Default Flickering Ceiling Lights

Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?

Thanks fellers!

Bob


Attached Thumbnails
Flickering Ceiling Lights-cbpanel-gif  
  #2   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic
external usenet poster
 
Posts: 575
Default Flickering Ceiling Lights

"Guv Bob" wrote in message m...
Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?

Thanks fellers!

Bob

===

PS -- I overlooked something important.... CB #9, receptacle near the door has a lamp plugged into it and it also flickers when the ceiling lights do. So that probably eliminates CB 1&3 as the problem. Also, it might be good to say that no appliances or heavy power users are running at the time of the flickering. I have looked for a common activity, but they flicker night or day, and whether anything else is running or not.

Thanks again.

  #3   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic
external usenet poster
 
Posts: 331
Default Flickering Ceiling Lights

On 2014-04-20, Guv Bob wrote:
"Guv Bob" wrote in message m...
Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?


Perhaps a loose screw in one of the holes of the neutral bus bar.



--
umop apisdn

  #4   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 4,045
Default Flickering Ceiling Lights

On Sun, 20 Apr 2014 07:53:55 -0800, "Guv Bob"
wrote:

"Jasen Betts" wrote in message ...
Perhaps a loose screw in one of the holes of the neutral bus bar.


Thanks Jason. I just now checked and all are snug. I'm thinking about moving
the 2 ceiling light CB's over to the other hot bar and try to isolate it that way.


I would also check for an intermittent circuit breaker.

If nothing obvious appears (like a circuit breaker on fire, smoking,
or cracked housing), put a clamp on ammeter on the wire to the
flickering circuit and see if you can detect the flickering. Testing
will take two people. Station one at the breaker box and have them
watch the ammeter. Follow the wiring around the house until you find
the bad connection by wiggling the wiring and wall jacks. My
guess(tm) is a junction box in the ceiling or under the floor, where
the wires are connected with electrical tape instead of wire nuts or
screw terminals.

If you do find tape, I strongly suggest you hire an electrician to
inspect your wiring as other such abominations may be lurking in the
wiring.

This is what you do NOT want to see:
http://diy.stackexchange.com/questions/2032/is-this-electrical-junction-up-to-code


--
Jeff Liebermann
150 Felker St #D
http://www.LearnByDestroying.com
Santa Cruz CA 95060 http://802.11junk.com
Skype: JeffLiebermann AE6KS 831-336-2558
  #5   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 575
Default Flickering Ceiling Lights

"Jasen Betts" wrote in message ...
On 2014-04-20, Guv Bob wrote:
"Guv Bob" wrote in message m...
Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?


Perhaps a loose screw in one of the holes of the neutral bus bar.


Thanks Jason. I just now checked and all are snug. I'm thinking about moving the 2 ceiling light CB's over to the other hot bar and try to isolate it that way.




  #6   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 15
Default Flickering Ceiling Lights

On 4/20/2014 8:25 AM, Jeff Liebermann wrote:


If you do find tape, I strongly suggest you hire an electrician to
inspect your wiring as other such abominations may be lurking in the
wiring.

This is what you do NOT want to see:
http://diy.stackexchange.com/questions/2032/is-this-electrical-junction-up-to-code


I'll see that and raise this:
https://www.youtube.com/watch?v=XKZU...layer_embedded

  #7   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 8,582
Default Flickering Ceiling Lights

On Sun, 20 Apr 2014 08:25:32 -0700, Jeff Liebermann
wrote:



This is what you do NOT want to see:
http://diy.stackexchange.com/questions/2032/is-this-electrical-junction-up-to-code

I like the way the yellow and orange picks up the copper color. It's
very attractive.
  #8   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 2,181
Default Flickering Ceiling Lights

On Sun, 20 Apr 2014 14:14:41 -0400, micky
wrote:

On Sun, 20 Apr 2014 08:25:32 -0700, Jeff Liebermann
wrote:



This is what you do NOT want to see:
http://diy.stackexchange.com/questions/2032/is-this-electrical-junction-up-to-code

I like the way the yellow and orange picks up the copper color. It's
very attractive.


Most of those "for-hire" home inspectors, that _buyers_ (fortunately
:-) pay for, can't even find the right end of a flashlight.

...Jim Thompson
--
| James E.Thompson | mens |
| Analog Innovations | et |
| Analog/Mixed-Signal ASIC's and Discrete Systems | manus |
| San Tan Valley, AZ 85142 Skype: Contacts Only | |
| Voice480)460-2350 Fax: Available upon request | Brass Rat |
| E-mail Icon at http://www.analog-innovations.com | 1962 |

I love to cook with wine. Sometimes I even put it in the food.
  #9   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 4,045
Default Flickering Ceiling Lights

On Sun, 20 Apr 2014 11:05:28 -0700, RosemontCrest
wrote:

On 4/20/2014 8:25 AM, Jeff Liebermann wrote:
If you do find tape, I strongly suggest you hire an electrician to
inspect your wiring as other such abominations may be lurking in the
wiring.

