Default SWA cables into "consumer" unit

In article , Toby
scribeth thus

"tony sayer" wrote in message
...

We have a new Sentry metalcald CU in a small remote building that just
supplies some CCTV and lighting equipment, on Two MCB's one at 6 amps
the other at 16 supplied by SWA cables. This is replacing an almighty
mess thats been there years and is downright dangerous.

The unit in question which is metal has some holes in the bottom which
are the same size as SWA glands. I presume its OK to use these to
terminate the SWA in directly as it were, taking the Earth banjo
directly to the Earth buss bar in the unit and the live and neutral
directly to the respective points.

Or as someone suggested earlier you have to take them via something like
a metal clad type connector box, with a small connector piece of conduit
as they mustn't be directly connected to the unit?. I think he's got
that confused with a plastic unit which I suppose you could do this with
but as the CU is metal then I can't see any real problem.

Anyone care to comment?..
--
Tony Sayer


If you are exporting the earth from the supplying building, then this is
fine, assuming it all fits nicely.

Are you using the armor as the earth?


Yes as well as one conductor..


How far is the building from the source of power?


Pole mounted transformer within 40 feet!..



Toby...


--