Honda eu 2000 Generator
Vaughn wrote:
After reading lhiggin's description of how to parallel these Hondas, I wonder if we could easily plug one into a wall socket with a variac to control the backwards grid meter speed :-) You first! I don't own one, but it seems safe enough, with a variac hooked up as an autotransformer and 2 light bulbs in series. If it syncs, the bulbs should be dark. Viewed in a fixed font: --------------sC----B---B------- | | C wall | Honda | C socket | | C -------------------------------- Moving the variac slider s downwards should make the bulbs light again. Then short out one bulb, then the other, put a Kill-a-Watt meter into the Honda socket, and run the exhaust into the 1/2" gas pipe of a $200 upside-down water heater, after removing the thermostat innards. Nick |
#2
Posted to alt.home.repair
|
|||
|
|||
Honda eu 2000 Generator
Try it nick , be the test monkey for 3000$ worth of goods, 1/2 inch
gas line wll restrict the motor to maybe 50% power. |
#3
Posted to alt.home.repair
|
|||
|
|||
Honda eu 2000 Generator
m Ransley wrote:
... 1/2 inch gas line wll restrict the motor to maybe 50% power. Would you have any evidence for this article of faith? Nick |
#4
Posted to alt.home.repair
|
|||
|
|||
Honda eu 2000 Generator
Sure nick call HONDA, and quit posting crap that can ruin a gen, yea
call Honda on that to. |
#5
Posted to alt.home.repair
|
|||
|
|||
Honda eu 2000 Generator
m Ransley errs again:
Sure nick call HONDA, Did that. Not much help. and quit posting crap that can ruin a gen... Ah, so you DON'T have any evidence for your article of faith. Just more smoke out your rear end, as usual. Ever tried thinking when posting? :-) Small Hondas have small exhaust ports. A 1/2" pipe would probably work. If it doesn't, removing the muffler and running the exhaust into the 3" top of a gas water heater should not be a problem. That would make more efficient counterflow heat exchange. What's your cogen experience? I did my first system in Doylestown, PA 15 years ago. PECO took a year to approve my permit. It's still running. Just got a fax inviting Pine Associates, Ltd. to submit a proposal for a system for the city of Norwalk, CN. They estimate $800K, for 400 Honda EU2000s and gas water heaters? :-) http://www.bid.ci.norwalk.ct.us. Nick |
#6
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
What is this in response to?
It sounds interesting, but I didn't see the front end.
I did a google search, but came up with just this. |
#7
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
What is this in response to?
Toller wrote:
It sounds interesting, but I didn't see the front end. I did a google search, but came up with just this. OK, so you replied to an existing post, didn't quote anything _and_ changed the subject, and you expect anyone to know what you're talking about? fwiw, having a newsreader that does real threading, it's related to Honda EU2000 generators - but since that was the subject of the message you replied to, you should know that. -- derek |
#8
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
What is this in response to?
"Derek Broughton" wrote in message ... Toller wrote: It sounds interesting, but I didn't see the front end. I did a google search, but came up with just this. OK, so you replied to an existing post, didn't quote anything _and_ changed the subject, and you expect anyone to know what you're talking about? fwiw, having a newsreader that does real threading, it's related to Honda EU2000 generators - but since that was the subject of the message you replied to, you should know that. -- You have a point; those people who don't have the whole thread will find my post to be nonsense. But those people couldn't answer my question anyhow. |
#9
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
What is this in response to?
