Lacustral wrote:

I'd like to use an exhaust fan (fan from a ceiling grille to outside) to
run overnight in the summer, with the windows open, so that my house is cool
in the morning. I'm not sure how much CFM is needed.


That depends on where you live and the house thermal mass and insulation
and how cool you want it. Whole house fans can work almost as well as AC
for all but a few days per year near Philadelphia. NREL says June has
average daily min and max temps of 61.8 and 81.7 F. July is the warmest
month, with 67.2 and 86.1 and humidity ratio w = 0.0133 pounds of water
per pound of dry air. An indoor fan or a window AC for dehumidification
can help ensure comfort in July.

I don't want a big powerful whole house fan because I'd like it to be
quiet. Just a small fan that keeps running overnight.


But you may need a large fan. Lasko's 2155A 16" window box fan has
a thermostat and sliding mounts to fit windows and it's efficient,
moving 2470 cfm with 90 watts on the highest of 3 speeds, and it's
fairly quiet. About $50 at ACE Hardware stores.

A house with an open window or two upstairs is a natural cool air trap.
At night, warm house air will rise up out of the window and cooler night
air will slide in and replace it. During the day, air stops moving. More
air and heat can flow with a fan that runs at night, eg an upstairs window
with a 1-way damper outside (eg plastic film, hinged at the top edge) and
an downstairs window with a damper inside and a differential thermostat or
an outdoor 70 F thermostat that runs the fan when outdoor air is cooler.

... can you tell me how much CFM gets your house down to the temperature
of the outside air


It can never reach the daily min, but a larger fan can keep it closer.
A Q cfm fan is like a 1/Q F-h/Btu thermal resistor or a Q Btu/h-F conductor
between outdoor air and the house mass. This may be the bottleneck, if the
exposed mass surface is large, with a 1.5 Btu/h-F-ft^2 airfilm conductance.

(I could calculate the cubic feet of airspace in my house, divide by CFM
of a fan, and come up with a guess, but I'm sure it's not that simple -
the hot stuff in the house is heating up the air, fans aren't completely
efficient about clearing out the inside air, etc.)


If a house has infinite thermal mass (most don't :-) and G Btu/h-F of
conductance and a Q cfm fan and a constant indoor temp Ti and 8-hour night
and 16-hour day temps Tn and Td and the fan moves 8Q(Ti-Tn) Btu at night
and the house gains 16(Td-Ti)G Btu/h during the day and these heatflows
are equal, Ti = (QTn+2GTd)/(Q+2G), approximately.

For example, G = 800 and Q = 100 and Ti = 80 and Tn = 70 makes
Ti = (100x70+2x800x80)/(100+1600) = 79.4. G = 400 and Q = 2470 makes
Ti = (2470x70+2x400x80)/(2470+800) = 72.4.

We might model a house with C Btu/h of thermal mass and G Btu/h-F of
conductance and a Q cfm fan and Tmin and Tmax indoor temps like this,
viewed in a fixed font like Courier:

1/Q (closed at night)
---www--- \---
| | --------------
| 1/G | Tmax . . .
Tn/Td ---------www--------*--- Tmin/Tmax . . .
| Tmin . .
| ------- -------
--- C night day
---
|
|
-

RCn = C/(Q+G) and RCd = C/G and Tmin=Tn+(Tmax-Tn)e^(-8/RCn) and
Tmax = Td+(Tmin-Td)e^(-16/RCd), and Tmin = [Tn+(Td-Tn)e^(-8/RCn)
-Tde^(-16/RCd-8/RCn)]/(1-e^(-16/RCd-8/RCn), if I did that right.

For example, C = 6000 and G = 400 and Q = 2470 and Ti = 80 and
Tn = 70 makes RCn = 2.1 hours and RCd = 15 hours, so...

