Default single or double pole switch for 240V baseboard heater

Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!

Part B:
The baseboard heaters are 2000W. If I put 2 of them on the same 20A
circuit I am at 83% of the rated breaker capacity (I am using standard
Siemens breakers). Do I really need to put each one on its own
breaker?

Thank you for your time,
William

  #2   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default single or double pole switch for 240V baseboard heater

You can't exceed 80%, so you could use 30 amp wire. A wall thermostat or
switch needs to disconnect both hot legs


" wrote in message
oups.com...
Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!

Part B:
The baseboard heaters are 2000W. If I put 2 of them on the same 20A
circuit I am at 83% of the rated breaker capacity (I am using standard
Siemens breakers). Do I really need to put each one on its own
breaker?

Thank you for your time,
William



  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 168
Default single or double pole switch for 240V baseboard heater


" wrote in message
oups.com...
Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!


120V circuit has a neutral and a hot; if you stand in a bath tub and touch
the two wires one by one, you will get shocked by the hot, and not by the
neutral

240V circuit has no neutral; it has two hots (each one is 120V relative to
ground). If you touch the two wires one by one, you get shocked twice.

If you switch off only one hot, then the heater wiring is still carrying
120V. This is potentially dangerous.


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 94
Default single or double pole switch for 240V baseboard heater


peter wrote:
" wrote in message
oups.com...
Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!


120V circuit has a neutral and a hot; if you stand in a bath tub and touch
the two wires one by one, you will get shocked by the hot, and not by the
neutral

240V circuit has no neutral; it has two hots (each one is 120V relative to
ground). If you touch the two wires one by one, you get shocked twice.

If you switch off only one hot, then the heater wiring is still carrying
120V. This is potentially dangerous.


Greetings,

I fail to understand why it is dangerous for the wire to be carrying
120V into the heater. So what? The (optional add-in) integrated
thermostat only breaks one pole. Are you saying it is dangerous?
Based on your posting alone it appears that if one is dangerous then
the other must be as well.

Please explain.

Thanks,
William

  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 94
Default single or double pole switch for 240V baseboard heater




" wrote in message
oups.com...
Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!

Part B:
The baseboard heaters are 2000W. If I put 2 of them on the same 20A
circuit I am at 83% of the rated breaker capacity (I am using standard
Siemens breakers). Do I really need to put each one on its own
breaker?

Thank you for your time,
William


RBM (remove this) wrote:
You can't exceed 80%, so you could use 30 amp wire. A wall thermostat or
switch needs to disconnect both hot legs


Greetings,

You cannot exceed 80% of the wire rating or of the breaker rating? I
thought it was of the breaker rating? And my real question is: are
baseboard heaters considered intermittent loads?

Thanks,
William



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,617
Default single or double pole switch for 240V baseboard heater


" wrote in message
oups.com...

peter wrote:
" wrote in message
oups.com...
Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!


120V circuit has a neutral and a hot; if you stand in a bath tub and
touch
the two wires one by one, you will get shocked by the hot, and not by the
neutral

240V circuit has no neutral; it has two hots (each one is 120V relative
to
ground). If you touch the two wires one by one, you get shocked twice.

If you switch off only one hot, then the heater wiring is still carrying
120V. This is potentially dangerous.


Greetings,

I fail to understand why it is dangerous for the wire to be carrying
120V into the heater. So what? The (optional add-in) integrated
thermostat only breaks one pole. Are you saying it is dangerous?
Based on your posting alone it appears that if one is dangerous then
the other must be as well.

Do it if you want to; it is neither legal nor safe.
With a switch off, there is to be no voltage at a device. With a single
pole switch, someone working on the heater will be very surprised.
Your heaters could easily be on for hours at a time. Do you think that is
intermittent?

Do what you what, but don't hope that people will tell you it is okay.


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 178
Default single or double pole switch for 240V baseboard heater

wrote:
peter wrote:
" wrote in message
oups.com...
Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!

120V circuit has a neutral and a hot; if you stand in a bath tub and touch
the two wires one by one, you will get shocked by the hot, and not by the
neutral

240V circuit has no neutral; it has two hots (each one is 120V relative to
ground). If you touch the two wires one by one, you get shocked twice.

If you switch off only one hot, then the heater wiring is still carrying
120V. This is potentially dangerous.


Greetings,

I fail to understand why it is dangerous for the wire to be carrying
120V into the heater. So what? The (optional add-in) integrated
thermostat only breaks one pole. Are you saying it is dangerous?
Based on your posting alone it appears that if one is dangerous then
the other must be as well.

Please explain.

Thanks,
William


What you are saying is true but I expect code requires a double pole.
Someone working on the unit would not depend on the thermostat to remove
all power but would most likely expect it to be removed by the switch.