"Toller" wrote:
"Derek Broughton" wrote in message ... Toller wrote: It sounds interesting, but I didn't see the front end. I did a google search, but came up with just this. OK, so you replied to an existing post, didn't quote anything _and_ changed the subject, and you expect anyone to know what you're talking about? fwiw, having a newsreader that does real threading, it's related to Honda EU2000 generators - but since that was the subject of the message you replied to, you should know that. -- You have a point; those people who don't have the whole thread will find my post to be nonsense. But those people couldn't answer my question anyhow. It isn't all about you. *plonk* |
#10
Posted to alt.home.repair
|
|||
|
|||
Honda eu 2000 Generator
Running 1/2" pipe is to small, there is increased resistance with
increased length of exuast, figure 4-7 elbows to pipe it through that will increase resistance, back pressure and increased head temps come into play. Increase back pressure and lower hp. The honda is already choked down so much you can hardly hear it run, lower hp on a 2000w unit, its already under powered for most users. Just hook up a pipe you say, what about water collecting at the low point and choking the motor off, or water dripping back into the cilinder, not good, you can ruin your motor. There will be water as the vertical rise cools. Just a few things to consider and why 1/2" won`t work. |
#11
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
I looked at an EU200i today. The exhaust port ID is about 0.7" into the
muffler, which attaches with a standard looking flange with two metric bolts. The pipe out of the muffler is about half that diameter. It burns 1.08 gallons of gasoline with a fuel value of 123.1K Btu in 4 hours at the 1600 W rated load, so it makes 6.4 kWh (21.8K Btu) of electricity and 101.3K Btu of heat (another 29.7 kWh), ie 36.1 kWh total, if it replaces electric resistance heating. So cogen makes economic sense at a gasoline price of $2/gallon if electricity costs more than 100x$2/36.1 = 5.5 cents/kWh, in simple terms. The ground isn't bonded to the neutral, with 60 volts from each pin to neutral, so a grounded plug into a wall socket would damage the inverter, so it needs to float or use an external isolation transformer. Nick |
#12
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
What is this in response to?
Don't troll
"Derek Broughton" wrote in message ... fwiw, having a newsreader that does real threading, it's related to Honda EU2000 generators - but since that was the subject of the message you replied to, you should know that. -- derek |
#13
Posted to alt.home.repair
|
|||
|
|||
Honda eu 2000 Generator
m Ransley wrote:
Running 1/2" pipe is to small... I disagree, but the pipe could easily be larger. ... what about water collecting at the low point The pipe would go to the top of the water heater, then back down through the 3" vent. Water would condense in the downward path and leave via a pinhole, but it wouldn't condense on the way up, because of the higher temperature. Nick |
#15
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
danny burstein wrote:
The ground isn't bonded to the neutral, with 60 volts from each pin to neutral, so a grounded plug into a wall socket would damage the inverter, so it needs to float or use an external isolation transformer. whoa.... are you saying it's a "double hot" outlet? We might call it that. Nick |
#16
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
wrote in message ... The ground isn't bonded to the neutral, with 60 volts from each pin to neutral, so a grounded plug into a wall socket would damage the inverter, so it needs to float or use an external isolation transformer. Nonsense. I plug mine into my transfer panal all the time. Vaughn |
#17
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
Vaughn wrote:
The ground isn't bonded to the neutral, with 60 volts from each pin to neutral, so a grounded plug into a wall socket would damage the inverter, so it needs to float or use an external isolation transformer. Nonsense. I plug mine into my transfer panal all the time. Hmmm. I'll check further. I got this from Maurice Higgins, who put those homemade parallel cable pictures on the web site. And IIRC, the EU2000 user's manual mentions this... Then again, PECO's off-peak rate is about 6 cents./kWh, so 5.5 isn't a big savings. Maybe the gas water heater should be part of a woodstove chimney, with a draft suction fan at the bottom and 3" galvanized pipe popped into the flue with the edges unsnapped to lessen liquid creosote corrosion. Nick |
#18
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
Vaughn wrote:
