


http://www.safeelectricity.org/results.asp?ID=213

What is nuisance tripping of a GFCI?
It takes only 5 mA (0.005 A) of current leakage from the hot wire to
the ground to cause a GFCI to trip. A small amount of leakage current
may be difficult to avoid in some normal circuits. Hand-held power
tools do not cause a tripping problem if the tool is maintained in
good condition. Some stationary motors, such as a bathroom vent fan or
fluorescent lighting fixtures, may produce enough leakage to cause
nuisance tripping. Another problem may be a long circuit with many
splices. If possible, keep GFCI circuits less than 100 feet long. To
avoid nuisance tripping, a GFCI should not supply:

Circuits longer than 100 feet
Fluorescent or other types of electric-discharge lighting fixtures
Permanently installed electric motors



On Mon, 16 Oct 2006 03:11:21 GMT, "Toller" wrote:

I have a fluorescent light plugged into and outlet that comes BEFORE a
GFCI
outlet on a circuit.
About 5% of the time I turn the light off (I have a switch leg going to
that
outlet) the GFCI trips.
It only happens when I have an air filter turned on that is plugged into
the
GFCI.

It is not clear to me why turning off the light would affect the GFCI
coming
after it. (Yes, I do have the GFCI installed correctly; not backwards.)
Even if there was a ground fault, and I can't see why there should be one,
the GFCI wouldn't see it.

Any ideas?



  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 49
Default Turning off fluorescent light trip GFCI on different ?


I have seen it before.

Even having the lighting on the line side or anywhere in the circuit
it can cause the ground fault to trip

I would suspect loose wring or somewhere there is leakage from the
grouding and grounded conductor.

Are the light fixtures grounded?


On Mon, 16 Oct 2006 04:30:22 GMT, "Toller" wrote:

But if the light is before the GFCI, it wouldn't matter what happened to the
current going through the ballast since it wouldn't affect the GFCI. Would
it?

"Tazz" wrote in message
news
May have something to do with the starting on the ballast. Rapid start
or instant start. A ballast in a fixture is essentially a transformer.
A transformer with an inductive load.

Reference.


http://www.safeelectricity.org/results.asp?ID=213

What is nuisance tripping of a GFCI?
It takes only 5 mA (0.005 A) of current leakage from the hot wire to
the ground to cause a GFCI to trip. A small amount of leakage current
may be difficult to avoid in some normal circuits. Hand-held power
tools do not cause a tripping problem if the tool is maintained in
good condition. Some stationary motors, such as a bathroom vent fan or
fluorescent lighting fixtures, may produce enough leakage to cause
nuisance tripping. Another problem may be a long circuit with many
splices. If possible, keep GFCI circuits less than 100 feet long. To
avoid nuisance tripping, a GFCI should not supply:

Circuits longer than 100 feet
Fluorescent or other types of electric-discharge lighting fixtures
Permanently installed electric motors



On Mon, 16 Oct 2006 03:11:21 GMT, "Toller" wrote:

I have a fluorescent light plugged into and outlet that comes BEFORE a
GFCI
outlet on a circuit.
About 5% of the time I turn the light off (I have a switch leg going to
that
outlet) the GFCI trips.
It only happens when I have an air filter turned on that is plugged into
the
GFCI.

It is not clear to me why turning off the light would affect the GFCI
coming
after it. (Yes, I do have the GFCI installed correctly; not backwards.)
Even if there was a ground fault, and I can't see why there should be one,
the GFCI wouldn't see it.

Any ideas?


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Turning off fluorescent light trip GFCI on different ?

try replacing GFCI it may be overly sensitive. I tossed one that
nuisance tripped too ofet, its replacement has been fine



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 12
Default Turning off fluorescent light trip GFCI on different ?

ANY flux on the common leg of the curcuit will cause the GFCI to trip down
stream,
assuming you have them wired in series.

"Toller" wrote in message
...
I have a fluorescent light plugged into and outlet that comes BEFORE a GFCI
outlet on a circuit.
About 5% of the time I turn the light off (I have a switch leg going to
that outlet) the GFCI trips.
It only happens when I have an air filter turned on that is plugged into
the GFCI.

It is not clear to me why turning off the light would affect the GFCI
coming after it. (Yes, I do have the GFCI installed correctly; not
backwards.) Even if there was a ground fault, and I can't see why there
should be one, the GFCI wouldn't see it.

Any ideas?



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Compact Fluorescent light bulbs? BE Home Repair 42 November 1st 05 03:05 PM
wiring confusion/ouside light James UK diy 1 May 25th 05 04:07 AM
FLUORESCENT LIGHT WITHOUT TRANFORMER AND STARTER ? mowhoong Electronics Repair 2 May 7th 04 10:13 PM
Light bulb malfunction Oldylocks Home Repair 12 February 5th 04 01:51 PM
strange problem connecting light to dimmer John Hunter Home Repair 6 January 19th 04 07:57 PM


All times are GMT +1. The time now is 09:09 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"