20 C=6000'house thermal mass (Btu/F)
30 G=400'house conductance (Btu/h-F)
40 Q=2470'fan cfm
50 RCN=C/(G+Q)'night time constant (hours)
60 RCD=C/G'day time constant (hours)
70 TN=70'night temp (F)
80 TD=80'day temp (F)
90 TMIN=(TN+(TD-TN)*EXP(-8/RCN)-TD*EXP(-16/RCD-8/RCN))/(1-EXP(-16/RCD-8/RCN))
100 TMAX=TD+(TMIN-TD)*EXP(-16/RCD)
110 PRINT TMIN,TMAX'min and max indoor temps (F)

70.14393 76.608

Nick

  #2   Report Post  
Posted to alt.home.repair,alt.building.construction,misc.consumers.house
 
Posts: n/a
Default fanpower needed to cool house overnight

Just for the record -- I have ~1600 sq. ft. in two stories. At night,
I put a box fan in one window, set on medium, blowing out. It matches
the window size almost exactly, so I don't bother to block the sides.
It is in a spare upstairs bedroom. By the time I walk back into my
bedroom, also upstairs, I can already feel the difference in temp. I
don't know how long it takes, since I just leave it on all night, but
when I get up in the morning, the entire house is cool.

Sometimes simple solutions will get you where you want to go.

Jo Ann

wrote:
Lacustral wrote:

I'd like to use an exhaust fan (fan from a ceiling grille to outside) to
run overnight in the summer, with the windows open, so that my house is cool
in the morning. I'm not sure how much CFM is needed.


That depends on where you live and the house thermal mass and insulation
and how cool you want it. Whole house fans can work almost as well as AC
for all but a few days per year near Philadelphia. NREL says June has
average daily min and max temps of 61.8 and 81.7 F. July is the warmest
month, with 67.2 and 86.1 and humidity ratio w = 0.0133 pounds of water
per pound of dry air. An indoor fan or a window AC for dehumidification
can help ensure comfort in July.

I don't want a big powerful whole house fan because I'd like it to be
quiet. Just a small fan that keeps running overnight.


But you may need a large fan. Lasko's 2155A 16" window box fan has
a thermostat and sliding mounts to fit windows and it's efficient,
moving 2470 cfm with 90 watts on the highest of 3 speeds, and it's
fairly quiet. About $50 at ACE Hardware stores.

A house with an open window or two upstairs is a natural cool air trap.
At night, warm house air will rise up out of the window and cooler night
air will slide in and replace it. During the day, air stops moving. More
air and heat can flow with a fan that runs at night, eg an upstairs window
with a 1-way damper outside (eg plastic film, hinged at the top edge) and
an downstairs window with a damper inside and a differential thermostat or
an outdoor 70 F thermostat that runs the fan when outdoor air is cooler.

... can you tell me how much CFM gets your house down to the temperature
of the outside air


It can never reach the daily min, but a larger fan can keep it closer.
A Q cfm fan is like a 1/Q F-h/Btu thermal resistor or a Q Btu/h-F conductor
between outdoor air and the house mass. This may be the bottleneck, if the
exposed mass surface is large, with a 1.5 Btu/h-F-ft^2 airfilm conductance.

(I could calculate the cubic feet of airspace in my house, divide by CFM
of a fan, and come up with a guess, but I'm sure it's not that simple -
the hot stuff in the house is heating up the air, fans aren't completely
efficient about clearing out the inside air, etc.)


If a house has infinite thermal mass (most don't :-) and G Btu/h-F of
conductance and a Q cfm fan and a constant indoor temp Ti and 8-hour night
and 16-hour day temps Tn and Td and the fan moves 8Q(Ti-Tn) Btu at night
and the house gains 16(Td-Ti)G Btu/h during the day and these heatflows
are equal, Ti = (QTn+2GTd)/(Q+2G), approximately.

For example, G = 800 and Q = 100 and Ti = 80 and Tn = 70 makes
Ti = (100x70+2x800x80)/(100+1600) = 79.4. G = 400 and Q = 2470 makes
Ti = (2470x70+2x400x80)/(2470+800) = 72.4.