The ground isn't bonded to the neutral, with 60 volts from each pin to neutral, so a grounded plug into a wall socket would damage the inverter, so it needs to float or use an external isolation transformer. Nonsense. I plug mine into my transfer panal all the time. Hmmm... IIRC, the EU2000 user's manual mentions this... I stand corrected. The note on page 14 of the on-line user's manual says the receptacle grounds are connected to the frame, and the wiring diagram on page 54 shows that, but I couldn't find any warning not to connect the rectangular pins to the ground, and Vaughn does this, so it seems OK :-) Nick |
#19
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
wrote in message ... Vaughn wrote: The ground isn't bonded to the neutral, with 60 volts from each pin to neutral, so a grounded plug into a wall socket would damage the inverter, so it needs to float or use an external isolation transformer. Nonsense. I plug mine into my transfer panal all the time. Hmmm... IIRC, the EU2000 user's manual mentions this... I stand corrected. The note on page 14 of the on-line user's manual says the receptacle grounds are connected to the frame, and the wiring diagram on page 54 shows that, but I couldn't find any warning not to connect the rectangular pins to the ground, and Vaughn does this, so it seems OK :-) Nick Best if the neutral and ground are tied together at one location. The ground is a saftey item. Neutral is designed to carry the current. House wiring, the ground and neutral are tied together at the entrance panel. No where else. |
#20
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
wrote in message ... I stand corrected. The note on page 14 of the on-line user's manual says the receptacle grounds are connected to the frame, and the wiring diagram on page 54 shows that, but I couldn't find any warning not to connect the rectangular pins to the ground, and Vaughn does this, so it seems OK :-) I think there may have been such an issue with the early versions of the inverter generators. Anyhow, page 18 specifically addresses connecting the generator to a building electrical system. Basically, it just tells you to use a transfer panel. Since the neutral is not connected to the ground internally in the generator (also P. 18) you may measure virtually anything (or nothing) from either power terminal to ground if you are using a sensitive meter. To see if that voltage is "real" (and not just a bit of leakage) use an incandescent test lamp instead of a meter. Vaughn Nick |
#21
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
"Vaughn" wrote in
: wrote in message ... The ground isn't bonded to the neutral, with 60 volts from each pin to neutral, so a grounded plug into a wall socket would damage the inverter, so it needs to float or use an external isolation transformer. Nonsense. I plug mine into my transfer panal all the time. Vaughn My little Yamaha plugs into my transfer panel also, and lives to generate another day, those cheap inverters on the other hand........... Rob |
#22
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
"Rob" wrote in message .. . My little Yamaha plugs into my transfer panel also, and lives to generate another day, those cheap inverters on the other hand........... Yes, as far as I know Yamaha makes a great inverter generator. You, on the other hand....... |
#23
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
I doubt it. Did you use a 10 megohm input impedance
voltmeter to measure it? wrote in message ... danny burstein wrote: The ground isn't bonded to the neutral, with 60 volts from each pin to neutral, so a grounded plug into a wall socket would damage the inverter, so it needs to float or use an external isolation transformer. whoa.... are you saying it's a "double hot" outlet? We might call it that. Nick |
#24
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
wrote in message ... Vaughn wrote: The ground isn't bonded to the neutral, with 60 volts from each pin to neutral, so a grounded plug into a wall socket would damage the inverter, so it needs to float or use an external isolation transformer. Nonsense. I plug mine into my transfer panal all the time. Hmmm... IIRC, the EU2000 user's manual mentions this... I stand corrected. The note on page 14 of the on-line user's manual says the receptacle grounds are connected to the frame, and the wiring diagram on page 54 shows that, but I couldn't find any warning not to connect the rectangular pins to the ground, and Vaughn does this, so it seems OK :-) For a lot of 'temporary' power sources that are meant to be connected into a regular utility fed service panel, it is common to leave the 'ground' and 'neutral' separated by the manufacturer. This gives you the most flexible configuration. In some code installations, the ground is tied to the service panel ground, and the neutral tied just to the panel neutral. And then the two are tied together in the service panel only. This type of connection allows for three-conductor transfer switch that switches two 'hots' and the neutral between grid and emergency power source. If the local power source has the neutral tied to ground at the generator/inverter, then when connected to the main service panel you have two ground-neutral ties (one at source, one at panel) and that's generally a bad thing. If the local generator/inverter is meant to be the sole source of power, then it can have neutral and ground tied at the source. It all varies with whether the inverter feeds the main panel or a sub-panel, whether it's the sole power source or there's a transfer switch from grid power, etc... With an output that is isolated from the ground, it isn't unusual to read about 1/2 the voltage output between 'hot' and a ground, but the exact reading depends on the meter and amount of circuitry. It's really just a form of 'leakage' and not a 'hard' reading. daestrom |