Kind of like power to a lamp with a non polarized plug being plugged
into a switchable socket. It is possible for the lamp to have voltage
even with the switch turned off.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 178
Default single or double pole switch for 240V baseboard heater

Rich256 wrote:
wrote:
peter wrote:
" wrote in message
oups.com...
Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!
120V circuit has a neutral and a hot; if you stand in a bath tub and
touch
the two wires one by one, you will get shocked by the hot, and not by
the
neutral

240V circuit has no neutral; it has two hots (each one is 120V
relative to
ground). If you touch the two wires one by one, you get shocked twice.

If you switch off only one hot, then the heater wiring is still carrying
120V. This is potentially dangerous.


Greetings,

I fail to understand why it is dangerous for the wire to be carrying
120V into the heater. So what? The (optional add-in) integrated
thermostat only breaks one pole. Are you saying it is dangerous?
Based on your posting alone it appears that if one is dangerous then
the other must be as well.

Please explain.

Thanks,
William


What you are saying is true but I expect code requires a double pole.
Someone working on the unit would not depend on the thermostat to remove
all power but would most likely expect it to be removed by the switch.

Kind of like power to a lamp with a non polarized plug being plugged
into a switchable socket. It is possible for the lamp to have voltage
even with the switch turned off.


My mind was somewhere else on that last statement!!! Thinking of the
outside of a socket I guess.
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default single or double pole switch for 240V baseboard heater


" wrote in message
The baseboard heaters are 2000W. If I put 2 of them on the same 20A
circuit I am at 83% of the rated breaker capacity (I am using standard
Siemens breakers). Do I really need to put each one on its own
breaker?


Yes, 83 % is too high.



You cannot exceed 80% of the wire rating or of the breaker rating? I
thought it was of the breaker rating?



If the wire is properly matched, it works out to both.

And my real question is: are
baseboard heaters considered intermittent loads?


What is intermittent about a heating element that maybe on from a few
minutes to hours at a time?

I'm glad I'm not your tenant. You seem to want to cheap out on this and
potentially cause a serious safety situation. Use the right double pole
switch, use the right wiring.


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,300
Default single or double pole switch for 240V baseboard heater

Rich256 wrote:

wrote:

peter wrote:

" wrote in message
oups.com...

Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!

120V circuit has a neutral and a hot; if you stand in a bath tub and
touch
the two wires one by one, you will get shocked by the hot, and not by
the
neutral

240V circuit has no neutral; it has two hots (each one is 120V
relative to
ground). If you touch the two wires one by one, you get shocked twice.

If you switch off only one hot, then the heater wiring is still carrying
120V. This is potentially dangerous.



Greetings,

I fail to understand why it is dangerous for the wire to be carrying
120V into the heater. So what? The (optional add-in) integrated
thermostat only breaks one pole. Are you saying it is dangerous?
Based on your posting alone it appears that if one is dangerous then
the other must be as well.

Please explain.

Thanks,
William


What you are saying is true but I expect code requires a double pole.
Someone working on the unit would not depend on the thermostat to remove
all power but would most likely expect it to be removed by the switch.

Kind of like power to a lamp with a non polarized plug being plugged
into a switchable socket. It is possible for the lamp to have voltage
even with the switch turned off.


I take it you meant to say, "even with the switch ON THE LAMP turned off"

Jeff

--
Jeffry Wisnia
(W1BSV + Brass Rat '57 EE)
"What do you expect from a pig but a grunt?"


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 114
Default single or double pole switch for 240V baseboard heater

I am happy as (insert expletive here) that you are NOT my landlord.

You've asked nearly the exact same question three times. You must be a real
cheap person.

FWIW, back when I rented, I (as the tenant) was responsible for the
utilities.

" wrote in message
oups.com...
Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!

Part B:
The baseboard heaters are 2000W. If I put 2 of them on the same 20A
circuit I am at 83% of the rated breaker capacity (I am using standard
Siemens breakers). Do I really need to put each one on its own
breaker?

Thank you for your time,
William



  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,300
Default single or double pole switch for 240V baseboard heater

HeatMan wrote:

I am happy as (insert expletive here) that you are NOT my landlord.

You've asked nearly the exact same question three times. You must be a real
cheap person.

FWIW, back when I rented, I (as the tenant) was responsible for the
utilities.

" wrote in message
oups.com...

Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!

Part B:
The baseboard heaters are 2000W. If I put 2 of them on the same 20A
circuit I am at 83% of the rated breaker capacity (I am using standard
Siemens breakers). Do I really need to put each one on its own
breaker?

Thank you for your time,
William





He's probably too cheap to convert that apartment to separate metering
so the tenant can pay for the electricity, and would then also have an
incentive not to waste it.

Or, maybe he's renting an "illegal apartment" in an area zoned only for
single family housing and can't do that. G

Jeff

--
Jeffry Wisnia
(W1BSV + Brass Rat '57 EE)
"What do you expect from a pig but a grunt?"
  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,963
Default single or double pole switch for 240V baseboard heater

On Sun, 10 Sep 2006 15:38:21 GMT, Rich256 wrote:

wrote:
peter wrote:
" wrote in message
oups.com...
Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!
120V circuit has a neutral and a hot; if you stand in a bath tub and touch
the two wires one by one, you will get shocked by the hot, and not by the
neutral

240V circuit has no neutral; it has two hots (each one is 120V relative to
ground). If you touch the two wires one by one, you get shocked twice.