We might model a house with C Btu/h of thermal mass and G Btu/h-F of
conductance and a Q cfm fan and Tmin and Tmax indoor temps like this,
viewed in a fixed font like Courier:

1/Q (closed at night)
---www--- \---
| | --------------
| 1/G | Tmax . . .
Tn/Td ---------www--------*--- Tmin/Tmax . . .
| Tmin . .
| ------- -------
--- C night day
---
|
|
-

RCn = C/(Q+G) and RCd = C/G and Tmin=Tn+(Tmax-Tn)e^(-8/RCn) and
Tmax = Td+(Tmin-Td)e^(-16/RCd), and Tmin = [Tn+(Td-Tn)e^(-8/RCn)
-Tde^(-16/RCd-8/RCn)]/(1-e^(-16/RCd-8/RCn), if I did that right.

For example, C = 6000 and G = 400 and Q = 2470 and Ti = 80 and
Tn = 70 makes RCn = 2.1 hours and RCd = 15 hours, so...

20 C=6000'house thermal mass (Btu/F)
30 G=400'house conductance (Btu/h-F)
40 Q=2470'fan cfm
50 RCN=C/(G+Q)'night time constant (hours)
60 RCD=C/G'day time constant (hours)
70 TN=70'night temp (F)
80 TD=80'day temp (F)
90 TMIN=(TN+(TD-TN)*EXP(-8/RCN)-TD*EXP(-16/RCD-8/RCN))/(1-EXP(-16/RCD-8/RCN))
100 TMAX=TD+(TMIN-TD)*EXP(-16/RCD)
110 PRINT TMIN,TMAX'min and max indoor temps (F)

70.14393 76.608

Nick


  #3   Report Post  
Posted to alt.home.repair,alt.building.construction,misc.consumers.house
 
Posts: n/a
Default fanpower needed to cool house overnight

No, I don't know, sorry. It's a 20-inch fan, the cheapo kind that goes
on sale at the hardware store for $12.97. Plastic housing, plastic
blades. Nothing very special about it, but it works just great for
exhausting the hot air and pulling in the cool air.

Jo Ann

Lacustral wrote:
) wrote:
Just for the record -- I have ~1600 sq. ft. in two stories. At night,
I put a box fan in one window, set on medium, blowing out. It matches
the window size almost exactly, so I don't bother to block the sides.
It is in a spare upstairs bedroom. By the time I walk back into my
bedroom, also upstairs, I can already feel the difference in temp. I
don't know how long it takes, since I just leave it on all night, but
when I get up in the morning, the entire house is cool.


Do you know how many CFM your box fan is?

Thanks
Laura


  #4   Report Post  
Posted to alt.home.repair,alt.building.construction,misc.consumers.house
Una
 
Posts: n/a
Default fanpower needed to cool house overnight

A key point that seems to need underlining here is that there
are two elements. The air exhaust (via fan), and air *intake*.
You can put in a humongous monster of a fan but if you don't
open enough windows and interior doors throughout the house,
the fan cannot get enough house air to exchange hence cannot
cool the house. This is especially true in a newer, "buttoned
up" heating/AC efficient house.

Also, a good reason to install a whole house fan in an attic
gable end (if you have one) is so that you have the choice of
running the fan to cool just the attic (indirectly cooling
the house, but with less perceptible noise and no draft), or
to cool the whole house directly, by opening the attic door,
selected windows, and interior doors (especially the bedroom
doors).

Catalogs (and websites) that specialize in farming equipment
usually include a huge selection of ventilation fans.

Una
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
fanpower needed to cool house overnight Bill Gill Home Repair 1 June 6th 06 07:37 PM
fanpower needed to cool house overnight Alec Home Repair 2 June 6th 06 04:03 PM
fanpower needed to cool house overnight Joseph Meehan Home Repair 0 June 6th 06 03:00 AM
Curb Appeal Ideas Needed For Lake House Renovation BettyM Home Repair 9 November 21st 05 06:31 PM
Buying house with no Central AC. Info needed. [email protected] Home Repair 14 March 22nd 05 04:04 PM


All times are GMT +1. The time now is 10:16 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"