  #1   Report Post  
Posted to alt.home.repair
John F.
 
Posts: n/a
Default Boiler Shuts Down

When the outside temps (I'm in upstate NY) get down to the teens and single
digits my boiler can't keep up with the heat loss. There is baseboard
cabinet (7 inch cabinet) running the entire perimeter of the first floor
exterior walls of the four rooms (each 13x13) the zone covers. The rooms
are 8' 9" and all walls are insulated to R-13. The windows are dbl
insulated glass and the basement ceiling below is insulated as well. The
heat pipes are also fully insulated in the basement. The boiler (oil fired
baseboard hot water 2 zone system) rated at 150,000 btu shuts down when it
reaches the 180 deg boiler/water temp. I've been told that the 180 deg is
the proper shut down. The thermostat calls for heat with a 2 degree drop in
temperature. Right now it only runs for about 10 minutes before it reaches
its 180 deg mark and then shuts down for about 15 mins. The result is a
net loss of room temperature especially at night of upwards of 6 to 8
degrees resulting in a room temp of 60 to 62 degrees by morning. If temps
go into the below zeros then the boiler never catrhches up even in the
daytime. So my question is what if anything can I do or have the oil
burner service company do to have the burner deliver heat for a longer
peiod. Your usual good input would be appreciated. Thanks. John


  #2   Report Post  
Posted to alt.home.repair
Speedy Jim
 
Posts: n/a
Default Boiler Shuts Down

John F. wrote:
When the outside temps (I'm in upstate NY) get down to the teens and single
digits my boiler can't keep up with the heat loss. There is baseboard
cabinet (7 inch cabinet) running the entire perimeter of the first floor
exterior walls of the four rooms (each 13x13) the zone covers. The rooms
are 8' 9" and all walls are insulated to R-13. The windows are dbl
insulated glass and the basement ceiling below is insulated as well. The
heat pipes are also fully insulated in the basement. The boiler (oil fired
baseboard hot water 2 zone system) rated at 150,000 btu shuts down when it
reaches the 180 deg boiler/water temp. I've been told that the 180 deg is
the proper shut down. The thermostat calls for heat with a 2 degree drop in
temperature. Right now it only runs for about 10 minutes before it reaches
its 180 deg mark and then shuts down for about 15 mins. The result is a
net loss of room temperature especially at night of upwards of 6 to 8
degrees resulting in a room temp of 60 to 62 degrees by morning. If temps
go into the below zeros then the boiler never catrhches up even in the
daytime. So my question is what if anything can I do or have the oil
burner service company do to have the burner deliver heat for a longer
peiod. Your usual good input would be appreciated. Thanks. John


It doesn't sound like a burner/boiler problem to me.

If the boiler is easily maintaining ~180F, the problem
seems to be that the circ pump and radiation can't *remove*
enough BTU from the water.

For example: Although the boiler has a rating of 150,000BTU/Hr,
let's say that the rads can only unload 50,000BTU/Hr.
The burner would only need to run 1/3 the time .

But the house needs 100,000BTU/Hr in coldest weather (example).
The boiler *could* produce that easily, but the rads can't
pump the BTU's into the house fast enough. So...house gets cold.

You may have to have someone re-calculate the fin-tube area
required and/or the pump capacity to deliver enough water velocity.

Jim
  #3   Report Post  
Posted to alt.home.repair
m Ransley
 
Posts: n/a
Default Boiler Shuts Down

You can raise the boiler temp to 190, the circulator pump could be weak,
but it doesnt sound right, are the radiators extremely hot, have they
been bled of air, does the circulator pump continue to run when the
boiler is not firing and thermostat is not satisfied, it should. How
many sq ft and what is your attic insulation. Are the baseboards
retrofit.

  #4   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default Boiler Shuts Down

If I'm reading your post correctly, it sounds like the entire system shuts
down when the boiler reaches 180, which it shouldn't. You have two zones and
I don't know if they are zone valves with one circulator or two circulators
but, in either case, the thermostat should control the circulation of the
hot water, and should keep it circulating until the thermostat is satisfied.