This is what you do NOT want to see:
http://diy.stackexchange.com/questions/2032/is-this-electrical-junction-up-to-code


I should mention that you can also do it wrong without the electrical
tape:
http://inspectapedia.com/electric/LowVoltageGERelayBox020DFs.jpg
http://inspectapedia.com/electric/Electrical_Inspector_Safety.htm

Hint: If you have an IR thermometer, use it to measure the
temperature of your circuit breakers. I had a problem at a rental
that I found that way. The breaker looked ok, but it wasn't. I've
also used an IR thermometer to test the integrity of low voltage high
current solar panel wiring and battery banks:
https://www.youtube.com/watch?v=SBAZ2UPheGQ

I'll see that and raise this:
https://www.youtube.com/watch?v=XKZU...layer_embedded


That's pretty bad. The #16awg(?) extension cord at the end is the
best part. Looking at the garage, I would guess that it's new
construction, probably added without the benefit of a building permit.

Many more of the same:
https://www.google.com/search?tbm=isch&q=bad+electrical+wiring
Perhaps we have an epidemic of bad wiring?

Why the OP expected to find advice on electrical wiring in two
electronics newsgroups will remain a mystery.

--
Jeff Liebermann
150 Felker St #D
http://www.LearnByDestroying.com
Santa Cruz CA 95060 http://802.11junk.com
Skype: JeffLiebermann AE6KS 831-336-2558
  #10   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic
external usenet poster
 
Posts: 8
Default Flickering Ceiling Lights

On 4/19/2014 11:12 PM, Guv Bob wrote:
Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?

Thanks fellers!

Bob


You have this:

Phase A hot ---CB----+---+--}}}---+
| | |
CL CL CL
| | |
Neutral -------------+---+--}}}---+
| | |
CL Cl Cl
| | |
Phase B hot ---CB----+---+--}}}---+

(CL = Ceiling Light, CB = circuit breaker. Switches omitted
for clarity.)

It's a shared neutral circuit, and is allowed by the USA
National electrical code.

Your symptom strongly suggests a loose connection in
the neutral path.

Ed


  #11   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 575
Default Flickering Ceiling Lights

"ehsjr" wrote in message ...
On 4/19/2014 11:12 PM, Guv Bob wrote:
Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?

Thanks fellers!

Bob


You have this:

Phase A hot ---CB----+---+--}}}---+
| | |
CL CL CL
| | |
Neutral -------------+---+--}}}---+
| | |
CL Cl Cl
| | |
Phase B hot ---CB----+---+--}}}---+

(CL = Ceiling Light, CB = circuit breaker. Switches omitted
for clarity.)

It's a shared neutral circuit, and is allowed by the USA
National electrical code.

Your symptom strongly suggests a loose connection in
the neutral path.

Ed


Thanks, Ed. That sounds reasonable to me. I'll check it out. All the flickering is on Phase A lights & receptacles. They all flicker at the same time. I called the power company today and they will send someone out this week to check the line up to the CP panel.

  #12   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 575
Default Flickering Ceiling Lights

"Jeff Liebermann" wrote in message

Why the OP expected to find advice on electrical wiring in two
electronics newsgroups will remain a mystery.


I know what you're saying. If there is a more appropriate usenet group please let me know. The only other one I could find was "alt.trades.electrician" which has not been active since 2012.

It's hard to tell from the names which groups people hang around. I recently had some questions about an automobile computer/electrical issue. These 3 groups had a lot of good advice. Hardly anything from the auto and computer groups.

  #13   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 367
Default Flickering Ceiling Lights

On Mon, 21 Apr 2014 16:46:48 -0800, "Guv Bob"
wrote:

"ehsjr" wrote in message ...
On 4/19/2014 11:12 PM, Guv Bob wrote:
Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?

Thanks fellers!

Bob


You have this:

Phase A hot ---CB----+---+--}}}---+
| | |
CL CL CL
| | |
Neutral -------------+---+--}}}---+
| | |
CL Cl Cl
| | |
Phase B hot ---CB----+---+--}}}---+

(CL = Ceiling Light, CB = circuit breaker. Switches omitted
for clarity.)

It's a shared neutral circuit, and is allowed by the USA
National electrical code.

Your symptom strongly suggests a loose connection in
the neutral path.

Ed


Thanks, Ed. That sounds reasonable to me. I'll check it out. All the flickering is on Phase A lights & receptacles. They all flicker at the same time. I called the power company today and they will send someone out this week to check the line up to the CP panel.


Might be on the pole. We had that problem years ago, 1 phase with a
bad connection. Took a few tries before they cleaned and tightend the
connection.

