Wiring guage and amps
Is this right for wiring?
14 gauge with 2 wires for lights and small appliances power outlets to a 20 amp breaker 12 gauge with 3 wires for the fridge, microwave, diswaher to a 20 AMP breaker 8 gauge with 3 wires for the stove top, oven, dryer to a 40 Amp breaker New panel size - do I add up the number of circuits needed and their amps? e.g. stove 40AMP + oven 40+ dryer 40+ light circuit 20 + small appliances 20+ fridge 20+ diswasher microwave garbage disposal 20 for a total of 200 AMP box needed? OR can I combine the stope top and oven for a total of 160??? Thanks for your help |
#2
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
get a 200 amp new main with the maximum nuber of breaker slots
available. service entrance cable and meter can must be replaced when upgrading to larger amp main panel 14 gauge wire is for 15 amps max 12 gauge for 20 amp max kitchen outlet circuits must be GFCI protected. |
#3
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
Mulan wrote:
Is this right for wiring? no, but you're kind of close. 14 gauge with 2 wires for lights and small appliances power outlets to a 20 amp breaker 12 gauge with 3 wires for the fridge, microwave, diswaher to a 20 AMP breaker 12 or 14 gauge wire for lights and convenience outlets. 14 gauge wire requires a 15A breaker. You can use a 20A or a 15A for #12 wire. (I use #14 wire and 15A breakers for lighting circuits and for light-duty but dedicated outlets, and I use #12 wire and 20A breakers for all convenience outlets and appliance outlets. You need at least two 20A circuits for the kitchen. 8 gauge with 3 wires for the stove top, oven, dryer to a 40 Amp breaker Yes, although #6 Aluminum might be cheaper if it's a long run. The dryer should probably be on a 30A circuit rather than 40A, and can use #10 wire. New panel size - do I add up the number of circuits needed and their amps? e.g. No. there are calculations in the back of the code book that tell you the minimum service size. stove 40AMP + oven 40+ dryer 40+ light circuit 20 + small appliances 20+ fridge 20+ diswasher microwave garbage disposal 20 for a total of 200 AMP box needed? OR can I combine the stope top and oven for a total of 160??? There's a "tap rule" that lets you combine the stove and oven on one circuit, I don't remember the details; it's very specific, but it will save you some money on big copper wire. (My pain pills for my bad back just kicked in and I don't trust my memory.) With an electric stove and electric dryer (what about your water heater?) you might need more than a 100A panel. You certainly don't need a 200A, although you might want a 200A to give you lots of room for expansion. Take a look at the 125A panels that I think are made for mobile homes. 125A is a nice size, imho. I installed a 150A when I upgraded the service in my old house, but the load calculations said I only needed a 70A service. (that was before I added the shop w/ air compressor and welder.) I use aluminum wire for most things over 30 amps, and copper for everything else. (I use copper for the big stuff too if it's a short run.) Hope this helps! Best regards, Bob |
#4
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
|
#5
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
Thank you, just to clarify this would be a third breaker panel for a
second kitchen. The main one upstairs is already full and this area is running off a smaller older breaker panel. Do I need 40 Amps for the stove and oven? Do lights and power outlets run on 15 or 20 AMPS? The lights in there now are old tube and knob going to and old breaker that has about 50 AMPS in it and a fan heater blows the circuit. I was going to rewire this area off that old breaker. wrote: get a 200 amp new main with the maximum nuber of breaker slots available. service entrance cable and meter can must be replaced when upgrading to larger amp main panel 14 gauge wire is for 15 amps max 12 gauge for 20 amp max kitchen outlet circuits must be GFCI protected. |
#6
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
Only kitchen counter outlets are required to be GFCI protected
wrote in message ups.com... get a 200 amp new main with the maximum nuber of breaker slots available. service entrance cable and meter can must be replaced when upgrading to larger amp main panel 14 gauge wire is for 15 amps max 12 gauge for 20 amp max kitchen outlet circuits must be GFCI protected. |
#7
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
8 gauge with 3 wires for the stove top, oven, dryer to a 40 Amp breaker