"John F." wrote in message
...
When the outside temps (I'm in upstate NY) get down to the teens and
single digits my boiler can't keep up with the heat loss. There is
baseboard cabinet (7 inch cabinet) running the entire perimeter of the
first floor exterior walls of the four rooms (each 13x13) the zone
covers. The rooms are 8' 9" and all walls are insulated to R-13. The
windows are dbl insulated glass and the basement ceiling below is
insulated as well. The heat pipes are also fully insulated in the
basement. The boiler (oil fired baseboard hot water 2 zone system)
rated at 150,000 btu shuts down when it reaches the 180 deg boiler/water
temp. I've been told that the 180 deg is the proper shut down. The
thermostat calls for heat with a 2 degree drop in temperature. Right now
it only runs for about 10 minutes before it reaches its 180 deg mark and
then shuts down for about 15 mins. The result is a net loss of room
temperature especially at night of upwards of 6 to 8 degrees resulting in
a room temp of 60 to 62 degrees by morning. If temps go into the below
zeros then the boiler never catrhches up even in the daytime. So my
question is what if anything can I do or have the oil burner service
company do to have the burner deliver heat for a longer peiod. Your usual
good input would be appreciated. Thanks. John



  #5   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Boiler Shuts Down

John, it can be tough to tell on some units if the circulator is
running, or not.

If the thermostat is closed, the circ pump should be running, and the
burner itself will run or not as needed to keep the water in the boiler
hot.

The only thing I can add to the replies here is to make sure the
thermostat doesn't have its anticipator set to give absurdly short
cycles.

Don't know how to check it on an electronic thermostat, but on a good
ol' mechanical one remove the cover and look for a little dial in the
middle of the metal coil, and see if its labeled.
If its set far into the 'shorter cycles' zone this could cause the
thermostat to shut off too quickly.
This is actually a little heater that is adjusted such that the
thermostat shuts off as the proper temp is approach so the temp doesn't
overshoot by a wide margin.

Dave



  #6   Report Post  
Posted to alt.home.repair
John F.
 
Posts: n/a
Default Boiler Shuts Down

The radiatorshave been purged they are not retrofits) are pretty hot but
they don't seem excessively hot; don't know if circulator keeps running but
will try and check that. The thing about the circulators though is that
they are the small water lubricated type. Many years ago I had these same
type and they would fail if they weren't used or run periodically during no
heating months. Attic insul is approx. r-25. The upstairs is very warm.
Thanks.


"m Ransley" wrote in message
...
You can raise the boiler temp to 190, the circulator pump could be weak,
but it doesnt sound right, are the radiators extremely hot, have they
been bled of air, does the circulator pump continue to run when the
boiler is not firing and thermostat is not satisfied, it should. How
many sq ft and what is your attic insulation. Are the baseboards
retrofit.



  #7   Report Post  
Posted to alt.home.repair
John F.
 
Posts: n/a
Default Boiler Shuts Down

Thanks for input. That cicrulator is sounding supicious now that it has
come up.
I'm sure the burner people will not like it as my conract includes
circulator replacement. Is there some easily done test without dismantling
system to see if the pump is weak or really bad?


"Speedy Jim" wrote in message
. com...
John F. wrote:
When the outside temps (I'm in upstate NY) get down to the teens and
single digits my boiler can't keep up with the heat loss. There is
baseboard cabinet (7 inch cabinet) running the entire perimeter of the
first floor exterior walls of the four rooms (each 13x13) the zone
covers. The rooms are 8' 9" and all walls are insulated to R-13. The
windows are dbl insulated glass and the basement ceiling below is
insulated as well. The heat pipes are also fully insulated in the
basement. The boiler (oil fired baseboard hot water 2 zone system)
rated at 150,000 btu shuts down when it reaches the 180 deg boiler/water
temp. I've been told that the 180 deg is the proper shut down. The
thermostat calls for heat with a 2 degree drop in temperature. Right now
it only runs for about 10 minutes before it reaches its 180 deg mark and
then shuts down for about 15 mins. The result is a net loss of room
temperature especially at night of upwards of 6 to 8 degrees resulting in
a room temp of 60 to 62 degrees by morning. If temps go into the below
zeros then the boiler never catrhches up even in the daytime. So my
question is what if anything can I do or have the oil burner service
company do to have the burner deliver heat for a longer peiod. Your
usual good input would be appreciated. Thanks. John

It doesn't sound like a burner/boiler problem to me.

If the boiler is easily maintaining ~180F, the problem
seems to be that the circ pump and radiation can't *remove*
enough BTU from the water.

For example: Although the boiler has a rating of 150,000BTU/Hr,
let's say that the rads can only unload 50,000BTU/Hr.
The burner would only need to run 1/3 the time .

But the house needs 100,000BTU/Hr in coldest weather (example).
The boiler *could* produce that easily, but the rads can't
pump the BTU's into the house fast enough. So...house gets cold.

You may have to have someone re-calculate the fin-tube area
required and/or the pump capacity to deliver enough water velocity.

Jim



  #8   Report Post  
Posted to alt.home.repair
John F.
 