#25
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
Rich256 wrote:
wrote in message Vaughn wrote: Nonsense. I plug mine into my transfer panal all the time. Hmmm... IIRC, the EU2000 user's manual mentions this... I stand corrected. The note on page 14 of the on-line user's manual says the receptacle grounds are connected to the frame, and the wiring diagram on page 54 shows that... Best if the neutral and ground are tied together at one location. The ground is a saftey item. Neutral is designed to carry the current. Maurice Riggins adds: Well... it's like I said... if you're reading 60V on the neutral line with respect to ground, would YOU connect neutral to ground? Remember that the neutral side of the EU output is unfused. Although the EU manual shows the wiring diagram, it doesn't show you what's in the inverter. That Vaughn is able to get away with shorting the 60V neutral to ground, and apparently then getting 120V instead of 60V on the hot side WRT ground, indicates the output is probably already transformer coupled in the inverter. I wouldn't have considered that a safe assumption to make. Nick |
#26
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
wrote in message ... Rich256 wrote: Maurice Riggins adds: Well... it's like I said... if you're reading 60V on the neutral line with respect to ground, would YOU connect neutral to ground? Remember that the neutral side of the EU output is unfused. Although the EU manual shows the wiring diagram, it doesn't show you what's in the inverter. That Vaughn is able to get away with shorting the 60V neutral to ground, and apparently then getting 120V instead of 60V on the hot side WRT ground, indicates the output is probably already transformer coupled in the inverter. I wouldn't have considered that a safe assumption to make. I made no assumptions. I simply took the time to read the manual. As both I and another poster pointed out, you are reading a leakage voltage because the ground is not referenced to the hot or neutral. You need to add a load to get a correct reading. Vaughn |
#27
Posted to alt.home.repair,alt.energy.homepower
|
|||
|
|||
Honda eu 2000 Generator
"Vaughn" wrote in message ... wrote in message ... Rich256 wrote: Maurice Riggins adds: Well... it's like I said... if you're reading 60V on the neutral line with respect to ground, would YOU connect neutral to ground? Remember that the neutral side of the EU output is unfused. Although the EU manual shows the wiring diagram, it doesn't show you what's in the inverter. That Vaughn is able to get away with shorting the 60V neutral to ground, and apparently then getting 120V instead of 60V on the hot side WRT ground, indicates the output is probably already transformer coupled in the inverter. I wouldn't have considered that a safe assumption to make. I made no assumptions. I simply took the time to read the manual. As both I and another poster pointed out, you are reading a leakage voltage because the ground is not referenced to the hot or neutral. You need to add a load to get a correct reading. Vaughn Correct. Since the ground is attached to the frame that means all the metal structure around the inverter is tied to that wire. If a high value resistor were tied between the ground and neutral the reading to the ground would most likely disappear. Just something to bleed off the induced voltage. As someone else said they are not tied together in the generator to avoid a double ground when tied into another system. It's too cold or I would fire up my generator and see what it reads. This does bring up an interesting subject in that when an RV is plugged into the generator the ground is still floating. RVs do not tie their grounds and return either. Well, not usually. If they do they often can't plug into many campground systems because the CGs use ground fault detectors. If the ground and return are tied together some current will flow in both wires tripping the detector. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Northstar 8000 W Honda generator, feedback | Home Repair | |||
Water heater wiring for generator hookup and to 120 VAC power? | Home Repair | |||
Repairing a Honda eu2000 Generator | Home Repair | |||
Honda Generator Service Bulletin #20 | Home Repair | |||
Generator FAQ | Metalworking |