If you switch off only one hot, then the heater wiring is still carrying
120V. This is potentially dangerous.


Greetings,

I fail to understand why it is dangerous for the wire to be carrying
120V into the heater. So what? The (optional add-in) integrated
thermostat only breaks one pole. Are you saying it is dangerous?
Based on your posting alone it appears that if one is dangerous then
the other must be as well.

Please explain.

Thanks,
William


What you are saying is true but I expect code requires a double pole.
Someone working on the unit would not depend on the thermostat to remove
all power but would most likely expect it to be removed by the switch.

Kind of like power to a lamp with a non polarized plug being plugged
into a switchable socket. It is possible for the lamp to have voltage
even with the switch turned off.


That reminds me of the way I first learned to connect 3-way light
switches. It's considered unsafe because the light can be off and
still have 120V connected to it.
--
106 days until the winter solstice celebration

Mark Lloyd
http://notstupid.laughingsquid.com

"How could you ask be to believe in God when there's
absolutely no evidence that I can see?" -- Jodie Foster
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 178
Default single or double pole switch for 240V baseboard heater

Mark Lloyd wrote:
On Sun, 10 Sep 2006 15:38:21 GMT, Rich256 wrote:

wrote:
peter wrote:
" wrote in message
oups.com...
Greetings,

Part A:
I have 240V baseboard heaters with the termostat inside the heater. I
want to put wall switches in the same place as the light switches so
that I can turn off the heaters when I leave the room without getting
down on the ground to adjust the thermostat. I know that a single pole
switch will work but I wanted to know if there was any reason the code
required a double pole switch? Thanks!
120V circuit has a neutral and a hot; if you stand in a bath tub and touch
the two wires one by one, you will get shocked by the hot, and not by the
neutral

240V circuit has no neutral; it has two hots (each one is 120V relative to
ground). If you touch the two wires one by one, you get shocked twice.

If you switch off only one hot, then the heater wiring is still carrying
120V. This is potentially dangerous.
Greetings,

I fail to understand why it is dangerous for the wire to be carrying
120V into the heater. So what? The (optional add-in) integrated
thermostat only breaks one pole. Are you saying it is dangerous?
Based on your posting alone it appears that if one is dangerous then
the other must be as well.

Please explain.

Thanks,
William

What you are saying is true but I expect code requires a double pole.
Someone working on the unit would not depend on the thermostat to remove
all power but would most likely expect it to be removed by the switch.

Kind of like power to a lamp with a non polarized plug being plugged
into a switchable socket. It is possible for the lamp to have voltage
even with the switch turned off.


That reminds me of the way I first learned to connect 3-way light
switches. It's considered unsafe because the light can be off and
still have 120V connected to it.



Yeah, but as I posted, I don't know where my mind what when I made that
last statement. Immediately after I hit the send button I realized what
I had said. With the switch off there should not be any voltage on the
lamp.

If plugged into an ordinary socket it could have voltage on the outside
rim of the socket.
  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 856
Default single or double pole switch for 240V baseboard heater

According to Toller :

Do it if you want to; it is neither legal nor safe.
With a switch off, there is to be no voltage at a device. With a single
pole switch, someone working on the heater will be very surprised.
Your heaters could easily be on for hours at a time. Do you think that is
intermittent?


Do what you what, but don't hope that people will tell you it is okay.


Ah, but it is. Call it crazy, but the NEC (and I believe the CEC
as well) permit the use of single pole thermostats with 240V heaters.

I don't like it either, and when installing a heater, I'll use
a two pole thermostat.

But, anybody fiddling with the wires of a 240V heater, relying
_only_ on a thermostat to shut power off, probably deserves what
they get.

As an interesting sidenote: somewhat akin to the special ampacity ruleso
for motors, the CEC has special provisions for dedicated electric heater
circuits.

While you cannot exceed the 80% rule for the breaker, you can load the
wire to 100% of its rating.

In other words, if you have a 15A heater on 120V, you can use
a 20A breaker and 14ga wire.

Which suggests to me that the continuous 80% ampacity limit is largely
for the breaker's benefit, not the wire.

This doesn't apply to the NEC.
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
single gang double 3-way switch theball Home Repair 2 May 27th 06 02:45 PM
How do I know if I need a new switch for 240v? Steve W Woodworking 32 April 29th 06 12:15 AM
Switch wiring question [email protected] UK diy 9 January 9th 06 06:38 PM
Electrical : 3 way -- Single Pole (Light Switch) AC Home Repair 7 November 24th 05 06:13 AM
Cost to install gas hot water heater Walleye Home Ownership 8 September 10th 03 04:20 AM


All times are GMT +1. The time now is 11:46 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"