Posts: n/a
Default Boiler Shuts Down

There are 2 zones each with it's own circulator and I just noticed up in
the insulation near the boiler on the return side there is a non-electric
flow control valve. If by "the entire system shuts down" you mean the
boiler that is correct.I believe I detect the circulator for the zone
involved running when I place my hand on it. When the boiler temp reaches
180+ boiler shots off and comes back on about 10-15 minutes later as room
temp causes the thermostat to still call for heat. I'm beginning to believe
that the total run of the heat loopis way too long. I don't know what
limitations there should be. A quick calclation gives me 200 plus feet some
of it is 1 and 1/4 inch pipe. The more I examine everything the more
questions I have. Time to make a call. Appeciate exeryone's expertise.
John


"RBM" rbm2(remove wrote in message
...
If I'm reading your post correctly, it sounds like the entire system shuts
down when the boiler reaches 180, which it shouldn't. You have two zones
and I don't know if they are zone valves with one circulator or two
circulators but, in either case, the thermostat should control the
circulation of the hot water, and should keep it circulating until the
thermostat is satisfied.



"John F." wrote in message
...
When the outside temps (I'm in upstate NY) get down to the teens and
single digits my boiler can't keep up with the heat loss. There is
baseboard cabinet (7 inch cabinet) running the entire perimeter of the
first floor exterior walls of the four rooms (each 13x13) the zone
covers. The rooms are 8' 9" and all walls are insulated to R-13. The
windows are dbl insulated glass and the basement ceiling below is
insulated as well. The heat pipes are also fully insulated in the
basement. The boiler (oil fired baseboard hot water 2 zone system)
rated at 150,000 btu shuts down when it reaches the 180 deg boiler/water
temp. I've been told that the 180 deg is the proper shut down. The
thermostat calls for heat with a 2 degree drop in temperature. Right now
it only runs for about 10 minutes before it reaches its 180 deg mark and
then shuts down for about 15 mins. The result is a net loss of room
temperature especially at night of upwards of 6 to 8 degrees resulting in
a room temp of 60 to 62 degrees by morning. If temps go into the below
zeros then the boiler never catrhches up even in the daytime. So my
question is what if anything can I do or have the oil burner service
company do to have the burner deliver heat for a longer peiod. Your
usual good input would be appreciated. Thanks. John





  #9   Report Post  
Posted to alt.home.repair
Edwin Pawlowski
 
Posts: n/a
Default Boiler Shuts Down


"John F." wrote in message
...
The radiatorshave been purged they are not retrofits) are pretty hot but
they don't seem excessively hot; don't know if circulator keeps running
but will try and check that. The thing about the circulators though is
that they are the small water lubricated type. Many years ago I had these
same type and they would fail if they weren't used or run periodically
during no heating months. Attic insul is approx. r-25. The upstairs is
very warm. Thanks.


Circulators do fail and they are about $50 to $70 to replace (for the
parts). One thing that I did not see was if the problem was new or if it
has always been that way. If it is new, I'd suspect poor circulation. If
it has always had lack of heating, I'd suspect poor design of the baseboard
setup. There may be not enough finned sections in each room.


  #10   Report Post  
Posted to alt.home.repair
John F.
 
Posts: n/a
Default Boiler Shuts Down


"Edwin Pawlowski" wrote in message
m...

"John F." wrote in message
...
The radiatorshave been purged they are not retrofits) are pretty hot
but they don't seem excessively hot; don't know if circulator keeps
running but will try and check that. The thing about the circulators
though is that they are the small water lubricated type. Many years ago I
had these same type and they would fail if they weren't used or run
periodically during no heating months. Attic insul is approx. r-25. The
upstairs is very warm. Thanks.


Circulators do fail and they are about $50 to $70 to replace (for the
parts). One thing that I did not see was if the problem was new or if it
has always been that way. If it is new, I'd suspect poor circulation. If
it has always had lack of heating, I'd suspect poor design of the
baseboard setup. There may be not enough finned sections in each room.


Have been in the house only 2 years. I became vaguely aware of the heat
loss last heating season but can't say I was aware of the frequency of
boiler on/off situation. There are no walls left on which to put finned
sections. As I mentioned in one of my replies there is some 200 feet and
more of heat loop but only about 100 feet of that is actual heat fin. The
rest is insulated piping in the unheated basement. I wonder if this length
of run is too long or does it matter. I'm wondering if cutting into the
current run and adding another zone would solve the problem assuming it's
not a cirulator problem.