The amperage varies by appliance, but all the above now require 4 wire circuits "Mulan" wrote in message oups.com... Thank you! Since the breaker panel part of it scares me but I have been "apprentice" to a lot of wiring installation for outlets, smoke detectors and lights. I think I can install all the wiring back to where the panel goes and then call in an expert for the mains to panel installation. My budget doesn't give me any other option. Maybe an electrician would not be willing to do that though. The water heater is on the other side of the house and has gas. There is gas in the room but I was given the electric stove top and oven and can't afford gas appliances. I was given the heater unit and all the cedar wood for a sauna too that someone tore out that I thought about sticking in the basement - any idea how much power that takes or if it would be 110 or 220? I hope your back feels better there is nothing worse than back pain zxcvbob wrote: Mulan wrote: Is this right for wiring? no, but you're kind of close. 14 gauge with 2 wires for lights and small appliances power outlets to a 20 amp breaker 12 gauge with 3 wires for the fridge, microwave, diswaher to a 20 AMP breaker 12 or 14 gauge wire for lights and convenience outlets. 14 gauge wire requires a 15A breaker. You can use a 20A or a 15A for #12 wire. (I use #14 wire and 15A breakers for lighting circuits and for light-duty but dedicated outlets, and I use #12 wire and 20A breakers for all convenience outlets and appliance outlets. You need at least two 20A circuits for the kitchen. 8 gauge with 3 wires for the stove top, oven, dryer to a 40 Amp breaker Yes, although #6 Aluminum might be cheaper if it's a long run. The dryer should probably be on a 30A circuit rather than 40A, and can use #10 wire. New panel size - do I add up the number of circuits needed and their amps? e.g. No. there are calculations in the back of the code book that tell you the minimum service size. stove 40AMP + oven 40+ dryer 40+ light circuit 20 + small appliances 20+ fridge 20+ diswasher microwave garbage disposal 20 for a total of 200 AMP box needed? OR can I combine the stope top and oven for a total of 160??? There's a "tap rule" that lets you combine the stove and oven on one circuit, I don't remember the details; it's very specific, but it will save you some money on big copper wire. (My pain pills for my bad back just kicked in and I don't trust my memory.) With an electric stove and electric dryer (what about your water heater?) you might need more than a 100A panel. You certainly don't need a 200A, although you might want a 200A to give you lots of room for expansion. Take a look at the 125A panels that I think are made for mobile homes. 125A is a nice size, imho. I installed a 150A when I upgraded the service in my old house, but the load calculations said I only needed a 70A service. (that was before I added the shop w/ air compressor and welder.) I use aluminum wire for most things over 30 amps, and copper for everything else. (I use copper for the big stuff too if it's a short run.) Hope this helps! Best regards, Bob |
#8
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
"RBM" rbm2(remove wrote in message ... Only kitchen counter outlets are required to be GFCI protected Sort of... If it's within 6 feet of the sink (read 'water'), it has to be GFCI protected. wrote in message ups.com... get a 200 amp new main with the maximum nuber of breaker slots available. service entrance cable and meter can must be replaced when upgrading to larger amp main panel 14 gauge wire is for 15 amps max 12 gauge for 20 amp max kitchen outlet circuits must be GFCI protected. |
#9
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
I know to never GFCI a fridge provided the outlet is behind the fridge so it cant be used for anything else. Honestly I think you should get a pros opinion before you begin as to the capacity of your main panel to handle the new sub panel. sadly copper price has skyrocketed today because of this it might be cheaper to buy a gas stove at a second hand shop and gas dryer too. the electric dryers cost to operate is going to kill you, same for electric hot water tanks, low capacity and high operating expense |
#10
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
ALL kitchen counter outlets MUST be GFCI protected
"HeatMan" wrote in message ... "RBM" rbm2(remove wrote in message ... Only kitchen counter outlets are required to be GFCI protected Sort of... If it's within 6 feet of the sink (read 'water'), it has to be GFCI protected. wrote in message ups.com... get a 200 amp new main with the maximum nuber of breaker slots available. service entrance cable and meter can must be replaced when upgrading to larger amp main panel 14 gauge wire is for 15 amps max 12 gauge for 20 amp max kitchen outlet circuits must be GFCI protected. |