Cheers
  #14   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 2,181
Default Flickering Ceiling Lights

On Mon, 21 Apr 2014 22:48:43 -0400, Martin Riddle
wrote:

On Mon, 21 Apr 2014 16:46:48 -0800, "Guv Bob"
wrote:

"ehsjr" wrote in message ...
On 4/19/2014 11:12 PM, Guv Bob wrote:
Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?

Thanks fellers!

Bob


You have this:

Phase A hot ---CB----+---+--}}}---+
| | |
CL CL CL
| | |
Neutral -------------+---+--}}}---+
| | |
CL Cl Cl
| | |
Phase B hot ---CB----+---+--}}}---+

(CL = Ceiling Light, CB = circuit breaker. Switches omitted
for clarity.)

It's a shared neutral circuit, and is allowed by the USA
National electrical code.

Your symptom strongly suggests a loose connection in
the neutral path.

Ed


Thanks, Ed. That sounds reasonable to me. I'll check it out. All the flickering is on Phase A lights & receptacles. They all flicker at the same time. I called the power company today and they will send someone out this week to check the line up to the CP panel.


Might be on the pole. We had that problem years ago, 1 phase with a
bad connection. Took a few tries before they cleaned and tightend the
connection.

Cheers


I had a bad neutral coming to the house. Furnace blower would fire
up, half of the house lights would dim, half would brighten.

Called SRP, got lip from the receptionist, read her the riot act,
serviceman there in 20 minutes :-}

Installed temporary, above ground, neutral, came back and trenched and
replace the whole feed.

...Jim Thompson
--
| James E.Thompson | mens |
| Analog Innovations | et |
| Analog/Mixed-Signal ASIC's and Discrete Systems | manus |
| San Tan Valley, AZ 85142 Skype: Contacts Only | |
| Voice480)460-2350 Fax: Available upon request | Brass Rat |
| E-mail Icon at http://www.analog-innovations.com | 1962 |

I love to cook with wine. Sometimes I even put it in the food.
  #15   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 8
Default Flickering Ceiling Lights

On 4/21/2014 8:46 PM, Guv Bob wrote:
"ehsjr" wrote in message ...
On 4/19/2014 11:12 PM, Guv Bob wrote:
Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?

Thanks fellers!

Bob


You have this:

Phase A hot ---CB----+---+--}}}---+
| | |
CL CL CL
| | |
Neutral -------------+---+--}}}---+
| | |
CL Cl Cl
| | |
Phase B hot ---CB----+---+--}}}---+

(CL = Ceiling Light, CB = circuit breaker. Switches omitted
for clarity.)

It's a shared neutral circuit, and is allowed by the USA
National electrical code.

Your symptom strongly suggests a loose connection in
the neutral path.

Ed


Thanks, Ed. That sounds reasonable to me. I'll check it out. All the flickering is on Phase A lights & receptacles. They all flicker at the same time. I called the power company today and they will send someone out this week to check the line up to the CP panel.


Bob,

With the flickering happening only on lights connected to
phase A it is less likely to be a loose neutral connection.

Ed


  #16   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 8
Default Flickering Ceiling Lights

On 4/21/2014 8:46 PM, Guv Bob wrote:
"ehsjr" wrote in message ...
On 4/19/2014 11:12 PM, Guv Bob wrote:
Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?

Thanks fellers!

Bob


You have this:

Phase A hot ---CB----+---+--}}}---+
| | |
CL CL CL
| | |
Neutral -------------+---+--}}}---+
| | |
CL Cl Cl
| | |
Phase B hot ---CB----+---+--}}}---+

(CL = Ceiling Light, CB = circuit breaker. Switches omitted
for clarity.)

It's a shared neutral circuit, and is allowed by the USA
National electrical code.

Your symptom strongly suggests a loose connection in
the neutral path.

Ed


Thanks, Ed. That sounds reasonable to me. I'll check it out. All the flickering is on Phase A lights & receptacles. They all flicker at the same time. I called the power company today and they will send someone out this week to check the line up to the CP panel.


Bob,

With the flickering happening only on lights connected to
phase A it is less likely to be a loose neutral connection.

Ed
  #17   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 575
Default Flickering Ceiling Lights

"ehsjr" wrote in message ...
On 4/21/2014 8:46 PM, Guv Bob wrote:
"ehsjr" wrote in message ...
On 4/19/2014 11:12 PM, Guv Bob wrote:
Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?

Thanks fellers!

Bob


You have this:

Phase A hot ---CB----+---+--}}}---+
| | |
CL CL CL
| | |
Neutral -------------+---+--}}}---+
| | |
CL Cl Cl
| | |
Phase B hot ---CB----+---+--}}}---+

(CL = Ceiling Light, CB = circuit breaker. Switches omitted
for clarity.)

It's a shared neutral circuit, and is allowed by the USA
National electrical code.