  #11   Report Post  
Posted to alt.home.repair
Ben
 
Posts: n/a
Default Boiler Shuts Down

Do you have zone valves, or pumps that are controlled by "there should
be 2" thermostats 180 degree temp sounds OK. When the boiler reaches
180 degrees the burner should shut off but the pump or pumps should
stay running until the room temps have reached the setting on the
t-stat. Check to see if the zone valves are open all the way (there is
a dial on the body of each zone valve) so you can open these manually.
The pumps could be bad or the Zone Valves could be bad!!!
Good Luck

  #12   Report Post  
Posted to alt.home.repair
Edwin Pawlowski
 
Posts: n/a
Default Boiler Shuts Down


"John F." wrote in message
...


Have been in the house only 2 years. I became vaguely aware of the heat
loss last heating season but can't say I was aware of the frequency of
boiler on/off situation. There are no walls left on which to put finned
sections.


In most cases, the baseboard enclosure runs the entire lingthof hte wall,
but it mayh only have a portion that is finned, the rest is copper tubing.
The amount of finned tubing is determined by the heat loss calculations done
for each room. You can do more fine tuning of the heat from rom to room by
closing the dampers on roms yo want cooler, thus allowing the temperature of
hte circulating water to remain a bit hotter as it travels to the next room
on the loop. In my case, some of the rooms have only 50% of the sections
finned, the rest plain tubing.


As I mentioned in one of my replies there is some 200 feet and
more of heat loop but only about 100 feet of that is actual heat fin. The
rest is insulated piping in the unheated basement. I wonder if this
length of run is too long or does it matter. I'm wondering if cutting
into the current run and adding another zone would solve the problem
assuming it's not a cirulator problem.


Splitting the run to two zones may help in some cases. The water is giving
heat to the tubing, that is giving heat to the fins, that are giving heat to
the air. As the water runs each foot, it is cooling down. It just may not
be hot enough by the time it gets to the last room. Running a section of
insulated tubing to the further zone will help as it will be a shorter
section.

If the boiler is cycling off and on, it has enough capacity to heat the
house. It is shutting off because it can make more heat than the rest of
the system can take away. Check to see how hot the return pipe is too.

If you are not getting enough heat in the house, the potential problems a
Not enough finned sections of baseboard
Missing or insufficient insulation.
Poor or no circulation (some circulators have speed controls so check for
them)
Poor layout of the zones


  #13   Report Post  
Posted to alt.home.repair
John F.
 
Posts: n/a
Default Boiler Shuts Down

Thanks for all the input. All the tubing is finned except of course what's
in the basement. I'm calling the oil company and will have them come and
test circulator and review the system so that by next winter's major heating
need I will be OK and maybe get some benefit this season.


"Edwin Pawlowski" wrote in message
et...

"John F." wrote in message
...


Have been in the house only 2 years. I became vaguely aware of the heat
loss last heating season but can't say I was aware of the frequency of
boiler on/off situation. There are no walls left on which to put finned
sections.


In most cases, the baseboard enclosure runs the entire lingthof hte wall,
but it mayh only have a portion that is finned, the rest is copper tubing.
The amount of finned tubing is determined by the heat loss calculations
done for each room. You can do more fine tuning of the heat from rom to
room by closing the dampers on roms yo want cooler, thus allowing the
temperature of hte circulating water to remain a bit hotter as it travels
to the next room on the loop. In my case, some of the rooms have only 50%
of the sections finned, the rest plain tubing.


As I mentioned in one of my replies there is some 200 feet and
more of heat loop but only about 100 feet of that is actual heat fin.
The rest is insulated piping in the unheated basement. I wonder if this
length of run is too long or does it matter. I'm wondering if cutting
into the current run and adding another zone would solve the problem
assuming it's not a cirulator problem.


Splitting the run to two zones may help in some cases. The water is
giving heat to the tubing, that is giving heat to the fins, that are
giving heat to the air. As the water runs each foot, it is cooling down.
It just may not be hot enough by the time it gets to the last room.
Running a section of insulated tubing to the further zone will help as it
will be a shorter section.

If the boiler is cycling off and on, it has enough capacity to heat the
house. It is shutting off because it can make more heat than the rest of
the system can take away. Check to see how hot the return pipe is too.

If you are not getting enough heat in the house, the potential problems
a
Not enough finned sections of baseboard
Missing or insufficient insulation.
Poor or no circulation (some circulators have speed controls so check for
them)
Poor layout of the zones



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New condensing boiler installation - truth or lies Martin Evans UK diy 57 July 2nd 05 03:13 PM
Condensing Boiler News RedOnRed UK diy 0 April 9th 05 06:37 PM
Mixing header and pumps John Aston UK diy 79 December 8th 04 10:50 AM
Noisy banging boiler what is the cause? Tim UK diy 8 November 3rd 04 10:36 PM
Boiler problem - hot water, cold radiators Dan the man UK diy 9 October 8th 03 12:26 AM


All times are GMT +1. The time now is 11:46 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"