#11
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
RBM wrote:
ALL kitchen counter outlets MUST be GFCI protected No they don't. The one for the fridge *should not* be protected. If you want to be a stickler about it, use a simplex receptacle for the fridge to indicate that it's a dedicated outlet. The 110V outlet behind the stove (it's there in case you want to install a gas stove) would not need to be protected. Same for an outlet for a built-in microwave. And that wall outlet way over there on the opposite wall, by the breakfast area. Best regards, Bob |
#12
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
Bob, refrigerator outlets and outlets for stove ignition are not counter
outlets, which is why they don't have to be GFCI protected. I repeat All kitchen counter outlets MUST be GFCI protected "zxcvbob" wrote in message ... RBM wrote: ALL kitchen counter outlets MUST be GFCI protected No they don't. The one for the fridge *should not* be protected. If you want to be a stickler about it, use a simplex receptacle for the fridge to indicate that it's a dedicated outlet. The 110V outlet behind the stove (it's there in case you want to install a gas stove) would not need to be protected. Same for an outlet for a built-in microwave. And that wall outlet way over there on the opposite wall, by the breakfast area. Best regards, Bob |
#13
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
RBM wrote:
Bob, refrigerator outlets and outlets for stove ignition are not counter outlets, which is why they don't have to be GFCI protected. I repeat All kitchen counter outlets MUST be GFCI protected Oops. I didn't see the word "counter" in there. I was too focused on "MUST". As the poet always used to say, Sorry 'bout that, Chief. Bob |
#14
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
|
#16
Posted to alt.home.repair
|
|||
|
|||
Wiring guage and amps
On 15 Jul 2006 21:41:20 -0700, "Mulan" wrote:
Is this right for wiring? 14 gauge with 2 wires for lights and small appliances power outlets to a 20 amp breaker 12 gauge with 3 wires for the fridge, microwave, diswaher to a 20 AMP breaker 8 gauge with 3 wires for the stove top, oven, dryer to a 40 Amp breaker New panel size - do I add up the number of circuits needed and their amps? e.g. stove 40AMP + oven 40+ dryer 40+ light circuit 20 + small appliances 20+ fridge 20+ diswasher microwave garbage disposal 20 for a total of 200 AMP box needed? OR can I combine the stope top and oven for a total of 160??? Thanks for your help Most of this has been answered, but ... Don't major appliances still have spec plates? On which things like max amperage draw are indicated? Have you looked for these? On 15 Jul 2006 22:25:37 -0700, "Mulan" wrote: Thank you, just to clarify this would be a third breaker panel for a second kitchen. The main one upstairs is already full and this area is running off a smaller older breaker panel. Ooooops. This complicates matters aplenty. Do you comtemplate a new elec. service entrance (pig-tails, etc) for a new box or a new box that is actually to be a sub-box or ??? Do I need 40 Amps for the stove and oven? Start with the specs on the appliance(s). Do lights and power outlets run on 15 or 20 AMPS? LIte duty circuits (ie lights, radios, etc) are generally 15A. The lights in there now are old tube and knob going to and old breaker that has about 50 AMPS in it and a fan heater blows the circuit. I was going to rewire this area off that old breaker. No comprehendere, senor. On 15 Jul 2006 22:39:21 -0700, "Mulan" wrote: Thank you! Since the breaker panel part of it scares me but I have been "apprentice" to a lot of wiring installation for outlets, smoke detectors and lights. I think I can install all the wiring back to where the panel goes and then call in an expert for the mains to panel installation. My budget doesn't give me any other option. Then I suspect you are in trouble. Maybe an electrician would not be willing to do that though. Unless maybe he's your brother-in-law or somesuch ... ... Seriously, if you have trouble estimating amp loads for your circuitry, it *sounds* like you are "out of your element". You can afford a 2nd kitchen but not an electrician? Beware, my friend, for the indications are that you are about to shoot your po' self in the foot? :-) Good Luck, Puddin' |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Electrical Wiring Hot Water Heater | Home Repair | |||
Wiring and plumbing a second kitchen | Home Repair | |||
Electricians - Have an electrical question | Metalworking | |||
240 volt wiring | Home Repair | |||
Garage welder wiring questions | Metalworking |