Your symptom strongly suggests a loose connection in
the neutral path.

Ed


Thanks, Ed. That sounds reasonable to me. I'll check it out. All the flickering is on Phase A lights & receptacles. They all flicker at the same time. I called the power company today and they will send someone out this week to check the line up to the CP panel.


Bob,

With the flickering happening only on lights connected to
phase A it is less likely to be a loose neutral connection.

Ed


Hi Ed, you are absolutely right! Take a bow! LOL!!! The power company tech checked out the field connection and the connector on the phase connected to the left side, with the flickering circuits, was the problem. He replaced all three of them.

I'll post a couple of photos to the 2 binary groups.

  #18   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic
external usenet poster
 
Posts: 575
Default Flickering Ceiling Lights

"Guv Bob" wrote in message ...
"ehsjr" wrote in message ...
On 4/21/2014 8:46 PM, Guv Bob wrote:
"ehsjr" wrote in message ...
On 4/19/2014 11:12 PM, Guv Bob wrote:
Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?

Thanks fellers!

Bob


You have this:

Phase A hot ---CB----+---+--}}}---+
| | |
CL CL CL
| | |
Neutral -------------+---+--}}}---+
| | |
CL Cl Cl
| | |
Phase B hot ---CB----+---+--}}}---+

(CL = Ceiling Light, CB = circuit breaker. Switches omitted
for clarity.)

It's a shared neutral circuit, and is allowed by the USA
National electrical code.

Your symptom strongly suggests a loose connection in
the neutral path.

Ed


Thanks, Ed. That sounds reasonable to me. I'll check it out. All the flickering is on Phase A lights & receptacles. They all flicker at the same time. I called the power company today and they will send someone out this week to check the line up to the CP panel.


Bob,

With the flickering happening only on lights connected to
phase A it is less likely to be a loose neutral connection.

Ed


Hi Ed, you are absolutely right! Take a bow! LOL!!! The power company tech checked out the field connection and the connector on the phase connected to the left side, with the flickering circuits, was the problem. He replaced all three of them.

I'll post a couple of photos to the 2 binary groups.

Attached Thumbnails
Flickering Ceiling Lights-connector1-jpg  
  #19   Report Post  
Posted to alt.binaries.schematics.electronics,alt.binaries.schematics.electronic,alt.home.repair
external usenet poster
 
Posts: 575
Default Flickering Ceiling Lights


"Guv Bob" wrote in message ...
"ehsjr" wrote in message ...
On 4/21/2014 8:46 PM, Guv Bob wrote:
"ehsjr" wrote in message ...
On 4/19/2014 11:12 PM, Guv Bob wrote:
Well, the lights started flickering again. In attached, CB 1 & 3 are a signal unit - tandem I think is the term. I removed them, cleaned all the contacts and checked all the wiring connections and all are fine. After that, no flickering for a few weeks. Now it started again this week. Connections are still tight.

No other devices are flickering. Wind doesn't make any difference, so it sounds to me like it's in the CB 1& 3 circuit. The ceiling light/fan in slot #8 doesn't flicker, nor do any lamps plugged into receptacles.

Any other ideas what might be the problem before I go out and buy a new CB?

Thanks fellers!

Bob


You have this:

Phase A hot ---CB----+---+--}}}---+
| | |
CL CL CL
| | |
Neutral -------------+---+--}}}---+
| | |
CL Cl Cl
| | |
Phase B hot ---CB----+---+--}}}---+

(CL = Ceiling Light, CB = circuit breaker. Switches omitted
for clarity.)

It's a shared neutral circuit, and is allowed by the USA
National electrical code.

Your symptom strongly suggests a loose connection in
the neutral path.

Ed


Thanks, Ed. That sounds reasonable to me. I'll check it out. All the flickering is on Phase A lights & receptacles. They all flicker at the same time. I called the power company today and they will send someone out this week to check the line up to the CP panel.


Bob,

With the flickering happening only on lights connected to
phase A it is less likely to be a loose neutral connection.

Ed


Hi Ed, you are absolutely right! Take a bow! LOL!!! The power company tech checked out the field connection and the connector on the phase connected to the left side, with the flickering circuits, was the problem. He replaced all three of them.

I'll post a couple of photos to the 2 binary groups.

Attached Thumbnails
Flickering Ceiling Lights-connector2-jpg  
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flickering Ceiling Lights Guv Bob Home Repair 85 April 20th 14 04:20 AM
Lights flickering John UK diy 6 January 1st 07 07:20 AM
Flickering Lights [email protected] Home Repair 12 April 21st 06 11:48 PM
Lights flickering [email protected] Home Repair 5 November 1st 05 06:40 PM
Flickering lights Peter Smithson UK diy 1 November 28th 04 08:49 PM


All times are GMT +1. The time now is 07:28 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"